Home heating automation

1172173174176178

Comments

  • Registered Users, Registered Users 2 Posts: 235 ✭✭ct_roy


    Just discovered this amazing thread!

    I'm looking to modernise my heating controls. I just converted the attic as an extra third floor bed room and the room is a bit bigger and cooler than my current "Bed" zone (3 bed room semi-d all located on the second floor). Ideally I'd like to be able to control the attic room as its own zone.

    My current setup (pics below)

    • Glow worm Energy 18s system boiler
    • Climote controller (which i believe also has a stat in it for the living zone?)
    • CTC stat in the Bed zone
    • 2 zones and separate hot water cylinder upstairs in the hot press

    From my initial research (and from reading the extremely useful threads here) I've shortlisted:

    • Drayton Wiser Kit
    • Hive
    • Tado X

    I'm useless at DIY, so will be getting a plumber/electrician to do any install work (but I'm a techy so comfortable with the networking side of things).

    My questions:

    1.) Are Drayton Wiser officially supported in Ireland? I spotted a few threads with people having issues getting the app working due to not having UK addresses - is that still a thing?

    2.) I was leaning towards Tado initially, but given the recent changes to their pricing/subscription requirements that's put me off them a bit. But I'm still willing to consider them if their system is compelling enough overall.

    3.) Where do I find reliable experts who can install either Wiser or Tado in the Dublin area? I tried Googling for Wiser installer experts in Ireland - but there doesn't seem to be much out there?

    4.) Any opinions (good or bad on whether I should be considering Hive?) I spotted that Bord Gais seem to offer a Hive install service.

    5.) For my new attic room, will I be able to create a new attic Zone that demands heat directly from the boiler? Basically I want a reliable way of keeping the new attic room on the third floor heated more frequently than the other two floors.

    boiler.jpeg climote.jpeg ctc.jpeg


  • Registered Users, Registered Users 2, Paid Member Posts: 8,632 ✭✭✭deezell


    Track down the location of the existing zone valves which split the flow to living , bed and HW. If they're all together in the upstairs hot press, then you should be able to branch off a flow and return to the attic room.

    Failing that you should be able to link it to the existing bedroom loops if the plumber can comfortably branch from an existing radiator flow and return. The new radiator could be fitted with a smart TRV head, which would allow it call the Bed zone, regulate that rooms temperature, and close it off from the Bed zone when its not needed. A Tado wireless kit would take care of the living room cintrol and HW timing, plus a Tado wired stat in place of the mechanical Bed zone one. A Tado TRV on the attic rad as discussed would give it some independence from the Bed Zone wired stat, it would use this as a relay to fire the boiler. A shortcoming of this is that all beds will heat when the attic TRV activates, as it's part of the same zone. A fully independent 3rd CH zone with its own wired stat or wireless if Hive or Drayton), is only possible with break out zone plumbing with its own zone valve operated by its stat.



  • Registered Users, Registered Users 2 Posts: 235 ✭✭ct_roy


    thanks for the quick reply @deezell - you're a legend :)

    >A shortcoming of this is that all beds will heat when the attic TRV activates, as it's part of the same zone.

    I'm probably ok with that shortcoming as I'll likely put smart TRV's on the second floor bedroom rads, meaning we could keep those rads off/low most of the time.

    Seems to be plenty of people installing Wiser looking at this thread. Do you know if there are any issues with their app when used in Ireland? 



  • Registered Users, Registered Users 2, Paid Member Posts: 8,632 ✭✭✭deezell


    Never heard of that, Drayton are made by Schneider, so hardly Farage influenced, 'stats for pratts'.



  • Hosted Moderators Posts: 10,322 ✭✭✭✭mik_da_man


    Absolutely no issues using Wiser here, I have two hubs working perfectly.

    You could use the same smart TRV solution using Wiser, if you have all rads on that loop you can group them whatever way needed.



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 2,145 ✭✭✭Paulzx




  • Registered Users, Registered Users 2 Posts: 22 JupiterCrossing


    PXL_20251214_135412660.jpg PXL_20251214_135438907.jpg PXL_20251214_135431272.jpg

    Had a new Oil boiler installed a while back after the last one died, Grant Vortex boiler. I am now looking at options to upgrade the controls in the house which are ancient.

