Riello rdb burner

  • 01-12-2014 07:27PM
    #1
    Registered Users, Registered Users 2 Posts: 73 ✭✭


    ran out of oil over the weekend and stuck a couple of barrels into tank until oil arrives on wednesday. Bled it as normal and nothing. the filter at the pump was manky. cleaned it and changed nozzle for new one.
    The burner now won't lockout. The fan is working and that is it. electrodes and photo sensor are clean.
    Any suggestions?


«1

Comments

  • Registered Users, Registered Users 2 Posts: 4,052 ✭✭✭jimf


    sounds like you may have a faulty photocell if the burner is running constantly and not firing or going to lockout


  • Registered Users, Registered Users 2 Posts: 73 ✭✭laois hibby


    is ther any way of testing it to be sure?


  • Registered Users, Registered Users 2 Posts: 1,019 ✭✭✭anthonyos


    If you disconnect it and see does it fire


  • Registered Users, Registered Users 2 Posts: 73 ✭✭laois hibby


    tried it. Still the same


  • Registered Users, Registered Users 2, Paid Member Posts: 12,948 ✭✭✭✭Dtp1979


    tried it. Still the same

    Could be the control box


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 4,052 ✭✭✭jimf


    did you disconnect it from the control box or just pull it from the burner


  • Registered Users, Registered Users 2 Posts: 73 ✭✭laois hibby


    just pulled it from the burner


  • Registered Users, Registered Users 2, Paid Member Posts: 12,948 ✭✭✭✭Dtp1979


    just pulled it from the burner

    Disconnect it from the control box


  • Registered Users, Registered Users 2 Posts: 4,052 ✭✭✭jimf


    isolate power and disconnect it from control box if the cell is faulty burner will fire for approx. 4/5 secs and then go to lockout


  • Registered Users, Registered Users 2 Posts: 73 ✭✭laois hibby


    still the same. Unplugged photo cell from control box. Still just the fan blowing.


  • Advertisement
  • Moderators, Home & Garden Moderators Posts: 6,707 Mod ✭✭✭✭Wearb


    still the same. Unplugged photo cell from control box. Still just the fan blowing.

    Plug it back in and try the same with solenoid ie disconnect it and see if that makes it go to lockout.

    Any dampness around the control box?


  • Registered Users, Registered Users 2 Posts: 73 ✭✭laois hibby


    when unplugging the solenoid it does switch off but when i plug it back in it does the same again.
    It won't go back to lock out.
    There doesn't seem to be any dampness really


  • Closed Accounts Posts: 2,008 ✭✭✭scudo2


    when unplugging the solenoid it does switch off but when i plug it back in it does the same again.
    It won't go back to lock out.
    There doesn't seem to be any dampness really
    Faulty solonide. a cheap item that most service engineers or plumbing shops have in stock.
    Replacing it is a DIY job if you want, but servicing with a flue gas analyzer is a proper service not a DIY service.


  • Registered Users, Registered Users 2 Posts: 4,052 ✭✭✭jimf


    don't forget those rdb control boxes have a mind of their own as well

    rdb and riello coils in general I think I changed maybe 2 in 6 years

    maybe best to get somebody to have a look for you who will have whatever part is needed and get it set up properly as the master scudo pointed out


  • Moderators, Home & Garden Moderators Posts: 6,707 Mod ✭✭✭✭Wearb


    jimf wrote: »
    don't forget those rdb control boxes have a mind of their own as well

    rdb and riello coils in general I think I changed maybe 2 in 6 years

    maybe best to get somebody to have a look for you who will have whatever part is needed and get it set up properly as the master scudo pointed out

    Who said scudo was the master???? :)


  • Registered Users, Registered Users 2 Posts: 4,052 ✭✭✭jimf


    Wearb wrote: »
    Who said scudo was the master???? :)

    now as you mention it I think it was himself :D:D

    I do know he referred to me recently as a part timer :eek::eek:


  • Registered Users, Registered Users 2 Posts: 73 ✭✭laois hibby


    for some reason its working fine now. I had the solenoid un plugged for a while and plugged it back in and switched the power on and up she went. I have an engineer coming on Thursday. Thanks for your help


  • Moderators, Home & Garden Moderators Posts: 6,707 Mod ✭✭✭✭Wearb


    jimf wrote: »
    now as you mention it I think it was himself :D:D

    I do know he referred to me recently as a part timer :eek::eek:

    Compared to Scudo, we are all part-timers. I think scudo has been at them for nigh on 80 years by now :) I think he deserve the title of Master. As a matter of fact I am going to start a campaign to have Master beneath his name, rather than "registered user" What you think mods???


  • Closed Accounts Posts: 1,590 ✭✭✭agusta


    Wearb wrote: »
    Plug it back in and try the same with solenoid ie disconnect it and see if that makes it go to lockout.

    Any dampness around the control box?
    Just wondering why would someone unplug the solenoid?,I cant see what it proves whether it goes to lockout or not..


  • Moderators, Home & Garden Moderators Posts: 6,707 Mod ✭✭✭✭Wearb


    agusta wrote: »
    Just wondering why would someone unplug the solenoid?,I cant see what it proves whether it goes to lockout or not..

