Home charge points (purchase/problems/questions) (See mod note post#1)

1123124126128129297

Comments

  • Registered Users, Registered Users 2 Posts: 12,995 ✭✭✭✭the_amazing_raisin


    I'd wonder about what you're using in the shed which requires 3 phase, unless you've a piece of equipment which will only run on 3 phase then you can get away with just upgrading your single phase supply

    Also, you'll likely be charging the car at night time to take advantage of cheaper electricity, so as long as you avoid any midnight welding or carpentry then you're probably safe

    If you have a charger with load balancing then the issue is mooted, the charger will reduce power down to zero if needed to prevent the house supply from being overloaded

    The Zappi should cover everything you need. The issue with the ID.3 is specific to that car and is because VW have a deep sleep mode which the Zappi sometimes can't wake it up from, it hasn't been reported on any other cars AFAIK

    "The internet never fails to misremember" - Sebastian Ruiz, aka Frost



  • Registered Users, Registered Users 2 Posts: 273 ✭✭electrofelix


    tl;dr - 3-ph + 22kW req getting dropped unless the electrician indicates I will definitely need at least 20kVA special connection. If 16kVA is enough to cover our future reqs regarding a extension in a few years, then it's just not worth it as has been patiently explained to me a few times now.
    KCross wrote: »
    The decision you need to make there is around how likely you are to get 3-phase in the future. Nothing you have described would suggest you need 3-phase but only your electrician and your wallet can really answer that.

    Bear in mind its not just the connection charges from the ESB, there is also the electrician charges for (re)wiring your consumer unit for 3-phase. It wont be cheap so you would need a really good reason to retrospectively install 3-ph in this country. Even then, 11kW would be fine for home charging. If you stick with 1ph then obviously 7kW is what you need.

    Thanks, going to try and at least confirm about whether an enhanced or special connection would be needed based on some of the existing electrical flickers we've seen as well as the occasional trip. Based on all the feedback I've received so far, unless definitely will need a 20kVA in the future, at which point maybe it's a tighter decision, 3-ph isn't going to be worth considering. So I think can scrub 22kW capable from list of requirements.
    KCross wrote: »
    No, it wouldnt.

    Big difference between getting the "enhanced supply" to a "3-phase supply" from a financial and electrical perspective. The enhanced supply is just taking you up to 16kVA from 12kVA (standard). You can go higher again and stay on single phase if you really need to.

    An enhanced supply is a higher rated fuse in the meter box and you have to upgrade the "tails" from the meter to your consumer unit (basically a thicker cable). You may have to upgrade the consumer unit too if it is too old. Getting 3ph in is alot more complicated.

    However, the shed/workspace you have described doesnt sound like it warrants 3-phase. 3-ph would be better, of course, for compressors but 32A supply to a shed isnt that big a deal for 1ph and I presume you would not be running those items during the night when the car is charging and with a load sensing charge point like the Zappi it wouldnt matter anyway as it would ramp up/down as the machinery comes on/off. Thats the whole point of getting a load sensing charge point.

    I have to admit, despite reading the ESB doc on charges a few times, I did not read it properly and missed the details around special single phase. So yes, definitely looks much cheaper assuming just would need 16kVA than 3-phase. Maybe if 20kVA was going to be needed it requires a bit more checking on the costs.

    It turns out the same electrician who will be hooking up my shed fits car chargers, so basically as he's done previous work on the house around water pressure pumps, electric shower, heating system upgrades, etc, he has a good idea on what is in the house and is just going to check what the usage is currently and then based on that and the plans around the shed, car charger, solar, and possible extension, he'll be able to explain where we are and how much additional ceiling would be useful.
    KCross wrote: »
    Possibly but you still dont need it at home. Do you care if your car finished charging at 3am instead of 6am?.... thats the primary benefit to you really.

    If you think you will pay the piper and get 3ph in, then get a 3ph charger but other than that just get a charge point that provides 7kW and it will do you fine.

    Worst case scenario is that you sell it on later and get a higher powered one then. Paying up front for something that you are very unlikely to utilise is the wrong direction, imo.

