Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Please note that it is not permitted to have referral links posted in your signature. Keep these links contained in the appropriate forum. Thank you.

https://www.boards.ie/discussion/2055940817/signature-rules
Hi all! We have been experiencing an issue on site where threads have been missing the latest postings. The platform host Vanilla are working on this issue. A workaround that has been used by some is to navigate back from 1 to 10+ pages to re-sync the thread and this will then show the latest posts. Thanks, Mike.
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

Zappi charge points

191012141527

Comments

  • Registered Users, Registered Users 2 Posts: 591 ✭✭✭NBar


    garo wrote: »
    Got another quote for 1200 v2 installed so probably going to go for it.

    Can you tell me with whom that is or pm me if you wish... Thanks


  • Posts: 7,499 ✭✭✭ [Deleted User]


    bb25dbd3-12a3-4020-8f07-b3399a3c9e34.jpg

    Came out to this error this morning,
    Had enough % for the day anyway but would have been nice to know the zappi was in fault status.
    can the hub alert you to faut status ?


  • Registered Users, Registered Users 2 Posts: 12,136 ✭✭✭✭KCross


    The more important question is why your voltage went to 201V!

    Do you have electric showers, heat pumps etc that would have been on at the same time as the car was pulling 32A?
    Are you in a rural area?

    If that becomes a common occurrence you need to talk to ESB and get them to look at that.


  • Posts: 7,499 ✭✭✭ [Deleted User]


    First time its happened and yes rural.
    Funnily I did notice the lights dim last night when turning on the shower which never happens.


  • Registered Users, Registered Users 2 Posts: 12,136 ✭✭✭✭KCross


    Funnily I did notice the lights dim last night when turning on the shower which never happens.

    Was the car charging at the same time as you turned on the shower?

    Being rural you are probably also sharing a transformer with a bunch of other houses and/or possibly a nearby farm which could be leaving you with low voltage.

    If it happens again I'd get an inexpensive energy monitor like this
    https://www.amazon.co.uk/Maxcio-Consumption-Monitoring-Overload-Analyzer/dp/B085M6GL2R/ref=asc_df_B085M6GL2R

    If you see that the voltage is consistently low (200-215) you need to talk to ESB who will put in a proper monitor at your meter and if they see consistent low voltage they will do some upgrade works.

    You should be getting a consistent 225-235V even with the car charging. If your neighbours are also heavy users it might be pulling it down.

    201V is awfully low, but might be just a blip too.


  • Posts: 7,499 ✭✭✭ [Deleted User]


    Car was not charging ,
    I believe it to be a blip .
    You could easily get scuppered if you needed a full SOC.
    Other chargers will tell you there is a problem via their app (Wallbox I believe)


  • Registered Users, Registered Users 2 Posts: 3,465 ✭✭✭JohnC.


    Is it safe to temporarily use a Zappi without a CT clamp? Without using anything else high-powered, obviously.

    I've got a Harvi in my setup but the Harvi seems to have stopped working. No life in the status light.


  • Registered Users, Registered Users 2 Posts: 11,890 ✭✭✭✭the_amazing_raisin


    JohnC. wrote: »
    Is it safe to temporarily use a Zappi without a CT clamp? Without using anything else high-powered, obviously.

    I've got a Harvi in my setup but the Harvi seems to have stopped working. No life in the status light.


    I think you can configure the Zappi to internally limit it's charge current. Maybe set it down to 16A until you get a new Harvi

    "The internet never fails to misremember" - Sebastian Ruiz, aka Frost



  • Registered Users Posts: 6,181 ✭✭✭championc


    JohnC. wrote: »
    Is it safe to temporarily use a Zappi without a CT clamp? Without using anything else high-powered, obviously.

    I've got a Harvi in my setup but the Harvi seems to have stopped working. No life in the status light.

    Just use it in Normal mode rather than ECO.

    You could check your Harvi by trying to power it from an external power source. I'm sure I read a posting on their forum where it was confirmed that a 9v source will do it. So even a 9v PP3


  • Registered Users Posts: 1,240 ✭✭✭loopymum


    Think I need to get a zappi as I have a heat pump, do I need the myenergie hub?


