Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Hi all! We have been experiencing an issue on site where threads have been missing the latest postings. The platform host Vanilla are working on this issue. A workaround that has been used by some is to navigate back from 1 to 10+ pages to re-sync the thread and this will then show the latest posts. Thanks, Mike.
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

Excessive cold air from air vent

  • 18-10-2020 10:17am
    #1
    Registered Users, Registered Users 2 Posts: 5,826 ✭✭✭


    We bought a new home with A3 energy rating. But the air vent in bedroom is providing cold air in excess at night, to an extent that I can feel the air gusts on my skull and it's very uncomfortable.

    Builder says he can't block the air vents. Is there an alternative option to solve this issue? Any advice?

    My neighbour has put up duct tape covering half of the vent. But it doesn't look great aesthetically.

    Please see attached image of air vent:

    20201018-101127.jpg


Comments

  • Registered Users, Registered Users 2 Posts: 393 ✭✭Biker1


    Anti draught vents are widely available and should do the trick. Because this is your only means of ventilation under no circumstances should you restrict the airflow like your neighbour did.


  • Registered Users, Registered Users 2 Posts: 5,826 ✭✭✭masterboy123


    Thanks for the tip.

    I will check it out now.

    Is it DIY job?
    Biker1 wrote: »
    Anti draught vents are widely available and should do the trick. Because this is your only means of ventilation under no circumstances should you restrict the airflow like your neighbour did.


  • Registered Users, Registered Users 2 Posts: 2,612 ✭✭✭Yellow_Fern


    The vent is there incase you close the windows. In other countries such vents are not needed as people are aware of the importance of opening the windows daily.


  • Registered Users, Registered Users 2 Posts: 21,808 ✭✭✭✭Water John


    These heat exchange vents have been mentioned in another thread. I have no experience of them but it's an interesting option. It's a heat exchanger. Beware it requires a 6 inch vent.
    https://www.google.com/search?q=suedwind%3A+ambientika+solo&oq=s&aqs=chrome.2.69i57j69i59l3j46i131i199i291i433j0i131i433j46i131i199i291i433j0i271.3140j0j15&sourceid=chrome&ie=UTF-8

    https://www.boards.ie/vbulletin/showthread.php?t=2057496673&page=5


  • Registered Users, Registered Users 2 Posts: 6,944 ✭✭✭con747


    We bought a new home with A3 energy rating. But the air vent in bedroom is providing cold air in excess at night, to an extent that I can feel the air gusts on my skull and it's very uncomfortable.

    Builder says he can't block the air vents. Is there an alternative option to solve this issue? Any advice?

    My neighbour has put up duct tape covering half of the vent. But it doesn't look great aesthetically.

    Please see attached image of air vent:

    20201018-101127.jpg

    Put something like this in, if your handy with diy should be easy enough. Just measure the dimensions on the hole. https://www.goodwins.ie/products/anti-draught-black-hole-ventilator-bm725-white-outer-cowl-3461399.html?filter_set[]=1413,1453,1497

    Don't expect anything from life, just be grateful to be alive.



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 5,826 ✭✭✭masterboy123


    300€ looks expensive to me plus installation cost
    Water John wrote: »
    These heat exchange vents have been mentioned in another thread. I have no experience of them but it's an interesting option. It's a heat exchanger. Beware it requires a 6 inch vent.
    https://www.google.com/search?q=suedwind%3A+ambientika+solo&oq=s&aqs=chrome.2.69i57j69i59l3j46i131i199i291i433j0i131i433j46i131i199i291i433j0i271.3140j0j15&sourceid=chrome&ie=UTF-8

    https://www.boards.ie/vbulletin/showthread.php?t=2057496673&page=5


  • Registered Users, Registered Users 2 Posts: 5,826 ✭✭✭masterboy123


    Will this effect the BER rating?