    The first one is the switch to turn the boiler off and on. I rotate it round till I hear a click, it only acts as an on/off with no actual thermostat control. The last 2, one is for the immersion and the other is timer located in the hot press for the boiler. The boiler can and does also heat the water when its on, although I can't separately heat the water and radiators.

    Looking for some advice please on modernising this system.

    Post edited by JupiterCrossing on


  • Registered Users, Registered Users 2, Paid Member Posts: 8,632 ✭✭✭deezell


    Vintage stuff alright. The Legrand is a thermostat, it should respond to temperature increases. When you rotate it right so that it clicks on, if you then set it back just enough that it doesn't click back off, a few degrees of room temperature increase should be enough to click it off. Having said that, its ancient and probably worn out mechanically, so it's now just acting as a crude switch, with its internal mechanical temperature sensitive gubbins probably knackered.

    Because it does act as a CH switch, provided the obscure Danfoss Randall timer (only 2 event in 24 hours) is on, a simple solution for you is a Tado wired thermostat kit, which will replace the Legrand. The Randall timer is then switched to always on, and the Tado provides both a timing schedule and temperature control via the two wire connection into the Legrand. Very simple and DIYable.

    It won't provide seperate HW only heating. This is sometimes inherent in old systems with just a mechanical timer and a wall thermostat, in that the wall stat only switches power to the circulation pump, or to a CH zone valve, and HW only is then heated when the timer is on but the wall stat is turned down. This doesn't appear to to be the case in your setup.

    You will need plumbing modifications to seperate out HW cylinder heating from radiator heating,but again, in old installations this is often not possible to easily achieve as the HW flow and return connection to the boiler is mid circuit on the same pipes as CH radiators. A plumber will quickly tell you if this a big job or not. Even if the HW flow is tapped straight after the boiler, having a zone valve fitted and wired to close CH and enable HW only heating will cost a fair few quid in plumbing materials and labour.

    A better future solution might be to install smart TRV's on the radiators to enable closure of these individually, but thats possibly an even bigger job if the existing rads don't have existing mechanical TRVs, with the required TRV valve body.

    Of course, the legacy solution was simple, just turn off the boiler in the fine weather, and heat HW from the immersion. That's become almost prohibitively expensive wirh current electricity costs, and if you have an old poorly insulated HW cylinder, ots even more costly.

    One final tip, you can buy the wireless Tado kit ( or orher brands like Hive or Drayton wiser) which have a receiver with a HW relay. You'd install this receiver in place of the Randall timer, turn the old Legrand stat permanently on, and just locate the wireless thermostat in a suitable living space to get a read of room temperature. This will work exactly the same as the wired stat option, a little more competence required for the wiring, but it will provide a relay for seperate HW timing should your plumbing be upgraded to support two zones. That just about covers all the angles. I've not dealt with putting electric immersion switches under smart thermostat control, thats a seperate discussion.

    .



  • Registered Users, Registered Users 2 Posts: 22 JupiterCrossing


    Thanks for taking the time to post that detailed reply @deezell. Hugely appreciated and you have cleared up everything really nicely in my head. I know it should act as thermostat but 100% it now just functions as on/off based on the click.

    I'll contact the guy who put in the new boiler and see if he knows off hand from working on it how big of a job or not it would be to support separate zones. I'll let his answer decide which option to go for in terms of which to replace.



  • Registered Users, Registered Users 2, Paid Member Posts: 8,632 ✭✭✭deezell


    Thats the right approach to take.

    Fwiw, All mechanical thermostats click when theyre set past the current room temperature, thats the point that the stat set temperature is increased beyond the actual temperature, causing the bimettalic strip actuator to overcome the spring resistance and flip the switch on. Equally, as the room heats further, the strip bends and overcomes the opposite spring pressure flipping the switch to 'off'.

    The knob is not an analogue adjustment like a volume control. There's a measure of lag or 'hysteresis' to use the technical term, wherby once its 'on', or off, it takes up to ± 2° heating or cooling to flip the switch. So if set to 20° say, it should click off at 22°, and as the room cools, it will click back on at say 18°. This cycling air temperature is averaged in terms of radiant heat, so you experience 20°.

