Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Hi all! We have been experiencing an issue on site where threads have been missing the latest postings. The platform host Vanilla are working on this issue. A workaround that has been used by some is to navigate back from 1 to 10+ pages to re-sync the thread and this will then show the latest posts. Thanks, Mike.
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

Radiators for A2W system

  • 07-02-2021 5:19pm
    #1
    Registered Users, Registered Users 2 Posts: 12,123 ✭✭✭✭


    Looking for recommendations on Radiators for an Air to Water heat Pump system, not realistic to redo the whole house to install underfloor heating


Comments

  • Registered Users, Registered Users 2 Posts: 395 ✭✭Biker1


    Gael23 wrote: »
    Looking for recommendations on Radiators for an Air to Water heat Pump system, not realistic to redo the whole house to install underfloor heating

    You need to get room by room heat loss calculation done. Only then will you know what output the radiators must achieve. Don't be fooled by sales talk saying you must install aluminium rads. 500w output from a steel rad is the same as 500w output from an aluminium rad at a given delta T. The only difference will be in the size of the two and is not as much as people think.


  • Registered Users, Registered Users 2 Posts: 12,123 ✭✭✭✭Gael23


    Biker1 wrote: »
    You need to get room by room heat loss calculation done. Only then will you know what output the radiators must achieve. Don't be fooled by sales talk saying you must installv aluminium rads. 500w output from a steel rad is the same as 500w output from an aluminium rad at a given delta T. The only difference will be in the size of the two and is not as much as people think.

    So could existing radiators be kept?


  • Registered Users, Registered Users 2 Posts: 1,627 ✭✭✭quentingargan


    Gael23 wrote: »
    So could existing radiators be kept?

    Again, you would need a room by room assessment, but you may find larger double radiators can be moved to replace smaller singles, leaving you to replace a smaller number


  • Registered Users, Registered Users 2 Posts: 12,123 ✭✭✭✭Gael23


    Who would do this heat loss assessment?


  • Registered Users, Registered Users 2 Posts: 395 ✭✭Biker1


    Gael23 wrote: »
    Who would do this heat loss assessment?

    Some heating suppliers can do it but only if they have the correct information in terms of u-values, room areas and volumes.
    "Rubbish in-rubbish out"