Heat Pump Running Costs

1121315171825

Comments

  • Registered Users, Registered Users 2 Posts: 901 ✭✭✭ColemanY2K


    I suspect I did it slightly differently with my 2100 sq ft new build bungalow. 0.5ACH is passive standard and when designing my house I used the PHPP tool. It's about €200 and really is very helpful in working out heat losses etc and how to achieve passive standard.

    The PHPP estimated in the region of 4kW heat loss. I was thinking a 6kW HP would be sufficient but was convinced by the plumber to go with a 8kW. It was commissioned in December but it wasn't until the end of January when the insulation between the joists had been completed. In the cold spell in February it performed well and same can be said since. In the bitterly coldest days it used 15 to 20kWh in a 24 hour period. This however was a time when the insulation above the ceiling was largely missing. I reckon next winter it won't use more than 15kWh in a 24hr period.

    At the moment it hasn't come on to heat the house in weeks, just comes on to top up the tank. It's currently using less than 4kWh per 24hr period.

    🌞 7.79kWp PV System. Comprised of 4.92kWp Tilting Ground Mount + 2.87kWp @ 27°, azimuth 180°, West Waterford 🌞



  • Registered Users, Registered Users 2 Posts: 3,942 ✭✭✭John.G


    I would be very careful choosing the correct sized unit, most manufacturers specify the output based on air to water temperatures of 7C/35C, but may not tell you that the performance then falls off at reducing air temps and/or with increasing water temperatures, Grant seem to sell a Aerona unit?, I looked at their site but it only gives the performance at this 7C/35C, Kingspan published figures below for Aero-Max units as well which gives some idea of the fall off in performance. I think the Aeronas have variable speed operation down to 50% whatever this means in minimum output at the various air/water temperatures.

    You have a estimated heat loss of 4.8kw, don't know if this is based on a standard OT temperature of say -5C or what but you may require a 8KW unit to give this output at -5C/45C.

    image.png


  • Moderators, Home & Garden Moderators Posts: 7,734 Mod ✭✭✭✭graememk


    Ecoforest also have graphs for performance and cop in the datasheets

    Screenshot_20240527-171443.png


  • Registered Users, Registered Users 2 Posts: 21,991 ✭✭✭✭Water John


    Daikin have an 8kw split unit



  • Registered Users, Registered Users 2 Posts: 483 ✭✭andyd12


    Heat loss calculation is based on -3 degree outside temp.

    Average indoor temp. of 21 degrees.

    Ground temp. of 9 degrees.

    0.5 air changes per hour.



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 3,287 ✭✭✭dominatinMC


    Given the current cold spell, I thought I'd resurrect this thread to get an idea of how HPs are performing. Just checked mine and consumed 25 kWh yesterday. House is 245m2 and rooms set to 21.5, with bedrooms at 19. All in all, probably not too bad.



  • Registered Users, Registered Users 2 Posts: 1,391 ✭✭✭Exiled Rebel


    I've removed the zones. Open loop system. 22/23 degrees throughout. The Mrs asked me to turn it down to 21 degrees last night so today onwards may show slightly lower numbers.

    34kWh yesterday, which is very high. Probably the highest ever daily recording by Shelly -shouldn't be a surprise given the fact it was only ever up at 22/23 degrees for the past 4 days or so - it's usually set to 21).

    From midnight to 7am this morning 6.5kWh was drawn by the HP from the grid. At that rate I'd expect to see the HP needing somewhere around 21kWh today so that could be an early indication the changes made last night are having an impact on consumption..



  • Registered Users, Registered Users 2 Posts: 863 ✭✭✭staples7


    I removed the zones also, averaging 10kwh daily in December. To be fair it was mild. House fairly constant 20'. Avg 2kwh for hot water (Dec total Heating 283.6, hot water 53.9) House size 2800sft. (House is in use all day every day with young kids) A1 rating officially thanks to solar (Realistically perhaps A3/A2). Windows are not triple glazed and theres lots of them.

    Just to add that all of the heating is on night rate @12c. my 6th year doing this and find results really good in terms of efficiency/cost. All done via timer logic on the Heat Pump app. eg if the temp is below 20/21 @ 1am heating kicks in. if by 4/5am it hasn't reached desired temp it keeps going until 7/8am.

    Slight adjustment needed in very cold weather but again all v easy by the app (On minus nights the daily figure could go up tp 20KWH). I do push the hot water to be fully heated by the time day rate kicks in. and after that it calls for it as it needs. Because hot water is so little of overall this probably makes very little difference.

    For the year 2024 (Heating = 1669KWH / Hot water = 649.5KWH). Obviously heating is off from April to Oct as the house would exceed 20' by itself.

    Above figures are very consistent yearly eg 2023 (Heating 1672KWH / Hot water =731KWH)

    All in all the yearly bill for hot water and heating is circa Eur 300.



