Heat Pump Running Costs

1246789

Comments

  • Registered Users, Registered Users 2 Posts: 831 ✭✭✭staples7


    2421KWH for the year, 733 of this was hot water. A2 house 260m2

    Bar the hot water, heating was exclusively on night rate @ 14c inc VAT

    (Water heating can come on at any time) Mitsubishi Ecodan HP, during winter maintains a pretty constant 20' but could dip to 19' on freezing mornings but would recover back to 20'+

    2022 was 2559Kwh

    2021 was 2774Kwh

    Pretty consistent and very happy with cost, your looking at under E500 to heat the house and provide constant hot water for the year.



  • Registered Users, Registered Users 2 Posts: 455 ✭✭zoom_cool


    House is 200m2 two storey extensively renovated UFH down stairs Alu Rads upstairs used in 2023 2163Kwh that includes Hot water Stats are at 20/21 downstairs and 19 Upstairs hope this helps.



  • Registered Users, Registered Users 2 Posts: 831 ✭✭✭staples7


    HP running at about 20kw per day this cold week, could prob do with a bump as ive seen 19' by night in the house.



  • Registered Users Posts: 1,004 ✭✭✭mitresize5


    Can anyone tell me where or how I get the number of kilo Watts used by the heat pump?


    First full billing cycle since we moved into renovated A2 retro fit and got a nasty surprise 😮



  • Registered Users, Registered Users 2 Posts: 2,972 ✭✭✭dominatinMC


    Very low usage, I'm averaging about 30kWh at the moment due to cold spell.



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 2,972 ✭✭✭dominatinMC


    Depends on the brand of pump, but usually you should be able to access this type of information from an interface/panel on the indoor unit.

    How much was your bill? If you haven't had a heat pump before, it will take a while to fine tune it and get it right for your house



  • Registered Users, Registered Users 2 Posts: 1,071 ✭✭✭TimHorton


    Lad I know has a Geothermal System from 10 + years ago , His bills are massive and we looked at his half hourly usage the other day (recent smart meter installed) and this week he is using 150 to 180 units per day ! What can he do to lower the usage - Installer not interested in resolving.



  • Registered Users, Registered Users 2 Posts: 336 ✭✭Eleusis


    The half hour usage on esbn site are weird. You have to half them to get accurate reading. (Unless you did that already)?

    Even after halving it, that's high though.



  • Registered Users Posts: 1,004 ✭✭✭mitresize5


    Thanks, the bill was 860e


    I'll look at the control panel to try and get the usage.

    First heat pump alright. Any suggestions for fine tuning it.


    The one thing that jumps out is it maybe heating the hot water too hot. Is this a 'thing'? In the shower the temperature of the water is too hot when the wheel is turned just a little over half way.



  • Moderators, Home & Garden Moderators Posts: 6,425 Mod ✭✭✭✭graememk


    Regarding bill, the amount is what everyone sees, but what was the actual use, did you have an estimated bill before hand?

    As it's a retrofit, did you live in the house before hand? (If you did what did you spend on gas/oil before)

    If you have a smart meter, you can see your half hourly use on esb networks website (separate from your supplier) - if you pull out the data file, you need to divide the power by 2 to get the kWh(units on electricity bill)

    Do you have radiators or underfloor?

    Is the house hot enough?

    Regarding Domestic hot water(DHW), the shower are thermostatic, it will mix the hot and cold to the set temperature, the kitchen tap would be a better indication of how hot the water is.

    I'm sure there's room to improve.. but if you can't measure, you can't improve.



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 336 ✭✭Eleusis


    Yea it's really hard to know how to help without you providing as much info as you can.

    If house is block then it is going to use a lot in the 1st days to get building fabric up to temp. Timber frame much faster(but cools faster too).

    House size?

    Underfloor/rads?

    Heat pump: brand? Split/mono? Size?

    What temp is dhw set to heat to?

    Unit usage before and after renovation(not how much the bill was) . Ideally compare to unit usage of the same periodbut the year before. Or go into heat pump controller to find your usage. All heat pumps should show this.



