Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Please note that it is not permitted to have referral links posted in your signature. Keep these links contained in the appropriate forum. Thank you.

https://www.boards.ie/discussion/2055940817/signature-rules
Hi all! We have been experiencing an issue on site where threads have been missing the latest postings. The platform host Vanilla are working on this issue. A workaround that has been used by some is to navigate back from 1 to 10+ pages to re-sync the thread and this will then show the latest posts. Thanks, Mike.
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

Home charge points (purchase/problems/questions) (See mod note post#1)

12357170

Comments

  • Moderators, Sports Moderators Posts: 19,192 Mod ✭✭✭✭slave1


    rolion wrote: »
    My spark has recommended 10sq mm but with some sort of metalic shielding,like H E R E .
    My charger 32A came with 6sq mm cable out of factory.

    If you're getting outside cabling then just go SWA all the way, no need for ducting then, just clip to wall/wherever


  • Registered Users, Registered Users 2 Posts: 11,476 ✭✭✭✭Ush1


    KCross wrote: »
    Thats interesting. So, maybe the €300 being quoted is excessive then but its alot easier for a RECI to provide a cert for his own work at a decent rate.

    Having to retrospectively provide a cert for someone else's work is going to cost more.

    Had a chat with him and the 300 has miraculously become 50 quid. :)


  • Registered Users, Registered Users 2 Posts: 1,450 ✭✭✭Batesy


    25% off Black Friday deal on Rolec Wall Pods @ evonestop.co.uk.

    Ordered myself a 32Amp tethered Type one delivered for €354 via Parcel Motel :D


  • Registered Users, Registered Users 2 Posts: 1,092 ✭✭✭KAGY


    Batesy wrote: »
    Is there a particular spec of cable to use to future proof?

    Is 6mm2 enough?
    Depends on the length, whether it's in a wall with insulation etc, but is rated for 32a


  • Registered Users, Registered Users 2 Posts: 1,450 ✭✭✭Batesy


    KAGY wrote: »
    Depends on the length, whether it's in a wall with insulation etc, but is rated for 32a

    My run will be about 4 metres indoors then 10 metres outdoors. I'm thinking of going 10sq mm armoured to future proof the cable run.

    Might be over kill??


  • Registered Users, Registered Users 2 Posts: 65,708 ✭✭✭✭unkel
    Chauffe, Marcel, chauffe!


    That's a fairly long run. You don't have to go 10mm2 (for 32A), but I think I would in your case.


  • Registered Users, Registered Users 2 Posts: 1,092 ✭✭✭KAGY


    http://www.doncastercables.com/technical-help/

    Cable size calculator to bs spec. Don't take as Gospel though


  • Closed Accounts Posts: 3,362 ✭✭✭rolion


    I find very peculliar EV car owners giving advise here about the type. length and maybe "i think i will go for i will not go with that cable or that length", all from behind the keyboard ...
    WTF are we paying the electrician to do their jobs for !? If the chap says 10 go for 10, otherwise leave the man to do his job.

    My guy said is his way or not signing any papers... hate it when i had to stay and watch him doing the work...

    Good luck.


  • Registered Users, Registered Users 2 Posts: 8,295 ✭✭✭n97 mini


    One thing about SWA is it's very stiff and doesn't do tight radius bends easily. The alternative is regular cable in ducting.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 755 ✭✭✭Zenith74


    rolion wrote: »
    I find very peculliar EV car owners giving advise here about the type. length and maybe "i think i will go for i will not go with that cable or that length", all from behind the keyboard ...
    WTF are we paying the electrician to do their jobs for !? If the chap says 10 go for 10, otherwise leave the man to do his job.

    I think it's just that most of us here are Electric Vehicle nerds, with the emphasis on Electric. So we like to nerd-out over chargers, the number of kW we'll be pumping, the sizes of cables required etc. First thing I did after getting two chargers installed was to stick them both on with all the lights and the oven to see the maximum kW to the house it would draw :rolleyes:

    The other thing though is that lots of us do DIY on our homes, so in my case for example I had ceilings down, floors up etc. so wanted to pull in cables for future EV chargers, pulled some in for future solar panels etc. Yes you could contract an electrician to answer the question or try to find a friendly one who would tell you over the phone, but hell loads of us have done that before, and this is a discussion forum, so why not shoot the **** about it here :).