    I will check if there is a 6 inch hole in the wall.
    con747 wrote: »
    Put something like this in, if your handy with diy should be easy enough. Just measure the dimensions on the hole. https://www.goodwins.ie/products/anti-draught-black-hole-ventilator-bm725-white-outer-cowl-3461399.html?filter_set[]=1413,1453,1497


  • Registered Users, Registered Users 2 Posts: 520 ✭✭✭Telly


    Is it just the inside vent? We have one of these and close the shutter in the winter. We got them in B&Q for a tenner yrs ago.


  • Subscribers Posts: 41,830 ✭✭✭✭sydthebeat


    Will this effect the BER rating?

    I will check if there is a 6 inch hole in the wall.

    From a BER point of view, If it's closeable it doesn't count and your BER improves.

    If it's non closeable it counts as ventilation losses


  • Registered Users, Registered Users 2 Posts: 5,826 ✭✭✭masterboy123


    This looks good and cheap option. I wonder if this will cause development of mould?
    Telly wrote: »
    Is it just the inside vent? We have one of these and close the shutter in the winter. We got them in B&Q for a tenner yrs ago.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 686 ✭✭✭steamsey


    You cold try the internal close-able vent. Close when windy or very cold. But probably a good idea in an A3 home to open very regularly to refresh air.

    You could also try a DR21 external draught reducing vent cover. Pretty easy to install if you can get to external vent.

    Two threads on them here. They work.

    Not much point in having an A3 house if cold air is blasting in all winter.

    https://www.boards.ie/vbulletin/showthread.php?t=2057939173

    https://www.boards.ie/vbulletin/showthread.php?p=109987340


  • Registered Users, Registered Users 2 Posts: 21,808 ✭✭✭✭Water John


    The item I put up would be a Heat Recovery gizmo. Houses that are A3 should have a full heat recovery ventilation system. That costs €5/6K.


  • Registered Users, Registered Users 2 Posts: 520 ✭✭✭Telly


    This looks good and cheap option. I wonder if this will cause development of mould?

    We’ve had these years and not a sign of mould


  • Registered Users Posts: 4,784 ✭✭✭KungPao


    Water John wrote: »
    These heat exchange vents have been mentioned in another thread. I have no experience of them but it's an interesting option. It's a heat exchanger. Beware it requires a 6 inch vent.
    https://www.google.com/search?q=suedwind%3A+ambientika+solo&oq=s&aqs=chrome.2.69i57j69i59l3j46i131i199i291i433j0i131i433j46i131i199i291i433j0i271.3140j0j15&sourceid=chrome&ie=UTF-8

    https://www.boards.ie/vbulletin/showthread.php?t=2057496673&page=5
    Does anyone have an idea of how much one of these would cost inc installation (hole needs drilling)?

    We will be getting new windows (planning to lose the trickle vents) so will need ventilation. Would be very interested in a few of these - maybe just downstairs.

    Would love a proper ducted heat recovery sytem upstairs. A idea of price if you know would be super too. Cheers.


  • Registered Users, Registered Users 2 Posts: 5,826 ✭✭✭masterboy123


    I have checked the dimensions of our vents and it is 25 cm (width) x 17 cm (height).

    I can't seem to find this in local stores yesterday which were open.

    Any idea where I could find it?
    Telly wrote: »
    We’ve had these years and not a sign of mould


  • Registered Users, Registered Users 2 Posts: 526 ✭✭✭downwesht


    Turn the vent upside down,you will have the same ventilation but the draught will be directed towards the ceiling,I did this and it worked.


  • Registered Users, Registered Users 2 Posts: 21,808 ✭✭✭✭Water John


    KungPao wrote: »
    Does anyone have an idea of how much one of these would cost inc installation (hole needs drilling)?

    We will be getting new windows (planning to lose the trickle vents) so will need ventilation. Would be very interested in a few of these - maybe just downstairs.

    Would love a proper ducted heat recovery sytem upstairs. A idea of price if you know would be super too. Cheers.

    Don't know, Probably have to get the units yourself and then having a handyman to install, if you can find one. Reaming a 5 or 6 inch hole doesn't qualify as fun.
    If you're looking at a MHRV system for upstairs it would make sense to make it whole house, usually €5/6K. Really only necessary and worthwhile where a building is well sealed.