  • Advertisement
  • Registered Users Posts: 1,770 ✭✭✭Nedved85


    You don't 'need' the hub but it is a nice feature to have as you can see what your house/car is using.

    If you buy a hub - you *might* need a harvi aswell - This reads the feed in from the ESB and in turns tells the hub what your house is using.


  • Registered Users, Registered Users 2 Posts: 1,874 ✭✭✭garo


    No you don't need a Harvi if your CT clamp is wired all the way back to the Eddi or Zappi. The Harvi is for when you cannot or do not want a wired connection from your CT clamp to a myenergi device.


  • Registered Users, Registered Users 2 Posts: 11,890 ✭✭✭✭the_amazing_raisin


    loopymum wrote: »
    Think I need to get a zappi as I have a heat pump, do I need the myenergie hub?

    No, you only need the hub in the UK as they require chargers to be connected to the internet to get the OLEV grant

    You might need a harvi to monitor your ESB connection if wiring the CT clamp that comes with the Zappi back to your meter is too difficult.

    I've order a hub and harvi anyway as I like to monitor my usage and I'd like the option of moving the Zappi to a different location with too much rewiring

    "The internet never fails to misremember" - Sebastian Ruiz, aka Frost



  • Registered Users, Registered Users 2 Posts: 12,136 ✭✭✭✭KCross


    https://myenergi.info/hub-firmware-release-3-041-26-11-2020-t2737.html

    New firmware now available for the hub (3.041) and both the old and new Zappi's.

    Good to see they are not abandoning the old Zappi hardware.

    Some of the fixes were already available for the v2 Zappi are now available for v1 Zappi, which is to fix an issue with eGolf and Model 3 charging along with a whole load of other fixes detailed here
    https://myenergi.info/zappi-v1-firmware-release-3-101-27-11-2020-t2741.html


    For those with SolarPV and batteries they also appear to have addressed some issues there but I dont have a battery myself so dont know what it actually fixes
    Improved interaction with DC battery
    Improved handling of AC batteries and power diverters

    This one used annoy me so glad they addressed that one
    It is now possible to define what mode the zappi boots into after a power cut / reboot


  • Moderators, Sports Moderators Posts: 19,192 Mod ✭✭✭✭slave1


    Careful with Hub update, my Eddi reverted to Australia mode when I updated the hub, took Myenergi forever to sort it over the phone after countless factory resets despite the issue being the funny channel the Eddi was on


  • Registered Users, Registered Users 2 Posts: 12,136 ✭✭✭✭KCross


    slave1 wrote: »
    Careful with Hub update, my Eddi reverted to Australia mode when I updated the hub, took Myenergi forever to sort it over the phone after countless factory resets despite the issue being the funny channel the Eddi was on

    All worked ok for me anyway including the Zappi (no Eddi in my setup though). Let’s hope the car charges tomorrow! :)


  • Registered Users, Registered Users 2 Posts: 6,875 ✭✭✭zg3409


    slave1 wrote: »
    Careful with Hub update, my Eddi reverted to Australia mode when I updated the hub, took Myenergi forever to sort it over the phone after countless factory resets despite the issue being the funny channel the Eddi was on

    My grid limit switched off on a previous update (there probably was a warning in small print) but in my case the limit was there to protect an old fuseboard from overload, so theoretically it could have overheated something. If you have an instant shower or heat pump or grid limit set up make a note of it and check its still active after any updates. I would also warn those who do not need an update, if its not broken....don't fix it


  • Registered Users, Registered Users 2 Posts: 11,890 ✭✭✭✭the_amazing_raisin


    Anyone know if it's possible to swap a tethered type 1 plug for a type 2? I'm guessing it's not easy since they're pretty weatherproof plugs

    "The internet never fails to misremember" - Sebastian Ruiz, aka Frost



  • Registered Users Posts: 6,181 ✭✭✭championc


    Anyone know if it's possible to swap a tethered type 1 plug for a type 2? I'm guessing it's not easy since they're pretty weatherproof plugs

    your best hope (and safest option) would be to replace the whole cable and the Type 2 head all the way back to the charger unit


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 7,821 ✭✭✭stimpson


    I’m pretty sure you can order them from Zappi.