  • Registered Users, Registered Users 2 Posts: 22,382 ✭✭✭✭Cyrus


    32.5kwh for us yesterday, 2,100 sq feet A3 rated, UFH downstairs and Rads two upper floors, downstairs 21, upstairs 19.5 (with small windows to increase the temp to get towel rails warm in the morning). As we are on a 12c night rate i push downstairs to 22 overnight and set it back to 21 at 8am so we end us using more units overnight (so 15.68 units between 12 and 8 am incl DHW (and from 11pm to 12am on the hour of night rate at the other end) and 17 units for the other 15 hours of the day!)

    open loop downstairs.



  • Registered Users, Registered Users 2 Posts: 1,746 ✭✭✭THE ALM


    Consumed 21.4kWh yesterday for both heating and hot water. Total for December was 345kWh.

    165m2 retrofit, single storey, radiators throughout and runs purely on weather compensation. We maintain a set temp of 19°

    The solar pv these last couples of days is great so running costs are low, I expect if we get the snow forecast the costs are going to increase some what.



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 3,287 ✭✭✭dominatinMC


    That's good going! I must experiment with the open loop/no zones approach in the future



  • Registered Users, Registered Users 2 Posts: 2,925 ✭✭✭ECO_Mental


    Moved to Bord Gais EV rate in October so my new strategy is to move as much as possible my HP consumption to the EV rate between 2-5am where the unit rate is 6.33cent. I can move the the DHW easy enough so set a schedule on the HP to only heat at 2am but I do boost it in the middle of the day for an hour where hopfully I would have excess PV and at least it will be warmer so efficeincy will be at its best.

    My heating strategy is to pump as much heat into the house between 3-5am by artifially setting the stat temps high (22-23degs) over all the house so all the loops are open. I am lucky in that I do have a very well insulated house with underfloor upstairs and downstairs so I can get great thermal mass. This thermal mass lasts me well into the evening on most days. I then have the heating coming back on at 7pm (after peak rates) but this time I split the zones into two, upstairs and downstairs. Heat downstairs first then upstairs later. I only have it coming on for about 2.5 hours at most and I have the temps set to thier ideal temp of 20degs so it might not come on at all if it mild.

    My aim is cost reduction which probably will not mean energy reduction as I am artifically pumping more heat at night to get thermal mass up, but at 6.33cent per kWh its for nothing practially so why not.

    Is it working…I think so, these graphs show my daily cost is not as volitile or as high compared to last winter and my cost per kWh for my heatpump has drastically reduced (second graph below) but the next week will tell a lot as to be honest we have not have an decent cold spell yet this winter

    image.png image.png

    Finally I did some regression analyis on my heating consumption based on Heating Degree days only (65% confidance so not great corelation) and comparing to 2023 and I am well below 2023 (but mostly this due to mild weather) and below predicted based on moving 28 day (long average but smooths out the curves)

    will post more data after the cold spell😎

    image.png

    6.1kWp south facing, South of Cork City



  • Registered Users, Registered Users 2 Posts: 22,382 ✭✭✭✭Cyrus


    where are you pulling the graphs from? id like to do something similar in home assistant but seems more complicated than it should be!



  • Registered Users, Registered Users 2 Posts: 2,925 ✭✭✭ECO_Mental


    All those graphs are the auld excel…I download the data from Grafana on HA and just update one or two spreadsheets to do more complex graphing and analyis.

    I do have energy trend graphs on Grafana on HA but unfortunetly back in November my SD card in my Pi4 failed resulting in me loosing about 12 days consumption data 😫😪😪 as also my daily backup to onedrive failed 12 days before my SD card failed and I didnt notice until too late. So as a result 3 years of flawless data is messed up a bit. My totals are ok just shows a **** spike where it caught back up in the consumption data. Still I use excel for any thing complex

    image.png

    6.1kWp south facing, South of Cork City



  • Registered Users, Registered Users 2 Posts: 404 ✭✭NedNew2


    I averaged 17 kWh/day for the heat pump in December (235m2 house). I use a single zone with a set temperature of 18 degrees (lucky to have a wife who thinks the body should naturally adapt to seasonal temperatures) and have a combination of underfloor heating and radiators. Heating, including water, was predominantly done in the 2-5 a.m. window with one or two minor top-ups during colder weather. This was all working well until the proper cold weather arrived yesterday 😉.



  • Registered Users, Registered Users 2 Posts: 22,382 ✭✭✭✭Cyrus


    its frustrating that HA cant recover info thats in the shelly DB for sure !



  • Registered Users, Registered Users 2 Posts: 955 ✭✭✭keno-daytrader


    210sqm house A1. We averaged 6kWh per day for Dec (used 185kwh heat and 51 kWh hot water).

    In this cold spell we are using 10-11 kWh per day on cheap night and EV rate. Open loop 2 floors ufh set at 21.5 downstairs and 19 upstairs.

    ☀️ 8.2kWp ⚡4kWp south, ⚡4.20kWp west



  • Registered Users, Registered Users 2 Posts: 3,456 ✭✭✭newhouse87


    Essentially you are heating 105sqm? I doubt upstairs set at 19 comes on much?



