Generator change over switch

  • 03-08-2019 3:53am
    #1
    Registered Users, Registered Users 2 Posts: 10


    Hi all I have a job coming up soon, which includes the install of a generator change over switch, just in relation to the main neutral from the ESB side is it a case of redirecting this though change over switch, and my main neutral from generator does this need to be earthed at generator?


«1

Comments

  • Registered Users, Registered Users 2 Posts: 9,605 ✭✭✭gctest50


    Just isolate your generator completey from the mains

    Crowbar it

    Backfeeds kill people


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    Rc3 wrote: »
    Hi all I have a job coming up soon, which includes the install of a generator change over switch, just in relation to the main neutral from the ESB side is it a case of redirecting this though change over switch, and my main neutral from generator does this need to be earthed at generator?

    A few more details would help.
    Domestic single phase installation? Manual changeover?

    I would:
    1) Have the ESB supply neutral and the generator neutral sharing the same neutral bar.
    2)Neither neutral would be switched.
    3)Normally the entire installation would only be neutralized at one point.


  • Registered Users, Registered Users 2 Posts: 22,584 ✭✭✭✭Steve


    I've done lots of commercial auto gen sets over the years, all TNC, all rely on ESB earthing.


  • Posts: 5,238 ✭✭✭ [Deleted User]


    I would not share neutrals.


    I would reconstruct the distribution as utility only circuits and maintained circuits.


    Three position, Centre off, changeover rotary cam switch. Kraus and Naimer make the best, not expensive, by standards.
    Or an automatic changeover with a 1ms delay timer.


    The installation will only have one neutralising point, at a time, when set up like this. One for utility and one for back-up.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    I would not share neutrals.

    Interesting, why?
    I would reconstruct the distribution as utility only circuits and maintained circuits.

    Not really sure what you mean :confused:
    Can you reword?
    Three position, Centre off, changeover rotary cam switch. Kraus and Naimer make the best, not expensive, by standards.
    Or an automatic changeover with a 1ms delay timer.

    Nothing wrong with a 3 position changeover switch:
    Position 1) ESB supply connected to load
    Position 2) OFF - Load disconnected from both supplies
    Position 3) Generator supply connected to load

    But why complicate by switching the neutral too?
    The installation will only have one neutralising point, at a time, when set up like this. One for utility and one for back-up.

    Understood, but what is the advantage of this set up?
    I have never seen it done this way.


  • Advertisement
  • Posts: 5,238 ✭✭✭ [Deleted User]


    Shared neutrals...One less thing to go wrong, I didn't sign off the installation how do I know there won't be a problem.
    Edit; [If the neutrals are separated I can run parallel isolated]..ie...morah powah!!! MwahaHAha....ah..ahem..

    Usually shore power loads exceed inverter loads.
    Or I don't want the missus running the immersion off my stand-by battery set.

    Electrode & neutralise the genset, continuous PE to ESB also, via terra firma and distribution.


  • Posts: 5,238 ✭✭✭ [Deleted User]


    2011 wrote: »
    Can you reword?


    High current loads on largest supply source.


    Mission critical loads on both.


  • Registered Users, Registered Users 2 Posts: 2,567 ✭✭✭Risteard81


    Steve wrote: »
    I've done lots of commercial auto gen sets over the years, all TNC, all rely on ESB earthing.

    I presume this was a mistake. TN-C = Terra/Neutral Combined, i.e. a PEN conductor within the consumer's installation.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    Shared neutrals...One less thing to go wrong

    So what is the possible fault that you feel this would remove?
    I didn't sign off the installation how do I know there won't be a problem.

    So you are saying that switching the neutral could reduce the risk of what exactly?
    Edit; [If the neutrals are separated I can run parallel isolated]..ie...morah powah!!! MwahaHAha....ah..ahem..

    You know that the sharing of a neutral does not prevent paralleling of generator and ESB supplies?
    Usually shore power loads exceed inverter loads.
    Or I don't want the missus running the immersion off my stand-by battery set.

    It is easy to load shed when on a generator supply, this is normal.
    It can be achieved just as easily with a shared neutral.
    Electrode & neutralise the genset, continuous PE to ESB also, via terra firma and distribution.