    Electronic or smart stats will trigger on 0.1 of a degree, and will also 'anticipate' the heating or cooling rate using learning, thus preventing overshoot when the stat has switched off the boiler but the temperature continues to rise as the rad is full of very hot water. Smart and electronic stats at the minimum use PID, proportional integral differential control algorithms, mathematical formula that wrecked my head in control systems lectures in college in the 70's, (and I love maths), so I'll forgive anyone who gets weak at the thoughts of it. Don't fret, its how all feedback control works, from audio filters to car shock absorbers.

    The actual temperature scale is completely worn off that old stat, so you don't even know what setting it's at.



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 22 JupiterCrossing


    I was a fellow control systems lecture sufferer in college. Thankfully I never had to see that stuff again after I finished. Having tested it a bit more you are completely right above. The change is so slow as its located in the biggest room in the house that I never noticed the click point moving.

    I was looking at the Tado kits you recommended. For anyone looking there is currently half off on the European site for the new X models - Smart Heating with tado° Smart Thermostat X Kit | tado° Shop – tado° Shop (Sale price €99,99)

    image.png


  • Registered Users, Registered Users 2, Paid Member Posts: 8,632 ✭✭✭deezell




  • Registered Users, Registered Users 2 Posts: 8,062 ✭✭✭MojoMaker


    Tado X controller question here - hopefully @deezell might click with this one.

    I have a Worcester/Bosch 18kw Greenstar 18i condensing boiler. In about 2 years so almost new. House is a single zone.

    We recently decided to put Tado TRVs on some of our rads - all good. We have a Tado X bridge unit in play, and have just had the Tado X wireless receiver/controller wired to the side of the boiler. It replaced an older EPH controller which had a traditional "Boost" button that you could hit once, twice, or 3 times for 1/2/3 hours of boiler time. All good.

    After the electrician installed the controller and left we noticed that pressing the Boost button on the Tado X controller either manually on the unit or via the Tado app does not ignite the boiler at all. Some texts back and forth with the electrician and he suggested he might have incorrectly wired the cable from the boiler into NC instead of NO. Sounds simple enough and he was coming back to do it anyway.

    Wind forward a couple of weeks, barely any heat in the gaff and having to cycle the boiler using the RESET button which really only gives us 5-10mins of boiler ignition I leaned on him a little to get out asap and please get it sorted for us - baltic here etc. Now he's changed his story and says he reckons the controller isn't compatible with the boiler at all (despite info on both the boiler and the Tado controller being sent to him prior to accepting the job) and he will only come out to put back on the old EPH controller, which means our investment in the Tado valves and bridge will have been in vain - and it was a few hundred euro already, not to mention the really expensive electrician call out fee. Sounds like a cop out on his part and a reluctance to admit or actually research the topic.

    I want to say he's wrong and to come out and do some proper due diligence for the task being asked - but for my own information can anyone cast any technical info my way?



  • Registered Users, Registered Users 2, Paid Member Posts: 8,920 ✭✭✭ongarite


    He is correct. Bosch don't support OpenTherm which third party controllers like Tado extension kit would use, instead they have their own proprietary closed system.

    You can go back to relay mode which is the easiest install but you will need additional TadoX hardware, the wired thermostat. It won't modulate like OpenTherm but still works fine.

    Reinstall EPH controller, set heating to always on & then program the TRVs with the wired thermostat as the zone controller.

    Edit: Does your existing system have a thermostat? Or did you just set it to come for 30 mins, 1 hour & that's it.

    Post edited by ongarite on


  • Registered Users, Registered Users 2, Paid Member Posts: 8,920 ✭✭✭ongarite




  • Registered Users, Registered Users 2, Paid Member Posts: 8,632 ✭✭✭deezell


    Who said @MojoMaker requested he connect the TadoX receiver via OpenTherm? It has a relay. He was replacing the EPH, also relay connected, so I'd imagine it was a simple wiring replacement, SL from the EPH NO or CH On terminal transferred to the NO (normally open) terminal of the TadoX receiver. That he suggested he himself had connected to NC does not inspire confidence. A simple press of the Tado X boost would have allowed him to check with a phase tester screwdriver that the mains was going out on NO. Then he arrives back and can't solve it. Did he, er, put a link from the Live L into the Com Terminal of the TadoX receiver? Unlike some controllers, Live is not prewired to the relay Com Terminal. You must do this if the the boiler expects a SL on a single wire to fire it.

