  • Registered Users Posts: 2,586 ✭✭✭karlitob


    Chawosfski wrote: »
    No it's just bad practice and against regulations

    Rcds , sure you can call a rec and the best option is to fit rcbos

    If you're concerned call a Rec about the installation

    No - I’m not concerned. You had mentioned it in your last post.

    If I get an Rcbo fitted will that stop it tripping?


  • Closed Accounts Posts: 61 ✭✭Chawosfski


    karlitob wrote: »
    No - I’m not concerned. You had mentioned it in your last post.

    If I get an Rcbo fitted will that stop it tripping?

    I pointed out a couple of bad habits , rcbos are not your issue here

    Unfortunately if you're so concerned about safety ,.maybe get a Rec to do your work in future


  • Registered Users Posts: 2,586 ✭✭✭karlitob


    Chawosfski wrote: »
    I pointed out a couple of bad habits , rcbos are not your issue here

    Unfortunately if you're so concerned about safety ,.maybe get a Rec to do your work in future

    Thanks for your time in pointing out the RECs bad habits.

    I not “concerned about safety”. I’m just asking for help as to why a new light fitting could trip and what I can do about it. You mentioned sheaths and rcbs and rcbos and recs, but that none of these things were the cause.

    Any advice as to how to fix this would be grateful. Appreciate you taking the time to post.


  • Closed Accounts Posts: 61 ✭✭Chawosfski


    karlitob wrote: »
    Thanks for your time in pointing out the RECs bad habits.

    I not “concerned about safety”. I’m just asking for help as to why a new light fitting could trip and what I can do about it. You mentioned sheaths and rcbs and rcbos and recs, but that none of these things were the cause.

    Any advice as to how to fix this would be grateful. Appreciate you taking the time to post.

    Sheathing can be a contributory factor to tripping

    These are general points i'm making , not specific to your fault


  • Registered Users Posts: 2,586 ✭✭✭karlitob


    Chawosfski wrote: »
    Sheathing can be a contributory factor to tripping

    These are general points i'm making , not specific to your fault

    Where the unsheathed earth goes into the terminal block - could I wire that directly into the earth on the fixture support. Could that help?


  • Advertisement
  • Registered Users Posts: 1,924 ✭✭✭whizbang


    Which number switch on the main board is popping ?

    Better to have all wires into terminal block, but no difference in electrical terms.

    Does it trip with only the bare earth disconnected ?


  • Registered Users Posts: 4,730 ✭✭✭meercat


    karlitob wrote: »
    Did that. Still popped.

    Now disconnect the spotlight and reconnect the led strip light and see what happens


  • Registered Users Posts: 2,586 ✭✭✭karlitob


    meercat wrote: »
    Now disconnect the spotlight and reconnect the led strip light and see what happens

    So
    - tried just having the earth in the terminal block. Still tripped
    - trip number 16 on the consumer unit
    - I tested for continuity (200 ohms on multimeter) on the wires for this light: live to neutral (no continuity), live to earth (no continuity), earth to neutral (01.3). Not sure what that means.
    - I tested continuity on the wires feeding the LED strip. Same as above.
    - I reconnected the LED and disconnected the new light fitting. Did not trip.

    So

    Should I try a normal bulb on this and see what happens?
    It’s a metal casing, could that be an issue?

    Thanks for your help meercat.


  • Registered Users Posts: 2,586 ✭✭✭karlitob


    Just knocked in another lampholder and halogen light I was working on - no problems at all.

    Just to say, that the new LED spotlight luminaire trips with and without a gu10 in it.

    I’ve also - for some reason most likely cos I have it - have tested all components in the luminaire with a multimeter. Everything seems fine.

    Not sure if it makes a difference but the lamp holder I knocked in was a 12v transformer to two g4 halogen lamps for the bedroom.


  • Registered Users Posts: 1,111 ✭✭✭rob w


    karlitob wrote: »
    Not sure how useful this is but the fixture does work.

    And just checked again - I didn’t hit the wire. No where near it.

    The light is working in this picture, but with no earth connected to the metal plate. It is possible that there is a short circuit to the metal plate (from the connector block on the plate) that is tripping when its earthed. It doesn't seem to be your wiring as I see you have another light working in its place now.


  • Advertisement
  • Registered Users Posts: 2,586 ✭✭✭karlitob


    rob w wrote: »
    The light is working in this picture, but with no earth connected to the metal plate. It is possible that there is a short circuit to the metal plate (from the connector block on the plate) that is tripping when its earthed. It doesn't seem to be your wiring as I see you have another light working in its place now.

    Yeah I had wondered that alright - whether it’s an issue with the earth or the initial power going through it. The new luminaire trips with all or each (L, E and N) in separately and both with and without a gu10 in. And without any other light on that switch. So I don’t think it’s a power / loading thing.

    It’s a metal casing and the instructions are keen for earthing. There does seem to be a lot of earth wires.

    Why does it need to earth to the fixing plate. Could I reduce the number of earth wires?


  • Registered Users Posts: 2,586 ✭✭✭karlitob


    Perhaps the second wire isn’t needed if the ring only has two core. In other words, if there’s 3 core only one of those earths are needed. If there’s a 2 core then 2 of those earths are needed.

