Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Hi all! We have been experiencing an issue on site where threads have been missing the latest postings. The platform host Vanilla are working on this issue. A workaround that has been used by some is to navigate back from 1 to 10+ pages to re-sync the thread and this will then show the latest posts. Thanks, Mike.
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

Cable Size between CU & Inverter

  • 02-02-2023 5:39pm
    #1
    Registered Users, Registered Users 2 Posts: 60 ✭✭


    Hi All,

    The folks are looking at solar (6kw inverter) and have a 6mm2 cable running between the shed and house.

    What would be the max distance between the CU & Inverter before it becomes unsafe?

    They will be getting a sparky out to provide guidance etc but they are like hens teeth at the moment.

    Obviously they would like to avoid digging the garden up but while they wait for the sparky, they are happy to craic on with ground works if they are way outside the max distance on a 6mm2.

    Thanks.



Comments

  • Moderators, Sports Moderators Posts: 19,196 Mod ✭✭✭✭slave1


    I've a 16m 6sq run, no issues



  • Registered Users Posts: 163 ✭✭johndoe11


    I had a 40m run to the shed that was 6mm2 cable. The installer wouldn't commission without it being a 16mm2. I have a 6kw hybrid inverter. A messy and costly job, but it's done now forever.



  • Registered Users, Registered Users 2 Posts: 60 ✭✭Scoobydoobydoo101


    Thank you @slave1 that's certainly good info.


    @JohnDoe that is precisely why they would like to avoid the work. I have 10mm2 myself over a similar run with no issues


    Looking at some online calculators they seem to suggest that a 6mm2 is suitable based on 30amps over 40m with 10%voltage drop....



  • Registered Users Posts: 163 ✭✭johndoe11


    Yeah I think 10mm2 would have been fine, but they said if going to that effort just put 16mm2 in. The said if it was a 6mm2 just dedicated to solar it might be ok, but I'm no expert on that. I just left the old 6mm2 in and ran the new cable to a new board beside the old one. Not much change from 1k when it's all done.