    In the OPs example we are talking about a domestic installation. Although there is no harm adding another electrode at the generator it will achieve little in a normal domestic installation. Most domestic generators are wheeled out and plugged in when required. Hooking up another earth electrode local to the generator will achieve very little, it would just complicate matters.

    Sharing a neutral means that the neutralizing does not have to be repeated at the generator.

    A common earth bar, neutral bar and neutralizing point is the norm for domestic, commercial and industrial installations. There may be specific reasons not to do this for special cases, but in the absence of this it is best to follow standard practice. The OP has not stated anything to suggest that this is a special case.
    High current loads on largest supply source.


    Mission critical loads on both.

    ...what has this got to do with sharing a neutral? :confused:
    Data centres don't switch neutrals and they are as mission critical as you can get.
    With mission critical loads one less thing to switch reduces the risk of failure of that component thus increasing security of supply.


  • Registered Users, Registered Users 2 Posts: 1,054 ✭✭✭Tuco88


    We always switched the neutral on a change over switch to a generator. Hager do a nice din rail mounted 63amp one for smaller installations.


  • Advertisement
  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    Tuco88 wrote: »
    We always switched the neutral on a change over switch to a generator. Hager do a nice din rail mounted 63amp one for smaller installations.

    I'm not saying it wouldn't work, I'm just asking why do it?


  • Posts: 5,238 ✭✭✭ [Deleted User]


    2011 wrote: »
    So what is the possible fault that you feel this would remove?



    So you are saying that switching the neutral could reduce the risk of what exactly?


    I don't like neutral buses. Bleed through on low energy circuits. Pd between neutral and earth due to cable resistance and inductance. Fault path through a defective RCD to a line worker during a power cut.

    I like the French System (parts of) Double Pole everything.

    2011 wrote: »
    You know that the sharing of a neutral does not prevent paralleling of generator and ESB supplies?


    With or without synchronisation?


    2011 wrote: »
    It is easy to load shed when on a generator supply, this is normal.


    Higher voltage on larger output.

    2011 wrote: »
    It can be achieved just as easily with a shared neutral.


    You're used to working on more expensive systems than I am I take it?


    2011 wrote: »

    Although there is no harm adding another electrode at the generator it will achieve little in a normal domestic installation.

    In the OPs example we are talking about a domestic installation.

    Lower loop impedance. No single point of failure.

    Lower Pd on N-PE.


    I use generators where there is no utility so my rules vary.
    Generator, electrode, meter, feeder.






    2011 wrote: »
    Most domestic generators are wheeled out and plugged in when required.



    I got one of those that runs off a battery. PM me for a drag race.
    Venue: I chose the WC. Mine's 2.5kVA and 20dB.
    effin' dinosaur transducers...spare me..:rolleyes:


    2011 wrote: »
    Hooking up another earth electrode local to the generator will achieve very little, it would just complicate matters.


    Like testing RCDs monthly as written on the device?




    2011 wrote: »

    Sharing a neutral means that the neutralizing does not have to be repeated at the generator.


    True.


    2011 wrote: »
    A common earth bar, neutral bar and neutralizing point is the norm for domestic, commercial and industrial installations. There may be specific reasons not to do this for special cases, but in the absence of this it is best to follow standard practice. The OP has not stated anything to suggest that this is a special case.


    Hrmm yes. I don't like it.
    But I'm odd. Here my cooker bypasses the RCD...why is that? Will I only drill through outlet conductors hanging family pictures?
    CU has a safety device, installer didn't use it, because government said that was ok...carry on...


    2011 wrote: »
    ...what has this got to do with sharing a neutral? :confused:
    Data centres don't do this and they are as mission critical as you can get.


    Nothing, You asked for clarification on why I'd split the consumer unit.


  • Registered Users, Registered Users 2 Posts: 1,054 ✭✭✭Tuco88


    I would say its good practice to isolate the L&N from the ESB, removing any risk of a possible backfeed.

    The Hager change over switch above mentioned, is designed for this (wiring diagram supplied) Figured it was the norm?

    Large 4 pole ones on the site I'm on.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    I don't like neutral buses. Bleed through on low energy circuits.

    Explain, what exactly is it you do not like and how does switching the neutral stop this?
    Pd between neutral and earth due to cable resistance and inductance.