    I was thinking more for convenience, if we forget or there is an issue with charging overnight, being able to charge quickly would be useful, but I get the point, can probably charge enough to do a couple of km and plug it in to a higher power one elsewhere.
    KCross wrote: »
    No issues there. Its been thought of and designed into every charge point. They are not live until it is plugged into a car and the car "asks" for the power.

    You dont need the lockable feature if you have a private driveway.

    Thanks, it wasn't entirely clear from reading the product descriptions.
    KCross wrote: »
    Again, is any of that gear going to be running at 1am in the morning when the car is charging? Even if it is, it doesnt matter as the charge point will ramp down to counteract the extra load. If you are close to the max already when the car wants to charge it simply wont start the charge session.

    All the more reason to have it actually. You absolutely want the charge point to sense those high loads so that it doesnt become the extra load that causes the fuse to blow.

    If you are close to the max already then you need the enhanced supply (16kVA) or maybe the 20kVA if your electrician works it out that you need it.

    It's more if I'm running into issues with power consumption excluding the car charger, if I was going to need 3-phase for the extra power in the future figured might as well aim to be able to benefit from it. But it's pretty clear I should check what we're actually using right now before making any plans around future proofing on 3-ph for any charger.
    KCross wrote: »
    Its not a Zappi fault. Its a fault on the car side.

    That's good to know.
    KCross wrote: »
    One of your requirements above is Solar integration. Do you have Solar already or is that another future proof idea?

    There are a few things to consider there. 3-ph does have an added benefit of being able to export more excess than single phase (11kW vs 6kW).

    The Zappi is the better known charge point for load sensing and Solar integration. Its hard to see passed it if you are serious about Solar, 3ph, app support and decent load management by default.

    The solar is coming, I don't know if it'll definitely be next year, or have to wait until the following, more a case of timing.

    I wasn't thinking about the 3-ph exporting more power. I have a feeling that the max I was expecting to produce would have been 4-5kW, so taking in the feedback, not enough for 3-ph to be of any benefit.

    Actually looking at some of the set ups recently as well to understand if 3-ph would cause any issues here and I got the impression that it complicates use of battery storage for solar installations so it would likely impose some limitations there. So yes, I'm slowly backing away from the 3-ph.

    I'd wonder about what you're using in the shed which requires 3 phase, unless you've a piece of equipment which will only run on 3 phase then you can get away with just upgrading your single phase supply

    It was more that I was thinking that our max power draw would be high enough that would end up needing to upgrade, however I definitely read the cost doc wrong so the different between the options are definitely prohibitive unless sure that I'll need it.

    I'd guess that heaters, compressors, vacuum, and a table or mitre saw running at the same time would probably be the extent in the shed. Maybe our couple of electrical gremlins are just bad choices on how some lighting is wired on to the wrong circuit as something else thus causing the LEDs to blow in one of the rooms rather than loading the supply overall at certain times.
    Also, you'll likely be charging the car at night time to take advantage of cheaper electricity, so as long as you avoid any midnight welding or carpentry then you're probably safe

    If you have a charger with load balancing then the issue is mooted, the charger will reduce power down to zero if needed to prevent the house supply from being overloaded

    Understood, the 3-ph was about taking advantage of the higher power based on the assumption I would need to upgrade the supply even if not getting the car charger, making it potentially worth considering. However based on the feedback here, as he's doing both the shed and will be doing the car charger now, he's going to check the current power usage to see if any upgrade is needed and unless it needs a special connection it's off the table from what I've learned.
    The Zappi should cover everything you need. The issue with the ID.3 is specific to that car and is because VW have a deep sleep mode which the Zappi sometimes can't wake it up from, it hasn't been reported on any other cars AFAIK

    Indeed, I'm giving the list of the 4 options to the electrician to see if he's got any experience with those particular ones. I did uncover one thing that might make the sync ev and zappi v2 slightly more attractive than the eo mini pro2 and wallbox copper sb. The former two don't require separate earth rod or additional device. should reduce the fitting cost for both of those. The eo mini pro2 appears to recommend a Garo earthing device. The wallbox cobber sb mentions requiring an earthing rod, not sure if that is inter-changeable with the garo earthing device, but definitely a bit extra cost.


