  • Registered Users, Registered Users 2 Posts: 510 ✭✭✭boosabum


    This is what we have become 🤣🤣🤣



  • Registered Users, Registered Users 2 Posts: 2,602 ✭✭✭SD_DRACULA


    I'd say a lot more than that in reality, the solis import value is way off

    image.png

    Seems to always use a tiny bit when the cooker/oven are on (even though usage is under 5kwh) quite annoying actually.

    Solis reports 0kwh import for most days this month but that is fake news in reality 😥



  • Registered Users, Registered Users 2 Posts: 1,469 ✭✭✭MAULBROOK


    Ah don't kill my buzz 😃. I don't mind i still have €121 credit left from the government money



  • Registered Users, Registered Users 2 Posts: 6,444 ✭✭✭championc


    And when I signed up with EI in Jan on their EV plan, I got a €300 credit. So added to the €200, I have only used about €180 in total since Jan. I could easily see myself getting all the way to October on credits !!!



  • Registered Users, Registered Users 2 Posts: 1,469 ✭✭✭MAULBROOK


    I got €210 credit when I signed up with EI last July. This has been the cheapest year for electricity.



  • Advertisement
  • Posts: 0 [Deleted User]


    When I looked at the Solis app a few times recently it appears my battery is discharging when it gets to 100%, despite there being plenty of excess to power the house etc.


    E.g.,

    -4Kw of power from solar

    -200W coming from the battery. Battery is at 100%.

    3. 2kW to house

    1kW to grid.


    So, it looks like theres power coming from the battery when not needed? Anyone seen this? Is my battery overcharging?

    I'm sure I've seen this question asked before here, but the search is brutal since they changed the site.



  • Registered Users, Registered Users 2 Posts: 12,890 ✭✭✭✭DrPhilG


    I got €200 credit with SSE, plus €675 credit from VW.


    Still nearly €700 in credit currently.



  • Registered Users, Registered Users 2 Posts: 54 ✭✭BoxerX


    I hope its okay to post a series of questions here. As I've got a deposit down on a fit happening in three weeks time, there are a few little things I'm just wanting to confirm and as I've clearly bored the pants off the installer, I thought I'd ask here.

    1 - I have a Solis Inverter being installed. The installer said it's likely to be mounted in the loft. My loft gets incredibly hot; in excess of 37 degrees one day last week. I know the Solis has a maximum of 60 degrees ambient temperature but how hot do these things get? I ask as if the product itself adds to the current ambient heat, we could be getting close to maximum. Or am I overthinking this?

    2 - I'm having an Eddi fitted. Can the Eddi work without a CT clamp? I ask as the immersion is dual element and to use the two outputs from the Eddi, the device needs to be mounted in the Hot Press which is away from the Consumer Unit. If the answer is 'no', can I safely assume I will need a Harvi?

    3 - Is access needed to the (outside) meter cupboard for any connections? Mine is inaccessible from inside the house and the Consumer Unit is remote to the meter box. Again, I ask as any connections needed will have to be surface run, not something I am enormously happy about!

    Thanks in advance for any answers, or remove if not allowed for any reason (new to this forum)



  • Registered Users, Registered Users 2 Posts: 563 ✭✭✭The devils


    1. My solis is in a lean too I built recently. The internal temp was 59.2 degrees then other day, at the moment its 50.3. They can get up to 75

    "void over heating ambient air temperature must be considered when choosing the inverter installation location. Ginlong recommends using a sun shade minimizing direct sunlight when the ambient air temperature around the unit exceeds 104°F/40°C."



  • Moderators, Science, Health & Environment Moderators Posts: 4,790 Mod ✭✭✭✭Tree


    Eddi needs a CT, doesn't have to be a Harvi if the installer can run cable to the consumer unit (which they'll be doing from your inverter anyway).

    My meter is far from the consumer unit, that would have been fine but my consumer unit is technically a secondary unit as I have the car charger installed between it and the meter. Installer had to run cables to the far side of the car unit rather than the normal consumer unit as planned.



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 6,444 ✭✭✭championc


    Have you any plans to install a Zappi ? Cat's can be connected to a Zappi and the Zappi and Eddi share the info internally over their radio / hub network



  • Registered Users, Registered Users 2 Posts: 54 ✭✭BoxerX


    No plans at the moment to install a Zappi as I don't have an EV and it will be several years before we do.

    I think the best option is a Harvi.

    Thanks!



  • Registered Users, Registered Users 2 Posts: 54 ✭✭BoxerX




  • Registered Users, Registered Users 2 Posts: 616 ✭✭✭idc


    Just got a zappi. Have been using granny cable last few weeks which has been great as it only uses 2.2 kW meant during middle of day I could be charging car and still charging battery (just much slower!). Is there a setting on Zappi i can do something similar? ie set it to charge the car at minimum of 1.4kW while the house batteries are still also charging but if batteries hit 100% the zappi will then use the 1.4 or higher?



  • Registered Users, Registered Users 2 Posts: 563 ✭✭✭The devils



    If zappi is set to eco it will draw from solar/grid ( it doesn't care where it gets energy from) @ 1.4kw, however if for example the batteries are full and your Pv is producing 4kw , well then your zappi will take that full amount and put into car.



  • Registered Users, Registered Users 2 Posts: 6,444 ✭✭✭championc


    Slight correction - the solar / grid / battery will be used when solar drops below 1.4kW, to bring charging up to 1.4kW

    But when solar excess exceeds 1.4kW, only solar is used.