    The relay being supplied volt free is to allow compatibility with volt free and low voltage control input boilers. Pop the cover on the receiver and see if the link is there, or post an image. The OpenTherm theory is a red herring. Bosch boilers and others will always have a simple SL or relay mode of firing the boiler. That's how the EPH fired it, so no OT used.

    At most there may have been a two wire connection from the boiker, carrying the live in and the SL back to the boiler. These two wires would have been connected to Com and No of the EPH if it had a volt free wiring scheme. Its also possible that L, N and SL wires came from the boiler to power the EPH, rather than having it on its own plug, which is not safe should the boiler be unplugged and the EPH left plugged in. It should have been a simple swap, and a simple test of the app/boost to confirm the relay was closing. Ill take a look at the greenstar wiring terminals to confirm it takes SL

    Another possibility is if the electrician mixed up the L and N into the Tado X, it will still operate normally, but if he did put a link from L to Com, it won't send live to the boiler SL. because Live in is connected to N, and Neutral in is connected to L. The boiler wont fire in this case as you're connecting N to it's SL cable.

    Post edited by deezell on


  • Registered Users, Registered Users 2, Paid Member Posts: 8,632 ✭✭✭deezell


    Screenshot_20260107_214132_Chrome(1).jpg

    TadoX receiver



  • Registered Users, Registered Users 2, Paid Member Posts: 8,632 ✭✭✭deezell


    A quick look at the installers manual shows that the boiler is supplied with live and neutral on terminals L and N of connector ST10, and this Live and Neutral is available to go out to a controller/timer/receiver, along with the SL back from the receiver, from terminals Ls, Ns, and Lr (Live return or Swithed Live). These three wires would already have been externally available on the EPH, no need to go inside the boiler cabinet, and incur the wrath of Jedward or a registered gas installer.

    Screenshot_20260110_091218_Chrome.jpg

    Note the digital interface EMS bus is listed as connector ST19, but its not shown, and EMS only mentioned once more in this manual as 'not used'. There is no chance that the sparks tried to make an EMS connection, let alone an OpenTherm one, not at the boiler end anyway. Who knows how he wired this up.



  • Registered Users, Registered Users 2 Posts: 8,062 ✭✭✭MojoMaker


    You're on the money @deezell - this is just a simple relay-based connector, basically the controller is only acting as an on/off switch - nothing more. No EMS or OT aspect to this.

    We have all the pieces in the puzzle installed:

    1. Smart TRVs on selected rads
    2. Tado X bridge
    3. Tado smart thermostats in selected rooms/zones
    4. Tado X wireless controller wired to the boiler. Only two leads visible, so as Deezell described.

    The only thing not working in the circuit is the ability of the Tado X controller to switch on/off the boiler - either manually via the "Boost" button on the top of the panel, or remotely via the app. It has to be a simple wiring connection error at the root of this.

    I don't think we need the innards of the boiler exposed, all that's required is a direct replacement for the EPH controller using the same two leads. I think once the electrician saw the panel light up he thought 'job done' and headed off. Then he doubled down by telling me the receiver could only be operated by the app as it was "wireless" - trying to explain why the boost button didn't work. Of course I didn't have the app installed and setup at that point as I was taking one step at the time.

    Now he's doubled down again saying he believes the boiler is not compatible with Tado X and will only come out to put the old EPH controller back on. Deezell's advice here shows this is clearly not true and at least I am armed with some info now to fight the corner.

    I may as well ask - I can disable power to the boiler ok, is this a job I should just take on myself?



  • Registered Users, Registered Users 2, Paid Member Posts: 8,632 ✭✭✭deezell


    If you've a phase tester screwdriver €2) to ttip terminals and check for live, go for it. Post a picture of the cables into the tadoX receiver. You will need the Tadox thermostat powered to send wireless instructions to the tadox receiver to close its relay. I'm assuming this is done.



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 8,062 ✭✭✭MojoMaker


    It's in the chain yes, just not fully operational yet. I would loke to confirm that even without anything else - TRVs, smart stats, Bridge X etc - that the Tado X receiver wired to the boiler can definitely act as a manual on/off switch for the boiler. Let's call that the baseline, and then the wireless functions - and/or using the app - layer over that etc.

