Heat Pump Running Costs

1131416181925

Comments

  • Registered Users, Registered Users 2 Posts: 2,925 ✭✭✭ECO_Mental


    The theory is that you reduce the number of heating zones in your house down to one if not two…the problem is if you have too many zones your HP could be coming on an off a lot and HPs work best in a low and steady state. Also what will happen if a heat stat comes on in your living room and its only calling for heat in your living room, then naturally the heat will transfer out of the living room to other rooms (unless its sealed very well!), thus that living room in effect is trying to heat all the house and might not get up to the set temp. There is a technical issue here also if you are heating one room as well, in that the flow temp and the return temp will become less and less and HPs need the return flow temp to be a good few degres less in order for the HP to work efficently.

    With an open loop you keep all the zones open so when the HP comes on its heating the entire house (not just one room) so the whole house comes up to the set temp. The HP should work as efficent as possible because its getting the required flow rates and return flow temp differential will be optimal.

    To do this there are a number of ways, some are technical in that you remove all the acuators that control the heating valves so they are all open or install a fancy heating control system that will alow this or you do what I did and trick it into doing it…

    In my case I have 12 zones😯 (220m2 A1 (A2 without PV!)) house and what I have done is artfically set the room temps to a high value and set the heating to come on at set times so when the heating comes on it comes on for all the house. My aim is cost reduction so I have it coming on at my EV rate which is 6.33c kWh between 3-5am but its heating the entire house to build thermal mass. This then lasts me well into the evening, at 7pm then after peak rates it comes back on again for a couple of hours, again all zones on. It seems to be working well enough, Im not doing much more than 20 kWh/day and is a lot better than last winter where I had the 12 zones working independantly.

    With this cold weather I think I will have to turn on the heating earlier in evening for another hour or two as I did feel in one or two rooms it was getting below what I would like (20deg). BUT if I am doing this I will mannually turn on the stats in as many rooms as possible. If the HP is on then its heating the entire house…my method requires a bit of attention but it interests me

    I will post more data after this week is over to see how I did

    (forget about that spike in the graph thats a data error 😪)

    image.png

    6.1kWp south facing, South of Cork City



  • Registered Users, Registered Users 2 Posts: 199 ✭✭Jo Satan


    My first winter in an A2 115sqm house with a heat pump.
    The heating was using 10kwh per day during November when temps were around 10- 12c.
    So I made some changes to the weather compensation curve dropping it a good bit with a view to adjusting up if required.
    20c at 15c and 32c at -5c and got the usage in December down to 5kwh per day.
    Its been 0c for the past week, the heating is using 400w per hour constantly with a flow temperature of 28c.
    Room temperatures have held at 20/21c.

    Is there a point where the heat pump loses efficiency due to the temps being set too low?
    I saw this being mentioned here

    What’s the Most Cost-Effective Way to Run a Heat Pump?



  • Registered Users, Registered Users 2 Posts: 3,456 ✭✭✭newhouse87


    Removing the actuator heads i find was easy way to create the open loop. You can use the flow meters on manifold then to direct more heat to different parts. I have my kitchen and sitting room where we are most at 23/22 ish respectively. Master Bedroom at 20/21 and other rooms we don't use i have less flow going to them so they sitting at 18 approx. Ye are lucky who have partners that like the house at 20, herself likes 22/23, much less the hoody is on. 1 programmable stat runs the house, set at these outside temps 11pm - 1pm @ 31deg flow temp. Mostly night rate when heat pump working hardest initially after starting up.



  • Registered Users, Registered Users 2 Posts: 2,925 ✭✭✭ECO_Mental


    I have a very well insulated and airtight house, to hit 22/23 degs would cost me a fortune and to keep them there the heating would be on full time….Anything over 21 I notice a big difference in trying to keep that temp. Can you not drop by 0.5deg and see if she notices. Half a degree can make a big difference espcially at those temps

    6.1kWp south facing, South of Cork City



  • Registered Users, Registered Users 2 Posts: 3,456 ✭✭✭newhouse87


    Its costing in these temps approx 28kwh for 242sqm bungalow and mostly nightrate so im happy enough even if it costs bit more. Sitting room may drop to 21.5 and kitchen to 22.5 at times, when running for set period it doesn't maintain exact temp. But kitchen was 22 this morning when i got up and sitting room 21. By 1pm both will be up another degree and will maintain that more or less until it comes on again at 11pm. I do think 20deg is bit chilly to watch tv, i go around in shorts and t shirt in house.