    Failing that they can be got here: https://evcables.co.uk/index.php/for-type-2-cars/tethered-cables.html


  • Registered Users Posts: 23 Kevin Forde


    Pretty easy to do, I did it to mine with an original Myenergi Zappi cable a couple of months ago.

    Much like rewiring a plug but photograph internal wiring before removing old cable and replace everything in *exactly* the same way. There are a couple of CT (current sensor) rings that need to go around the cables in a specific way.
    Make sure cables are done up nice and tight.

    If that sounds at all worrying, then you should get an electrician to do it...

    Replacement cables can be bought from Myenerrgi.

    Replacement in accordance with instruction manual does not void warrenty - from manufacturers site -
    https://myenergi.info/swapping-the-tethered-cable-from-type-1-to-type-2-t432.html


  • Registered Users Posts: 23 Kevin Forde


    Did I mention that the power should be off at the board before attempting any of this?
    Pretty easy to do, I did it to mine with an original Myenergi Zappi cable a couple of months ago.

    Much like rewiring a plug but photograph internal wiring before removing old cable and replace everything in *exactly* the same way. There are a couple of CT (current sensor) rings that need to go around the cables in a specific way.
    Make sure cables are done up nice and tight.

    If that sounds at all worrying, then you should get an electrician to do it...

    Replacement cables can be bought from Myenerrgi.

    Replacement in accordance with instruction manual does not void warrenty - from manufacturers site -
    https://myenergi.info/swapping-the-tethered-cable-from-type-1-to-type-2-t432.html


  • Registered Users, Registered Users 2 Posts: 11,890 ✭✭✭✭the_amazing_raisin


    Did I mention that the power should be off at the board before attempting any of this?

    Haha, don't worry I figured that one out myself :D

    "The internet never fails to misremember" - Sebastian Ruiz, aka Frost



  • Registered Users Posts: 106 ✭✭47akak


    Has anyone on installed a Zappi V2 with solar PV and battery?

    I want to future proof the install for a 2nd Zappi charger and solar PV with a battery probably on the AC side. I need a CT sensor for the house load and a separate sensor for the battery. There are 3 CT sensor inputs. Will the grid CT monitor the solar export or should I run a third cat5? Or is it ok to use the 4 twisted pairs in one cable for various things? It's no problem running cable right now. It will be a problem in future.


  • Registered Users Posts: 6,181 ✭✭✭championc


    47akak wrote: »
    Has anyone on installed a Zappi V2 with solar PV and battery?

    I want to future proof the install for a 2nd Zappi charger and solar PV with a battery probably on the AC side. I need a CT sensor for the house load and a separate sensor for the battery. There are 3 CT sensor inputs. Will the grid CT monitor the solar export or should I run a third cat5? Or is it ok to use the 4 twisted pairs in one cable for various things? It's no problem running cable right now. It will be a problem in future.

    Yep, I have Solar PV, AC Battery and a Zappi v2.

    Obviously, in this particular setup, the Zappi needs 3 CT Clamps to read all 3 independently.
    One pair of a Cat5 should be all you need for each CT


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 542 ✭✭✭gomamochi1


    championc wrote: »
    Yep, I have Solar PV, AC Battery and a Zappi v2.

    Obviously, in this particular setup, the Zappi needs 3 CT Clamps to read all 3 independently.
    One pair of a Cat5 should be all you need for each CT
    Hi
    I have a solis hybrid inverter with 4.8 kw pylontech batteries and solar array. Is it possible to connect the zappi 2 to the solar pv as I understand I can't as its dc coupled ie ct clamp comes after the inverter and the other ct clamp is on the mains.


  • Registered Users Posts: 6,181 ✭✭✭championc


    gomamochi1 wrote: »
    Hi
    I have a solis hybrid inverter with 4.8 kw pylontech batteries and solar array. Is it possible to connect the zappi 2 to the solar pv as I understand I can't as its dc coupled ie ct clamp comes after the inverter and the other ct clamp is on the mains.

