Heat Pump Running Costs

Options
2456714

Comments

  • Registered Users Posts: 2,477 ✭✭✭ECO_Mental


    Here is my moving 7 day average of my heat pump to take up the ups and downs over the last 12 months practically. A1 new build house 210m2 House (A2 without Solar PV)

    As you can see during an average winter day its between 20-25 kWh/day, from about April to October I was doing about 5 kWh/day or less

    The big spike in December was obviously the very cold snap we had for a week or so. 2 adults and a 17 and 19 year old that like to take VERY long showers at least once a day so that contributes a lot to the consumption. Underfloor heating everywhere including upstairs and I think I have 13 zones!

    I am happy with it no stat set above 20 deg and all bedrooms and halls set to 19 degs. I log it using home assistant so I can see if its on all the time and usaully someone has set a stat to 22 degs or something.


    6.1kWp south facing, South of Cork City



  • Registered Users Posts: 1,341 ✭✭✭Nelbert


    Well insulated yes. House is 1970s semi-D post renovation (full gutting, 90mm dry lining on main house, 120mm on extension, 150mm underneath ground floor, spray foam in the attic dormer) still some queries on air tightness but nothing major.

    Heat pump set to heat on night rate gives us a pleasant wake up then solar gain can take us through to night rate most of the time (sometimes overheat us!).

    Recent automation to boost hot water if below a certain temp at 7am means less likely to heat water on day rate too.

    So mixture of insulation and being smart as possible on when to call for heat to keep costs down.

    With the milder weather of the last week I'm already seeing drop off in energy usage (improved efficiency and less heat demand).



  • Registered Users Posts: 1,408 ✭✭✭DC999



    Hats off @theintern + @zoom_cool. That's an amazingly low amount per day. To give a comparison, heating our 5x5m sitting room / kitchen (old 'leaky' house) is using the same as your whole house. That's heated between an electric rad and gas boiler rad and set to 20.5C.



  • Registered Users Posts: 443 ✭✭zoom_cool


    @DC999 thanks for comment I think more is to do with the auxiliaries and not the heat pump like flilow rates on the manifolds and heat pump on weather compensation and lots of plumbers don't want to know how to setup correctly. You need to tweak them until you hit the sweet spot.



  • Registered Users Posts: 700 ✭✭✭gandalfio


    Cheers for all the replies. We've managed to bring the daily usage right down through lots of tinkering. Last few days read 9.2, 8.8. 7, 6.6, and 4 yesterday.

    We've been leaving the downstairs stat at 18 once we go to bed and pretty much leave it there until the following evening.

    However, whilst our overall energy usage has come down greatly, it has plateaud and we're using the same amount of units per day whether the heat pump is running at 9kwh or 4. All other appliances, lights etc are being used in the same way each day.

    Any reason why this could be happening?

    Another issue were having is the following. Two of our bedrooms don't heat as well/retain heat as well the master bedroom.

    The master bedroom is always really warm and the rad is never turned above 3. Whereas the other rooms' rads are all turned to 5 and still have issues heating and retaining heat. 

    It seems that its more retaining the heat is the issue as the radiators have been tested and are working well.



  • Advertisement
  • Registered Users Posts: 1,341 ✭✭✭Nelbert


    If it's heat retention check for air tightness. Seals around windows and properly installed vents (with seals around it so that air travels through the intended part and not gaps around it).

    Other thing is location. Our rooms with south east facing windows call for less heat than our north west ones especially in winter.



  • Registered Users Posts: 8,745 ✭✭✭893bet


    Are those rooms on the north side of the house?

    Is there potentially additional air leakage in them?

    Your problem sounds like a heat retention issue overall. Was there an Airtightness test done on your house during build?



  • Moderators, Home & Garden Moderators Posts: 5,802 Mod ✭✭✭✭graememk


    Most likely that it is warmer outside.

    Do you notice a rise when more showers or baths are taken in a day? Your heating your hot water too.

    A 200L tank if heated by an immersion could easily use 10kwh.



  • Registered Users Posts: 700 ✭✭✭gandalfio


    One of the rooms is dual aspect, one window facing east and the other facing south. The other bedroom is facing west.

    No difference re shower usage etc. The overall meter reading is consistently the same every day the last week day. Even when one day on the heat pump was 9 and yesterday was 4.