  • Advertisement
  • Registered Users, Registered Users 2, Paid Member Posts: 10,144 ✭✭✭✭10-10-20


    Folks, could one of you cast an eye on this question which I made a stab at…?



  • Registered Users, Registered Users 2 Posts: 411 ✭✭Eleusis


    How on earth did you get your underfloor to get to 40 degrees?I have an ecodan with underfloor and a large slab. I actually want to yo get it to 50 degree to avail of cheap night but it simply will not do it unless it's on for days.

    There seems to be something inbuilt that only allows the flow temp to it to be approx 5 degrees higher than return temp. This means my return temp would have to be 35 degrees if I wanted 40 degrees flow temp. And my slab would have to be 35 degrees then and the house would be unbearable hot. It would take a few days to do this too.

    If my floor is say 21 degrees the highest flow temp I can get would be approx 26 degrees even if I have it set to 40 degrees.

    Somehow your ecodan will put in flow temps more than delta t of 5?? Would love to see your old settings.



  • Registered Users, Registered Users 2 Posts: 1,520 ✭✭✭FastFullBack


    Can I ask why in a well insulated and airtight house is it very difficult and costly to hit 22/23 degs?

    I'm in my first winter in a new build with ground source heat pump and UFH (ground and 1st floor). I'm running the heat pump at night and can easily get it to 21, but last night I tried to get it to 22 and it only got to 21. House aint cold, but curious why getting up to 22 would be difficult and especially I would expect being well insulated and airtight would help?



  • Registered Users, Registered Users 2 Posts: 955 ✭✭✭keno-daytrader


    These were the readings a few months into winter for our new build, the tile floors would be absolutely roasting.

    I turned off auto adapt by a dip switch as the more I read about auto adapt the more it seemed like it was designed for a radiator built system and not for underfloor heating. I then experimented with fixed flow temps and weather compensation, but in the end went with fixed flow.

    I believe it was the auto adapt that was letting the flow temp so high.

    Our first Dec we used 363kWh, this Dec we used 185 kW just about half of that first year that the installer set up.

    COP that Dec was 2.60(with auto adapt), COP this Dec was 4.69

    ☀️ 8.2kWp ⚡4kWp south, ⚡4.20kWp west



  • Registered Users, Registered Users 2 Posts: 2,925 ✭✭✭ECO_Mental


    Because it low temp heating its not designed for heating houses up to those temps….the actual underfloor water flow temps are only in the high 20s low 30s to to get the air temps into the mid 20s is hard enough.

    6.1kWp south facing, South of Cork City



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 955 ✭✭✭keno-daytrader


    Yes all valves are open on manifold and no trv's. I want the whole slab to heat up and and use it as a thermal store thru out the day. I dont want any cold rooms stealing heat from the rest of the building fabric.

    ☀️ 8.2kWp ⚡4kWp south, ⚡4.20kWp west



  • Registered Users, Registered Users 2 Posts: 411 ✭✭Eleusis


    Just an FYI. The ecodan by default turns the immersion on to heat the floor after a set amount of time has passed and the room temp has not got up to temp. I think it was set to 30 mins on mine. This is not long enough for underfloor to react(especially with a thick slab)

    I had similar awful cop until I figured this out. However it wasn't as bad as I thought because I didnt even have the immersion connected and I don't intend to either. But the ecodan measures the cop as if the immersion was on.

    WC and constant flow temp settings I don't think would activate the immersion.

    This could be why your COP was so off on room heat mode(which is I presume what you are referring to as auto adapt mode. If you do have immersion connected or you just want accurate COP you can turn the settings.



  • Registered Users, Registered Users 2 Posts: 955 ✭✭✭keno-daytrader


    I turned off both heaters for underfloor and hot water in settings, so that wasn't my issue. My system came with auto adaptation mode set to on. I'm not sure if this defaults to on or off but I subsequently found out it should only be used for rads and not underfloor heating.

    I had to manually turn to off dip switch SW5-2 to turn off auto adaptation mode. This solved my sky high energy usage. Then it was just a matter of tweaking the system.