    Correct. The Zappi can only see the AC output of Hybrid inverters AFTER power is diverted to your batteries. You could maybe use the ECO mode to fudge it pulling xx% from the Grid, where xx% would equal the amount going to the battery, meaning that zero would go to the battery, but you could end up drawing from the grid.

    You might be able to restrict the charging rate of the battery, so more power is exported out of the inverter, but with the risk of that going back to the grid.

    Remember, a Zappi only starts charging in ECO+ mode once the solar excess is at least 1.4kW


  • Registered Users, Registered Users 2 Posts: 11,890 ✭✭✭✭the_amazing_raisin


    championc wrote: »
    Correct. The Zappi can only see the AC output of Hybrid inverters AFTER power is diverted to your batteries. You could maybe use the ECO mode to fudge it pulling xx% from the Grid, where xx% would equal the amount going to the battery, meaning that zero would go to the battery, but you could end up drawing from the grid.

    You might be able to restrict the charging rate of the battery, so more power is exported out of the inverter, but with the risk of that going back to the grid.

    Remember, a Zappi only starts charging in ECO+ mode once the solar excess is at least 1.4kW


    I've been looking at getting solar with a Victron Quattor inverter. The Quattro essentially acts as a pass through inverter, you connect the power from the grid to AC-in and the solar/batteries to DC-in and it sends power to the house on AC-out


    I've been thinking it might work better with a Zappi if I connect the Zappi between the Meter and the Quattro inverter, then when the Quattro is exporting the Zappi will see this and charge the EV without draining the battery


    I'd need to check this with Victron and MyEnergy but it might be a solution for people considering DC coupled batteries

    "The internet never fails to misremember" - Sebastian Ruiz, aka Frost



  • Registered Users Posts: 6,181 ✭✭✭championc


    I've been looking at getting solar with a Victron Quattor inverter. The Quattro essentially acts as a pass through inverter, you connect the power from the grid to AC-in and the solar/batteries to DC-in and it sends power to the house on AC-out


    I've been thinking it might work better with a Zappi if I connect the Zappi between the Meter and the Quattro inverter, then when the Quattro is exporting the Zappi will see this and charge the EV without draining the battery


    I'd need to check this with Victron and MyEnergy but it might be a solution for people considering DC coupled batteries

    First of all, you can only connect inverters which have been specifically certified for Ireland. A general EU EN-50438 is not sufficient.

    Secondly, you need to understand that electricity is not like water. It flows everywhere simultaneously. What happens is that sources feed of the highest voltage, so generated power in your home will ways be about 1v AC higher than the grid, and this is how it is used or is unused, is exported (or more to the point, drawn out) from your house

    So the only benefit that there can ever be Solar and Inverter wise is if you could have Solar PV DC going straight into a car as DC, since you convert it to AC and the car converts it back to DC


  • Registered Users, Registered Users 2 Posts: 1,874 ✭✭✭garo


    Question for Zappi v2 owners. I usually leave my charger in Eco+ mode with an overnight boost timer. I find that occasionally after the car has finished charging but the cable still connected to it the car will start drawing power at the full 7.4 kW during the day to “top up”. Shouldn’t this not be happening when I am still in Eco+ mode. I have solar and right now there is almost no export so the car should not be charging at all during the day.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 475 ✭✭jspuds


    garo wrote: »
    Question for Zappi v2 owners. I usually leave my charger in Eco+ mode with an overnight boost timer. I find that occasionally after the car has finished charging but the cable still connected to it the car will start drawing power at the full 7.4 kW during the day to “top up”. Shouldn’t this not be happening when I am still in Eco+ mode. I have solar and right now there is almost no export so the car should not be charging at all during the day.

    I have a Zappi v1 but think its the same, have you set the green level in eco+ to 100%?


  • Registered Users, Registered Users 2 Posts: 1,874 ✭✭✭garo


    jspuds wrote: »
    I have a Zappi v1 but think its the same, have you set the green level in eco+ to 100%?