  • Registered Users Posts: 4,784 ✭✭✭KungPao


    Water John wrote: »
    Don't know, Probably have to get the units yourself and then having a handyman to install, if you can find one. Reaming a 5 or 6 inch hole doesn't qualify as fun.
    If you're looking at a MHRV system for upstairs it would make sense to make it whole house, usually €5/6K. Really only necessary and worthwhile where a building is well sealed.
    Cheers.


    Yeah, I had to drill, drill, and drill again, then bash through recently for a kitchen extractor - definitely not fun, hoping to avoid having to do it again. Handyman probably for the best.


  • Registered Users, Registered Users 2 Posts: 915 ✭✭✭homewardbound11


    The BER specialists will know this here but is it even possible to get a BER of A3 without controlled ventilation?


  • Registered Users, Registered Users 2 Posts: 393 ✭✭Biker1


    Not only is it possible to achieve an A3 with natural ventilation it is acceptable in the 2019 reg's. Utter madness!!


  • Advertisement
  • Subscribers Posts: 41,830 ✭✭✭✭sydthebeat


    Biker1 wrote: »
    Not only is it possible to achieve an A3 with natural ventilation it is acceptable in the 2019 reg's. Utter madness!!

    2019 regs are bringing ratings to A2

    And under tgd f 2019 every air tightness test that is less than 3 m3/hr/m2 requires MHRV.


  • Registered Users, Registered Users 2 Posts: 9,474 ✭✭✭TheChizler


    Water John wrote: »
    These heat exchange vents have been mentioned in another thread. I have no experience of them but it's an interesting option. It's a heat exchanger. Beware it requires a 6 inch vent.
    https://www.google.com/search?q=suedwind%3A+ambientika+solo&oq=s&aqs=chrome.2.69i57j69i59l3j46i131i199i291i433j0i131i433j46i131i199i291i433j0i271.3140j0j15&sourceid=chrome&ie=UTF-8

    https://www.boards.ie/vbulletin/showthread.php?t=2057496673&page=5
    I was thinking these sounded great but something was niggling at me, I just realized they might have a fundamental flaw. These work by extracting air at say 17 litres/s for 70 seconds, with the heat from the air accumulating in the ceramic, then reversing the flow for another 70 seconds, dumping the stored heat into the house in the fresh air, most of the heat is recovered. Sounds great.

    Until you realize that the 1190 litres of stale air extracted has to be immediately replaced with air from somewhere else: leaks elsewhere in the house. The same is true when the flow is reversed and 1190 litres of fresh air pumped into the house has the displace the same amount, which is pushed out though those same leaks. So effectively you have this heat exchanger, which is theoretically 96% efficient in its own right, alternatively causing the same amount of warm air elsewhere to be dumped directly outside, and cold air drawn in. Is this any better than a basic extractor fan? Maybe it only loses half the heat as a normal fan?


  • Registered Users, Registered Users 2 Posts: 21,808 ✭✭✭✭Water John


    You raise a very pertinent point. It's a cheapish solution to a problem. Possibly a second basic vent in a cool part of the house.

    OP that's a very large vent? In old money that's 10 inch by 6.5 inches.


  • Closed Accounts Posts: 1,862 ✭✭✭un5byh7sqpd2x0


    Water John wrote: »
    You raise a very pertinent point. It's a cheapish solution to a problem. Possibly a second basic vent in a cool part of the house.

    OP that's a very large vent? In old money that's 10 inch by 6.5 inches.

    I'd suspect those are the dimensions of the vent cover.


  • Registered Users, Registered Users 2 Posts: 5,826 ✭✭✭masterboy123


    Vent cover is 25 cm (width) x 17 cm (height), which is almost the same in inches that you have posted.

    Water John wrote: »
    You raise a very pertinent point. It's a cheapish solution to a problem. Possibly a second basic vent in a cool part of the house.

    OP that's a very large vent? In old money that's 10 inch by 6.5 inches.


  • Registered Users Posts: 126 ✭✭FitzElla


    I posted another thread on a similar problem. It is a little frustrating to find an A3 house that is super air tight and insulated and then find vents (aka big holes in the wall) everywhere as acceptable ventilation.