    Make sense?



  • Registered Users, Registered Users 2, Paid Member Posts: 8,632 ✭✭✭deezell


    At the minimum you must add the wall thermostat and the receiver to the app as devices. You will also need the bridge powered up and connected to the router. The wall stat, TRVs, Bridge and receiver communicate with each other wirelessly (but not by WiFi). The bridge provides the link to the Internet, and from there to the App.

    If you go to settings/rooms and devices, you'll see the rooms you've created. With a wireless starter kit, its a list of just one, say 'Sitting Room'. This will show the wireless temperature sensor in it's list of devices. If you click on the > to the left off 'Sitting Room', you will see the sensor serial no. listed as the measuring device, and the receiver serial no. as the Zone controller, as in this image

    Screenshot_20260111_202317_tado.jpg

    [

    The above image is from V3 Tado, but afaik the interface for Tadox is identical, it's the same app. The boost button on the receiver has a 30min default time. In the app, the manual time setting of the associated measuring device, the Wireless stat, can be set to a custom time, or to finish with the next scheduled change, or until you manually cancel.



  • Registered Users, Registered Users 2 Posts: 963 ✭✭✭WildCardDoW


    Some of that reply is 100% ChatGPT haha.

    I'll disagree with deezell in that I do believe you can wire the receiver and just press boost to test the wiring without the app setup, but based on his extensive knowledge I'm more than likely wrong. I've only installed it once and was confident I did the exact thing you're requesting.



  • Registered Users, Registered Users 2, Paid Member Posts: 8,632 ✭✭✭deezell


    Yes you can, but what's the point? You could just as easily wire up a light switch. You should get all the parts connected and added to the app, test it on the kitchen table, just use a phase tester to see if NO lights up with mains for all the possible inputs, turning up the stat manually, via the app, via the boost. Then transfer It to the EPH wiring.

    if @MojoMaker is an AI as you think and just wants to switch something on and off, he already could do that with the EPH. I dunno, he hasn't posted an image of the receiver wiring. Maybe hes on a slow charger.

    Straight out of the box the receiver might/should respond to its boost buttons, these also double as pconfiguration buttons, though I'm only familiar with V3. It's not a manual switch though, the boost settings have default time once its all up and running, 30 mins iirc. I've never operated any Tado devices without first adding them to the system, and assigning measuring device and zone controller. A wireless kit on a new app install will default to the two devices anyway, as thats the minimum, and of course they must be paired to the bridge first in order for the app to see them. A wired stat is the simplest, it sets itself as measuring and controller from the beginning.

    It gets trickier when you start adding additional wired stats for say an S plan system and adding a wireless stat later can cause problems if the receiver grabs the first wired device as its measuring device. You will have to go into installer mode on the stat display to move it to its own zone, by assigning it as relay 2. It can get messed up, but ultimately, you can see what any 'room' is using as its measuring device, and to which relay, (wired stat or extension kit receiver), it's using as a zone controller.

    Let's see what @MojoMaker, or his AI alter ego has to say!



  • Registered Users, Registered Users 2 Posts: 963 ✭✭✭WildCardDoW


    Main reason is simply to save time, it's a lot quicker to press the button physically then trigger it via the app with the setup. Also reduces risk of opening devices you don't end up using if you fear you can't get the core device (receiver) working.

    It also answers the below query:

    I would loke (like) to confirm that even without anything else - TRVs, smart stats, Bridge X etc - that the Tado X receiver wired to the boiler can definitely act as a manual on/off switch for the boiler.

    As to the second part, I'm only stating that Mojo used AI to construct part of their response (has all the hallmarks such as very positive feedback) not that they themselves are AI. Specifically these two parts, the rest is 50/50.

    You're on the money @deezell - this is just a simple relay-based connector, basically the controller is only acting as an on/off switch - nothing more. No EMS or OT aspect to this.

    We have all the pieces in the puzzle installed:

    * Smart TRVs on selected rads

    * Tado X bridge

    * Tado smart thermostats in selected rooms/zones

    * Tado X wireless controller wired to the boiler. Only two leads visible, so as Deezell described.

