Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie

Domestic Solar PV Quotes 2020

Options
17172747677164

Comments

  • Registered Users Posts: 1,700 ✭✭✭Deagol


    maw wrote: »
    no idea, this is as received on quote today

    You'd want to get clarification of what they are quoting as it's not clear which type of inverter they are offering.

    Wouldn't recommend the Alpha battery either. They have the same issue as the Pylontech's I see frequently offered. That '5.7kw' model has a maximum output current of only 56A - this means the maximum power output from it is around 2.4kw. Between base load and a cooker ring that's as much as it will do.


  • Registered Users Posts: 50 ✭✭maw


    Deagol wrote: »
    You'd want to get clarification of what they are quoting as it's not clear which type of inverter they are offering.

    thanks a mill. does it seem way off or reasonable otherwise?


  • Registered Users Posts: 1,470 ✭✭✭MAULBROOK


    maw wrote: »
    thanks a mill. does it seem way off or reasonable otherwise?

    About €1500 too much.


  • Moderators, Sports Moderators Posts: 18,717 Mod ✭✭✭✭slave1


    maw wrote: »
    how does this compare??


    Battery System (Alpha)

    3.25kp of modules kitted to a 3kW Inverter

    14 x Bisol Premium 325w Monocrystalline modules (All black modules)*

    Bisol Mounting system on a Slate roof

    1 x Projoy Fire Safety Switch

    AC Switch Gear

    Alpha 5 kWp Inverter kitted to 5.7kWh storage capacity

    Costing

    €10000(inclusive of VAT)

    +€500(Eddie Hot Water Diverter)

    €3000 (SEAI Grant)

    €7500 Final cost after grant incentive

    Previous poster was correct, you need to get clarity to get that 3kW inverter off the quote and that quote is thousands off what you should be paying.
    Also get quote without a battery, work out the payback on battery, it's massive even doubtful it would pay back before it pops it's clogs.
    Better off with more panels and a straight single phase dual MPPT inverter like Solis, that's the quote you need.
    Post back their update.

    My stuff for sale on Adverts inc. outdoor furniture, roof box and EDDI

    My Active Ads (adverts.ie)



  • Moderators, Home & Garden Moderators Posts: 5,827 Mod ✭✭✭✭graememk


    Looks like the Solar inverter and battery inverter are separate devices.

    things dont add up, 14 325 panels is 4.55kwp.


  • Advertisement
  • Registered Users Posts: 1,470 ✭✭✭MAULBROOK


    graememk wrote: »
    Looks like the Solar inverter and battery inverter are separate devices.

    things dont add up, 14 325 panels is 4.55kwp.

    The more i read this the sloppier it gets. Like they couldn't be arsed.


  • Registered Users Posts: 79 ✭✭Lleyn elec


    Where is the best site to purchase panels and inverters from?
    I’m a registered electrical contractor and have a 63x40 shed with a south facing roof on one.
    Looking at a 6kW system, is there any model of inverter that is popular and type tested? Just looking at the NC6 form here at the moment.


  • Registered Users Posts: 50 ✭✭maw


    very helpful guys, thanks a lot. will let you know how it goes. more quotes to receive yet


  • Registered Users Posts: 1,470 ✭✭✭MAULBROOK


    Lleyn elec wrote: »
    Where is the best site to purchase panels and inverters from?
    I’m a registered electrical contractor and have a 63x40 shed with a south facing roof on one.
    Looking at a 6kW system, is there any model of inverter that is popular and type tested? Just looking at the NC6 form here at the moment.

    https://solartricity.ie/

    Solis works for me,


  • Moderators, Home & Garden Moderators Posts: 5,827 Mod ✭✭✭✭graememk


    MAULBROOK wrote: »
    https://solartricity.ie/

    Solis works for me,

    Yeah Good guys there at solartricity, Register yourself as a trade too, Might start a whole new aspect of your business!

    Midsummer is another one, Register there too and compare.

    I have 20 of the 360w Longi on a 6kw inverter.


  • Advertisement
  • Registered Users Posts: 427 ✭✭Geeyfds53573


    Deagol wrote: »
    You'd want to get clarification of what they are quoting as it's not clear which type of inverter they are offering.