  • Registered Users, Registered Users 2 Posts: 12,995 ✭✭✭✭the_amazing_raisin


    I'd consider getting an energy monitor like below

    https://openenergymonitor.org/

    You can take a look at the power consumption of your house and hopefully get an idea of what it pushing you towards the limit of your current connection

    It sounds a bit like you might have a fault in your wiring, an LED bulb really shouldn't be pushing you over the limit, they typically only draw a few watts anyway

    "The internet never fails to misremember" - Sebastian Ruiz, aka Frost



  • Registered Users, Registered Users 2 Posts: 273 ✭✭electrofelix


    It sounds a bit like you might have a fault in your wiring, an LED bulb really shouldn't be pushing you over the limit, they typically only draw a few watts anyway

    They are however sensitive if there is something drawing a high load going on and off whens it on, and it was often on most of the day


  • Moderators, Home & Garden Moderators Posts: 7,016 Mod ✭✭✭✭graememk


    They are however sensitive if there is something drawing a high load going on and off whens it on, and it was often on most of the day

    Should look to getting a surge protection device (SPD) fitted in your consumer unit,

    It's similar idea to the surge protection in the extension lead, but it's replaceable and covers the whole installation.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 273 ✭✭electrofelix


    I'd consider getting an energy monitor like below

    https://openenergymonitor.org/

    You can take a look at the power consumption of your house and hopefully get an idea of what it pushing you towards the limit of your current connection

    That definitely looks interesting, also interesting to see the open source for the car charger, shame it's a power interlock based approach instead of load balancing, as otherwise it might tempt me away from some of the other solutions.

    It appears at least some of the car charges with the dynamic load balancing have this built in since they are monitoring the load placed on the supply, so it comes bundled. If we end up selecting one that doesn't expose this info, I'll probably consider picking one up.


  • Registered Users, Registered Users 2 Posts: 269 ✭✭baby fish


    Some questions about charging, haven't really looked into this so just starting here:

    1.Any features that need to get/avoid or are all chargers more or less the same?
    2. Anything to future proof the installation?
    3. Any suggestion of chargers to get/avoid
    4. Can the charger location be any distance from the fuse board as long as a suitable cable is supplying the charger?
    5. Sometime in future when we have 2 EV , is it just add another charger box with its own supply from fuseboard? Will having a 2nd EV reduce charge rate if both are charging at same time?


  • Registered Users, Registered Users 2 Posts: 12,995 ✭✭✭✭the_amazing_raisin


    baby fish wrote: »
    Some questions about charging, haven't really looked into this so just starting here:

    1.Any features that need to get/avoid or are all chargers more or less the same?
    2. Anything to future proof the installation?
    3. Any suggestion of chargers to get/avoid
    4. Can the charger location be any distance from the fuse board as long as a suitable cable is supplying the charger?
    5. Sometime in future when we have 2 EV , is it just add another charger box with its own supply from fuseboard? Will having a 2nd EV reduce charge rate if both are charging at same time?

    Here's my take

    1. Consider a charger with load balancing if you have some heavy consumers of electricity in your house (heat pump, electric shower)
    2. Cable for a 32Amp (7kW) charger even if you're only getting a 3kW one. Swapping a charger later is much easier than running a new cable. Some people suggest running cat-6 cabling to your charger, I wouldn't say I see the point
    3. Zappi, EO Mini and Wallbox tend to get good reviews
    4. I guess there is a technical limit where the current drop is too high, but unless you're talking hundereds of metres you should be fine. I've about 15m of cable from my charger to fuse box and no issues
    5. You'll definitely need load balancing in this case, 2 EVs charging at 7kW will put you right at the limit for the enhanced ESB connection (16kVA).

    The Zappi has the ability to run 2 chargers from a single connection, you can wire them back to the same cable as your original charger. You'll need to configure a group limit and the chargers will ensure they stay under this limit.

    The 2 Zappis can be configured to prioritise 1 charger over another, or to share the available power

    "The internet never fails to misremember" - Sebastian Ruiz, aka Frost



  • Registered Users, Registered Users 2 Posts: 20,816 ✭✭✭✭Cyrus


    tl;dr - 3-ph + 22kW req getting dropped unless the electrician indicates I will definitely need at least 20kVA special connection. If 16kVA is enough to cover our future reqs regarding a extension in a few years, then it's just not worth it as has been patiently explained to me a few times now.



