Bruthal wrote: » A 3 phase generator, as with any 3 phase supply, would be problematic with open neutral on any earthing system.
Tuco88 wrote: » If the premises had a TN-S system. I would imagine not switching the DSO Neutral would be problematic if a fault occurred on the generator side like a broken neutral?
2011 wrote: » As I am sure you know there can be valid reasons for switching earths in some scenarios.
Reisers wrote: » Obvious to an electrician
2011 wrote: » I am not trying to be smart but it is not obvious.
Reisers wrote: » Live Poles obviously
Sir Liamalot wrote: » I don't think there is ever a good reason to switch the PE.
Reisers wrote: » All poles should be switched for a domestic backup generator IMO.
Reisers wrote: » I already said in my post the neutral doesn't have to be switched according to rules, I don't know why you're asking the question.
Reisers wrote: » Most of these domestic installs the spark is leaving a 63A plug for a Genny
Someone will come along after and connect a 110-0-110 genny and short it
Steve wrote: » Point is you DO. in a TNC system you always know the neutral will be earthed at least somewhere close to the installation. If you separate the neutral and earth from the mains you risk a floating neutral and a floating earth from an incorrectly grounded generator. This also gives the risk of a faulty appliance that has a neutral to earth connection gaining a lethal potential.
Reisers wrote: » My opinion is it's safer for domestic to switch all poles as you don't know what will be hooked up down the road in a domestic situation.
2011 wrote: » Everyone is entitled to an opinion but it doesn’t mean much unless you back it up with some reasons. Other than the reasons stated in the thread, have a read RECI do this now. Their role is to ensure compliance with ET101 so if you can point to where these rules state that the neutral must be switched you may have a point.
No reason not to ,although there's nothing in rules or code of practice say's you have to
Reisers wrote: » Do Esbn still have authority to inspect domestic setups?
Tuco88 wrote: » Somebody makes a mistake wiring the plug on the generator... Its been damaged owner tries to fix it. Polarity incorrect, now a potential live on the ESB side?
Sir Liamalot wrote: » LEDs not turning off when the switch is open.
In your scenario what if the gene is sited 100m from the neutralising point geographically with another 100m coiled cable in the middle of the circuit. Still zero pd?
Do people only turn their genset on before the line workers test their metal?
So what's all this anti-islanding nonsense that's mandatory on all EU grid-tied inverters about? Buncha Jessies?
Now imagine the feeder cable from the genset is a two-core DIY jobber?
I'll ask the electrons next time I attempt it so.;)
Load shedding parallel operating supplies. Dial the voltage high on the more capable supply and it will power the lion's share.
In retrospect, I'd say the reason I split the consumer unit is because I don't enable the user to undermine the system. A back-up genset is for back-up not business as usual. eg. no immersion during a power cut. Or conversely on a barge clothes drier only from shore power.
Me neither.
I work where there is no or not enough utility power, or I accept a big red socket and don't ask questions.
...other than my own domiciles, some are off-grid some are hybrid, the house I use half the year is utility fed.
Because the neutralisation point is right beside the supply source and there's multiple earths.
minus electrode, plus network meh...perhaps
More of them further away...you could be right.
Everything fails 2011, it's just a matter of how and when. I focus a lottov attention on redundancy and failsafery. See houses are easy..they don't move and vibrate and get horsed around...
Double fail to danger. Isolation after first fail.
The government endorse it.
Danger to the grid is temporary installations are not always the same every setup.
We adopt best practice to remove doubt and potential risk from unforeseen.
2011 wrote: » Explain, what exactly is it you do not like and how does switching the neutral stop this?
2011 wrote: » No potential difference as the earth and the neutral are joined together (at the neutralizing point). In your case at the genny, in mine at the cut out.
2011 wrote: » Yes there may be a bit of "noise" on the neutral at some points on the circuit due to the nature of some loads, is this what you mean?
2011 wrote: » Line workers test first and then earth all conductors. Neutral conductor is connected to earth at multiple points (at the traffo and at each installation).
2011 wrote: » Not sure how a defective RCD would increase the risk to line workers.
2011 wrote: » It can be done with both, but only with permission.
2011 wrote: » Not sure what you mean.
