  • Registered Users, Registered Users 2 Posts: 2,413 ✭✭✭KrisW1001


    There's only marginal advantage, for a very high cost, in replacing a 1500 V DC system with 3000 V. It won't happen.

    The only realistic alternative was to switch DART to 25 kV AC to match what will most likely eventually be used on the longer distance network, but even that poses insurmountable problems. The first problem is that it makes the DART trains slightly heavier and slightly more expensive. Plus you have the cost of replacing the current OHLE. The bigger issue would be operational, though: you'd have to completely close the DART lines to do that voltage change, and because existing DART stock can't use AC, it immediately becomes obsolete, reducing your capacity and resilience overnight.

    Basically, 1500 V has the advantage of incumbency, so as the electric local network expands, it will use that voltage. Higher voltage is still better for long distance use, but that doesn't prevent inter-city trains running on 1500 V lines: these trains are all available in dual-system versions that allows them to operate on 25 kV or 1500 V: we're not the only country to have different line voltages; actually, having all lines in a county on the same electrification system is the exception, not the rule.

    DC lines over 3000 V are a very new development (the electronics needed to efficiently produce DC at this voltage did not exist until the 1980s). They might be an option here, especially as mainline electrification isn't happening soon, but again, operational concerns are against such a choice.

    That's because we would still need to interoperate with NIR, which is likely to follow UK practice and use 25 kV AC. If we decided to use HVDC, say 11 kV, for long distance services, then Connolly-Belfast trains would end up being "special" again as they'd need to support three voltages: 1500 VDC, 11kV DC and 25 kV AC. In pure technical terms this is not an issue, but we're only now getting away from the need to have special stock for Belfast (when both sides adopt ETCS): it'd be a shame to have to go back to that situation.



  • Moderators, Motoring & Transport Moderators, Technology & Internet Moderators Posts: 23,624 Mod ✭✭✭✭bk


    yes we are sticking to 1500 VDC for the dart network, both existing and expanded. While the plan for future intercity is 25 kV AC.

    The new DART trains are only specified for 1500 DC (+battery), while the tender for the new Enterprise fleet to Belfast is spec’d for dual voltage 1500 DC/25kV AC (+ diesel generator until the 25kV AC is rolled out).

    An eventual new Cork fleet is likely to look the same as the Belfast one.



  • Registered Users, Registered Users 2 Posts: 4,366 ✭✭✭goingnowhere


    I'd imagine the Cork fleet will basically be the Belfast fleet with a different seat mix, unclear if the contract includes a broad framework order option to save hassle with tendering again, assuming the fleet works out.



  • Registered Users, Registered Users 2 Posts: 274 ✭✭PlatformNine


    I think the enterprise fleet is supposed to be initially 1.5kV DC + battery + diesel, with a 25kV AC being installed and the diesel engines being removed after the rollout of 25kV OHLE? That's at least what the tender I have downloaded says, though reading it through it seems it initially only requires it to be battery diesel hybrid, the 1.5kV DC is wanted, but not required. Though that tender might have been updated, or I might also be looking at the wrong tender.

    I hope they pick 25kV AC for CACR electrification. I can't say I understand the differences even after reading everything posted here, but it at least sounds like for new systems it makes more sense to start from scratch with 25kV AC? Especially if it can allow some standardisation between commuter and IC units.

    The requirements are very different though aren't they? Could an AC variant of the D+ sets work better? At least then they would be designed for commuter service, and it couldn't hurt to have better standardisation between the different commuter fleets. And if they don't need all 150 sets from the D+ framework for the future DART services, could it be possible to order 20-30 sets under the existing framework modified for CACR services? Other than the 25kV AC and maybe a new livery, would they need any other modifications?



  • Registered Users, Registered Users 2 Posts: 2,413 ✭✭✭KrisW1001


    Standardisation between commuter and IC trains isn’t that desirable, as they have very different patterns of use. It's much better to standardise equipment based on role: i.e., have one type of intercity EMU and one type of commuter EMU per generation. That way, stock can be added or moved from place to place easily.

    It would be better for CACR to be 1.5 kV DC, as that would allow for common commuter stock (the Alstom X'Trapolis DART trains at 1500 V DC) everywhere in the country. Basically, your suggestion of using extra framework purchases, but without the need for modifications.