    No offence intended.



  • Registered Users, Registered Users 2, Paid Member Posts: 8,632 ✭✭✭deezell


    None taken by me, though you might get a visit from a disgruntled 🤖. I pose technical questions directly to Google all the time, in relation to various devices configuration, av, phone, car obd and coding, routers and internet ,smart home, garden tractirs and power tool repair, and of course heating.

    Aside from the AI semi correct answers, I'm hoping to get hits from real human sources, reddit, specific product forums, discussion groups, technical manuals and youtube explainers. (not facebook though). These are the real goldmine, only the other day I found the full dealer procedure for troubleshooting and calibration of my cars rear camera system. This is not available to the public, so no surprise it had a url with a . ru domain. 'Oh! those Russians', as Boney M would sing. Fittingly, the song is Ras-Putin.

    Keep up the AI detection. I prefer to use my own flawed and trusty Longmans grammar which was painlessly fed into our heads in primary school, no beatings,unlike the Irish language psychos.



  • Registered Users, Registered Users 2 Posts: 8,062 ✭✭✭MojoMaker


    I'm sorry, I don't get the AI references.

    Anyway, yes your suggestion of getting the whole circuit working is a sound one @deezell. I believed that the first step in the chain was/should be to get the Tado X receiver working correctly on NO/NC and turning on/off the boiler if I press the buttons.

    Then I was going to test the ability of the wireless smart stats to trigger the relay on the receiver and ignite/switch off the boiler.

    Then the last step would be to verify that an override via the app is possible - i.e. I should be able to open the app and switch on/off the boiler via the Boost function.

    Just want to check the logic etc.

    The reason I got rid of the EPH controller, which was entirely manual, was so that we could move to an automated solution with remote access, which the EPH technology could not support (too old).



  • Registered Users, Registered Users 2, Paid Member Posts: 8,632 ✭✭✭deezell


    Just follow the steps in the wireless starter kit instructions, starting with installing the App and getting the bridge, stat and receiver added, WIFi connected to the bridge, and stat and receiver paired to the Bridge

    Have them all powered and working. With the app controlling the receiver, or the manual controls on the thermostat doing the same. Only then connect the boiler firing SL wire to the NO contact. You can bench test all these before mounting.



  • Registered Users, Registered Users 2 Posts: 4,976 ✭✭✭Roberto_gas


    I have this weird issue where tado is sending signal to boiler to turn on through motorized valve relays through a RF switch(hotpress on 2 nd floor to boiler on ground) but boiler just does not kick heating even tho the RF switch is on and boiler is on. Restarting tado has fixed it twice. Once boiler heating also kicked in when I hit manual on RF switch. Any idea if this an issue with Tado? Motorised valves? RF switch or the boiler itself?

    Thanks



  • Advertisement
  • Registered Users, Registered Users 2, Paid Member Posts: 8,632 ✭✭✭deezell


    That might be the relay in the motorised valve, or the valve itself sticking. In this design, knows as S plan, the switched live voltage for CH from the Tado receiver, the RF switch you mentioned , goes to motorised valve, nowhere else. This valve must actuate and fully open at which point the rotating mechanical valve motor mechanism operates a microswitch which then sends live to the boiler SL input, instructing it to fire. There would be a second valve doing a similar operation, sending hot water flow to the HW cylinder, firing the boiler also. Many homes will have three motorised valves, upstairs CH and downstairs CH and HW.

    You can check the mechanical action of these valves while looking at them. Turn the the CH up high, the valve should whirr and an indicator lamp if fitted will light. There is also a mechanical lever to manually open the valve mechanism, this can be moved to indicate the resistance of the actual flow valve. It should move with a firm press. If there is no indication lamp, you would need a meter or a phase tester to check that the SL voltage of the valve is being sent to the boiler. This SL voltage comes out of the valves usually on the Orange wire from the valve body, and can be tested at the wiring centre box where all the zone valve cables terminate.

    If the zone valve is sticking, or it's motor has failed, you can get your heating going in an emergency mode by just opening the CH valve's mechanical lever and lock it in position on the notch. You can then fire the boiler using the other zone, HW, and when the boiler fires for this, hot flow will go to the rads as well as the cylinder.