    FWIW I went with 10sqmm T+E flat for mine, price difference from 6sqmm is negligible, it's not too much more difficult to work with, so while I'm going to the effort of putting it down walls etc. why not...


  • Registered Users, Registered Users 2 Posts: 65,708 ✭✭✭✭unkel
    Chauffe, Marcel, chauffe!


    rolion wrote: »
    WTF are we paying the electrician to do their jobs for !? If the chap says 10 go for 10, otherwise leave the man to do his job.

    If we let car salesmen do their jobs and we took their advice, none of us would be driving an EV ;)


  • Registered Users, Registered Users 2 Posts: 477 ✭✭icom


    Batesy wrote: »
    Anyone foresee any Black Friday deals on home charger units??

    EV Onestop are doing 25% off all wallpod chargers for Black Friday

    https://evonestop.co.uk/collections/black-friday/products/wallpod-ev-charging-unit-type-2-socket-16-32-amp3-6-7-2kw-ip65

    Rolec Wallpod Type 2 16/32 amp for £250.80 including VAT


  • Registered Users, Registered Users 2 Posts: 1,589 ✭✭✭Stealthirl


    rolion wrote: »
    I dont get the beauty with Zappi in relation to load balancing and load limiting.

    From my own testing i can run an electric shower and oven and the car will still charge at 6.6 but stick on the kettle and the car charge drops until something is turned off. The kettle in my test and then it goes back up to 6.6 :)

    In my case i have a priority switch already so id have to add another one and it would also be safer to have a soft change rather then a hard stop.


  • Registered Users, Registered Users 2 Posts: 65,708 ✭✭✭✭unkel
    Chauffe, Marcel, chauffe!


    Stealthirl wrote: »
    From my own testing i can run an electric shower and oven and the car will still charge at 6.6

    Does not compute.

    Standard Irish connection is 63A = 14kW

    Shower 9-10kW + car 6.6kW + oven 3kW = 18.6-19.6kW, so not possible. Unless your oven was in the off cycle (it goes on and off all the time on the thermostat) and your shower is a very low power one


  • Registered Users, Registered Users 2 Posts: 755 ✭✭✭Zenith74


    unkel wrote: »
    Does not compute.

    Standard Irish connection is 63A = 14kW

    Shower 9-10kW + car 6.6kW + oven 3kW = 18.6-19.6kW, so not possible. Unless your oven was in the off cycle (it goes on and off all the time on the thermostat) and your shower is a very low power one

    I'm not sure it's quite that black and white unkel. For example I am looking at a screenshot from my Effergy showing 20kw being drawn (two chargers, oven, kettle, fridge, toaster) which is ~83A. Not sure if I have a 63A or 80A fuse, but either way I would be over it.

    That's not to say just because you can draw more than you're supposed to that you should, over loading wiring will not cause an immediate failure, it will just heat up slowly and maybe one time you charge and have a long shower on a sunny day and the heat is enough to start a fire. But just saying the ESB fuse does not necessarily blow the moment you go over 63.001A and wiring does not necessarily fail the minute you overload it either...


  • Advertisement
  • Registered Users Posts: 1,587 ✭✭✭DesperateDan


    Anyone know what this Zappi tweet means: https://twitter.com/MyEnergiLTD/status/1068039153286172673


  • Registered Users, Registered Users 2 Posts: 65,708 ✭✭✭✭unkel
    Chauffe, Marcel, chauffe!


    Zenith74 wrote: »
    I'm not sure it's quite that black and white unkel. For example I am looking at a screenshot from my Effergy showing 20kw being drawn (two chargers, oven, kettle, fridge, toaster) which is ~83A. Not sure if I have a 63A or 80A fuse, but either way I would be over it.

    I'd say you have a 80A supply. I'm no expert on this but I very much doubt a 63A supply would sustain an 83A draw without the fuse blowing.


  • Registered Users, Registered Users 2 Posts: 618 ✭✭✭bonoman66


    Anyone know what this Zappi tweet means: https://twitter.com/MyEnergiLTD/status/1068039153286172673

    New range of Zappi's being revealed at approx 2:30pm or 3:30 pm today I think..


  • Registered Users, Registered Users 2 Posts: 618 ✭✭✭bonoman66




  • Registered Users, Registered Users 2 Posts: 9,474 ✭✭✭TheChizler


    Anyone watch the event? Any idea when the new one will be available?