    No potential difference as the earth and the neutral are joined together (at the neutralizing point). In your case at the genny, in mine at the cut out.

    Yes there may be a bit of "noise" on the neutral at some points on the circuit due to the nature of some loads, is this what you mean?
    Fault path through a defective RCD to a line worker during a power cut.

    Line workers test first and then earth all conductors.
    Neutral conductor is connected to earth at multiple points (at the traffo and at each installation).

    Not sure how a defective RCD would increase the risk to line workers.
    With or without synchronisation?

    It can be done with both, but only with permission.
    Higher voltage on larger output.

    Not sure what you mean.
    You're used to working on more expensive systems than I am I take it?

    I don't work on domestic installations, so maybe.
    I only work on the design / start up / commissioning etc.
    Lower loop impedance. No single point of failure.

    Why would be be lower? I would argue the opposite, without a switched neutral the impedance would be very slightly less.

    The phase would have equal impedance, however if connected to utility neutral the earth return path would have lower resistance as there are more parallel return paths.

    Lower Pd on N-PE.

    If you measure the potential difference between the MET and the main neutral bar in a neutralized installation and get anything more than a negligible voltage there is something very wrong and switching the neutral won't fix this.

    I use generators where there is no utility so my rules vary.
    Generator, electrode, meter, feeder.

    ....so you are a special case. This is exactly why in my last post I said "There may be specific reasons not to do this for special cases, but in the absence of this it is best to follow standard practice. The OP has not stated anything to suggest that this is a special case. ". My answers were directed at the OP.

    Like testing RCDs montly as written on the device?

    It won't hurt but earth electrodes generally have a resistance to earth of more than 150 Ohms to earth so it won't achieve a lot especially when you consider that in a domestic installation it won't be far from the other earth rod (belonging to the same installation).

    It is not a "bad idea". In fact you are probably right, I have to admit it would be better practice for a permanently connected generator, I guess my point is that you shouldn't expect a whole lot from it.

    This would always be done in an industrial installation, but that is on a whole other scale and there would be multiple earth electrodes around the genny + it could be much further away.
    True.

    :)
    Hrmm yes. I don't like it.
    But I'm odd. Here my cooker bypasses the RCD...why is that will I only drill through outlet conductors hanging family pictures.

    It is all about assessing the risk and then bringing in appropriate measures to mitigate that risk. There would be nothing wrong with installing an RCD on the cooker circuit, but then where do you stop? Metal conduit for the entire circuit just in case? Oversize the conductors too? Arc fault detection devices on every circuit? All cables to be MICC?
    There needs to be a balance, and someone has to call it. The rules set the minimum standards, the designer can always choose to exceed this.
    CU has a safety device, installer didn't use it, because government said that was ok...carry on...

    The government don't write the wiring rules, "expert" volunteers do.
    Although some are definitely more "expert" than others ;)
    Nothing, You asked for clarification on why I'd split the consumer unit.

    Fair enough :)


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    Tuco88 wrote: »
    I would say its good practice to isolate the L&N from the ESB, removing any risk of a possible backfeed.

    This is the closest I have seen to a convincing answer :)

    So if I connect the neutral from my generator to the ESB neutral which I have checked is connected to by MET and the MET is connected to my earth rod(s) where is the increased risk of a back feed?

    Remember the changeover switch will not allow the generator to be in circuit with the grid.


  • Posts: 5,238 ✭✭✭ [Deleted User]


    2011 wrote: »
    Explain, what exactly is it you do not like and how does switching the neutral stop this?


    LEDs not turning off when the switch is open. Trying to isolate a load to find shared neutrals downstream in the installation that then need to be tailed back to distribution. Polarity reversal danger in DIY fly leads.
    Not issues with a switched neutral bus, but with a bus mentality.
    Less to go wrong without it.

    2011 wrote: »
    No potential difference as the earth and the neutral are joined together (at the neutralizing point). In your case at the genny, in mine at the cut out.


    In your scenario what if the gene is sited 100m from the neutralising point geographically with another 100m coiled cable in the middle of the circuit. Still zero pd?

    2011 wrote: »
    Yes there may be a bit of "noise" on the neutral at some points on the circuit due to the nature of some loads, is this what you mean?


    It's cleaner for the sake of a wire in a terminal that's already in the enclosure.