    So ECO can drain your battery if you don't have some automation controlling it (or keep an eye on it)



  • Registered Users, Registered Users 2 Posts: 3,492 ✭✭✭randombar


    By any chance does anyone have a spare zappi CT clamp? The price for postage of them from myenergi is just wrecking my head.



  • Registered Users, Registered Users 2 Posts: 459 ✭✭munsterfan2




  • Registered Users, Registered Users 2 Posts: 23 MTK_1966


    Hi, My installer is coming next month to install panels. I am just wondering how this typically works.

    Do they send someone out to inspect, and plan the install with me beforehand, or do they just turn up on the day and start installing?

    Do the installers typically toidy up after themselvses e.g if they need to drill holes in walls do they re-plaster around the area or do I have to do that?

    I have a small wind turbine that I can install and it crosses my mind that I should hook it up to the inverter also. Is this possible?

    I am beginning to panic a little as the date approaches. Anything I should be doing to plan for this?



  • Registered Users, Registered Users 2 Posts: 54 ✭✭BoxerX


    I understand where you're coming from!

    In less than three weeks I too have the installers in to fit a solar PV system. The lack of communication is worrying me too.

    I've thought the system through with the help from people on here and already purchased a Harvi and an extra CT clamp as there is no easy route through from the Hot Press where the immersion and Eddi will be, and the Consumer Unit. Even if the installer knows of a way, it has to be easier for him to use a Harvi to send the signal....and the extra CT clamp will add the import figure onto the Eddi display.

    I've never known installers of anything to tidy up after themselves! When I finished this house (I bought it at first fix) the electrician, plumber, plasterers and carpet fitters all left a mess behind. The plumber pulled up my block paving outside to run an oil pipe and didn't re-lay it. I was 4 years on the sites in the UK and I left anywhere I went at least as tidy as I found it, seems things have changed.

    Sorry I couldn't be more help, but you are not alone in your panic, for what its worth.



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 1,689 ✭✭✭THE ALM


    Our installers just turned up on the day and after a brief chart about what was involved they went about there business, wouldn't have known they were there other than a load of panels on the roof and having to pick up a few cable ties afterwards.



  • Moderators, Education Moderators, Home & Garden Moderators Posts: 8,299 Mod ✭✭✭✭Jonathan


    My installer provided a Harvi free of charge as it was easier/quicker than trying to pull the CT cable. You might be able to return the items you bought if they aren't used.



  • Registered Users, Registered Users 2 Posts: 3,492 ✭✭✭randombar


    I wasn't a big fan of the Harvii myself, found it wasn't that accurate at lower watts.

    Also you'll be very surprised at how fast the installation is after.



  • Registered Users, Registered Users 2 Posts: 54 ✭✭BoxerX


    That's exactly my thinking. I reckoned it was better to have two than to have none 👍️



  • Registered Users, Registered Users 2 Posts: 6,444 ✭✭✭championc


    Just regarding the wind turbine, that would emit DC but maybe at 12v or 24v. It would have to go through a charge controller to give a more balanced output and realistically into it's own inverter.

    Be aware anyone that windings and magnets on Chinese clones are inferior and have been shown to generate fook all



  • Moderators, Education Moderators, Home & Garden Moderators Posts: 8,299 Mod ✭✭✭✭Jonathan


    Details of new Solis 6G Hybrid inverters announced on their FB page earlier: https://www.facebook.com/2092924957605425/posts/pfbid0G5W9y92umKAPeusTMjSHn49MWh5xVPhtA5Wgy2mhuAKrv9441oVS6Q9nhuTGD8tEl/


    125A battery charge/discharge on the 6kW model looks like a good enhancement, along with ability to parallel multiple units.


    @DrPhilG maybe you should have waited a few weeks. 😉



  • Moderators, Motoring & Transport Moderators Posts: 6,524 Mod ✭✭✭✭Irish Steve


    Even more interesting for me is that there is also a 3 phase unit, with parallel connection option, and an ability to also support generator communication, and as it's Solis, it should come with Irish regulatory approval. That could make life a lot easier for me, given the system I want here.

    It also will make multiple panel orientation a lot easier, with 2 to 4 MPPT's available.

    The full technical spec and manual for the 3 phase unit isn't on line yet.

    The interesting things now will be the price, and availability.

    Shore, if it was easy, everybody would be doin it.😁



  • Registered Users, Registered Users 2 Posts: 12,890 ✭✭✭✭DrPhilG


    Well my upgrade isn't happening yet, at least not the inverter. So who knows what he'll show up with!



  • Registered Users, Registered Users 2 Posts: 12,890 ✭✭✭✭DrPhilG


    Expansion day today. Unfortunately for me, I miscalculated the panel length when landscape. The lads counted it up and if I moved to 2 rows of 6 in landscape, I'd be only about 50mm from the left/right sides so not an option.


    Instead they're going to move the existing 9 portrait on the garage down a bit and put all 4 new ones in landscape above. Not as aesthetically pleasing but not to worry.


    It actually means I can fit more. With a 2x6 landscape layout it would be 12 max. This way I can fit all 4 new panels on the garage which is south facing, and leave the house as it is.


    13 panels @40v is comfortably within the 600v max per string. Plus if I ever track down 2 more, I'll chuck them on the house roof for 13 each, 8kWp system.



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 6,444 ✭✭✭championc


    I wouldn't have been worrying about the 50cm, since you'll no longer be needing to worry about the grant. And sure it's low down and around the back too