    Wouldn't recommend the Alpha battery either. They have the same issue as the Pylontech's I see frequently offered. That '5.7kw' model has a maximum output current of only 56A - this means the maximum power output from it is around 2.4kw. Between base load and a cooker ring that's as much as it will do.

    If you have multiple Pylontechs I assume a higher output is higher?


  • Moderators, Home & Garden Moderators Posts: 5,827 Mod ✭✭✭✭graememk


    If you have multiple Pylontechs I assume a higher output is higher?

    Yep, they are wired in parallel When you have more than one unit, They are 15S (15 cells, 3.2v) 48V nominal Voltage

    So with 2 you can pull 112A which is about 5.3kw, if the inverter supports it.


  • Registered Users Posts: 12 Tarant


    graememk wrote: »
    Yep, they are wired in parallel When you have more than one unit, They are 15S (15 cells, 3.2v) 48V nominal Voltage

    So with 2 you can pull 112A which is about 5.3kw, if the inverter supports it.

    Be aware for the Pylontech, if the temp is below 13c it only charges at 10 amp x 52volt = 500 watt (discharge is still 25 amp = 1.25kw)
    Was thinking of designing a heater for it (oneday)


  • Registered Users Posts: 427 ✭✭Geeyfds53573


    graememk wrote: »
    Yep, they are wired in parallel When you have more than one unit, They are 15S (15 cells, 3.2v) 48V nominal Voltage

    So with 2 you can pull 112A which is about 5.3kw, if the inverter supports it.

    Thanks a mill glad I asked so Max AC 5000v may not cut it but an inverter Max AC @5500v will


  • Moderators, Sports Moderators Posts: 18,717 Mod ✭✭✭✭slave1


    Lleyn elec wrote: »
    Where is the best site to purchase panels and inverters from?
    I’m a registered electrical contractor and have a 63x40 shed with a south facing roof on one.
    Looking at a 6kW system, is there any model of inverter that is popular and type tested? Just looking at the NC6 form here at the moment.

    If you’re a registered electrician why not purchase up North, if properly invoiced/delivered to a ROI business address you should get exclusive of VAT as the gear was immediately exported from NI.

    My stuff for sale on Adverts inc. outdoor furniture, roof box and EDDI

    My Active Ads (adverts.ie)



  • Registered Users Posts: 1,700 ✭✭✭Deagol


    Thanks a mill glad I asked so Max AC 5000v may not cut it but an inverter Max AC @5500v will

    It's to do with maximum output current from the battery. It's not quoted in the quotes - you need to go to manufacturer site and look at specifications.

    To get maximum output power (watts) you multiply the maximum sustained current (be careful, lots of them quote a peak value which is only for 10sec) by the battery voltage (usually 48volts).

    So for the Alpha 5.7kw - it's a 48v x 56amps (sustained max)=2688watts or ~2.7kw. Note that there are other things that feed in like ambient temperature etc but the max is the best to look at as it gives best scenario.

    If you want to see the difference - look at Pylontech 5kw vs Puredrive 5kw max current...both 5kw but one is ~50A output and other is ~100A.


  • Registered Users Posts: 427 ✭✭Geeyfds53573


    Deagol wrote: »
    It's to do with maximum output current from the battery. It's not quoted in the quotes - you need to go to manufacturer site and look at specifications.

    To get maximum output power (watts) you multiply the maximum sustained current (be careful, lots of them quote a peak value which is only for 10sec) by the battery voltage (usually 48volts).

    So for the Alpha 5.7kw - it's a 48v x 56amps (sustained max)=2688watts or ~2.7kw. Note that there are other things that feed in like ambient temperature etc but the max is the best to look at as it gives best scenario.

    If you want to see the difference - look at Pylontech 5kw vs Puredrive 5kw max current...both 5kw but one is ~50A output and other is ~100A.

    Thanks think I understand ... well so so ...but what are you looking for on the inverter size to see if the inverter supports it?


  • Registered Users Posts: 1,700 ✭✭✭Deagol


    Thanks think I understand ... well so so ...but what are you looking for on the inverter size to see if the inverter supports it?

    Technically - inverter changes DC to AC, the solar panels produce DC power, our grid is AC. So the convention is that inverter refers to solar panel to grid power.