    Has anyone retrofitted MHRV have an idea of cost? Would it be possible to re-use the existing MEV extract ducting? Would only mean having to put in the supply side which would be mostly upstairs.


  • Registered Users, Registered Users 2 Posts: 9,474 ✭✭✭TheChizler


    FitzElla wrote: »
    Has anyone retrofitted MHRV have an idea of cost? Would it be possible to re-use the existing MEV extract ducting? Would only mean having to put in the supply side which would be mostly upstairs.
    Tangent to the conversation but I wonder would it be possible to install ducting through a disused chimney flue? In my house that would allow direct ventilation to every room without any visible ducting.


  • Closed Accounts Posts: 1,862 ✭✭✭un5byh7sqpd2x0


    I've exactly the same problem as the OP, also in an A3 house. My house came with the "hit & miss" vent covers internally which are as useful as a chocolate teapot when closed as the draft (and the light & noise) still comes in through them.


  • Registered Users, Registered Users 2 Posts: 5,826 ✭✭✭masterboy123


    Our vents do not even have the options to cover it.

    I am searching online if I can get a cover slider if at all possible?

    Thank you all.
    I've exactly the same problem as the OP, also in an A3 house. My house came with the "hit & miss" vent covers internally which are as useful as a chocolate teapot when closed as the draft (and the light & noise) still comes in through them.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 34,104 ✭✭✭✭listermint


    Just get the square covers which push the air out to the sides the direct it correctly flat to the wall rather than out on you. Your measuring in wrong btw. Measure just the pipe diameter that's what your covering should be 110mm. Take off old vent fit new. Paint wall around.


    Also tell your neighbour to take his tape off. He will get mould in his bedroom. That's not where you want it .


  • Registered Users, Registered Users 2 Posts: 5,826 ✭✭✭masterboy123


    Yes, i am trying to find the white square cover which has a slider.
    Alternatively, I am thinking to put the vents upside down, that way the air will be pushed upwards.

    I am trying to find it online but no luck. If someone could please post link to purchase it online.
    listermint wrote: »
    Just get the square covers which push the air out to the sides the direct it correctly flat to the wall rather than out on you.


    Also tell your neighbour to take his tape off. He will get mould in his bedroom. That's not where you want it .


  • Registered Users, Registered Users 2 Posts: 4,441 ✭✭✭blackbox


    It seems crazy to insulate a house carefully to achieve an A rating and then poke a big hole in the wall.

    OP, if there is air coming in, there must also be air going out. Have you tried draught-proofing your bedroom door to stop the air current?


  • Registered Users, Registered Users 2 Posts: 21,808 ✭✭✭✭Water John




  • Registered Users, Registered Users 2 Posts: 34,104 ✭✭✭✭listermint


    Yes, i am trying to find the white square cover which has a slider.
    Alternatively, I am thinking to put the vents upside down, that way the air will be pushed upwards.

    I am trying to find it online but no luck. If someone could please post link to purchase it online.

    White square covers with sliders are gak. They're straight out of the 80s it's horrendous builders are still even putting that crap on your house there. The vent bears no resemblance to the hole.

    Get a 110mm circle vent with closer if you must. They are on eBay. Make sure yours is 110mm. If not get the square ones which direct air left and right .

    Avoid the rectangular ones with abundance. The circle ones are about 4 euro on eBay replace all them in your house it will look. Neater and like it should have if the builders bothered their arse.


  • Registered Users, Registered Users 2 Posts: 34,104 ✭✭✭✭listermint


    listermint wrote: »
    White square covers with sliders are gak. They're straight out of the 80s it's horrendous builders are still even putting that crap on your house there. The vent bears no resemblance to the hole.

    Get a 110mm circle vent with closer if you must. They are on eBay. Make sure yours is 110mm. If not get the square ones which direct air left and right .

    Avoid the rectangular ones with abundance. The circle ones are about 4 euro on eBay replace all them in your house it will look. Neater and like it should have if the builders bothered their arse.