  • Registered Users Posts: 700 ✭✭✭gandalfio


    We're only living in the house 6 weeks. Builder has sent Joule heat pump technicians round. They recalibrated the thermostats (stats were reading the temperature 2 degrees above what our own thermometer showed). But the heat retention issues remain in the two bedrooms and the downstairs bathroom. Joule suggested the stats might need to be moved, or the rooms need bigger radiators. But the builder is refusing to budge and won't offer anymore assistance. Is there anything else we can do here?



  • Advertisement
  • Moderators, Home & Garden Moderators Posts: 5,802 Mod ✭✭✭✭graememk


    No idea where to go re the builder. (although 4kwh a day for heat is pretty good!)

    but

    Wheres the thermostats for the bedrooms, All individual? or a shared stat?

    My thinking is : Changing the thermostatic valve, doesnt create a call for heat, just tries to put a upper limit of the heat.

    Master bedroom gets warm first, maybe its the first on the loop, the thermostat is also satisfied, heating turns off, other bedrooms get nothing. (even though they are at 5)

    What happens if you turn the master bedroom off completely?

    Are you taking meter readings for the Kwh value or is that just the heatpump?



  • Registered Users Posts: 700 ✭✭✭gandalfio


    The 4kwh per day was just yesterday when it pretty much no heat was called for for the day.

    There are 2 stats. One in the hall, and one on the landing.

    Haven't tried turning any rads off completely. We were told by the plumber never to turn any to 0. Any idea why?

    The readings I've been taking are under the daily/weeks usage statistics on the panel attached to the tank in the hot press. I'm also taking daily unit readings from the main energy meter for the house.



  • Moderators, Home & Garden Moderators Posts: 5,802 Mod ✭✭✭✭graememk


    I understand, so the 4kwh is heat only then? Not the rest of the house.

    Don't know why not to turn off completely, possibly to do with efficiency but once temperature is reached for the rad valve it would be closed see this : (heat geek)

    https://youtu.be/zpTVIeUh04E

    But as one room is too warm I'd be considering closing the lockshield on the other side of the radiator a bit more, to restrict flow to that radiator and allow more heat to go to the other rooms.

    The other rooms might not be properly heated as the thermostat could be cutting out too soon. Thats why I suggested to turn the master bedroom off completely, just to see what changes.



  • Registered Users Posts: 700 ✭✭✭gandalfio


    Yeah the 4kwh is for heat only. But the meter readings for entire house are the same each day even though the heat is fluctuating from 10kwh per day to 4kwh. Can't understand why.



  • Registered Users Posts: 586 ✭✭✭theintern


    The only way to work this out is to get something like a Shelly EM (I have one of these) and hook it to your heat pump circuit and the main circuit. Or get an _Emporia Vue 2_ (I think that's the name) that seems to have a bunch of clamps so you could clamp every circuit.


    Then buy some power monitoring plugs to monitor specific appliances like the washing machine etc.

    You'd be surprised how much some appliances use like the cooker, washing machine etc. A night rate meter and sticking these on timer can make a big difference. Home Assistant provides a great dashboard to bring this all together.


    EDIT - I was thinking of the Emporia Vue 2.

    Post edited by theintern on


  • Registered Users Posts: 586 ✭✭✭theintern


    I just went into the settings of my unit. My above estimations weren't including power used by the indoor unit, just what was used by the outdoor unit (different circuits on my fuse box), so were under estimating overall system usage. The nice thing is now I have readings for the total electricity input to my A2W system over the year. Here it is.

    140sqm new build, A2. Thermostats generally @ 21 degrees.

    Figures are total energy units used / total heat units generated (heat pumps being greater than 100% efficient

    Jan - 467 / 1396

    Feb - 318 / 956

    Mar - 262 / 726

    Apr - 136 / 367

    May - 69 / 153

    June - 65 / 146

    July - 68 / 134

    Aug - 62 / 139

    Sep - 87 / 215

    Oct - 204 / 645

    Nov - 339 / 1084

    Dec - 683 / 1657

    Total - 2760 / 7618 - 276% efficiency.

    7.56 units per day consumed

    Max units per day across a month - 22.03 (Dec)

    Min per day across a month - 2 (Aug)

    On my current price plan (EI, 5.5 discount, day/night meter, assuming usage of 66% day rate vs 33% night rate usage) works out at a hair under €1000 for the year. €998 to be precise. Assuming 2023 is like 2022. In reality the cost was less than this for 2022, as I was on a better plan.