  • Registered Users, Registered Users 2 Posts: 20,365 ✭✭✭✭Cyrus


    We used 73kwh in the house yesterday (no car charging), thats the highest i have seen it since i started tracking.

    I dont have a discrete HP monitor yet but on more temperate days (earlier in Jan) we would use around 40khw so all that extra is HP for sure.

    I had to increase the flow temps as it was struggling to get the house up to temp downstairs where we have UFH (and we installed solid wood floors over it so less efficient)



  • Registered Users, Registered Users 2 Posts: 2,530 ✭✭✭ECO_Mental


    My 7 day average is up around 30 kWh/day and that includes DHW eg showers which is pretty good. No where near as much as December 22 (42kWh/day) where we had another really cold spell but that was a lot more windy. What I find if its windy it sucks a lot more heat out but this spell of weather is way more settled.


    6.1kWp south facing, South of Cork City



  • Registered Users Posts: 164 ✭✭johndoe11


    46kwh for me on heating yesterday with air/water heat pump 250sq metre house, probably be similar if not more today. Considering it was barely above 0, I don't think it's too bad.

    676 kwh on heating and DHW used since the start of January. House is maintained at 21c downstairs and seems to hold this even at - 6.1c last night. I've got rid of setback during the day as house was getting cold.




  • Registered Users, Registered Users 2 Posts: 586 ✭✭✭idc


    Hoping this does not derail thread but what kind of electricity plan would most heat pump users have. Like is there a call for electricity for heatpump 24/7 or can the majority of heating been done via a day/night plan thus most of the kWh used is at least at a cheaper rate?

    Similarly would it crazy to switch to smart plan with like 3-4 hour EV cheap rate but higher day rate as you'd be using expensive day rate for most of the winter to power heatpump?



  • Registered Users Posts: 164 ✭✭johndoe11


    I'm on smart plan but not the cheap EV night window rate. I am now leaving it running the same temp 24hr, weather compensated, running more at night didnt work for me. It will typically use much less during the day during normal winter weather, but the current cold spell means its running much more during the day.

    I have solar and 15kwh battery so I can switch a good bit to night rate.

    I think you'd need a very big battery to make the EV cheap rate work with a heat pump.



  • Registered Users Posts: 1,064 ✭✭✭Mr Q


    My setup is similar to yours. I just let the HP run 24hrs and the DHW at night rate only.

    I can get the full day from the battery so it's all night rate cost anyway. With some losses in the cycle.

    I found it used more kWh per day if I heated the house more at night than letting it do it evenly through the day.



  • Registered Users, Registered Users 2 Posts: 2,972 ✭✭✭dominatinMC


    Similar usage here. 245 m2 house, living areas between 22-21 degC and bedrooms etc at 19 degC.

    Agree completely on the wind factor. Although I've a well insulated house, it's a very exposed site and when the storms hit, the house takes the brunt of them and I see the usage go up. Hence, not looking forward to this weekend!



  • Moderators, Home & Garden Moderators Posts: 6,425 Mod ✭✭✭✭graememk


    I suppose if you didn't have a big battery, using more to preheat at night is better cost wise.

    But if you have the battery, it doesn't matter to preheat at night. As long as you can stay on battery power.



  • Registered Users Posts: 164 ✭✭johndoe11


    You must have a big battery. For the last few weeks, I'd be a good bit shy of getting through the day rate hours even with a 15kw battery. I'm aiming to add another 15kw before next winter, that should cover me most days then.



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 2,646 ✭✭✭newhouse87


    Approx 28-30 this snap including dhw. Running fixed flow 31 9am to 10pm. House cools to 19/20 overnight and back to 21/22 by midday. Last winter would have been using 60+ on these days with installer settings 242sqm ufh.



  • Registered Users Posts: 1,064 ✭✭✭Mr Q


    30kWh battery, usable about 24kWh currently.

    Highest usage this week was 28kWh for the heating system over 24hrs. That is from a meter in a sub board that covers the HP, stats and pumps.

    I'm not sure how much of that was DHW but the battery is comfortably covering the 15 hours of day rate. I do have solar to top it up but it is East/West and has only averaged 4kWh per day for January.