    DC is better suited to a railway that has trains stopping and starting regularly - note how nearly all of the world's metros run on DC, even those built in the late 20th century. The use of DC means that the trains are a little lighter, more space efficient, cheaper and less complex than if they were using AC (AC trains need transformers on board to reduce the line voltage down to something the traction motors can use). The disadvantage is that the lower voltage means that more substations are required for a given length of track, but this is an acceptable compromise on small-area networks - it also increases the resilience of the network, as a single substation fail won't black out a huge section of the network.

    Inter-city trains will be converted to dual-voltage once there's any electrified mainline for them to run on, but there are sections of track shared by intercity and commuter services: CACR includes the Mallow-Kent mainline, so that will need to be electrified too, and probably before the main Cork-Dublin line. Your choice is between making commuter trains dual voltage, or intercity trains dual voltage (ripping out the DC network and making the whole country AC is a non-starter), and the cost savings are in keeping the commuter trains as simple as possible - they do the most trips, and unlike intercity units, they don't cruise, so can't use momentum to compensate for higher weight.

    Incidentally, 1500 V DC trains operate at up to 250 km/h in France; in an Irish context, where we're targeting 200km/h and not aiming beyond 250 km/h ever, there's no speed penalty with using 1500 V DC. (Anything above 250km/h needs higher voltages, which until very recently has meant using AC).

    It may even make sense for all of the final approaches to stations to be electrified at 1500 V DC, as that would allow any of the tracks to be used by both “DART” and Inter-city stock.



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 92 ✭✭A1ACo


    The IE electrification report i mentioned re DART Expansion rail electrification assessment of 08/04/2019 can be found here:

    Annex-5-1-DART-Expansion-Rail-Electrification-Assessment.pdf

    and above noted a - 2011 - 'GDA rail electrification network study' for 1.5kv DC for DART network expansion.

    Also, i didnt quite remember correctly from above, but from a post I made last year under the 'Railway Electrification' thread was this for comparison to the DART:

    'Belgian electrical current for its 3kv DC system, is 2500 amperes (Amp.), so its maximum electrical power available to trains is 7.5MW.

    The Italian electrical current for its 3kv DC system, is 4000 amperes (Amp.), so its maximum electrical power available to trains is a higher 12MW.

    It was also stated, that the Netherlands electrical current for its 1.5kv DC system, is 4000 amperes (Amp.), so its maximum electrical power to its trains is 6MW (half the Italian power).

    Does anyone know for comparison, what Irish Rail’s electrical current for its 1.5kv DC system, is in amperes (Amp.), and its maximum electrical power to trains?'



  • Registered Users, Registered Users 2 Posts: 434 ✭✭Ireland trains


    I think goingnowhere was referring to Cork’s intercity fleet, not commuter.

    With regards to enterprise traction, “The next generation Enterprise trains were initially described as tri-modes, but Railway Gazette International understands that they will primarily be electro-diesel multiple-units, fitted with small traction batteries to reduce emissions at stations and depots. The trains will remain largely dependent on their diesel powerpacks in the early years, pending a firm decision on how or whether to electrify more of the route between the two cities.”

    https://www.railwaygazette.com/passenger/dublin-belfast-boost-in-irish-timetable-recast/66799.article



  • Moderators, Motoring & Transport Moderators, Technology & Internet Moderators Posts: 23,624 Mod ✭✭✭✭bk


    You are correct, at least according to the tender description, it says:

    Initial traction power will be Internal Combustion Engine (ICE) Battery Electric (using the existing 1.5 kV DC OHLE) with the train designed to transition to a net zero carbon operation during its life by the removal of the diesel power generation for replacement with dual OHLE power supply equipment.

    So initially it will be Diesel generator + battery + 1.5 kV DC OHLE, with in future the Diesel generator being removed so Battery + 25kV AC + 1.5kV DC

    The market consultation document specifically mentions that NI Railways are planning to install 25kV AC from Belfast to the border.

    I suppose that could allow IR the option of either continuing 1.5kV DC from Drogheda to the border or also switch to 25kV AC from Drogheda to the border. But either way it would end up Dual voltage.

    On the battery, I'd assume it will have relatively smaller batteries then the DART BEMU's. More a hybrid type battery setup, focused on enough size to take advantage of regenerative braking and allow the Diesel generators to run at a more efficient level. Maybe allow them to idle on battery while in stations and perhaps even run on battery on the approaches to stations at lower speeds. Would help cut down emissions on and near stations.