    Am I miles off the Mark?


  • Closed Accounts Posts: 61 ✭✭Chawosfski


    A new house should definitely fix this

    But there's always a chance the new house could have the same problem


  • Registered Users Posts: 2,586 ✭✭✭karlitob


    Chawosfski wrote: »
    A new house should definitely fix this

    But there's always a chance the new house could have the same problem

    It is new!

    What do you think about the earthing?


  • Registered Users Posts: 2,586 ✭✭✭karlitob


    Fixed.

    Spot the difference.


  • Registered Users Posts: 1,111 ✭✭✭rob w


    karlitob wrote: »
    Fixed.

    Spot the difference.

    If that has fixed it, there was potentially a short from the earthed metal bracket on the ceiling to a live conductor. It may now be live itself as you have disconnected the earth. It was there for a reason and that's why it was tripping.

    Have you fixed the light back up to the bracket yet?


  • Registered Users Posts: 2,586 ✭✭✭karlitob


    karlitob wrote: »
    Fixed.

    Spot the difference.

    Noooooooooooo!!!!!


    It worked. Then I screwed the fixture up. Then it popped again. Arghhhhh!!!!


  • Registered Users Posts: 2,586 ✭✭✭karlitob


    rob w wrote: »
    If that has fixed it, there was potentially a short from the earthed metal bracket on the ceiling to a live conductor. It may now be live itself as you have disconnected the earth. It was there for a reason and that's why it was tripping.

    Have you fixed the light back up to the bracket yet?

    See above

    Popped again once I screwed it back up. I had wondered if the extra earth if there was only 2 core rather than 3 core.

    So - where am I?

    I’ve multimeter’d the luminaire. Everything makes sense.

    I’ve multimeter’d the ceiling wires - I think they all make sense (the earth and live on 200ohm showed a read of 01.3).

    I’ve put different fixtures in - albeit without an earth.

    I’ve tried each wire (l,n and earth) in only - all trip.

    The only permutation I haven’t tried is to fit it fully - screw it up and see what happens?

    It’s getting tiring at this stage!

    Thanks for help.


  • Registered Users Posts: 24,647 ✭✭✭✭punisher5112


    Your screwed into the cable at the fittin fixing anchor.


  • Registered Users Posts: 2,586 ✭✭✭karlitob


    Your screwed into the cable at the fittin fixing anchor.

    That makes sense. But I really haven’t. I’m nowhere near where the wire is coming from.


  • Advertisement
  • Registered Users Posts: 24,647 ✭✭✭✭punisher5112


    Is it screwed up into metal?


  • Registered Users Posts: 2,586 ✭✭✭karlitob


    Your screwed into the cable at the fittin fixing anchor.

    Is there a fix?


    I presume - knock a hole, and new wire/new connection.


  • Registered Users Posts: 24,647 ✭✭✭✭punisher5112


    Take screws out, I'd say it's hit the neutral, these are looped, fitting to fitting.

    You need to find where cable is damaged or run a new one or connector blocks on affected point.


  • Registered Users Posts: 2,586 ✭✭✭karlitob


    Is it screwed up into metal?

    I’ve only had a incandescent light on it once for 1 week, there was a metal fixing plate and the glass cracked so we took it back. It’s into wood one side and plaster only at the other.

    So as to be nowhere near the wire this time - and to change the orientation of the fitting so that the screws don’t show, I sunk two holes. I was careful, I felt nothing - plaster board gave way and I have two plugs and screws in so it’s not into joist or anything.


  • Registered Users Posts: 2,586 ✭✭✭karlitob


    Take screws out, I'd say it's hit the neutral, these are looped, fitting to fitting.

    You need to find where cable is damaged or run a new one or connector blocks on affected point.

    Is there a way to test before I do all that?

    Thanks for your help by the way.


  • Registered Users Posts: 24,647 ✭✭✭✭punisher5112


    karlitob wrote: »
    Is there a way to test before I do all that?

    Thanks for your help by the way.

    You would need to look at the cable at the point where you screwed up. This means cutting a hole enough to do a joing, into a junction box.

    Look up wago connector they're absolutely brilliant for connecting cables.

    The neutral set up tend to be throughout the house so say 4 rooms, these will all have a neutral shared between them, the live then comes up from the switch, the earth may also be shared depends on how it was wired.


  • Closed Accounts Posts: 61 ✭✭Chawosfski


    So it was the obvious all along

    You'll be going on 'til u kill someone


  • Closed Accounts Posts: 61 ✭✭Chawosfski


    As said you'll have to access the damage now

    Simply taking out the screw isn't enough


  • Registered Users Posts: 2,586 ✭✭✭karlitob


    Bingo!

    Thought I’d no slack - cable just very stiff. Pulled through now. Will strip and attach.

    Thanks gents.


  • Advertisement
  • Closed Accounts Posts: 61 ✭✭Chawosfski


    karlitob wrote: »
    Bingo!

    Thought I’d no slack - cable just very stiff. Pulled through now. Will strip and attach.

    Thanks gents.

    You're some clown, you said u didn't hit the wire

    I saw a job onetime where there was a slabnail through a t+e

    The meter was flying but fuse wasn't blowing

    That's the additional hazard where there's no rcd, although not their primary purpose