  • Advertisement
  • Closed Accounts Posts: 3,362 ✭✭✭rolion


    My "juice" charger , charging technical details,as per mobile app:
    Wondering why i fitted a 32A cable if Leaf doing only 15A ( i know,the on-board 3.3kw only)

    467200.jpg


  • Registered Users, Registered Users 2 Posts: 7,821 ✭✭✭stimpson


    rolion wrote: »
    My "juice" charger , charging technical details,as per mobile app:
    Wondering why i fitted a 32A cable if Leaf doing only 15A ( i know,the on-board 3.3kw only)

    467200.jpg

    Futureproofing. The extra cost of a 32A cable is marginal and if your charger supports 7.2KW then you may as well. I’ve a Zappi with a 32A cable but the Outlander only charges at 3.6KW.


  • Registered Users, Registered Users 2 Posts: 65,708 ✭✭✭✭unkel
    Chauffe, Marcel, chauffe!


    Every EV for sale today charges at 7kW. It would have been a huge mistake only installing a 16A charger (and 16A rated cables, 16A/25A RCBO, etc.)


  • Registered Users, Registered Users 2 Posts: 12,452 ✭✭✭✭DrPhilG


    unkel wrote: »
    Every EV for sale today charges at 7kW. It would have been a huge mistake only installing a 16A charger (and 16A rated cables, 16A/25A RCBO, etc.)

    I'm up to my elbows with some folk on the UK i3 owners page who insist that the i3 will only charge at 3.6kw on an 11kw post if its using a single phase cable.

    They also reckon that our 22kw posts are 3x7kw rather than 2x11kw?

    I gave up trying to understand it.


  • Registered Users, Registered Users 2 Posts: 22,217 ✭✭✭✭ELM327


    DrPhilG wrote: »
    I'm up to my elbows with some folk on the UK i3 owners page who insist that the i3 will only charge at 3.6kw on an 11kw post if its using a single phase cable.

    They also reckon that our 22kw posts are 3x7kw rather than 2x11kw?

    I gave up trying to understand it.
    Morons.


    If you connect to an 11kW post with a 32a single phase cable the i3 should take 32a/7kW not 16a. It can use 2 of the phases to give 32a single phase. At least that's my understanding of it. I stand to be corrected by someone who knows what they are talking about of course! I mean even in my Ioniq I get 7kW 32a from a 11kW 16a 3phn post


    How could the post be 3*7kW that doesn't make sense. The UK haven't a clue, they refer to them as "fast chargers" anyway sure :D:D:D


  • Registered Users, Registered Users 2 Posts: 12,136 ✭✭✭✭KCross


    DrPhilG wrote: »
    I'm up to my elbows with some folk on the UK i3 owners page who insist that the i3 will only charge at 3.6kw on an 11kw post if its using a single phase cable.

    They also reckon that our 22kw posts are 3x7kw rather than 2x11kw?

    I gave up trying to understand it.

    The confusion there Phil is whether it is truly an 11kW post or a 22kW post which you are sucking 11kW from.

    If its an 11kW only post it will be 16Ax3ph and if you stick a 1ph cable on that you will only get 16A off it, like they said. So they are right there, imo.

    However, most of our SCP's are 22kW (32Ax3ph) so if you stick a 1ph 32A cable on that your i3 will pull 32A from one phase and give you 7kW.

    If you stick a 3ph 32A (or 3ph 16A) cable on it you will get 16Ax3p=11kW.


    Making sense yet?

    Basically an 11kW i3 can pull 16A per phase when connected to a 3ph supply.
    And it can pull 32A from one phase when connected to a 1ph supply by combining two 16A rectifier inputs on that one phase.


  • Registered Users, Registered Users 2 Posts: 1,589 ✭✭✭Stealthirl


    unkel wrote: »
    Does not compute.

    Standard Irish connection is 63A = 14kW

    Shower 9-10kW + car 6.6kW + oven 3kW = 18.6-19.6kW, so not possible. Unless your oven was in the off cycle (it goes on and off all the time on the thermostat) and your shower is a very low power one

    80A=17.6Kw :D
    But i was wrong about the kettle,it was the oven that dropped the car charge rate :o


  • Registered Users, Registered Users 2 Posts: 65,708 ✭✭✭✭unkel
    Chauffe, Marcel, chauffe!


    So you do have a 80A connection?


  • Registered Users, Registered Users 2 Posts: 7,821 ✭✭✭stimpson


    80A is actually 18.4kW as voltage is 230V.


