2011 wrote: » Can you reword?
Sir Liamalot wrote: » I would not share neutrals.
I would reconstruct the distribution as utility only circuits and maintained circuits.
Three position, Centre off, changeover rotary cam switch. Kraus and Naimer make the best, not expensive, by standards. Or an automatic changeover with a 1ms delay timer.
The installation will only have one neutralising point, at a time, when set up like this. One for utility and one for back-up.
Rc3 wrote: » Hi all I have a job coming up soon, which includes the install of a generator change over switch, just in relation to the main neutral from the ESB side is it a case of redirecting this though change over switch, and my main neutral from generator does this need to be earthed at generator?