    Thanks, going to try and at least confirm about whether an enhanced or special connection would be needed based on some of the existing electrical flickers we've seen as well as the occasional trip. Based on all the feedback I've received so far, unless definitely will need a 20kVA in the future, at which point maybe it's a tighter decision, 3-ph isn't going to be worth considering. So I think can scrub 22kW capable from list of requirements.



    I have to admit, despite reading the ESB doc on charges a few times, I did not read it properly and missed the details around special single phase. So yes, definitely looks much cheaper assuming just would need 16kVA than 3-phase. Maybe if 20kVA was going to be needed it requires a bit more checking on the costs.

    It turns out the same electrician who will be hooking up my shed fits car chargers, so basically as he's done previous work on the house around water pressure pumps, electric shower, heating system upgrades, etc, he has a good idea on what is in the house and is just going to check what the usage is currently and then based on that and the plans around the shed, car charger, solar, and possible extension, he'll be able to explain where we are and how much additional ceiling would be useful.



    I was thinking more for convenience, if we forget or there is an issue with charging overnight, being able to charge quickly would be useful, but I get the point, can probably charge enough to do a couple of km and plug it in to a higher power one elsewhere.



    Thanks, it wasn't entirely clear from reading the product descriptions.



    It's more if I'm running into issues with power consumption excluding the car charger, if I was going to need 3-phase for the extra power in the future figured might as well aim to be able to benefit from it. But it's pretty clear I should check what we're actually using right now before making any plans around future proofing on 3-ph for any charger.



    That's good to know.



    The solar is coming, I don't know if it'll definitely be next year, or have to wait until the following, more a case of timing.

    I wasn't thinking about the 3-ph exporting more power. I have a feeling that the max I was expecting to produce would have been 4-5kW, so taking in the feedback, not enough for 3-ph to be of any benefit.

    Actually looking at some of the set ups recently as well to understand if 3-ph would cause any issues here and I got the impression that it complicates use of battery storage for solar installations so it would likely impose some limitations there. So yes, I'm slowly backing away from the 3-ph.




    It was more that I was thinking that our max power draw would be high enough that would end up needing to upgrade, however I definitely read the cost doc wrong so the different between the options are definitely prohibitive unless sure that I'll need it.

    I'd guess that heaters, compressors, vacuum, and a table or mitre saw running at the same time would probably be the extent in the shed. Maybe our couple of electrical gremlins are just bad choices on how some lighting is wired on to the wrong circuit as something else thus causing the LEDs to blow in one of the rooms rather than loading the supply overall at certain times.



    Understood, the 3-ph was about taking advantage of the higher power based on the assumption I would need to upgrade the supply even if not getting the car charger, making it potentially worth considering. However based on the feedback here, as he's doing both the shed and will be doing the car charger now, he's going to check the current power usage to see if any upgrade is needed and unless it needs a special connection it's off the table from what I've learned.



    Indeed, I'm giving the list of the 4 options to the electrician to see if he's got any experience with those particular ones. I did uncover one thing that might make the sync ev and zappi v2 slightly more attractive than the eo mini pro2 and wallbox copper sb. The former two don't require separate earth rod or additional device. should reduce the fitting cost for both of those. The eo mini pro2 appears to recommend a Garo earthing device. The wallbox cobber sb mentions requiring an earthing rod, not sure if that is inter-changeable with the garo earthing device, but definitely a bit extra cost.

    afaik earth rods are a uk requirement but not here.


  • Registered Users, Registered Users 2 Posts: 273 ✭✭electrofelix


    Cyrus wrote: »
    afaik earth rods are a uk requirement but not here.

    Just had that confirmed by the electrician here today as well, so seems like the install is really just down to how complex the box is to fix to the wall and where the cable has to be run from.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 710 ✭✭✭galvo_clare


    Thanks for all the knowledge gleaned on this thread. My needs are simple as I’ll only occasionally have an EV and in an office environment I won’t need load balancing for showers etc.

    I ordered a basic 32A Rolec with RCBO and DC protection built in for £350. There’s a sub board within 4m of where I want the charger on the other side of a wall and my sparks has confirmed that it’s more than up to the job.
    The whole thing should come in under €500 so it can be done without breaking the bank.
    I’m not grant eligible so it’s the right way to go for me.