  • Registered Users, Registered Users 2 Posts: 12,136 ✭✭✭✭KCross


    stimpson wrote: »
    80A is actually 18.4kW as voltage is 230V.

    You are right, but you won’t have an 80A connection by default unless you paid extra for it.

    Are you sure you have an 80A connection?


  • Advertisement
  • Registered Users Posts: 80 ✭✭optimal


    Does anyone know if there’s any way to be absolutely sure as to exactly what you are allowed to draw. I can’t find anything on my bill. There is the maximum import capacity but not sure if that only applies to commercial companies. It would be really useful to know.
    unkel wrote: »
    So you do have a 80A connection?


  • Registered Users, Registered Users 2 Posts: 7,821 ✭✭✭stimpson


    optimal wrote: »
    Does anyone know if there’s any way to be absolutely sure as to exactly what you are allowed to draw. I can’t find anything on my bill. There is the maximum import capacity but not sure if that only applies to commercial companies. It would be really useful to know.

    The main fuse on your supply coming in to the house. It’s probably 63A.


  • Registered Users, Registered Users 2 Posts: 12,136 ✭✭✭✭KCross


    optimal wrote: »
    Does anyone know if there’s any way to be absolutely sure as to exactly what you are allowed to draw. I can’t find anything on my bill. There is the maximum import capacity but not sure if that only applies to commercial companies. It would be really useful to know.

    Not really. The main fuse is just below your outside meter but it’s sealed and you can’t just pull it out to see.

    If you didn’t pay for an upgraded supply you should assume you have a 60A fuse in there. Upgraded supply has 80A fuse.


  • Registered Users, Registered Users 2 Posts: 7,821 ✭✭✭stimpson


    KCross wrote: »
    Not really. The main fuse is just below your outside meter but it’s sealed and you can’t just pull it out to see.

    If you didn’t pay for an upgraded supply you should assume you have a 60A fuse in there. Upgraded supply has 80A fuse.

    Yeah my bad. I knew there was something written on the fuse, but it says 60/80A


  • Registered Users Posts: 80 ✭✭optimal


    stimpson wrote: »
    The main fuse on your supply coming in to the house. It’s probably 63A.

    So and pardon my ignorance, can you keep drawing power til the fuse trips or will you be charged for going over a set figure?


  • Registered Users, Registered Users 2 Posts: 7,821 ✭✭✭stimpson


    optimal wrote: »
    So and pardon my ignorance, can you keep drawing power til the fuse trips or will you be charged for going over a set figure?

    It will trip if you go over. And you need to get the esb out to replace it.

    The electrician should design the system so that it doesn’t happen, using a priority switch to limit current to the charger when there is another large load or installing a sophisticated charger like the Zappi.


  • Registered Users Posts: 80 ✭✭optimal


    stimpson wrote: »
    It will trip if you go over. And you need to get the esb out to replace it.

    The electrician should design the system so that it doesn’t happen, using a priority switch to limit current to the charger when there is another large load or installing a sophisticated charger like the Zappi.

    Thanks. I got my Zappi and harvi 😀


  • Registered Users, Registered Users 2 Posts: 12,136 ✭✭✭✭KCross


    stimpson wrote: »
    Yeah my bad. I knew there was something written on the fuse, but it says 60/80A

    Yeah the fuse holder is compatible with 60A and 80A. The thing is you dont know which it is unless you open it and eyeball it (breaking the seal, which you are not allowed do)

    optimal wrote: »
    So and pardon my ignorance, can you keep drawing power til the fuse trips or will you be charged for going over a set figure?

    In theory your main fuse on your consumer unit should trip before the fuse in the meter box blows . The fuse on the consumer unit is your responsibility and you can change that yourself.

    If, for some reason, the ESB fuse blows you have to get them out to change that and they will charge you for the privilege.


  • Registered Users, Registered Users 2 Posts: 1,589 ✭✭✭Stealthirl


    unkel wrote: »
    So you do have a 80A connection?
    Yes
    stimpson wrote: »
    80A is actually 18.4kW as voltage is 230V.
    So i could change the limit on the zappy from 17.6 if i was willing to risk the fuse...Think ill just leave it at 17.6
    optimal wrote: »
    Does anyone know if there’s any way to be absolutely sure as to exactly what you are allowed to draw. I can’t find anything on my bill. There is the maximum import capacity but not sure if that only applies to commercial companies. It would be really useful to know.