    2011 wrote: »
    Line workers test first and then earth all conductors.
    Neutral conductor is connected to earth at multiple points (at the traffo and at each installation).


    Do people only turn their genset on before the line workers test their metal?



    So what's all this anti-islanding nonsense that's mandatory on all EU grid-tied inverters about? Buncha Jessies?






    2011 wrote: »
    Not sure how a defective RCD would increase the risk to line workers.


    Now imagine the feeder cable from the genset is a two-core DIY jobber?




    2011 wrote: »
    It can be done with both, but only with permission.




    I'll ask the electrons next time I attempt it so.;)



    2011 wrote: »
    Not sure what you mean.


    Load shedding parallel operating supplies. Dial the voltage high on the more capable supply and it will power the lion's share.


    In retrospect, I'd say the reason I split the consumer unit is because I don't enable the user to undermine the system. A back-up genset is for back-up not business as usual. eg. no immersion during a power cut. Or conversely on a barge clothes drier only from shore power.



    2011 wrote: »
    I don't work on domestic installations, so maybe.
    I only work on the design / start up / commissioning etc.


    Me neither. I work where there is no or not enough utility power, or I accept a big red socket and don't ask questions.
    ...other than my own domiciles, some are off-grid some are hybrid, the house I use half the year is utility fed.




    2011 wrote: »
    Why would be be lower?

    Because the neutralisation point is right beside the supply source and there's multiple earths.


    2011 wrote: »
    I would argue the opposite, without a switched neutral the impedance would be very slightly less.


    minus electrode, plus network meh...perhaps





    2011 wrote: »
    The phase would have equal impedance, however, if connected to utility neutral the earth return path would have lower resistance as there are more parallel return paths.


    More of them further away...you could be right.





    2011 wrote: »
    If you measure the potential difference between the MET and the main neutral bar in a neutralized installation and get anything more than a negligible voltage there is something very wrong and switching the neutral won't fix this.




    I got a nice tingle wiring a socket trailing lead while plugged in, with the feeding socket switch off once upon a time. I reckon twas 60Vac by the shimy of her.

    Neutral earth fault I was the fault path, isolated live.
    That house had huge resistance between the PE and the plumbing.

    ...very wrong or not...it happens!
    2011 wrote: »
    ....so you are a special case.


    Yeah well I haven't had an electron get the better of me yet. Few draws, zero losses.


    2011 wrote: »

    It won't hurt but earth electrodes generally have a resistance to earth of more than 150 Ohms to earth so it won't achieve a lot especially when you consider that in a domestic installation it won't be far from the other earth rod (belonging to the same installation).

    I mentioned the DIY trailing leads already.







    2011 wrote: »
    It is not a "bad idea". In fact you are probably right, I have to admit it would be better practice for a permanently connected generator, I guess my point is that you shouldn't expect a whole lot from it.

    Everything fails 2011, it's just a matter of how and when. I focus a lottov attention on redundancy and failsafery. See houses are easy..they don't move and vibrate and get horsed around...




    2011 wrote: »
    It is all about assessing the risk and then bringing in appropriate measures to mitigate that risk.

    I find, being a preventer of extra low voltage conflagrations that a lot of peoples comfort with risk if they even realise it to be so...can be higher than others.


    2011 wrote: »
    There would be nothing wrong with installing an RCD on the cooker circuit,


    Other than breaking the law to move a cable 4 inches...I will, no problem.


    2011 wrote: »
    but then where do you stop?


    Double fail to danger. Isolation after first fail.




    2011 wrote: »
    The government don't write the wiring rules, "expert" volunteers do.
    Although some are definitely more "expert" than others ;)

    The government endorse it. An expert is an expert, 10 000 hours at that skillset gets you consideration to the accolade. A professional is a person who has convinced another human to perform a job or task for money.


    If in doubt we measure it.



    Danger to the grid is temporary installations are not always the same every setup. We adopt best practice to remove doubt and potential risk from unforeseen.


    All my K&N cams have N terminals on them too.


  • Registered Users, Registered Users 2 Posts: 1,054 ✭✭✭Tuco88


    Somebody makes a mistake wiring the plug on the generator... Its been damaged owner tries to fix it. Polarity incorrect, now a potential live on the ESB side?