    For battery systems the convention is that you use a 'Hybrid' inverter.

    A hybrid inverter has effectively two subsystems:

    1) A standard DC-AC converter (the inverter).
    2) A battery charging circuit (DC-DC)

    And because of that it gets a wee bit complicated.

    Lets take a 5kw inverter : generally, the 5kw part refers to the maximum DC-AC conversion rate. But, for the battery side - you need to be sure the battery can output at x rate of current. AND, what can the inverter do from the battery. That's because the batteries are 48V x max current (current * volts=watts/kilowatts). Whereas the panels voltage is summed (the panels are wired in series so each one you add makes voltage higher NOT current higher) so the voltage from the panels is much higher (and hence lower current).

    So: golden rule I guess. The max current output of the inverter is much more important than the Kw output value.

    Reading this back I'm not sure it's coherrent... sorry...

    Best I can say is ask people here about specific models and we can probably better answer!


  • Moderators, Home & Garden Moderators Posts: 5,827 Mod ✭✭✭✭graememk


    Deagol wrote: »
    Technically - inverter changes DC to AC, the solar panels produce DC power, our grid is AC. So the convention is that inverter refers to solar panel to grid power.

    For battery systems the convention is that you use a 'Hybrid' inverter.

    A hybrid inverter has effectively two subsystems:

    1) A standard DC-AC converter (the inverter).
    2) A battery charging circuit (DC-DC)

    And because of that it gets a wee bit complicated.

    Lets take a 5kw inverter : generally, the 5kw part refers to the maximum DC-AC conversion rate. But, for the battery side - you need to be sure the battery can output at x rate of current. AND, what can the inverter do from the battery. That's because the batteries are 48V x max current (current * volts=watts/kilowatts). Whereas the panels voltage is summed (the panels are wired in series so each one you add makes voltage higher NOT current higher) so the voltage from the panels is much higher (and hence lower current).

    So: golden rule I guess. The max current output of the inverter is much more important than the Kw output value.

    Reading this back I'm not sure it's coherrent... sorry...

    Best I can say is ask people here about specific models and we can probably better answer!

    Havent looked into hybrid inverter much.

    I am wondering is there even a DC-DC converter in it. Solar is 200-300V DC

    And they all can charge from the grid.

    It would be easier to put it all to AC and then just use a transformer and rectifier to charge the batteries - It would also need to have an inverter that can run in parallel with the Solar inverter. (and also on 48v) It cant use the same inverter that it uses for the solar.

    So basically its a AC storage inverter and normal Solar inverter all in one box.

    Which also means that if you crack it open, you might be able to stick a CT on the battery side of the hybrid inverter (although... warranty is out the window)


  • Registered Users Posts: 1,700 ✭✭✭Deagol


    graememk wrote: »
    Havent looked into hybrid inverter much.

    I am wondering is there even a DC-DC converter in it. Solar is 200-300V DC

    And they all can charge from the grid.

    It would be easier to put it all to AC and then just use a transformer and rectifier to charge the batteries - It would also need to have an inverter that can run in parallel with the Solar inverter. (and also on 48v) It cant use the same inverter that it uses for the solar.

    So basically its a AC storage inverter and normal Solar inverter all in one box.

    Which also means that if you crack it open, you might be able to stick a CT on the battery side of the hybrid inverter (although... warranty is out the window)

    I would guess there's a DC-DC converter - doing it via an AC xfmr and bridge rectifier or similar would be very inefficient and more expensive. But without looking at the specs carefully and maybe opening one up it's not something I know for sure.

    EDIT: Yes, checked it: MPPT is a DC-DC converter and that seems to be the common denominator with Hybrid.


  • Advertisement
  • Registered Users Posts: 427 ✭✭Geeyfds53573


    Deagol wrote: »
    Technically - inverter changes DC to AC, the solar panels produce DC power, our grid is AC. So the convention is that inverter refers to solar panel to grid power.

    For battery systems the convention is that you use a 'Hybrid' inverter.

    A hybrid inverter has effectively two subsystems:

    1) A standard DC-AC converter (the inverter).
    2) A battery charging circuit (DC-DC)

    And because of that it gets a wee bit complicated.