  • Registered Users, Registered Users 2 Posts: 955 ✭✭✭keno-daytrader


    For Dec the upstairs zone didnt come on that much, but in this cold spell, its been on the whole night. I run the HP from 11pm to 8am.

    ☀️ 8.2kWp ⚡4kWp south, ⚡4.20kWp west



  • Registered Users, Registered Users 2 Posts: 3,456 ✭✭✭newhouse87


    The joys of 2 stories. Yeah I run 11pm to 1pm in this cold spell, mostly nigh rate like yourself but heating 242 sqm bungalow more or less double amount of your usage. Still had no bill for December with govt credit so I'm happy with the heating these days compared to first winter in house with less then optimal setup of heating system.



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 955 ✭✭✭keno-daytrader


    Im also delighted after learning about heat pumps. Our first winter was awful they way the installer left it, basically just left on dumb mode so they dont have to come back, it ate electricity, shockingly inefficient.

    Now it runs like a dream.

    ☀️ 8.2kWp ⚡4kWp south, ⚡4.20kWp west



  • Registered Users, Registered Users 2 Posts: 1,391 ✭✭✭Exiled Rebel


    193m2 A1 rated bungalow. We averaged 10kWh per day in December.

    Currently averaging 20kWh over the full 5 days of January.

    On my current tariff heating and hot water would have cost circa. €400 in 2024. The solar FIT credit from the summer wipes that completely out.



  • Registered Users, Registered Users 2 Posts: 798 ✭✭✭feelings


    i'm going to cry reading these. A2 rated 220sqm and we average 20-30kWh for Dec and for 2 days over the last week hit approx 100Kwh each day. Temps are set at downstairs 20 and upstairs 19.

    The crowd that sold the system is absolutely useless - telling me that our energy consumption is normal. I've rang around and no one else seems to know of the system (french crowd). Is there anyone who would come out to fine tune the system for us?



  • Registered Users, Registered Users 2 Posts: 483 ✭✭andyd12


    Who are they?

    What flow temperature are you running?

    Open/closed loop etc?



  • Registered Users, Registered Users 2, Paid Member Posts: 3,349 ✭✭✭hold my beer


    How are you all getting the usage info? I've a Samsung Heat Pump. Can you get info from the units?



  • Registered Users, Registered Users 2 Posts: 3,287 ✭✭✭dominatinMC


    I've an Ecodan and you can get some info. such as electricity consumption, heat delivered (space vs. DWH), etc. from the control panel on the inside unit. I'd imagine it's similar with other types of HP



  • Registered Users, Registered Users 2 Posts: 3,287 ✭✭✭dominatinMC


    That is unreal, fair play for fine tuning your system to get that sort of performance. Can you explain the open loop concept please?



  • Registered Users, Registered Users 2 Posts: 955 ✭✭✭keno-daytrader


    I experimented with all sorts of technics at the start because our heat pump was consuming huge amounts of electricity.

    We have a Mitsubishi Ecodan.

    The installer had set it on auto adapt which really is meant for radiators, we have underfloor heating. The flow temps to the underfloor were in mid 40s and was running like an oil boiler, on for an hour then off, rinse and repeat, insanity really for a heat pump. I suspect this is the case for most heat pump homes in Ireland without fine tuning.

    Once we embraced the idea of low and slow, meaning leave on for long long periods of time on a low flow temp, for the entire house, our usage plummeted.

    In the end I found that using as few zones as possible, so for us zone 1 downstairs, zone 2 upstairs.

    Heat all rooms even if not used.

    Use a fixed flow temp of 26-30C.

    All underfloor loops in house are open.

    Obviously all houses, will have different levels of insulation and airtightness and many will not get away with such a low flow temp, but the concept will be the same for all heatpumps, low and slow with as little zones as possible, leave heat pump on even when not home. Some will find this impossible to grasp, but it works.

    ☀️ 8.2kWp ⚡4kWp south, ⚡4.20kWp west



  • Registered Users, Registered Users 2 Posts: 3,287 ✭✭✭dominatinMC


    Cheers, I think we might have discussed this approach before. I'm actually using a similar approach, albeit with slightly higher flow temps (~34 degC) to compensate for the fact I have rads and UFH on my ground floor (we put on an extension with UFH which explains the mix of heating components).

    I am finding my usage to be quite good, and favourable compared to some of my friends. Although given that it's averaging around 30kWh/day at the moment, it's not as good as yours! As you say though, it's hard to compare houses.

    When you say that all underfloor loops are open, what are you referring to? Have you manually opened them at the manifold or something? And what, in theory, is the benefit of this?

    Thanks again, appreciate your input here!



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 311 ✭✭on_the_roots


    100kwh/day is absolutely insane, even eventually. Are you sure you measured it correctly?

    Do you charge an EV with big batteries by any chance?



Advertisement