Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Hi all! We have been experiencing an issue on site where threads have been missing the latest postings. The platform host Vanilla are working on this issue. A workaround that has been used by some is to navigate back from 1 to 10+ pages to re-sync the thread and this will then show the latest posts. Thanks, Mike.
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

Eddi not heating water long - config required?

  • 02-04-2022 5:24pm
    #1
    Registered Users Posts: 46


    Hi

    I have a good PV system installed along with 6Kw Inverter and 5kWH battery. Any excess power is passed to the eddi where it heats the immersion. One thing I notice is the eddi doesn’t stay on long before the “Max Temp Reached” appears on its screen. We do get piping hot water after it’s been on but we’re still supplementing with the boiler. It doesn’t seem like we would get a full tank of hot water from eddi alone.


    I’ve checked the setting on the immersion rod and it’s set to max and is a 36 inch rod. We’re exporting up on 20kwH per day in the last week so I wanted to double check there isn’t something else I should be doing to ensure the eddi could be staying on any longer which would allow us to turn the boiler off.


    Is there any additional config I need to check on the eddi?


    thanks!



«1

Comments

  • Registered Users, Registered Users 2 Posts: 2,894 ✭✭✭Nolars


    Recently got eddi installed but on the boost options it's showing two options?



  • Registered Users Posts: 6,181 ✭✭✭championc




  • Registered Users, Registered Users 2 Posts: 2,894 ✭✭✭Nolars


    How come the boost 2 is on when excess is going to the water? I just assumed it would be boost 1? I must look more into it I'm not familiar with it yet



  • Registered Users Posts: 6,181 ✭✭✭championc


    You'll need to post screenshots, because I've no idea as to what you are referring to



  • Moderators, Education Moderators, Home & Garden Moderators Posts: 8,216 Mod ✭✭✭✭Jonathan


    Is it a dual element immersion? Are you heating the sink element rather than the bath element? They usually share a single thermostat, which would cut out but with only top of tank hot.



  • Advertisement
  • Registered Users Posts: 46 irewestlad


    Hey @Jonathan


    Im not sure if it’s dual - I presume it is as it’s a relatively new tank.

    how would I check if it’s sink or bath?



  • Registered Users Posts: 189 ✭✭connesha


    Check the load the eddi is sending.

    Normally the sink is 2kw and the bath is 3kw



  • Registered Users Posts: 46 irewestlad


    Hey @connesha

    good point, I’ve never seen the load going to 3kw. How would I change it over so that it’s heating the bath element?



  • Registered Users, Registered Users 2 Posts: 16,322 ✭✭✭✭Ha Long Bay


    Do you have the myenergi app setup? You can set the priority there for tank 1 and tank 2. I'm sure that is easy to set on the unit itself as well.



  • Registered Users Posts: 189 ✭✭connesha


    Use boost to determine, rather than waiting for excess.

    When tank is not boiling, boost heater1 for a few mins, see what’s being sent.

    Then boost heater 2.

    if one is 2kw and other is 3kw, then set the 3kw one as the priority. This will avoid wiring change.



  • Advertisement
  • Registered Users Posts: 46 irewestlad


    @Ha Long Bay , no don’t have the hub (but I hear the new zappi will have it integrated - anyone hear anything about that?)

    i changed the priority this morning between Heater 1 and Heater 2 on the eddi itself. @connesha I’ll try that boost trick and see what results I get, cheers



  • Moderators, Science, Health & Environment Moderators Posts: 4,726 Mod ✭✭✭✭Tree


    It depends on what it's connected to, for a 2 element immersion (bath/sink), you probably have boost one connected to one and boost two connected to the other. If you've got immersion and some other component, then it'll correspond tot hat. Get on to your installer is probably your best bet



  • Moderators, Home & Garden Moderators Posts: 6,284 Mod ✭✭✭✭graememk


    And for 2 element immersion using the sink is pointless as priority, as the thermostat is tied to both.

    When the sink one gets too hot it will cut out both.



  • Administrators Posts: 392 Admin ✭✭✭✭✭System


    This discussion was created from comments split from: Solar PV Hints, Tips & Troubleshooting.


  • Moderators, Education Moderators, Home & Garden Moderators Posts: 8,216 Mod ✭✭✭✭Jonathan


    Merged these posts from Hints, Tips and Troubleshooting over.

    Will add an item to the FAQ later as same issue posted twice in 24 hours.



  • Registered Users, Registered Users 2 Posts: 7,822 ✭✭✭stimpson


    I don’t think this necessarily true. I have 2 separate elements for my immersion (300l factory insulated tank). I know that many of the older ones had a dual element with a single stat.

    My Eddi will heat the top one until the stat kicks in then it heats the bottom one until that stat kicks in. Then it tries the top one again and so on. Here’s yesterdays graphs:



    In the Eddi manual it says that you can install a De-stratification pump which will pump hot water from the top to the bottom of the tank and can be driven by one of the Eddi channels and will ensure the whole tank gets heated even if you only have a single element. See page 50 of the manual.

    https://myenergi.com/wp-content/uploads/2019/04/eddi_manual_v2.3_english.pdf



  • Registered Users Posts: 46 irewestlad


    Ok so tried the boost option from the eddi - Heater 1 drew 2kw but Heater 2 drew nothing (0kw). Does this suggest it’s not set up right or the second rod is gone in the immersion? I’ve attached a pic of the cap of the immersion which suggests Heater 2 should be 2.8kw.