  • Registered Users, Registered Users 2 Posts: 72,751 ✭✭✭✭L1011


    Going to be interesting to see what speed (if any) they can change from OHLE <> diesel at. Putting pantographs up at speed isn't the safest thing to do.



  • Moderators, Motoring & Transport Moderators, Technology & Internet Moderators Posts: 23,624 Mod ✭✭✭✭bk


    Doesn't the Enterprise normally stop at Drogheda anyway? Do it when stopped at the station.



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 72,751 ✭✭✭✭L1011


    Yes, but if delivered before OHLE reaches Drogheda, the transition would be Malahide.

    Not sure there's as many entitled lawyers to throw JRs in against DART+ North, but nothing can be trusted here.



  • Moderators, Motoring & Transport Moderators, Technology & Internet Moderators Posts: 23,624 Mod ✭✭✭✭bk


    From Malahide they would likely be operating at slower speed anyway. I'm sort of assuming that if you can't get electrification through planning, you are even less likely to get quad tracking of the northern line, so they will be stuck behind DART's anyway.

    Or if electrification isn't extended to Drogheda, they don't even bother with 1.5kW DC at Malahide given the relatively short distance. Just operate on Diesel + Battery to Connolly. Might be a nice way to embarrass the government into getting electrification done.



  • Registered Users, Registered Users 2 Posts: 7,351 ✭✭✭Pete_Cavan


    If BEMUs are doing the job between Malahide and Drogheda, why would you go to the cost of electrifying at 1.5kV DC? Surely it'd be better just going with 25kV AC and doing Malahide - Belfast in one go.



  • Moderators, Motoring & Transport Moderators, Technology & Internet Moderators Posts: 23,624 Mod ✭✭✭✭bk


    I believe operating BEMU's in the long run is more expensive then electrifying. The engineering options report mentions having to replace the batteries every 9 years, and remember you have to do that on both the trains and the BESS in Drogheda. Cost probably adds up over time.

    Plus you are limited in the number of BEMU's you can operate out of Drogheda. I'm not 100% which option they went with, but I think it is just 3 trains per hour out of Drogheda. With electrification they are planning 5 trains per hour.



  • Registered Users, Registered Users 2 Posts: 7,351 ✭✭✭Pete_Cavan


    I was thinking that services north of Malahide would be operated using 25kV AC stock. It is probably more appropriate for that type of outer commuter service. The logic behind using 1.5kV DC is allowing for DARTification but doing that with BEMUs probably negate much of that logic now.

    Regarding electrifying being cheaper in the long run, would that also apply to 1.5kV DC over such a distance? The batteries would take us well into the 2030s, really should be electrifying all Malahide - Belfast in one go at that stage.



  • Registered Users, Registered Users 2 Posts: 2,204 ✭✭✭Economics101


    You fear that "if they can't get electrification through planning", is I hope unwarranted. It speaks volumes about the planning czars that there should be any possibility of electrification being blocked. We would be the laughing stock of Europe.



  • Moderators, Motoring & Transport Moderators, Technology & Internet Moderators Posts: 23,624 Mod ✭✭✭✭bk


    The Railway Order submitted for DART+ Coastal North is for Malahide to Drogheda to use 1.5kV DC. The RO hasn't been approved yet, but assuming ABP do, then it is pretty much set in stone.

    It is just 37km, it really isn't a particularly long distance. The batteries taking us to 2030 isn't the point, it is the cost of the batteries over the next 40 years or more. Replacing the batteries 4 or 5 times over a 40 to 50 year lifetime of the train versus electrification.

    You also have the consider the 3 BEMU's versus 5 EMU's from Drogheda, that isn't a small matter. The options report looked at options from 5 or 6 BEMU's from Drogheda, but apparently that involved a big increase in cost as it would require building extra sidings/platforms to hold trains for recharging. So you have to balance that big cost (+ batteries over 40 years) against the electrification.

    Also DC tends to be better for DART type services, it is less complicated and allows for lighter trains.

    BTW The options reported goes into the cost of different options, but all the info is redacted as it was a Freedom of Information request. However the impression I get is that electrification is a serious money saver in the long term.