2011 wrote: » I don't work on domestic installations, so maybe. I only work on the design / start up / commissioning etc.
2011 wrote: » Why would be be lower?
2011 wrote: » I would argue the opposite, without a switched neutral the impedance would be very slightly less.
2011 wrote: » The phase would have equal impedance, however, if connected to utility neutral the earth return path would have lower resistance as there are more parallel return paths.
2011 wrote: » If you measure the potential difference between the MET and the main neutral bar in a neutralized installation and get anything more than a negligible voltage there is something very wrong and switching the neutral won't fix this.
2011 wrote: » ....so you are a special case.
2011 wrote: » It won't hurt but earth electrodes generally have a resistance to earth of more than 150 Ohms to earth so it won't achieve a lot especially when you consider that in a domestic installation it won't be far from the other earth rod (belonging to the same installation).
2011 wrote: » It is not a "bad idea". In fact you are probably right, I have to admit it would be better practice for a permanently connected generator, I guess my point is that you shouldn't expect a whole lot from it.
2011 wrote: » It is all about assessing the risk and then bringing in appropriate measures to mitigate that risk.
2011 wrote: » There would be nothing wrong with installing an RCD on the cooker circuit,
2011 wrote: » but then where do you stop?
2011 wrote: » The government don't write the wiring rules, "expert" volunteers do. Although some are definitely more "expert" than others
Tuco88 wrote: » I would say its good practice to isolate the L&N from the ESB, removing any risk of a possible backfeed.
Sir Liamalot wrote: » I don't like neutral buses. Bleed through on low energy circuits.
Pd between neutral and earth due to cable resistance and inductance.
Fault path through a defective RCD to a line worker during a power cut.
With or without synchronisation?
Higher voltage on larger output.
You're used to working on more expensive systems than I am I take it?
Lower loop impedance. No single point of failure.
Lower Pd on N-PE.
I use generators where there is no utility so my rules vary. Generator, electrode, meter, feeder.
Like testing RCDs montly as written on the device?
True.
Hrmm yes. I don't like it. But I'm odd. Here my cooker bypasses the RCD...why is that will I only drill through outlet conductors hanging family pictures.
CU has a safety device, installer didn't use it, because government said that was ok...carry on...
Nothing, You asked for clarification on why I'd split the consumer unit.
2011 wrote: » So what is the possible fault that you feel this would remove? So you are saying that switching the neutral could reduce the risk of what exactly?
2011 wrote: » You know that the sharing of a neutral does not prevent paralleling of generator and ESB supplies?
2011 wrote: » It is easy to load shed when on a generator supply, this is normal.
2011 wrote: » It can be achieved just as easily with a shared neutral.
2011 wrote: » Although there is no harm adding another electrode at the generator it will achieve little in a normal domestic installation. In the OPs example we are talking about a domestic installation.
2011 wrote: » Most domestic generators are wheeled out and plugged in when required.
2011 wrote: » Hooking up another earth electrode local to the generator will achieve very little, it would just complicate matters.
2011 wrote: » Sharing a neutral means that the neutralizing does not have to be repeated at the generator.
2011 wrote: » A common earth bar, neutral bar and neutralizing point is the norm for domestic, commercial and industrial installations. There may be specific reasons not to do this for special cases, but in the absence of this it is best to follow standard practice. The OP has not stated anything to suggest that this is a special case.
2011 wrote: » ...what has this got to do with sharing a neutral? Data centres don't do this and they are as mission critical as you can get.
Tuco88 wrote: » We always switched the neutral on a change over switch to a generator. Hager do a nice din rail mounted 63amp one for smaller installations.
Sir Liamalot wrote: » Shared neutrals...One less thing to go wrong
I didn't sign off the installation how do I know there won't be a problem.
Edit; [If the neutrals are separated I can run parallel isolated]..ie...morah powah!!! MwahaHAha....ah..ahem..
Usually shore power loads exceed inverter loads. Or I don't want the missus running the immersion off my stand-by battery set.
Electrode & neutralise the genset, continuous PE to ESB also, via terra firma and distribution.
High current loads on largest supply source. Mission critical loads on both.
Steve wrote: » I've done lots of commercial auto gen sets over the years, all TNC, all rely on ESB earthing.