  • Registered Users, Registered Users 2 Posts: 3,971 ✭✭✭mp3guy


    I have the same element. Is this something as simple as you already heating water with the boiler before the Eddi gets a chance to heat it during the day?



  • Registered Users Posts: 46 irewestlad


    @mp3guy, I don’t believe so, I turned off the water oil boiler time yesterday and the hot water ran out today after two showers. It was after the hot water ran out I tried the boost trial which I mentioned about in my last post so in theory I should have seen the full 2.8kw go to the immersion



  • Registered Users, Registered Users 2 Posts: 580 ✭✭✭idc


    Do you happen to still have a switch for bath/sink ? As I have a dual element the eddi is connected via original wiring with the bath/sink switch still in use!! Just leave on bath all the time (if I change tank I would get a better configuration of heating elements and thermostats)

    As heater 2 drew 0k can you check if it's even connected to anything!



  • Advertisement
  • Registered Users Posts: 46 irewestlad


    I don’t seem to have a bath/sink switch. I think I’ll need to get a sparks out to check the wiring for me. It would appear that Heat 2 isn’t connected at all!!?



  • Moderators, Home & Garden Moderators Posts: 6,284 Mod ✭✭✭✭graememk


    I was careful in my wording there, I specifically said the dual element immersion with a single stat, not dual immersions.

    Dual immersions are a completely different ball game. Perfect for that.



  • Registered Users, Registered Users 2 Posts: 7,822 ✭✭✭stimpson



    You actually said "2 element immersion" which is a little ambiguous.



  • Registered Users, Registered Users 2 Posts: 800 ✭✭✭niallers1


    I had this problem, Looks like the sink / bath switch might be wired the wrong way.

    When I press the switch to sink it heats the 2.8kw element and when I switch to bath it heats the 2kw element.



  • Registered Users, Registered Users 2 Posts: 2,568 ✭✭✭bullit_dodger


    If that's the case, no wiring required.....just change the "Priority" on the EDDI (I had the same problem).



  • Registered Users Posts: 46 irewestlad


    But my problem is that there is nothing being sent when I put on Heater 2 (Bath). It hasn’t been wired correctly. I have a sparks coming out soon to have a look at it. Thanks!



  • Registered Users Posts: 46 irewestlad


    Thanks for everyone's insights here, it turned out that the Sink immersion rod was wired up. It's been changed over to the bath rod and I'm enjoying a hot tank of water everyday now



  • Moderators Posts: 12,384 ✭✭✭✭Black_Knight


    Newbie questions here.

    I've an Eddie which appears to be tipping away at times (500-600W being consumed) and says "Max Temp Reached", yet i've no hot water. Tank 1 only shows activity. Tank 2 has no activity.

    1. How can I tell if i've a dual element immersion or not?
    2. What's the eddi doing with this power given i've no hot water?
    3. WTF is going on?

    Thanks all.



  • Moderators, Home & Garden Moderators Posts: 6,284 Mod ✭✭✭✭graememk


    What happens when you hit boost on the eddi? What power does it use?

    Max temp reached happens when the immersion cuts out



  • Advertisement
  • Moderators Posts: 12,384 ✭✭✭✭Black_Knight


    Nothing. No power is consumed. It looks as though it's going to boost, but then switches back to Max Temp Reached after a few seconds.

    I've been told it's a single immersion tank.

    So from my understanding, the immersion dictates when to turn off the zappi? But how? Isn't the immersion just a heating element that's either on or off? What sets the temperature?



  • Moderators, Home & Garden Moderators Posts: 6,284 Mod ✭✭✭✭graememk


    Have you ever used the immersion pre eddi?

    Is there a little red button on your immersion?

    If you dont see it, It is likely to be under the cover, (turn the eddi off)

    There is a overtemperature switch that can be triggered.

    Normally the thermostat in the immersion cuts out the immersion before it gets too hot, That extra thermal cutout is an extra layer of protection.

    If its popped out, you can push it in with something.

    If that doesnt work, the immersion could be busted.

    (if unsure, post photos and can work from there.)



  • Moderators Posts: 12,384 ✭✭✭✭Black_Knight


    Cool. Thanks for the detailed reply. It's a new tank and new immersion. I'll have a look shortly.

    Can I just set the Eddi to 0 to turn it off when I'm having a look at the immersion for the overtemperature switch?



  • Moderators, Home & Garden Moderators Posts: 6,284 Mod ✭✭✭✭graememk


    Yeah the button at the bottom of the eddi completely turns it off. I think its on/bypass/off. I think bypass just switches on the immersion. (Or even just flip the mcb for it, to be sure)

    Is there any other switches or anything between the eddi and the immersion?