    Yeah, I doubt there would be any issues with electrification. But that was sort of my point if something relatively easy like electrification doesn't get approved, then no hope for quad tracking as that will be more controversial. The overall point being I assume Drogheda will be electrified and that the Enterprise replacements will switch over while stopped at Drogheda.

    BTW the electrification part of the DART+ West got approved by ABP without any notable issues. Just the depot that was the major issue and junction closures. I don't see electrification being a big deal on the Northern line, it should be relatively straight forward.



  • Registered Users, Registered Users 2 Posts: 14,097 ✭✭✭✭Zebra3




  • Registered Users, Registered Users 2 Posts: 7,351 ✭✭✭Pete_Cavan


    The RO is one thing but it remains to be seen if that actually happens. The BEMUs make it very easy for the government to put that part of DART+ Coastal North on the long finger (other aspects of it have to happen to facilitate increase in services).

    I didn't say anything about not electrifying the line so not sure why you are talking about the cost of the batteries over the next 40 years. My point is that electrification doesn't necessarily have to be to 1.5kV DC. If going with that, probably best to continue it all the way to Belfast and not needing Enterprise trains compatible with 25kV AC.



  • Registered Users, Registered Users 2 Posts: 24,743 ✭✭✭✭lawred2


    Other than waffle and costly consultant's reports, is there anything in train right now with Irish rail?

    I don't mean timetables, new carriages or signalling. But something that will actually increase capacity and improve punctuality in Dublin?



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 15,586 ✭✭✭✭loyatemu


    new carriages and signalling will increase capacity. The carriages have started arriving and the signalling has been installed on the existing Dart line.

    Punctuality should (in theory) improve with the new signalling but it'll still be Irish Rail running the system and I don't have much confidence in them. I got the Dart yesterday and the morning train was 10 minutes late and the evening train 15 minutes late. This is after they rolled back their timetable changes to "improve punctuality". Meanwhile on the northside some people were trapped on stationary trains for up to an hour due to a signalling failure.



  • Registered Users, Registered Users 2 Posts: 24,743 ✭✭✭✭lawred2


    I was one of them for a time but was one of the fortunate ones to be able to jump onto a bus.

    All I can see over the last decade as a daily user is a continual disimprovement on almost all fronts.



  • Registered Users, Registered Users 2 Posts: 2,413 ✭✭✭KrisW1001


    Why would we try to force NIR to install any 1500 V DC systems? There are no 1500 V mainlines at all in the UK (Tyne and Wear Metro is the only railway of any kind to use it), and NIR has always relied heavily on engineering guidance from other UK operators.

    The decision to use 1.5kV DC in the Republic is because we have a significant investment in 1500 V rail that we would lose completely if we changed. From. NIR's point of view, deliberately starting a two system network is stupid.

    Also, using 1500V means building a substation every 6-8 km. That's acceptable in a populated area where you've got towns (and stations) at the same kind of distances from each other, but it's not true north of Drogheda. For 25 kV the spacing is over 30 km, which is much more suited to a railway through a more rural area.



  • Moderators, Motoring & Transport Moderators, Technology & Internet Moderators Posts: 23,624 Mod ✭✭✭✭bk


    The new DART trains are specified and built to run on 1.5kV DC, they aren’t dual voltage, unlike the upcoming Enterprise fleet.

    So if Malahide to Drogheda was 25kV AC, then our DART’s couldn’t run on the OHLE, they would need to use the batteries for the lifetime of the trains, 40+ years.

    I suppose you think you could retrofit dual voltage on the DART fleet, but that would be extremely costly to do and would add unwanted weight and complexity to the DART fleet.

    Every 10 minutes you’d have DART’s switching pantographs at Malahide, a complete nightmare scenario for reliability.

    No, this really doesn’t make any logical or economic sense. 1.5kV DC to Drogheda makes sense, it allows us to keep the DART fleet simple and reliable, just regular single voltage operation like we have already been doing for the past 40 years. While Drogheda is the perfect location for the Enterprise to switch between 25kV AC and 1.5kV DC as it stops there anyway.

    Keep in mind the DART fleet is much larger then the intercity fleet and also much more important. Reliability is key for commuter services.