  • Registered Users Posts: 700 ✭✭✭gandalfio


    How do you find the total units for indoor and outdoor combined? Are the units shown on the digital panel on the hot water tank for indoor or outdoor?

    Separate question, is 60 degress for 20 minutes once a week sufficient for anti-legionella?



  • Registered Users Posts: 586 ✭✭✭theintern


    It's a Daikin unit and shows the total units consumed. The units it displays as used for heating are the exact same as what my clamp is measuring on the 'outdoor' circuit in my circuit board, and then on top of that there's energy used to heat water. It shows each separately and also shows the total.



  • Registered Users Posts: 1,341 ✭✭✭Nelbert


    This is good info, my usage is similar, but my monitoring only started properly in August and I've been eager to establish what my water heating requirement is to consider an Eddi for hot water in summer. I thought it would be a purchase based on convenience rather than return on investment financially. But if you consider your March to September usage it's ~3 years payback (rough day rate of 40c longer if you consider night rate but with my hot water usage profile day is more appropriate for me) which is reasonable given the additional convenience Vs cheaper alternatives that wouldn't be as smart in terms of limiting to excess.



  • Registered Users Posts: 1,408 ✭✭✭DC999


    If you have a D/N meter heat the water at night and stop just before cheap rate ends. Then you only need to boost during day.

    If it's a well insulated tank, and ideally large enough too, set the immersion to a hotter temp. Means you've stored hotter water and dropping a bit in temp during the day matters less. Then it won't need much boost immersion heat for showers later in the day.

    You can try that before getting an Eddi and see how it goes.



  • Advertisement
  • Registered Users Posts: 1,341 ✭✭✭Nelbert


    I already do that. The water gets a boost at 7am back up to 50⁰.

    An Eddi could bring me to 65⁰ on a sunny day which would eliminate the need for the boost (post Legionella Cycle to 65 we get 2 showers and it drops to 50-55 depending on length).

    We have random daytime showers and baths for the small people in the house as necessary along with washing up etc that often means another boost on day rate. I could avoid the day boost and likely the 7am boost during summer with an Eddi is the thinking.



  • Registered Users Posts: 700 ✭✭✭gandalfio


    Is 60 degress for 20 minutes once a week sufficient for anti-legionella?



  • Registered Users Posts: 1,341 ✭✭✭Nelbert


    Mine goes to 65 every 15 days for 30 mins (goes to 67 before turning off so never drops below 65 that quick anyway given its done at 2am).

    I've no idea what the guidance is on it.



  • Moderators, Home & Garden Moderators Posts: 5,802 Mod ✭✭✭✭graememk




  • Registered Users Posts: 778 ✭✭✭staples7


    Bumping this thread, what types of kWh usage are people seeing from Heat pumps this winter.

    Im averaging out around 10 this month 2.5 of that is hot water.

    The remaining 7/8 is on night rate at 14c so happy enough.

    When we get a cold snap that daily usage will go up a little. House constant 20-21 degrees.

    *EcoDan Mitsubishi HP. 2800sqft A2 house, family of 5 home at home all day



  • Registered Users Posts: 2,854 ✭✭✭dominatinMC


    That seems like very reasonable usage. I have same HP, same size house (roughly) and same temperatures, and I'm using 14kWh/day on average. Tbh I was happy enough with that before seeing your post 😂



  • Registered Users Posts: 848 ✭✭✭keno-daytrader


    3.06kWh/day heating

    2.37kWh/day hot water

    so about 5.5kWh/ day for both, 16 days so far this month.


    Ecodan hp , 2450 sqft A1 house. 21.5c house 48c hot water

    ☀️ 6.72kWp ⚡2.52kWp south, ⚡4.20kWp west



  • Registered Users Posts: 778 ✭✭✭staples7


    I think you're still pretty good there, I could easily be up to that if I ran the HP a little longer. And will hit that at colder temps too.



  • Registered Users Posts: 778 ✭✭✭staples7




  • Advertisement
  • Registered Users Posts: 848 ✭✭✭keno-daytrader


    Yeah, I went and took the course and did the airtightness myself. It was a real pain in the ass, but so worth it in the end as most builders dont give a hoot once it comes in under regs, and the current regs are a bit of a joke.

    Although Im not on night rate, so I only run the hp between 10am and 6pm.

    ☀️ 6.72kWp ⚡2.52kWp south, ⚡4.20kWp west