    ☀️ 8.2kWp ⚡4kWp south, ⚡4.20kWp west



  • Registered Users, Registered Users 2 Posts: 1,861 ✭✭✭poker--addict


    I know arguments for maximising open zones and the concept of not leaving one room cold, I wonder especially about the one room cold one and how marginal this might be.

    We have one very large unused room, on upper floor, a part of house with relatively bad and inaccessible insulation. I think it's fine to not try heat this all the time? I manage this zone to only come on for a few hours on night rate electricity to keep out the lowest temps but it's probably not hitting 17 in cold weeks of winter unless there's been some solar gain warming whole place

    😎



  • Registered Users, Registered Users 2 Posts: 1,746 ✭✭✭THE ALM


    Yesterday was probably as bad a day for running a heat pump in the midlands as any, freezing fog and temp not above 0° all day.

    Consumed 32.35kWh, producing 108.6kWh for both heating and hot water so giving a COP of 3.37.

    Total cost for all electricity was €11.88 which includes EV charging on the 4 hour EV rate. Produced about 2.8kWh from the PV.



  • Registered Users, Registered Users 2 Posts: 3,287 ✭✭✭dominatinMC


    Thanks for the detailed reply. I have a few questions, and possibly also looking for some advice (not asking for much!😅).

    1. You mention your HP comes on between 3-5 am, but surely it runs for longer than that to get the whole house up to temperature? Would you have a rough idea for how long on a typical winters day?
    2. Maybe you have mentioned this before, but what fixed flow temp are you running?

    In my case, I have a mix of rads and UFH (due to a sizeable extension) on our ground floor, and rads upstairs. We spend most of our time in the extension, which is an open plan kitchen-dining-living space. Currently, I am applying the 'low and slow' approach here, where the HP comes on from 14:00 - 18:00 and gets the space up to around 21-21.5 degC (like you I set the stats to artificially high values to drive the HP). Come 18:00, heating of the open plan space ceases and a stat in our master bedroom calls for heat - which also heats all the remaining rooms. This happens from 18:00 - 21:00 and keeps rooms to 19degC. However, I'm wondering would you recommend doing these two heating operations simultaneously, rather than one after the other? Given that the bedrooms etc. are heated by rads, I'm not sure if there is a thermal mass there to heat.



  • Registered Users, Registered Users 2 Posts: 2,925 ✭✭✭ECO_Mental


    First things first I am no expert in heat pumps just a grumpy dad messing with the heating trying to save money.... 😋

    Anyway on a typical winters day mid to high single digits and above the heating (not including DHW) alone runs for 2 hours at night (3-5am) and then for 2.5 hours from 19:00 to 21:30 so that's 5.5 hours in total. Up until this week where we had the artic vortex this was working great for my house. I am sure on warmer winters days I could cut back on this but I just leave it alone for now. I would really like to automate it more in Home Assistant like predicting the next days weather etc and I had plans for this but her indoors put a stop to it😪

    I am not running fixed flow temps there is weather compensation on the HP so it goes higher for colder weather and lower for the milder weather. For example this evening the flow temp is 35 -36 degs and its about 0 degs outside.

    Like you in the evening I do spilt the heating and concentrate on downstairs for the first 1.5 hours, then overlap for a half hour then only upstairs….I initially had all the zones on but I thought it wasn't heating up as fast downstairs when we needed it. At night its all on!! I count the EV rate at 6.5cent as almost free heating.

    What I would say every house is different with different layouts so at the end of the day it what works best for you and its trial and error. Given that you have rads upstairs in the bedroom I would think leaving these this last in the evening is a good strategy.

    I do think though that if the HP is on then you need to be heating as much area as possible so one room is not stealing heat from another room. I think you can have systems that outputs really low flow temps and are literally on all day long but just tip away on the background and I might be able to trick my HP into that but I don't think there is any need for my house.

    There is a poster on here @championc and he posts his live data from his heat pump and you can see his flow temps and all the data here is a link to the thread its in the plumbing forum, so you might get some more insights.

    My DIY installed Vaillant AroTherm Plus is now LIVE — boards.ie - Now Ye're Talkin'

    and a link to his live HP data

    https://emoncms.org/app/view?name=championc&readkey=5e5a2bd11d69740be46a55e1793e551d

    image.png

    6.1kWp south facing, South of Cork City



  • Registered Users, Registered Users 2 Posts: 7 DelE30


    Averaging 24kwh usage per day to maintain a A2 rated 3 bed new build in Roundwood at 21C. Samsung Gen 6 HP.