  • Registered Users, Registered Users 2 Posts: 2,870 ✭✭✭MicktheMan


    Last winter would have been using 60+ on these days with installer settings 242sqm ufh.

    Do you mind me asking what were the errant installer settings?



  • Registered Users, Registered Users 2 Posts: 2,646 ✭✭✭newhouse87


    Wc set too high. My flow last winter would have been 40+ in these conditions, now 31. Not quite installer but I feel running house as 1 zone has made huge improvement too. Hall used be cold last winter but now flow going All over as all loops open and whole house feels Much warmer. Employing setback overnight as my house retains heat v well helps too.



  • Registered Users, Registered Users 2 Posts: 20,365 ✭✭✭✭Cyrus


    How do you open the zones?



  • Registered Users, Registered Users 2 Posts: 2,646 ✭✭✭newhouse87


    Remove actuator heads. Means when heat called for, all the areas of house will receive heat.



  • Moderators, Home & Garden Moderators Posts: 6,425 Mod ✭✭✭✭graememk


    Also turn the relevent thermostats of the removed heads down as low as possible so it doesn't generate a false all for heat



  • Registered Users, Registered Users 2 Posts: 2,646 ✭✭✭newhouse87


    All depends what way they want to run. Personally using 1 timed stat works for me, all other stats just tell me what temperature is in the room as I have then down @ 15 so will never call. Some people open zones but still use each room as stat on/off.



  • Registered Users, Registered Users 2 Posts: 336 ✭✭Eleusis


    Using approx 15kwh per day for heating and 3.5kwh for hot water. 220m2 recently renovated. Inside temps around 20-21 degrees. Running weather comp. Flows approx 27 degrees




  • Advertisement
  • Registered Users Posts: 126 ✭✭hero25


    how does one adjust the flow setting/temperature?



  • Registered Users, Registered Users 2 Posts: 2,646 ✭✭✭newhouse87


    Unreal usage in this weather. My hp cycles too much below x28 but not hope 27 would, get my house to 22/21.



  • Registered Users, Registered Users 2 Posts: 336 ✭✭Eleusis


    I have no idea how to see if my ecodan is short cycling. Does anyone know is there a way to find out?



  • Registered Users Posts: 164 ✭✭johndoe11


    That is unreal low. What part of the country are you in? Not the Midlands i bet with that sort of consumption and current weather!



  • Registered Users, Registered Users 2 Posts: 336 ✭✭Eleusis


    Yes in midlands. . Leitrim. Was -6 this morning at 7am



  • Registered Users, Registered Users 2 Posts: 2,646 ✭✭✭newhouse87


    Have you a lots of loops in your ufh? Haven't seen that low flow temp these conditions before.



  • Advertisement
  • Registered Users Posts: 114 ✭✭Scoopsire


    What type of work had you done on your house? Assume lots of insulation upgrades?



  • Registered Users Posts: 899 ✭✭✭ColemanY2K


    Used 40 and 45kWh over the previous two days respectively and averaging around 50 during this cold spell.

    What you say could be where I'm going wrong as I have removed the actuators but all the stats bar 1 are set to 21 degrees and were previously 22 or 23.

    It's a pity the cold spell is coming to an end as it'll be hard to judge if reducing the temp setting on the stats makes a difference.

    🌞 7.79kWp PV System. Comprised of 4.92kWp Tilting Ground Mount + 2.87kWp @ 27°, azimuth 180°, West Waterford 🌞



  • Registered Users Posts: 164 ✭✭johndoe11


    Fair play to you. My house is A1, If i ran 27 flow (with presumably 20-22 return), my wife would run me. The house would be 17/18 degrees. My flow is 32.5 at -6.

    Same temp here last night, I used more than you in about 6 hours.



  • Registered Users, Registered Users 2 Posts: 2,646 ✭✭✭newhouse87


    I would try running a fixed flow of 31 for say 13 hours and on again at 9am. See how the house reacts. That's my exact schedule. Best I found so far. Again though that doesn't mean it will work for your house. Have you insulation done?