    Lets take a 5kw inverter : generally, the 5kw part refers to the maximum DC-AC conversion rate. But, for the battery side - you need to be sure the battery can output at x rate of current. AND, what can the inverter do from the battery. That's because the batteries are 48V x max current (current * volts=watts/kilowatts). Whereas the panels voltage is summed (the panels are wired in series so each one you add makes voltage higher NOT current higher) so the voltage from the panels is much higher (and hence lower current).

    So: golden rule I guess. The max current output of the inverter is much more important than the Kw output value.

    Reading this back I'm not sure it's coherrent... sorry...

    Best I can say is ask people here about specific models and we can probably better answer!

    Thanks Deagol


  • Moderators, Home & Garden Moderators Posts: 5,827 Mod ✭✭✭✭graememk


    Deagol wrote: »
    I would guess there's a DC-DC converter - doing it via an AC xfmr and bridge rectifier or similar would be very inefficient and more expensive. But without looking at the specs carefully and maybe opening one up it's not something I know for sure.

    EDIT: Yes, checked it: MPPT is a DC-DC converter and that seems to be the common denominator with Hybrid.

    Mppt is the tracking hardware to get the most out of the panels, is nearly on all inverters (basically all grid tied ones)
    All we need is bigclive.com to do a tear down on one and see how it really works.


  • Registered Users Posts: 453 ✭✭phester28


    Does anyone know if a hybrid inverter will supplement the solar on high demands. I.E When you want to boil your kettle


  • Registered Users Posts: 1,700 ✭✭✭Deagol


      phester28 wrote: »
      Does anyone know if a hybrid inverter will supplement the solar on high demands. I.E When you want to boil your kettle

      Not sure what you mean? Do you mean if the battery is charged and you go from being net producing to consuming will the battery make up the shortfall? If so, yes - inverter constantly monitors and balances to use battery in case were load is higher than solar is supplying.

      There are settings in the inverters were you can adjust the behaviour as well - but I've left mine well alone :)


    1. Registered Users Posts: 6,068 ✭✭✭championc


      phester28 wrote: »
      Does anyone know if a hybrid inverter will supplement the solar on high demands. I.E When you want to boil your kettle

      I assume you are looking to clarify as to whether the kettle can draw a COMBINATION of both Solar and Battery sourced energy simultaneously. If so, then yes.


    2. Posts: 0 [Deleted User]


      Anyone use solarpvs.ie, just looking for reviews as I am looking at getting them to do mine. Its gilroys?

      Would you count it normal to ask for a deposit?


    3. Registered Users Posts: 1,700 ✭✭✭Deagol


      Anyone use solarpvs.ie, just looking for reviews as I am looking at getting them to do mine. Its gilroys?

      Would you count it normal to ask for a deposit?

      Don't know anything about them but the website is very amateur - spelling and grammar errors in abundance. If that's the care and attention they take doing their work then I'd be questioning the care and attention they might take doing the solar install. Could be that they just hired a cheap web designer of course but you'd expect someone would take a good look at their own 'shop window' .....

      I'd recommend to make sure you get some recommendations from other clients first... :cool:


    4. Moderators, Home & Garden Moderators Posts: 10,140 Mod ✭✭✭✭BryanF


      Anyone use solarpvs.ie, just looking for reviews as I am looking at getting them to do mine. Its gilroys?

      Would you count it normal to ask for a deposit?
      recommendation /comments on specific companies by PM thanks


    5. Registered Users Posts: 360 ✭✭samdeluxjones


      Got a quote from one of the wholesalers mentioned in this thread.

      Longi 360w @ €93.29 X 16

      Solis 5Kw Hybrid €1029.30

      Pylon2.4Kwh battery €680 X 2

      16 panel tree system ground mount €1500

      €160 delivery.

      Is there much difference or advantages going for the modular lithium ion batteries or the ones that look like car batteries apart from cost?

      What are main reasons for choosing between 12, 24 & 48v batteries?

      Thanks.


    6. Advertisement
    7. Registered Users Posts: 1,700 ✭✭✭Deagol



      What are main reasons for choosing between 12, 24 & 48v batteries?

      Thanks.

      Inverter is current limited - so for example assuming inverter has max output of 100amps:: 12v X 100Amps= 1.2kw / 24v X 100amps=2.4kw etc.


    This discussion has been closed.