    Ah good point. I set it to 55% back in October to catch the last rays. I'll up it to 100%. But even so shouldn't be charging at 7.4kW in Eco+.


  • Registered Users, Registered Users 2 Posts: 11,890 ✭✭✭✭the_amazing_raisin


    Does anyone know what the minimum charging power of the 3 phase Zappi is

    AFAIK it's 1.4kW for single phase, so would it be 4.2kW for 3 phase

    Does that mean if you're on a 3 phase supply you'll need to be exporting 4.2kW before your Zappi will kick in?

    "The internet never fails to misremember" - Sebastian Ruiz, aka Frost



  • Moderators, Home & Garden Moderators Posts: 6,283 Mod ✭✭✭✭graememk


    Does anyone know what the minimum charging power of the 3 phase Zappi is

    AFAIK it's 1.4kW for single phase, so would it be 4.2kW for 3 phase

    Does that mean if you're on a 3 phase supply you'll need to be exporting 4.2kW before your Zappi will kick in?

    I think it's 6 amps.

    I wonder was that the issues around the three phase zappis and the Hyundai/kia when switching between the eco mode and the normal charge mode.

    Maybe it can choose whether to charge on single phase or 3 phase.


  • Registered Users, Registered Users 2 Posts: 11,890 ✭✭✭✭the_amazing_raisin


    graememk wrote: »
    I think it's 6 amps.

    I wonder was that the issues around the three phase zappis and the Hyundai/kia when switching between the eco mode and the normal charge mode.

    Maybe it can choose whether to charge on single phase or 3 phase.

    I'm guessing here, but if it can do single phase mode I assume it's only on L1, as the car probably can't charge on single phase via L2 or L3

    "The internet never fails to misremember" - Sebastian Ruiz, aka Frost



  • Moderators, Home & Garden Moderators Posts: 6,283 Mod ✭✭✭✭graememk


    I'm guessing here, but if it can do single phase mode I assume it's only on L1, as the car probably can't charge on single phase via L2 or L3

    Yeah.

    Only on L1.. oh I get ya. If you have 3 phase you'd have a 3 phase solar Inverter.

    When the Kia/hyundai charge on single phase I think they bridge the L1&2 together. And didn't release it when it switched to 3 phase. Tripping breakers and the like.


  • Registered Users, Registered Users 2 Posts: 1,874 ✭✭✭garo


    garo wrote: »
    Ah good point. I set it to 55% back in October to catch the last rays. I'll up it to 100%. But even so shouldn't be charging at 7.4kW in Eco+.


    So I did a fast charge the other night and when the Zappi started pulling it showed electricity coming from the sun symbol and not the grid. And in the morning it had 33% next to the green symbol. I am positive the CT sensor is hooked to the right wire next to the meter. And last year it was detecting grid export/import correctly.


  • Registered Users, Registered Users 2 Posts: 12,136 ✭✭✭✭KCross


    garo wrote: »
    So I did a fast charge the other night and when the Zappi started pulling it showed electricity coming from the sun symbol and not the grid. And in the morning it had 33% next to the green symbol. I am positive the CT sensor is hooked to the right wire next to the meter. And last year it was detecting grid export/import correctly.

    Maybe the CT configuration in the Zappi menu has been reset to defaults?
    Did you do a firmware update recently?


  • Registered Users, Registered Users 2 Posts: 1,874 ✭✭✭garo


    Nope no firmware updates. I did have an RCD fault last month. The indicator turned red - after the car had fully charged overnight but was plugged in. I will check the CT config again.


  • Registered Users, Registered Users 2 Posts: 1,874 ✭✭✭garo


    Turns out I had both CT1 and CT3 set to Grid. I only have one CT so not sure where the config came from.


  • Advertisement
  • Registered Users Posts: 106 ✭✭47akak


    With the Zappi V2, I read in the thread it doesn't need a RCBO, they're not expensive, just wondering why that is or if there is any reason not to use an RCBO with the Zappi V2?