  • Registered Users Posts: 899 ✭✭✭ColemanY2K


    Airtightness is just if not more important. I'm guessing they have an airtightness rating of less than 1 ACH and bags of insulation. Deep retrofits of bungalows can achieve passive levels of performance.

    🌞 7.79kWp PV System. Comprised of 4.92kWp Tilting Ground Mount + 2.87kWp @ 27°, azimuth 180°, West Waterford 🌞



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 336 ✭✭Eleusis


    13 loops. I think it's low cause build quality and insulation is very high. House has a continuous unbroken wrap of insulation. UFH throughout. It's also airtight, triple glazed with heat recovery.



  • Registered Users, Registered Users 2 Posts: 2,646 ✭✭✭newhouse87


    The unbroken wrap must be it, hard to get that done properly. I'd have the rest myself.



  • Registered Users Posts: 899 ✭✭✭ColemanY2K


    Almost finished, I reckon another two/three evenings and it'll be done. It's hard to get a good run at it with me having to work during the day, spend a couple hours in the evening with the little one and on top of that out of the country 2 days a week.

    Cheers for the advice. First thing I'll do is reduce the temp on the stats to see what happens and then Iook to set a schedule to see how the house reacts.

    🌞 7.79kWp PV System. Comprised of 4.92kWp Tilting Ground Mount + 2.87kWp @ 27°, azimuth 180°, West Waterford 🌞



  • Registered Users, Registered Users 2 Posts: 2,646 ✭✭✭newhouse87


    Hectic alright. Yeah just have 1stat calling for heat for the 13hours then have setback overnight. Open loops.bestvtry when insulation done. Note your current settings too as my way may not work for your house.



  • Registered Users, Registered Users 2 Posts: 520 ✭✭✭feelings


    Our a2w hit 75-85kw usage yesterday. Previous two days 55-65 each day, had been 20-25 up to the cold spell. 😔



  • Registered Users, Registered Users 2 Posts: 1,071 ✭✭✭TimHorton


    Is that what you were expecting when you installed the system?



  • Registered Users, Registered Users 2 Posts: 2,646 ✭✭✭newhouse87


    Label each actuator for what loop it is before removing. You could try dominatinmc approach first, fixed flow before my approach. He has similar usage to me.



  • Registered Users, Registered Users 2 Posts: 3,419 ✭✭✭randombar


    Hi Folks,

    Usage for the last four days with my ecodan split unit. (250m2 house)

    I've limited the flow rate to improve the COP (COP = 3 ish at the moment) and I've also disabled that immersion.

    I'm also using the temperature mode rather than weather comp, I've 4 hrs cheap rate so try and blast the heat in the place for four hours, unfortunately most of the cheap time is spent heating the water rather than space heating.

    Some people have said I should heat the water all the time rather than the cheap rate but that doesn't make sense to me.

    Should I be limiting the flow rate at all if I want to blast the heat? i.e. if I heat the place faster at 8c with a COP of 2.5 it's better than heating the place slower at 40c with a COP of 3.



  • Registered Users Posts: 899 ✭✭✭ColemanY2K


    ya i've done that. lets see how it goes today.

    🌞 7.79kWp PV System. Comprised of 4.92kWp Tilting Ground Mount + 2.87kWp @ 27°, azimuth 180°, West Waterford 🌞



  • Registered Users Posts: 1,004 ✭✭✭mitresize5


    Hi,

    Bill 860e - 2156 units used in billing period. Nothing to compare it to as we weren't in the house last year.

    House is block built with 72.5mm internal insulation and pumped cavity, 600mm insulation in the attic, triple glazing new windows and doors

    House size is 2350sq feet

    Underfloor under polished concrete downstairs, radiators upstairs

    Panasonic 9Kw heat pump

    DHW set to 54 degrees - seems excessive

    Stats set to 22 downstairs and 20 upstairs, have dropped them by 1 degree each

    ... the DHW looks like the first place to address, anything I've seen on line suggests 48/49 should suffice

    any suggestions appreciated

    thanks