riello 40 oil pump problem

  • 30-11-2011 02:30PM
    #1
    Registered Users, Registered Users 2 Posts: 17


    i cannot adjust the pump presssure. i have a gauge on and it flickers from 16 to 20 bar. no matter what way i adjust the screw there is no change. any ideas gladly welcome


Welcome!

It looks like you're new here. Sign in or register to get started.
«1

Comments

  • Closed Accounts Posts: 902 DoneDL
    ✭✭✭


    Gauge might be on its way out but aiir in the oil pipe, drive coupling worn, bypass screw fited when it shouldn`t be, blocked filter. 16 or 20 bar is not welome on a domestic oil burner, its far, far too high.


  • Registered Users, Registered Users 2 Posts: 2,842 Billy Bunting
    ✭✭✭


    okeedokee wrote: »
    i cannot adjust the pump presssure. i have a gauge on and it flickers from 16 to 20 bar. no matter what way i adjust the screw there is no change. any ideas gladly welcome

    Why did you want to adjust the oil pressure ?


  • Registered Users, Registered Users 2 Posts: 17 okeedokee


    thanks for the help, problem was air. turned the oil off ,fully drained the pump and lines then re-primed and burner fired up first time.


  • Registered Users, Registered Users 2 Posts: 44,079 Micky Dolenz
    ✭✭✭✭


    okeedokee wrote: »
    thanks for the help, problem was air. turned the oil off ,fully drained the pump and lines then re-primed and burner fired up first time.


    Nice one,

    And there was me changing the pump :P


  • Hosted Moderators Posts: 3,496 DGOBS
    ✭✭✭


    Wildly fluctuating oil pressure is nearly always a sign of oil starvation, the gauge jumps about (assume you had tried turning it up, when it was jumping at so high a pressure) but would usually be more of partial blockage that air.

    If in doubt, always fit a vacuum gauge (see they do have uses!!) and check to see if the pump is ok, and if you see a pressure generated on the vacuum, it's a fuel/filter/blockage (assuming the tank isn't below the pump level)


  • Advertisement
  • Closed Accounts Posts: 185 chimmy chonga
    ✭✭


    My Riello 40 pump works intermittently what can cause this? This happened over the Christmas so I took the pump off and checked the filter gave it a general clean re installed it and off she went. It kept going until I switched it off but when I tried to re start –nothing. Any ideas? I checked the fuel supply and all is wel, I’m getting a spark but the nozzle is dry.


  • Registered Users, Registered Users 2 Posts: 2,842 Billy Bunting
    ✭✭✭


    It kept going until I switched it off but when I tried to re start –nothing.

    Is the motor/pump actually running :confused:


  • Hosted Moderators Posts: 3,496 DGOBS
    ✭✭✭


    Sounds like a pump or solenoid from the limited info given


  • Closed Accounts Posts: 185 chimmy chonga
    ✭✭


    Is the motor/pump actually running :confused:
    Yes the pump runs for about 5 seconds then lock out.


  • Hosted Moderators Posts: 3,496 DGOBS
    ✭✭✭


    If solenoid is good, you have fuel, and blast tube remains dry (ie no fuel into chamber) then your pump is knackered


  • Advertisement
  • Closed Accounts Posts: 185 chimmy chonga
    ✭✭


    DGOBS wrote: »
    If solenoid is good, you have fuel, and blast tube remains dry (ie no fuel into chamber) then your pump is knackered
    I have to agree with you there - I checked around and they have one in Heatmerchants €95. Can I just replace the old pump or do I need to have it commissioned?


  • Registered Users, Registered Users 2 Posts: 17 okeedokee


    DGOBS wrote: »
    If solenoid is good, you have fuel, and blast tube remains dry (ie no fuel into chamber) then your pump is knackered
    I have to agree with you there - I checked around and they have one in Heatmerchants €95. Can I just replace the old pump or do I need to have it commissioned?

    Are you sure the link from the motor to the pump is ok , they do get worn. Do you have a gauge to fit on the pump to check the pressure to make sure the pump is turning.


  • Registered Users, Registered Users 2 Posts: 2,842 Billy Bunting
    ✭✭✭


    I have to agree with you there - I checked around and they have one in Heatmerchants €95. Can I just replace the old pump or do I need to have it commissioned?

    Have you eliminated the solenoid? because if not and you replace the pump you will be back to square one. You will at least need a oil presure gauge, ideally it should be commissioned.

    The link (Drive coupling) okeedorkee refers to will be visible when the pump is removed


  • Hosted Moderators Posts: 3,496 DGOBS
    ✭✭✭


    I have only ever really come across worn couplings where the appliance is very old, or there is a pump issue causing excessive wear


  • Closed Accounts Posts: 185 chimmy chonga
    ✭✭


    okeedokee wrote: »
    Are you sure the link from the motor to the pump is ok , they do get worn. Do you have a gauge to fit on the pump to check the pressure to make sure the pump is turning.
    I don't have a gauge I thought that the pump would have been tested in the factory.
    The plastic link is a bit floppy so I'd need a new one of those anyway. I've since found out that the burner is about fifteen years old and it doesn't look as though anyone has be at it in quite a long while.