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    Ok, first off Sir Liamalot & Tuco88 thanks for the friendly debate. I find it very interesting. I always believe in challenging what others say, it is only by doing this that we learn from each other. Now I will attempt to answer your questions :)

    LEDs not turning off when the switch is open.

    I had direct experience with this before in a power station. It was caused by noise on the neutral (which I referred to in an earlier post). I believe that this was due to the high frequency switching of a large number of nonlinear loads within the installation. As the load profile changed the intensity of the LEDs varied. The issue was solved in the end by a combination of good earthing and the way the supply was switched off to the LEDs. Sharing or not sharing the main neutral bar would not change this.
    In your scenario what if the gene is sited 100m from the neutralising point geographically with another 100m coiled cable in the middle of the circuit. Still zero pd?

    In my scenario I am dealing with a domestic set up, as such the tails from the meter to the main distribution board are short, the generator is not far away and the generator is small (< 10 kVA).

    However, lets discuss your scenario and assume that the generator has a cable run of around 200m from the main distribution board. When the generator is supplying a load a current flows down the phase of the supply cable and returns on the neutral. Due to the resistance of the cable a volt drop will occur, this will mean that the neutral will be at a different potential with respect to earth at the cable end that is furthest from the neutralization point. The magnitude of the volt drop will be a function of the resistance of the cable and the current flowing through it.

    As discussed a generator can be neutralized your way or mine, let's look at each:

    ⦁ Your way, neutralized at the genny: Due to the volt drop on the cable there will be a larger potential difference between the main neutral bar and the MET.

    ⦁ My way, neutralized much closer to the main board: Due to the proximity of the neutralization point to the main neutral bar and the MET the potential difference will be reduced.

    Regardless of which way you do this if there is anything more than a negligible potential difference between the main neutral bar and the MET you have a problem! This would most likely be due to an undersized cables resulting in excessive volt drop and excessive earth fault loop impedance. Would you not agree?
    Do people only turn their genset on before the line workers test their metal?

    Sometimes, but not always. This is why arc flash PPE is worn and all phases and neutral are comprehensively connected to earth.
    So what's all this anti-islanding nonsense that's mandatory on all EU grid-tied inverters about? Buncha Jessies?

    Where did the inverter come from?
    Honestly? I am not familiar with this perhaps you can tell me.

    I am going to guess that this is another special situation as such it has special requirements which may well include switching the neutral. This does not sound like not a normal standby generator in a domestic installation.
    Now imagine the feeder cable from the genset is a two-core DIY jobber?

    Ok, I'm imagining. Please continue...
    I'll ask the electrons next time I attempt it so.;)

    My point is that a generator should not synced with the mains supply without approval regardless of what the electrons say :D
    Load shedding parallel operating supplies. Dial the voltage high on the more capable supply and it will power the lion's share.

    Ok, I see what you mean now. By load shedding I mean that when on generator supply in island mode loads deemed to be nonessential can be disconnected. As only essential loads are supplied by the generator the demand on it is reduced to a manageable level.

    If not in island mode and paralleling then the voltage output of the genny should be adjusted so appropriately so as to avoid the scenario that you described. My understanding is that this is achieved by varying the excitation of the rotor. All important stuff but it sounds like you would be sharing a neutral which I thought you were trying to avoid? How you you propose to parallel without sharing the neutral?
    In retrospect, I'd say the reason I split the consumer unit is because I don't enable the user to undermine the system. A back-up genset is for back-up not business as usual. eg. no immersion during a power cut. Or conversely on a barge clothes drier only from shore power.

    I would think that I could design that for you with a shared neutral bar. Do you believe me?
    I love the idea of a barge BTW :)
    Me neither.

    Most of what you discuss seems to be specialised so I would not be surprised if more bespoke solutions are make sense.
    I work where there is no or not enough utility power, or I accept a big red socket and don't ask questions.

    So a world away from a small domestic standby genny that may get used once every 10 years.
    ...other than my own domiciles, some are off-grid some are hybrid, the house I use half the year is utility fed.

    From what I have seen to date they look very interesting.
    Because the neutralisation point is right beside the supply source and there's multiple earths.

    That all depends on where you measure it. I would argue that the most important measurement is at the main distribution board (which is where a genny would normally be connected to the rest of the installation). Are you suggesting that there would be a better earth at the generator than at the main DB?
    minus electrode, plus network meh...perhaps

    Exactly :)
    More of them further away...you could be right.