  • Registered Users Posts: 6,181 ✭✭✭championc


    47akak wrote: »
    With the Zappi V2, I read in the thread it doesn't need a RCBO, they're not expensive, just wondering why that is or if there is any reason not to use an RCBO with the Zappi V2?

    Personally, I just went the total belt and braces route - for the sake of a few quid


  • Registered Users, Registered Users 2 Posts: 505 ✭✭✭stiofan85


    championc wrote: »
    Personally, I just went the total belt and braces route - for the sake of a few quid

    Thanks for this. Got my Zappi in yesterday and sparks was not able to verify the integrated RCD despite showing him the manual. He didn't have the required tester (which I only found out about when I looked up testing the RCD on a Zappi on YouTube...)

    He is coming back to install a RCBO tomorrow. What type of RCBO did you have installed? I just want to make sure it's the right one he gets - I understand the high level operation of an RCBO, but I don't understand the difference in say type A/B, or the timing etc...

    Thanks


  • Moderators, Society & Culture Moderators Posts: 39,783 Mod ✭✭✭✭Gumbo


    stiofan85 wrote: »
    Thanks for this. Got my Zappi in yesterday and sparks was not able to verify the integrated RCD despite showing him the manual. He didn't have the required tester (which I only found out about when I looked up testing the RCD on a Zappi on YouTube...)

    He is coming back to install a RCBO tomorrow. What type of RCBO did you have installed? I just want to make sure it's the right one he gets - I understand the high level operation of an RCBO, but I don't understand the difference in say type A/B, or the timing etc...

    Thanks

    Should the registered sparks not be supplying or at the very least specifying it?


  • Registered Users, Registered Users 2 Posts: 505 ✭✭✭stiofan85


    Gumbo wrote: »
    Should the registered sparks not be supplying or at the very least specifying it?

    He is getting it and specifying. I'm asking what Championmc put in.


  • Registered Users Posts: 6,181 ✭✭✭championc


    stiofan85 wrote: »
    He is getting it and specifying. I'm asking what Championmc put in.

    It's a 32A Gato RCBO. It says B32A if that is the bit about whether it's A or B. I just went to the local wholesalers and asked for a 32A RCBO and that's what they gave me


  • Administrators, Computer Games Moderators, Sports Moderators Posts: 32,395 Admin ✭✭✭✭✭Mickeroo


    Anyone with a gen 1 zappi had this happen?

    hDNrMTCl.jpg

    Only noticed it today, could have been like that for a while. Presume I've been wrapping it too tightly around the unit and it's gradually messed up the covering.


  • Moderators, Society & Culture Moderators Posts: 39,783 Mod ✭✭✭✭Gumbo


    stiofan85 wrote: »
    He is getting it and specifying. I'm asking what Championmc put in.

    32A Curve B According to their website.

    https://myenergi.com/product/zappi/#product-specs


  • Moderators, Home & Garden Moderators Posts: 6,283 Mod ✭✭✭✭graememk


    Mickeroo wrote: »
    Anyone with a gen 1 zappi had this happen?


    Only noticed it today, could have been like that for a while. Presume I've been wrapping it too tightly around the unit and it's gradually messed up the covering.

    Ive seen that happen on a lot of strain reliefs from welders to computer cables,

    Im sure a new strain relief/gland could be got and the cable re-terminated, you'd lose a couple of inches.

    Prevention of it would be keeping that first loop a bit looser, not pulled tight around it. (same goes for any cable, the smoother the bend at joints the better.


  • Advertisement
  • Administrators, Computer Games Moderators, Sports Moderators Posts: 32,395 Admin ✭✭✭✭✭Mickeroo


    graememk wrote: »
    Ive seen that happen on a lot of strain reliefs from welders to computer cables,

    Im sure a new strain relief/gland could be got and the cable re-terminated, you'd lose a couple of inches.

    Prevention of it would be keeping that first loop a bit looser, not pulled tight around it. (same goes for any cable, the smoother the bend at joints the better.

    Would I be OK to just stick a bit of masking tape around it for now? It's working away fine just a bit worried it would get damaged. Now that I've spotted it I'll make sure I make the first loop loose anymore.