    Worryingly my energy generation figures are also averaging 24-25kwh per day. Can't understand why this is not higher if system COP should be over 3?



  • Registered Users, Registered Users 2, Paid Member Posts: 10,144 ✭✭✭✭10-10-20


    Where are you reading the "energy generation" figure from? Off the HP system/app or off another device or energy monitor? A screenshot might help us.



  • Registered Users, Registered Users 2 Posts: 7 DelE30


    Hi! So I'm getting this off the controllers screen. See below for last week. HP ran for 10-11hrs each day.

    I've also posted here so don't want to spam two threads! All help appreciated.

    20250105_213747988_iOS.jpg 20250105_213813603_iOS.jpg


  • Advertisement
  • Registered Users, Registered Users 2, Paid Member Posts: 10,144 ✭✭✭✭10-10-20


    See what the lads on that other thread think as I don't have a HP, so I'd just be a professional guesser. 😁



  • Moderators, Home & Garden Moderators Posts: 7,734 Mod ✭✭✭✭graememk


    Somethings not right at all. Generation (output) should be at least 2-3x in a worst case scenario



  • Registered Users, Registered Users 2 Posts: 863 ✭✭✭staples7


    Would be interesting to know how high your consumption went to keep house at 23' in minus conditions this week? 23' for most might be a bit uncomfortable heat wise. each to their own but I would say 20'c is probably the sweet spot. I know I generally have a daily usage of about 10kwh to maintain 19.5'/20' In normal winter conditions. That went top to about 30kwh daily this week. if I wanted 23' id be doubling that I would think.



  • Registered Users, Registered Users 2 Posts: 1,861 ✭✭✭poker--addict


    Can people quoting daily KW quote their house size, and ideally year of build or at least BER. KW per day without context is somewhat meaningless. 20kw in a brand new house 120sqm with only two people who would be disaster, or amazing if a 300sqm house from 2004

    😎



  • Registered Users, Registered Users 2 Posts: 3,456 ✭✭✭newhouse87


    Kitchen area 22/23 and sitting room 21/22 this week.I don't keep them at that,it's what they get to from running all night. Yesterday approx 34 mostly night rate, not bad as it's bungalow so heating whole house 242sqm. Bedrooms generally 20. I'd find 20 bit chilly watching tv in shorts, 22 I'd consider sweet spot.



  • Registered Users, Registered Users 2 Posts: 798 ✭✭✭feelings


    No EV.

    Hit 120kwh yesterday and the house never reached higher than 19.5, calling for heat all day. (set at 20.5 downstairs and 19.5 upstairs).

    It seems that the unit is just constantly calling for heat but it's not heating. I noticed the rads upstairs were never warm yesterday (not even the usual luke warm) aswell.

    The UFH downstairs, while not cold, is never "warm".

    I only had the unit serviced a few weeks ago. Could they have damaged or changed something?



  • Registered Users, Registered Users 2 Posts: 2,925 ✭✭✭ECO_Mental


    6.1kWp south facing, South of Cork City



  • Registered Users, Registered Users 2 Posts: 798 ✭✭✭feelings


    Yep. Not including hot water and regular electricity.

    The guys who installed it are useless. So I'm trying to figure this out myself.



  • Registered Users, Registered Users 2 Posts: 61,079 ✭✭✭✭unkel


    Tbh, sounds like your install sizing was just about perfect. It was exceptionally cold yesterday, the country hits -10C maybe only once in a decade. Sizing your system for an outlier cold day would make it less efficient the rest of the time.

    19.5C is still comfortable enough imho. If that is not enough, buy a couple of €10 fan heaters in power city for the next time it gets this cold, maybe sometime between 2030 and 2040 😂

    "Make no mistake. The days of the internal combustion engine are definitely numbered" - Quentin Willson, 1997



  • Advertisement
  • Moderators, Home & Garden Moderators Posts: 7,734 Mod ✭✭✭✭graememk


    120kWh, in a day, thats a consistent 5kW for 24 hrs. What size heatpump do you have and what make? Just making sure everything is good, where you measuring the 120kWh of use?