    :)

    Everything fails 2011, it's just a matter of how and when. I focus a lottov attention on redundancy and failsafery. See houses are easy..they don't move and vibrate and get horsed around...

    I couldn't agree more. I have been working on the design of a SIL2 system (to IEC 61508) for the last year.

    I find, being a preventer of extra low voltage conflagrations that a lot of peoples comfort with risk if they even realise it to be so...can be higher than others.

    Double fail to danger. Isolation after first fail.

    That may be enough in most cases but a risk assessment may determine that dual failure tolerance is not sufficient.
    The government endorse it.

    You are correct, but when I look at IS10101 (the draft) and ET101 I don't see a requirement to switch the neutral.
    Danger to the grid is temporary installations are not always the same every setup.

    Agreed.
    Each case should be carefully assessed, but I am talking about a normal set up with a small standby genny which are fundamentally very similar. You are focusing on the more bespoke work that you normally do which demand different solutions.
    We adopt best practice to remove doubt and potential risk from unforeseen.

    Yes, but best practice always starts with identifying the risks.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    Tuco88 wrote: »
    Somebody makes a mistake wiring the plug on the generator... Its been damaged owner tries to fix it. Polarity incorrect, now a potential live on the ESB side?

    Worth considering.

    Not ideal, so think it through.
    The phase from the genny is now connected to the MET and the installation earth rod in addition to multiple earth rods that are external to the installation. The neutral from the genny is now disconnected from the grid as it is connected to the phase of the change over switch.....


  • Closed Accounts Posts: 79 ✭✭Reisers


    All poles should be switched for a domestic backup generator IMO.

    No reason not to ,although there's nothing in rules or code of practice say's you have to


  • Advertisement
  • Closed Accounts Posts: 79 ✭✭Reisers


    Do Esbn still have authority to inspect domestic setups?

    They won't pass it without neutral switched


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    Reisers wrote: »
    All poles should be switched for a domestic backup generator IMO.

    Everyone is entitled to an opinion but it doesn’t mean much unless you back it up with some reasons.
    No reason not to ,although there's nothing in rules or code of practice say's you have to

    Other than the reasons stated in the thread, have a read :)
    Reisers wrote: »
    Do Esbn still have authority to inspect domestic setups?

    RECI do this now. Their role is to ensure compliance with ET101 so if you can point to where these rules state that the neutral must be switched you may have a point.


  • Closed Accounts Posts: 79 ✭✭Reisers


    2011 wrote: »
    Everyone is entitled to an opinion but it doesn’t mean much unless you back it up with some reasons.



    Other than the reasons stated in the thread, have a read :)



    RECI do this now. Their role is to ensure compliance with ET101 so if you can point to where these rules state that the neutral must be switched you may have a point.

    I already said in my post the neutral doesn't have to be switched according to rules, I don't know why you're asking the question.

    My opinion is it's safer for domestic to switch all poles as you don't know what will be hooked up down the road in a domestic situation.


  • Registered Users, Registered Users 2 Posts: 22,584 ✭✭✭✭Steve


    Reisers wrote: »
    My opinion is it's safer for domestic to switch all poles as you don't know what will be hooked up down the road in a domestic situation.
    Point is you DO. in a TNC system you always know the neutral will be earthed at least somewhere close to the installation.

    If you separate the neutral and earth from the mains you risk a floating neutral and a floating earth from an incorrectly grounded generator. This also gives the risk of a faulty appliance that has a neutral to earth connection gaining a lethal potential.


  • Closed Accounts Posts: 79 ✭✭Reisers


    Steve wrote: »
    Point is you DO. in a TNC system you always know the neutral will be earthed at least somewhere close to the installation.

    If you separate the neutral and earth from the mains you risk a floating neutral and a floating earth from an incorrectly grounded generator. This also gives the risk of a faulty appliance that has a neutral to earth connection gaining a lethal potential.
    I don't fit domestic changeover switches as I don't like them unless theyre connected to a fixed generator tn-s and grounded.In that case the neutral doesn't need switching.