  • Moderators, Society & Culture Moderators Posts: 42,179 Mod ✭✭✭✭Gumbo


    Thanks for all the knowledge gleaned on this thread. My needs are simple as I’ll only occasionally have an EV and in an office environment I won’t need load balancing for showers etc.

    I ordered a basic 32A Rolec with RCBO and DC protection built in for £350. There’s a sub board within 4m of where I want the charger on the other side of a wall and my sparks has confirmed that it’s more than up to the job.
    The whole thing should come in under €500 so it can be done without breaking the bank.
    I’m not grant eligible so it’s the right way to go for me.

    Damn. I was just about put up an ad for a Garo 32a charger for €250. You could have saved even more!


  • Registered Users, Registered Users 2 Posts: 710 ✭✭✭galvo_clare


    Such is life.. Someone else can grab it and get a great deal.
    Gumbo wrote: »
    Damn. I was just about put up an ad for a Garo 32a charger for €250. You could have saved even more!


  • Registered Users, Registered Users 2 Posts: 3,460 ✭✭✭Felexicon


    Here's my take

    1. Consider a charger with load balancing if you have some heavy consumers of electricity in your house (heat pump, electric shower)
    2. Cable for a 32Amp (7kW) charger even if you're only getting a 3kW one. Swapping a charger later is much easier than running a new cable. Some people suggest running cat-6 cabling to your charger, I wouldn't say I see the point
    3. Zappi, EO Mini and Wallbox tend to get good reviews
    4. I guess there is a technical limit where the current drop is too high, but unless you're talking hundereds of metres you should be fine. I've about 15m of cable from my charger to fuse box and no issues
    5. You'll definitely need load balancing in this case, 2 EVs charging at 7kW will put you right at the limit for the enhanced ESB connection (16kVA).

    2. Run the Cat6. Some chargers require it for load management
    3. For multiple chargers go for Zappi or Wallbox
    4. There is no limit on how long the cable run can be. You just need to increase the size of cabling after certain distances.


  • Registered Users, Registered Users 2 Posts: 19 bakerie


    Gumbo wrote: »
    Damn. I was just about put up an ad for a Garo 32a charger for €250. You could have saved even more!


    See your PMs!


  • Moderators, Society & Culture Moderators Posts: 42,179 Mod ✭✭✭✭Gumbo


    bakerie wrote: »
    See your PMs!

    Thanks.
    I put the ad in adverts today and in the for sale sticky at the top of the forum. It was sold before lunch!

    https://www.boards.ie/vbulletin/showthread.php?t=2057599743&page=82


  • Registered Users, Registered Users 2 Posts: 14,043 ✭✭✭✭fits


    Just placed order on ID.3. Just re the charging unit What now? I want to install a zappi. Can I order it online and get our electrician to install it? Do I have to wait until car is registered in our name before applying for grant? I’d prefer to have it in before car comes.


  • Registered Users, Registered Users 2 Posts: 12,321 ✭✭✭✭KCross


    fits wrote: »
    I want to install a zappi. Can I order it online and get our electrician to install it?

    Yes, as long as he is a registered electrician that can provide a cert.
    Do I have to wait until car is registered in our name before applying for grant?

    No, but you do need grant approval letter before you do any work

    Checkout the SEAI website. All the info is there.


  • Posts: 7,497 ✭✭✭ [Deleted User]


    Zappi RCD problems
    I've had a few random RCD trips on my zappi (once a month approx).
    Seen a few others with the same problem on facebook.
    Contacted them and its a known fault so they are sending me a new unit.
    Just in case anyone else is having the problem.


  • Registered Users, Registered Users 2 Posts: 676 ✭✭✭TheWonderLlama


    Very useful info, i must report mine as well. Cheers.


  • Advertisement
  • Posts: 7,497 ✭✭✭ [Deleted User]


    Very useful info, i must report mine as well. Cheers.

    From their facebook
    "if you send an email to support@myenergi.com with “RCD Tripped” as the subject, together with your address, phone number and a picture of the sticker on the side of the zappi,"

    I had to send them 3/4 other pictures from the service menus.