  • Closed Accounts Posts: 185 chimmy chonga
    ✭✭


    DGOBS wrote: »
    I have only ever really come across worn couplings where the appliance is very old, or there is a pump issue causing excessive wear
    OK thanks - the burner is in an old house and I believe it's about fifteen years old.


  • Hosted Moderators Posts: 3,496 DGOBS
    ✭✭✭


    At 15 years old, the wise move would be replace the burner (comes with a 1 year warranty) not just the pump

    The pumps are preset in the factory, but have found plenty pre-set to 6.5bar!, and different appliances and fuels require different set pressures


  • Closed Accounts Posts: 185 chimmy chonga
    ✭✭


    DGOBS wrote: »
    At 15 years old, the wise move would be replace the burner (comes with a 1 year warranty) not just the pump

    The pumps are preset in the factory, but have found plenty pre-set to 6.5bar!, and different appliances and fuels require different set pressures
    Yeah I agree, however due to overspending at Christmas I don't have the 3-400 for a new burner, I'm up to my goolies in debt just to have this place! Thanks for your help :)


  • Registered Users, Registered Users 2 Posts: 17 okeedokee


    Sometimes you can pick up 2 nd hand burners complete and serviced for 100 - 150 euro. Check some of the smaller companies that are upgrading boilers at the moment, you might pick one up that was replaced


  • Registered Users, Registered Users 2 Posts: 17 okeedokee


    okeedokee wrote: »
    Are you sure the link from the motor to the pump is ok , they do get worn. Do you have a gauge to fit on the pump to check the pressure to make sure the pump is turning.
    I don't have a gauge I thought that the pump would have been tested in the factory.
    The plastic link is a bit floppy so I'd need a new one of those anyway. I've since found out that the burner is about fifteen years old and it doesn't look as though anyone has be at it in quite a long while.
    The reason for the gauge is to check the oil pressure, on mine I had no oil and the pressure was really high, pressure for kerosene is 8 - 10 bar


  • Advertisement
  • Closed Accounts Posts: 185 chimmy chonga
    ✭✭


    okeedokee wrote: »
    Sometimes you can pick up 2 nd hand burners complete and serviced for 100 - 150 euro. Check some of the smaller companies that are upgrading boilers at the moment, you might pick one up that was replaced
    Great idea! Can you suggest a place?


  • Registered Users, Registered Users 2 Posts: 17 okeedokee


    okeedokee wrote: »
    Sometimes you can pick up 2 nd hand burners complete and serviced for 100 - 150 euro. Check some of the smaller companies that are upgrading boilers at the moment, you might pick one up that was replaced
    Great idea! Can you suggest a place?
    Golden pages, don't know anyone direct. Try a fresh post specifically for a 2nd hand burner , you never know your luck


  • Registered Users, Registered Users 2 Posts: 2,842 Billy Bunting
    ✭✭✭


    Try adverts.ie or donedeal.ie, remember! you will still need to commision it for your boiler. :eek:


  • Closed Accounts Posts: 185 chimmy chonga
    ✭✭


    okeedokee wrote: »
    Golden pages, don't know anyone direct. Try a fresh post specifically for a 2nd hand burner , you never know your luck
    Thanks !:)


  • Closed Accounts Posts: 185 chimmy chonga
    ✭✭


    Try adverts.ie or donedeal.ie, remember! you will still need to commision it for your boiler. :eek:
    Gotcha ! Thanks.....


  • Closed Accounts Posts: 185 chimmy chonga
    ✭✭


    I put a new pump in and it worked well – for about a minute. The burner clicked off and then back on again and kept doing this. There is fuel getting to the nozzle and I’m getting a spark. The vent at the side is opening so I presume the pump is doing it’s job. I checked the solenoid and it’s working.
    I removed the photo cell and cleaned it and tried starting again without the cell and it made no difference. What else can I try?? Please…..


  • Hosted Moderators Posts: 3,496 DGOBS
    ✭✭✭


    Sounds like its either incorrectly set (too much air?) or recycling flue gases, again with no pressure gauge your at nothing!


  • Closed Accounts Posts: 185 chimmy chonga
    ✭✭


    DGOBS wrote: »
    Sounds like its either incorrectly set (too much air?) or recycling flue gases, again with no pressure gauge your at nothing!
    I took the burner out of the boiler and switched it on (in an open garage space) and I get a good flame but it switches off after a couple of seconds starts again and stops and so on...


  • Hosted Moderators Posts: 3,496 DGOBS
    ✭✭✭


    Again, this tells you nothing and a dangerous practice


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 1,289 .243
    ✭✭✭


    I took the burner out of the boiler and switched it on (in an open garage space) and I get a good flame but it switches off after a couple of seconds starts again and stops and so on...
    open up the air intake another cpl of notches and see what happens