    On certain solenoid faults it can cause continuous running rather than lockout. If after disconnecting it, the boiler locks out, it proves that the solenoid was preventing the lockout.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 4,052 ✭✭✭jimf


    I was always told to disconnect a coil from its power source rather than just from the stem


    as its a magnetic field unless it has somewhere to discharge its energy it can cause burn out even a drill bit or screwdriver in the hole would probably save it

    lets await the masters view us pupils are probably talkin schite in his absence


  • Closed Accounts Posts: 1,590 ✭✭✭agusta


    Wearb wrote: »
    On certain solenoid faults it can cause continuous running rather than lockout. If after disconnecting it, the boiler locks out, it proves that the solenoid was preventing the lockout.
    My viewpoint,if photocell proved good by disconnecting from control box,

    , Continous running of a rdb burner can also be caused by the motor not giving 50 volts to control box and by a faulty control box.

    So if solenoid is perfectly good and you disconnect it the burner might go to lockout out, but its still not ruling out the motor or control box.I would think the only way to be sure, is to test the solenoid resistance, which should be 100ohms


  • Moderators, Home & Garden Moderators Posts: 6,707 Mod ✭✭✭✭Wearb


    agusta wrote: »
    My viewpoint,if photocell proved good by disconnecting from control box,

    , Continous running of a rdb burner can also be caused by the motor not giving 50 volts to control box and by a faulty control box.

    So if solenoid is perfectly good and you disconnect it the burner will go to lockout out but its still not ruling out the motor or control box.I would think the only way to be sure, is to test the solenoid resistance, which should be 100ohms

    So in your instance what was keeping the burner from going to lockout, seeing as it went to lockout when solenoid was disconnected?

    They can fail with different faults and resistance measurement is always a good idea, as is voltage on white wire of motor.


  • Registered Users, Registered Users 2 Posts: 4,052 ✭✭✭jimf


    I would think if the coil goes open circuit it can not complete the command from the control box hence continuous running

    as the coil in a sense in now the end of the circuit

    this is my understanding of open circuit voltage

    to test disconnect 1 wire from the coil I think the burner wont go to lockout

    agusta you have an rdb burner would you check please and let me know what happens


  • Moderators, Home & Garden Moderators Posts: 6,707 Mod ✭✭✭✭Wearb


    I think open circuit would cause lockout. It is the partly burned out wiring that causes continuos running when caused by solenoid.
    Perhaps the master will confirm this.


  • Registered Users, Registered Users 2 Posts: 4,052 ✭✭✭jimf


    Wearb wrote: »
    I think open circuit would cause lockout. It is the partly burned out wiring that causes continuos running when caused by solenoid.
    Perhaps the master will confirm this.

    but current can only exist when the circuit is closed


  • Moderators, Home & Garden Moderators Posts: 6,707 Mod ✭✭✭✭Wearb


    jimf wrote: »
    but current can only exist when the circuit is closed

    There will be different resistance depending on how much damage there is to the coil, so the current/resistance may not be what the control box expected.

    Oh where is Shane when I need him :(


  • Registered Users, Registered Users 2 Posts: 4,052 ✭✭✭jimf


    Wearb wrote: »
    There will be different resistance depending on how much damage there is to the coil, so the current/resistance may not be what the control box expected.

    Oh where is Shane when I need him :(

    snooping around in the backround bursting his whole laughing at us job****es talking through our rear orifices :eek::eek:


  • Closed Accounts Posts: 1,590 ✭✭✭agusta


    If a rdb solenoid goes open circuit,the motor would run continous.Also if the two wires are removed from solenoid the motor should still run continous as its and open circuit.
    my take how to control box and solenoid coil communicate

    A/ control box gives 27 volts dc to solenoid coil [to pull in needle valve]
    V=IR
    27=I x100
    I=0.27 amps
    control box looks for 0.27 amps approx back through the blue wire.

    B/when the controls box gets 0.27amps approx back to the control box it drops the voltage being send out through the brown wire to 3 volts [to hold needle valve]
    V=IR
    3=I X 100
    I=0.03amps
    When the burner is in operation the control box should be receiving approx 0.03 amps approx back through the blue wire to the control box

    then again i could be wrong:)


  • Advertisement
  • Moderators, Home & Garden Moderators Posts: 6,707 Mod ✭✭✭✭Wearb


    agusta wrote: »
    If a rdb solenoid goes open circuit,the motor would run continous.Also if the two wires are removed from solenoid the motor should still run continous as its and open circuit.
    my take how to control box and solenoid coil communicate

    A/ control box gives 27 volts dc to solenoid coil [to pull in needle valve]
    V=IR
    27=I x100
    I=0.27 amps
    control box looks for 0.27 amps approx back through the blue wire.

    B/when the controls box gets 0.27amps approx back to the control box it drops the voltage being send out through the brown wire to 3 volts [to hold needle valve]
    V=IR
    3=I X 100
    I=0.03amps
    When the burner is in operation the control box should be receiving approx 0.03 amps approx back through the blue wire to the control box

    then again i could be wrong:)

    Your figures look correct ( I haven't done the calculation) but the solenoid going open circuit is the same as having it disconnected from control box. So open circuit solenoid doesn't cause continuous running. It is the incorrect resistance that causes continuous running, not total open circuit.
    Perhaps I am not being very eloquent on my explanation and not getting my point across or else JimF may be right. But I doubt if a Munster man would know more than a Leinster man. They have been living off beating all blacks for way too long :))))))
    Ok back to my first Xmas party. It is starting to come to life and time for my rendition of BOOLAVOGUE.