  • Registered Users, Registered Users 2 Posts: 12,321 ✭✭✭✭KCross


    Zappi RCD problems
    I've had a few random RCD trips on my zappi (once a month approx).
    Seen a few others with the same problem on facebook.
    Contacted them and its a known fault so they are sending me a new unit.
    Just in case anyone else is having the problem.

    Zappi v1 or v2?


  • Registered Users, Registered Users 2 Posts: 4,576 ✭✭✭eagerv


    Zappi RCD problems
    I've had a few random RCD trips on my zappi (once a month approx).
    Seen a few others with the same problem on facebook.
    Contacted them and its a known fault so they are sending me a new unit.
    Just in case anyone else is having the problem.


    Our Zappi2 has just been replaced, but a different problem. Hope yours arrives a bit quicker, ours took almost 8 weeks due to Irish customs. Had to pay €131 before it was released.. (Myenergi to reimburse us)


  • Posts: 7,497 ✭✭✭ [Deleted User]


    eagerv wrote: »
    Had to pay €131 before it was released.. (Myenergi to reimburse us)

    Zappi2

    :(
    was there any problem getting the customs refund ?


  • Registered Users, Registered Users 2 Posts: 4,576 ✭✭✭eagerv


    Zappi2

    :(
    was there any problem getting the customs refund ?


    Hasn't been refunded yet, only about two weeks since we returned unit, probably hasn't arrived yet..:pac:


  • Registered Users, Registered Users 2 Posts: 1,527 ✭✭✭Tony H


    any one get their ev grant into their bank account recently , im about 5 weeks waiting and just wondering how long its taking at the moment .


  • Registered Users, Registered Users 2 Posts: 273 ✭✭electrofelix


    After narrowing down my list of charge points to Zappi, Eo mini pro 2, Sync EV and Wallbox Copper SB, I showed them to my wife and Zappi came out as the preferred, partially due to my initial mentioning of app issues with the eo. Since someone here shared there is no real issue with the eo app I've gone back to see if I've missed anything, and the main place I'm struggling to get a handle on is the solar support. (I have to admit the neatness of the eo mini pro2 and sync ev chargers have grown on me, which is partially why I'm checking again).

    Multiple mentions that if you're interested in solar, Zappi is the way, but I can't tell what it is that makes the integration better?

    eo mini pro 2 is listed as having solar support, and although some websites list the sync ev as not having it, a user here has an install with solar integration.
    Patmwgs wrote: »
    I went with the sync ev charger for £500 +vat from uk, it also has solar integration, rcbo and no need for earth rod.

    As far as I can tell solar integration involves a CT Clamp on the supply and one on line coming from the Solar PV install with software in the charger matching the charge to the Solar PV output to prevent pulling from the grid.

    Both the Zappi and Eo have this (and presumably the sync ev unless it's some kind of custom set up?), is there something else the Zappi has that makes it easier to integrate that is missing from the other two? Or is this just good marketing and early mover for the Zappi? The only thing I can think of is possibly better battery integration support because I can't find anything on the eo or sync ev about it. Even for Zappi there isn't much mentioned, but I did come across https://www.youtube.com/watch?v=GRPVCidL9oA. The harvi with multiple CT clamps if you run out of hard wiring slots and settings around avoiding draining the battery for the Zappi are the only hint that I have that makes it easier to integrate with solar.

    Got the grant approval on Friday, so lining up to complete the purchase soon.


  • Posts: 7,497 ✭✭✭ [Deleted User]


    eagerv wrote: »
    Had to pay €131 before it was released.. (Myenergi to reimburse us)

    Just got a DHL shipping confirmation from them.
    has this at the bottom.
    maybe they have the tax stuff sorted

    Optional Services:
    Duties and Taxes Paid
    Residential Address
    Fuel Surcharge
    Brexit Adjustment
    Emergency Situation
    Estimated Delivery Date
    By: May 12, 2021


  • Registered Users, Registered Users 2 Posts: 14,043 ✭✭✭✭fits


    Just ordered a car. When can I apply for the SEAI grant?


  • Advertisement
  • Moderators, Society & Culture Moderators Posts: 42,179 Mod ✭✭✭✭Gumbo


    fits wrote: »
    Just ordered a car. When can I apply for the SEAI grant?

    Straight away.
    My neighbor had his installed before the car arrived!