    Normal supply is 12kVA
    Enhanced is 16kVA [you can upgrade to this easily enough if you home is modern]

    After that things get expensive as you a liable for any related price to upgrade the line to your house but they offer a 20kVA single phase line and above along with 3 phase.

    You can get a separate 12kVA connection for a family apartment


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 791 ✭✭✭RonnieL


    I'm sure it has been stated on this thread previously, but shopping around for charger installation prices is a must. I got two local (SAFE registered) electricians to give me quotes to install a Zappi which I bought with my car. The first came in at 675 plus vat. The second was 200 plus vat. The second lad seemed a lot more clued in too.


  • Registered Users, Registered Users 2 Posts: 7,821 ✭✭✭stimpson


    I just paid my spark for the install. €170 in VAT. In fairness he was here doing other work at the same time. €150 after the grant for a Zappi installation. Not too shabby.


  • Registered Users, Registered Users 2 Posts: 1,149 ✭✭✭deadduck


    picked up my leaf yesterday. only quote i've got so far for charger installation is €375 plus VAT by powerwise in Kill. That's for the labour, cabling and RCBO, and then they will supply the charger on top, or I can supply my own

    if anyone has any recommendations of someone decent around Kildare/Newbridge/Naas i'd appreciate it


  • Registered Users, Registered Users 2 Posts: 1,544 ✭✭✭denismc


    Is anyone else finding it difficult to get an electrician to do an install for the charger?

    I have contacted 14 different electricians and only managed to get a single quote!
    The one guy that did give me a quote has not responded to my calls or texts.
    At first I thought it was that the electricians were just too busy, but now I am thinking there is some other reason they don't want to do the job.
    Is it the paper trail that is scaring them away?
    Any electrician out there want to shed some light?
    At this rate I will end up selling the unit and just using the granny cable


  • Registered Users, Registered Users 2 Posts: 65,708 ✭✭✭✭unkel
    Chauffe, Marcel, chauffe!


    You obviously haven't tried Nigel Daly? He's the biggest installer of EV charge points in the country. Not cheap, but it's a professional outfit and they do a good job. They install nationwide.


  • Registered Users, Registered Users 2 Posts: 1,544 ✭✭✭denismc


    unkel wrote: »
    You obviously haven't tried Nigel Daly? He's the biggest installer of EV charge points in the country. Not cheap, but it's a professional outfit and they do a good job. They install nationwide.
    No I haven't tried Nigel yet but may have to.
    I just don't understand why so many electricians don't even want to quote for what is a simple job.!


  • Advertisement
  • Registered Users Posts: 80 ✭✭optimal


    Zenith74 wrote: »
    I'm not sure it's quite that black and white unkel. For example I am looking at a screenshot from my Effergy showing 20kw being drawn (two chargers, oven, kettle, fridge, toaster) which is ~83A. Not sure if I have a 63A or 80A fuse, but either way I would be over it.

    That's not to say just because you can draw more than you're supposed to that you should, over loading wiring will not cause an immediate failure, it will just heat up slowly and maybe one time you charge and have a long shower on a sunny day and the heat is enough to start a fire. But just saying the ESB fuse does not necessarily blow the moment you go over 63.001A and wiring does not necessarily fail the minute you overload it either...

    I’m struggling with this one too. My 12kw heat pump and fast charge Leaf were running together (unintentionally) for over an hour with no issue. In theory this should be about 19kw. I’m on a standard supply which I thought was 12kVA. I’ve a 63A “fuse” in customer unit and 63/80 A at meter. Any ideas?


  • Registered Users, Registered Users 2 Posts: 12,136 ✭✭✭✭KCross


    optimal wrote: »
    I’m struggling with this one too. My 12kw heat pump and fast charge Leaf were running together (unintentionally) for over an hour with no issue. In theory this should be about 19kw. I’m on a standard supply which I thought was 12kVA. I’ve a 63A “fuse” in customer unit and 63/80 A at meter. Any ideas?

    Common misunderstanding. Your 12kW heat pump isnt pulling 12kW, thats its output not its input! ;)

    When the HP is running it's probably pulling around ~2.5kW


  • Registered Users Posts: 80 ✭✭optimal


    KCross wrote: »
    Common misunderstanding. Your 12kW heat pump isnt pulling 12kW, thats its output not its input! ;)

    When the HP is running it's probably pulling around ~2.5kW

    Thanks. That makes sense!! It’s a 4hp (4cv ?) compressor which I think equates to around 3kw then.
    It’s great to have people here that know what they’re talking about!!