  • Moderators, Sports Moderators Posts: 19,192 Mod ✭✭✭✭slave1


    There's a hollow tube alongside the heating element, inside this is a temp stat that dictates when max temp reached and the immersion will turn off.



  • Moderators Posts: 12,384 ✭✭✭✭Black_Knight


    That seems to have been it. Adjusted the immersion and boost boosted not a bother. Solar put a bit into it too afterwards. I'll keep an eye over the next day or so



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 347 ✭✭Liam2021


    Just wondering is there a way I can stop the eddie using solor power to heat the water. Currently on energia ev plan so it would be worth more to ne to export all the power generated during the day and not heat water



  • Registered Users, Registered Users 2 Posts: 6,981 ✭✭✭con747


    Just turn it off at the switch underneath it? Might be a way in the settings as well but not sure.

    Don't expect anything from life, just be grateful to be alive.



  • Moderators, Home & Garden Moderators Posts: 6,284 Mod ✭✭✭✭graememk




  • Registered Users, Registered Users 2 Posts: 2,568 ✭✭✭bullit_dodger


    All those good suggestions and will work fine, but easiest is just to use the "Stop" function as that's exactly what it's for.....(under "Settings")

    Then you can still have the timers set.



  • Registered Users, Registered Users 2 Posts: 347 ✭✭Liam2021


    Will this mode keep the schedules I have set for cheap tariff tines?



  • Advertisement
  • Moderators, Sports Moderators Posts: 19,192 Mod ✭✭✭✭slave1


    No, it's a total stop.

    Another alternative is to just stop on the App so then you can control from anywhere, if you change the export margin then you are tied to having to use the physical EDDI as this cannot be changed via the App.

    I'm in the exact same boat and just use the App in the morning to turn it off, if evening showers required I check the hot water temp and then can throw the EDDI back on for a while via the App until temps good enough



  • Moderators, Arts Moderators, Recreation & Hobbies Moderators Posts: 10,731 Mod ✭✭✭✭Hellrazer


    You could just limit the EDDI to 1 amp - Settings - supply grid - device limit.

    It will only draw (or should I say use) .24 kilowatts.

    Then if the solar is generating the rest will be exported or used to charge your batteries.

    Then schedule a boost on your EV rate at the times you want. A boost will over ride the grid supply setting and provide full power to the immersion.



  • Moderators, Science, Health & Environment Moderators Posts: 4,726 Mod ✭✭✭✭Tree


    I can also recommend* going down the home assistant rabbithole, cause then you can programatically stop/start/boost...


    *I am not responsible for your sanity, operating system, budget, or spending the rest of your life chasing little automation tweaks...



  • Registered Users Posts: 205 ✭✭OO7FITZY


    Appreciate if anyone could help with this issue I have today

    Eddi has been consistantly heating my hot water every day for the last year since I got it installed as part of an overall solar PV/battery system, but today for some unknown reason it suddenly stopped?

    Odd thing is it heated the water for 20 mins this AM as per manual boost instruction, but then when I tried the boost function again later today it did not heat the water

    I can clearly see on the myenergi app that is it not pulling down any Kw to heat the cylinder and the battery is not draining either and the water is cold (even though the app says it is boosting as does the screen on the eddi unit)

    The myenergi app also shows no usage (except the 20 mins boost this AM) - all other boosts have failed

    I have always used the boost function manually through the app and no issues

    I've tried the manual boost function through the eddi unit and that also does not work

    I've turned the unit off and on using the switch at the bottom of the unit and repeated above steps and that has not worked

    I'm lost as to what the issue could be?



  • Moderators, Home & Garden Moderators Posts: 6,284 Mod ✭✭✭✭graememk


    Check the over temperature trip on the immersion, it's likely that has tripped



  • Registered Users, Registered Users 2 Posts: 3,314 ✭✭✭ratracer


    Do you know if the over-temp trip itself can become faulty?
    I have similar issues, but there is never a feel of that resetting. I can hear the thermostat on the immersion clock on and off if I adjust the temp on it.



  • Registered Users Posts: 205 ✭✭OO7FITZY


    THX GRAEMEMK

    I'll search it up in the morning - is this something I can do or do I need an electrician?



  • Moderators, Home & Garden Moderators Posts: 6,284 Mod ✭✭✭✭graememk


    Some immersions have a red button on top that you press back in to reset.

    Others is under the lid (caution, potentially live terminals, switch eddi to off, and not bypass) ones I've seen is a tiny white button that you need to push in with a small screwdriver.

    If unsure take a picture and see.

    If it keeps happening more investigation is needed.

    Over temp trip is unlikely to become faulty, but it does not reset automatically,

    The normal thermostat is known to become faulty, and it can be replaced fairly easily on some immersions, some are not replaceable.

    My immersion failed completely and the terminals got really hot and that tripped the over temperature on mine. (Melty cables, no eddi just an immersion timer)



  • Registered Users Posts: 205 ✭✭OO7FITZY


    had a look at this - can't see a reset switch when I took the cover off



  • Moderators, Home & Garden Moderators Posts: 6,284 Mod ✭✭✭✭graememk


    Can't see it, could be new immersion time, it's a bit crusty!



  • Advertisement
Advertisement