    Most of these domestic installs the spark is leaving a 63A plug for a Genny
    Someone will come along after and connect a 110-0-110 genny and short it


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    Reisers wrote: »
    I already said in my post the neutral doesn't have to be switched according to rules, I don't know why you're asking the question.

    I'm asking because you also say that ESBN "won't pass it without neutral switched" in the very next post.
    This seems suggest that ESBN won't permit something that is complaint with the rules. Can you explain?

    Reisers wrote: »
    Most of these domestic installs the spark is leaving a 63A plug for a Genny

    Read the previous post by Steve and you will see that you are making a stronger argument for not switching the neutral.
    Someone will come along after and connect a 110-0-110 genny and short it

    And what would the consequence of that be? Would anyone be at risk and how?

    Are you aruging this a valid reason for running the risk that the genny would not be neutralized at any point?


  • Posts: 5,238 ✭✭✭ [Deleted User]


    Reisers wrote: »
    All poles should be switched for a domestic backup generator IMO.


    I don't think there is ever a good reason to switch the PE.


  • Closed Accounts Posts: 79 ✭✭Reisers


    I don't think there is ever a good reason to switch the PE.
    Live Poles obviously


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    Reisers wrote: »
    Live Poles obviously

    I am not trying to be smart but it is not obvious.


  • Advertisement
  • Closed Accounts Posts: 79 ✭✭Reisers


    2011 wrote: »
    I am not trying to be smart but it is not obvious.

    Obvious to an electrician


  • Posts: 5,238 ✭✭✭ [Deleted User]


    Marine Inverters switch the PE as standard in thru-put.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    Reisers wrote: »
    Obvious to an electrician

    Nope, I am an electrician :)

    As I am sure you know there can be valid reasons for switching earths in some scenarios.


  • Registered Users, Registered Users 2 Posts: 1,054 ✭✭✭Tuco88


    If the premises had a TN-S system. I would imagine not switching the DSO Neutral would be problematic if a fault occurred on the generator side like a broken neutral?


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    Tuco88 wrote: »
    If the premises had a TN-S system. I would imagine not switching the DSO Neutral would be problematic if a fault occurred on the generator side like a broken neutral?

    I have never seen TN-S used by ESBN, in fact I would be surprised if they use it at all.

    Do you mean that because TN-S is neutralized at the local transformer a broken neutral on the utility side would mean it would not be neutralized anywhere? I suppose that when there is a power outage it is possible that as part of the repairs the star point of the local transformer may no longer be grounded.

    I'm not sure but perhaps in this more unusual example it may make sense to break the neutral so that a generator specific neutraliziation point could be switched into circuit when the generator is in use. To me it would seem risky to have the only neutralization point external to the installation. I am open to correction on this, but that is my opinion.

    As you know most installations in Ireland are TN-C-S, so normally this concern would not apply.


  • Posts: 5,238 ✭✭✭ [Deleted User]


    2011 wrote: »
    As I am sure you know there can be valid reasons for switching earths in some scenarios.


    ...couldn't afford a transformer?


  • Advertisement
  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    Tuco88 wrote: »
    If the premises had a TN-S system. I would imagine not switching the DSO Neutral would be problematic if a fault occurred on the generator side like a broken neutral?

    A 3 phase generator, as with any 3 phase supply, would be problematic with open neutral on any earthing system.


  • Posts: 5,238 ✭✭✭ [Deleted User]


    Bruthal wrote: »
    A 3 phase generator, as with any 3 phase supply, would be problematic with open neutral on any earthing system.

    I've seen that cost clients 10s of thousands of Eurobucks. Bad distro. Technician plugged in without metering. Blew the PSUs outtov one third of a festival stage video wall


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    I've seen that cost clients 10s of thousands of Eurobucks. Bad distro. Technician plugged in without metering. Blew the PSUs outtov one third of a festival stage video wall

    Yea I seen it myself in a neighbours house a few years ago. Lot if ruined items.


  • Closed Accounts Posts: 79 ✭✭Reisers


    Bruthal wrote: »
    Yea I seen it myself in a neighbours house a few years ago. Lot if ruined items.

    I've done it and seen it happen


  • Closed Accounts Posts: 79 ✭✭Reisers


    Its probably the reason I only buy electrical equipment with external power supplies where possible and separates- none of this combi stuff


  • Advertisement
  • Posts: 5,238 ✭✭✭ [Deleted User]


    I'd advise metering the supply over installing remote detonation devices.