  • Registered Users, Registered Users 2 Posts: 618 ✭✭✭bonoman66


    Had my Zappi Charger installed this morning by John from Nigel Daly's Team.

    Here's my unsolicited feedback & a few pics in case it helps anyone...

    Work Carried Out: Supply and Installation of Zappi EV Charger at my House.

    Disclaimer: I am not in any way related to Nigel Daly's Company or Employee's (that I know of!). I'm not employed or being paid by Nigel Daly for my feedback. This is my own unsolicited feedback.



    Feedback:


    I'll be getting my first EV soon & I had been researching what I needed to have ready in advance of the car arriving. I chose a MyEnergi Zappi EV Charger (5 Meter Tethered Unit, Type 2) based on its ability to integrate with Solar Panels in the future if I decide to get them, for its reputation among those EV owners who have already purchased & been using it, and (because I have an Electric Shower installed in my home) for its ability to dynamically determine what current/power is being used within the house at any point so it then can adjust the power/current sent to the car when it is charging. (Using its CT Clamp). So it avoided the need to purchase an additional Priority Switch.

    The next thing I had to determine was who to ask to do this work.

    Again, I read a lot of online forums and one name repeatedly came up in terms of that company's Expertise, Skill, Knowledge & Ability to deliver a professional service and high quality finish - Nigel Daly.

    I understood that there may have been cheaper alternatives - eg for me to source & acquire the charger unit myself & then separately find an electrician to install it.

    I decided because I wanted the least amount of hassle / inconvenience with the highest level of service, professional finish, & someone that understood all the paperwork & who met all the criteria required for me to submit my EV Home Charger SEAI Grant Application, that I would choose Nigel Daly for this work.

    I asked Nigel to source the charger & install it.

    Right from my initial contact with Nigel's Team - Kelly, I could tell this was going to be a positive experience. Kelly was very responsive to all my questions & a good communicator using email & calling me on my phone. Nigel himself also provided me with information through email & over the phone. So it was great to see such a high level of customer focus & responsiveness at all levels within the company.

    Kelly was very efficient in scheduling the work & providing me with time frames that suited me.

    I subsequently got a follow up call from one of the Installation Electricians in Nigel's' Team (John) & he arranged a mutually agreeable installation day / time with me.

    On the morning of the scheduled work, John was travelling a long distance to get to me & constantly kept me appraised of his location & updated me (through text messaging) with expected arrival times. I found this very helpful & not something that other tradespeople had bothered to do in the past for me.

    John arrived on time & all ready & prepared for the job. He had obviously already been fully briefed by Kelly & Nigel on what I needed done as he knew exactly what the job was & there were no surprises for him & I did not have to explain everything.

    John was an absolute professional. He provided such a high level & standard of work that it went above what I had expected (and I have high standards!). He went out of his way to explain what he was going to do at each stage of the work & ensured I was comfortable with it.

    Observing John at work, it was apparent that he was highly skilled, had done this exact type of install many times & to me, he was so efficient I think he could have almost done the work with a blindfold on (not that it would be safe to do that of course :-)).

    John was so incredibly neat & tidy at every stage (Drilling out from the internal fuse box in the house, attaching & routing protective cable trunking on the side of the house, installing & testing the EV charger for me).

    I cannot recommend Nigel Daly & his team (thanks again Kelly & John) highly enough for their outstanding level of responsiveness, customer service, for getting things right first time, for their attention to detail & faultless install of my Home EV Charger.

    Well done Nigel to you & your team. You obviously surround yourself with the right type of people - great personalities, superb customer focus / responsiveness, combined with expertise knowledge & professionalism.

    You & your company deserve any & all success based on what you did for me this morning.

    In my eyes - great value for my money & a totally happy customer.


  • Closed Accounts Posts: 3,362 ✭✭✭rolion


    bonoman66 wrote: »

    In my eyes - great value for my money & a totally happy customer.

    Great ad...

    Personal,i am not a fan of Zappi due to that if you will have solar PV at some point in time, you need more than 5KW installed power to make sure you get benefits of the internal smart electronics (thats the main selling point of the unit).

    Can we see the interior as well,please.

    Thanks.