    This is mine. Fitted myself


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 5,826 ✭✭✭masterboy123


    Adjustable Air Vent, HG POWER 4" Ventilation Grille Cover Stainless Steel Extractor Outlet for Bathroom Office Kitchen Ventilation https://www.amazon.co.uk/dp/B07QNWP73P/ref=cm_sw_r_wa_apa_i_qbZKFb593AM8M?_encoding=UTF8&psc=1

    How's this guys??


  • Registered Users, Registered Users 2 Posts: 5,826 ✭✭✭masterboy123


    I have checked, the diameter of vent is 15 cm.
    listermint wrote: »
    Get a 110mm circle vent with closer if you must. They are on eBay. Make sure yours is 110mm. If not get the square ones which direct air left and right .


  • Registered Users, Registered Users 2 Posts: 2,858 ✭✭✭MicktheMan


    sydthebeat wrote: »
    2019 regs are bringing ratings to A2

    And under tgd f 2019 every air tightness test that is less than 3 m3/hr/m2 requires MHRV.

    And, imo, if over 3 m3/hr/m2 is truly a wasted opportunity!


  • Registered Users Posts: 301 ✭✭spose


    FitzElla wrote: »
    I posted another thread on a similar problem. It is a little frustrating to find an A3 house that is super air tight and insulated and then find vents (aka big holes in the wall) everywhere as acceptable ventilation.

    Has anyone retrofitted MHRV have an idea of cost? Would it be possible to re-use the existing MEV extract ducting? Would only mean having to put in the supply side which would be mostly upstairs.

    I did a retrofit. We were doing work on the house anyway which meant I could get access to the downstairs rooms. Spent 4K on all the kit


  • Registered Users Posts: 37 pablo57


    listermint wrote: »
    This is mine. Fitted myself
    Thanks for this (and to everyone on the thread for sharing their experiences) - just ordered a few to try to sort out some seriously draughty rooms we've had all winter.

    Wonder if any of you have any suggestions for the predicament I've attached. Just one of several joyous bits of work we've encountered in a house we bought 2 years ago. These rectangular grilles are throughout the house, all fitted horizontally except for this one, and I always knew there was a reason! Is a smaller square adjustable grille my only option here?


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 61 ✭✭EVGR


    If the duct size is 100mm and there is no fire or boiler in the room, you can try these https://munsterdiy.com/collections/ventilation-products/products/wall-vent

    The square is about 16x16cm. Would that suit your space?

    I'm surprised I see so few recommendations for them. Do people dont know they exist?


  • Registered Users Posts: 21 realflash17


    I am in the final stages of a build and I can already see the issue raised by the OP being an issue for us on a couple of 6" vents on the bedrooms that may catch the south westerly wind.

    At the moment the steel vent covers are on the outside, plastered in.

    I still have open access to the pipe from the inside and I am contemplating reducing the size of the pipe in the middle from 6" to 3" by inserting in a 3" pvc pipe tilting outwards and insulating around it with foam, then a close-able cover on the inside(that hopefully does not have to be ever closed unless stormy). I think/hope that should supply plenty of fresh air on a daily basis in addition to windows being opened in morning too.

    I would monitor for first 6 months and see how it goes, inspecting pipe for any moisture build up etc and possibly even removing the 3" in the future if room temperature was comfortable and see how that goes.

    Anyone done anything similar?

    I know of a few people who have moved into new homes and blocked up vents already which does seem madness. Not saying my idea is ideal either but hoping a reduction in pipe size might find a nice balance between comfort and fresh air supply.



  • Registered Users, Registered Users 2 Posts: 393 ✭✭Biker1


    As it's a new build the only way you can have natural ventilation is if your airtightness test result is between 3 and 5m3/hr/m2. As most houses are coming in below 3m3/hr/m2 the requirement is for either mechanical extract or MVHR. With mechanical extract you only need wall vents with an equivalent opening of 2500m2 in each habitable room.(less than 70mm diameter) For natural ventilation you may require more than one 150mm diameter hole, depending on the size of the room. New houses with natural ventilation are known as swiss cheese houses because of this.



Advertisement