  • Closed Accounts Posts: 79 ✭✭Reisers


    Marine Inverters switch the PE as standard in thru-put.

    maybe standard in the sailing or boating forum but has no relevance here

    "switching devices shall not be installed in a protective conductor"

    Rules 543.3.3


  • Closed Accounts Posts: 79 ✭✭Reisers


    2011 wrote: »
    I am not trying to be smart but it is not obvious.

    I'd say it's fairly obvious to any electrician

    The PE isn't normally referred to as a pole or a supply pole for switching purposes


    Poles refer to live conductors


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    Reisers wrote: »
    I'd say it's fairly obvious to any electrician

    As I am an electrician I can comment with some authority on what I feel is or is not obvious to an electrician :)

    Anyway you have clarified your position and we all agree on this point so let’s move on rather than argue about it.

    How about answering the questions put to you here?

    https://www.boards.ie/vbulletin/showpost.php?p=110941597&postcount=27


  • Closed Accounts Posts: 79 ✭✭Reisers


    2011 wrote: »
    As I am an electrician I can comment with some authority on what I feel is or is not obvious to an electrician :)

    Anyway you have clarified your position and we all agree on this point so let’s move on rather than argue about it.

    How about answering the questions put to you here?

    https://www.boards.ie/vbulletin/showpost.php?p=110941597&postcount=27

    I don't fit domestic changeover switches as generators connected are not typically fit for the purpose


    If i had to fit a changeover switch and a plug for a domestic generator to be connected later- i would be switching all live poles .


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    Reisers wrote: »
    I don't fit domestic changeover switches as generators connected are not typically fit for the purpose

    Why are the generators that are typically fitted not fit for purpose?
    If i had to fit a changeover switch and a plug for a domestic generator to be connected later- i would be switching all live poles .

    Yeah I see that.
    Reisers wrote: »
    I already said in my post the neutral doesn't have to be switched according to rules, I don't know why you're asking the question.

    I'm asking because you also say that ESBN "won't pass it without neutral switched" in the very next post.
    This seems suggest that ESBN won't permit something that is complaint with the rules. Can you explain?

    Reisers wrote: »
    Most of these domestic installs the spark is leaving a 63A plug for a Genny

    Read the previous post by Steve and you will see that you are making a stronger argument for not switching the neutral.
    Someone will come along after and connect a 110-0-110 genny and short it

    And what would the consequence of that be? Would anyone be at risk and how?

    Are you aruging this a valid reason for running the risk that the genny would not be neutralized at any point?


  • Registered Users, Registered Users 2 Posts: 22,584 ✭✭✭✭Steve


    Reisers wrote: »
    Someone will come along after and connect a 110-0-110 genny and short it
    2011 wrote: »
    And what would the consequence of that be? Would anyone be at risk and how?

    This is perplexing me. do 110-0-110 generators even exist? If so, why?
    110VAC is considered lethal which is why 55-0-55 is used on sites via a CTE traffo.

    I don't see a reason for 110-0-110 to exist, but I'm open to correction.

    Yes, I've googled them, no results.

    Theory aside, in real life, this would just stall the generator and stop it instantly as it wouldn't handle the short circuit current. I've seen 1200A FGW sets lock up instantly - installed as max demand changeover in shopping centres - because of no load shedding before the ACB's switched.


  • Closed Accounts Posts: 79 ✭✭Reisers


    https://www2.theiet.org/forums/forum/messageview.cfm?catid=205&threadid=24199

    I was called out to a changeover switch

    There was N-E faults on the lighting circuits draining the generator with nothing switched on.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    Reisers wrote: »
    I was called out to a changeover switch

    There was N-E faults on the lighting circuits draining the generator with nothing switched on.

    That doesn’t even make sense.


  • Registered Users, Registered Users 2 Posts: 9,605 ✭✭✭gctest50


    Reisers wrote: »
    I don't fit domestic changeover switches as generators connected are not typically fit for the purpose


    If i had to fit a changeover switch and a plug for a domestic generator to be connected later- i would be switching all live poles .

    A 240 <
    > 240 isolating transformer & under/over relay would be nice since you'd never know what effort of a generator would get plugged into it