    I literally can’t think of a single benefit of doing 25kV from Malahide:

    • Need to retrofit dual voltage onto the new DART fleet at massive cost (or continue to use batteries for the lifetime of the train).
    • Enterprise now need to stop at Malahide to switch pantographs and voltage, an extra unneeded stop
    • DART now also need to do complicated voltage switch over at Malahide every 10 minutes!

    And your comment about the government long fingering Drogheda electrification makes no sense, why would they long finger that, only to turn away and then approve 25kV to Malahide instead, that doesn’t make logical sense.



  • Registered Users, Registered Users 2 Posts: 2,204 ✭✭✭Economics101


    Even if we wanted to, we could not "force" NI to install 1500V DC. They have decided in peinciple to go 25kv AC, when the oppostunity arises. The real question is will the DC-AC changeover be at Drogheda or Dundalk (i.e the border). AFAIK, you can change from one system to the other while on the move, as elsewhere in Europe.



  • Registered Users, Registered Users 2 Posts: 2,413 ✭✭✭KrisW1001


    I can't see it anywhere but Drogheda. There's no point in extending a 1500 V DC network through such a sparsely-populated part of the country. Between Drogheda and Malahide you have Bettystown/Laytown (population 15,000), Balbriggian (24,000), Skerries (10,000) and Donabate (10,000). Between Drogheda and Dundalk there's only Dunleer (population 2,000).

    1500 V DC is expensive over long distance; that extra cost only pays off when you've got a lot of traffic on the line: the section north of Drogheda is unlikely to every see more than 3 trains (total) an hour.

    Changing from system to system while on the move is possible, but it's always preferable to do it at lower speeds.

    There's an interesting, but off-topic here, question about what happens to the "fast" lines on the quad-track section into Dublin: they could be electrified at 25 kV as they'd be limited to long-distance use, but I can't help thinking that making them 1500 V too would provide a lot more operational flexibility to IÉ: basically, if all approach lines are 1500 V, then any EMU can use any stretch of track within the GDA - and you can't end up stranding a DART train due to a points error.



  • Registered Users, Registered Users 2 Posts: 1,130 ✭✭✭riddlinrussell


    The only possible aspect that would 'force' 1500v on NI is if they wanted to electrify their own commuter lines and wanted to go DC, they 'might' choose 1500v so they could borrow DART stock for flexibility and the intercity could use 1500v as specced.

    Drogheda is the logical switchover point, nowhere else makes a lick of sense



  • Registered Users, Registered Users 2 Posts: 7,351 ✭✭✭Pete_Cavan


    But if going with 1.5kV DC from Malahide to Drogheda, why not do the same for Drogheda to the border which is much the same distance? My point is that they are accepting the substations requirement to Drogheda, why not accept it beyond?

    We wouldn't be "forcing" NIR to do anything but it would make sense for them to coordinate with us as the networks are connected (ideally planned and operated as a single network, like the electricity grid). What is done on a separate network in Britain is irrelevant.

    There are stopping services from Newry to Belfast so 1.5kV DC is most appropriate there. If going with 1.5kV DC between Dublin and Drogheda, the only place 25kv AC really makes sense is between Drogheda and Newry. Given the relatively short distances involved, one voltage makes sense. It would simplify the Enterprise new stock if the plan if the dual voltage requirement was removed.



  • Registered Users, Registered Users 2 Posts: 7,351 ✭✭✭Pete_Cavan


    See my reply above. My point is the Dublin - Belfast line should be considered and either do the whole lot in one voltage or maximise the distance of 25kV AC. Going with 1.5kV DC for one third and 25kV AC for two thirds doesn’t make much sense, particularly as 1.5kV DC is more appropriate for much of the 25kV AC section.



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 2,413 ✭✭✭KrisW1001


    It's not distance, it's population: number of paying customers served per substation is the measure that matters. I listed the intermediate stops up to Drogheda, and the one after it.

    Nothing in NI will be 1.5kV DC. It's completely against NIR's long-term electrification plans, and against UK rail electrification practice in general. There's no problem running commuter rail on AC: most German S-Bahn services (all but Hamburg and Berlin’s hybrid Metro/S-Bahns) are on the same AC system as the national rail.

    Again, we are only expanding our 1500 DC system because we've a large investment that we would otherwise lose completely (why we made that investment rather than choosing 25kV AC is an interesting discussion, but there were good reasons). If starting from scratch, as NIR is, there isn't that much an advantage.