Domestic solar PV quotes 2018

1646567697096

Comments

  • Registered Users, Registered Users 2 Posts: 1,646 ✭✭✭Conar


    digzy wrote: »
    Hi lads
    Looking for a bit of free info please
    I live in an old house. I've new windows and attic insulated. I've the air to water system installed. My electricity bills have been seriously steep (6k over last 9 months). hence I'm looking into other sources of electricity. I was given the following quote

    1. 26 x 310 Mono JA Panels
    2. 1 x Solax Inverter 3 Phase
    3. 1 x 9kw Solax Battery
    4. Ground works for cable to be done by client as per agreed and discount allowance included.

    Caldor will process all grant paperwork & will claim the grant on your behalf. BER included as standard.

    Total price would be €18,500 inc. Vat (after grant)


    I was told by the rep/engineer that I'd be shaving 60% off the bills which I'd be happy with. However, I'm hearing that these panels may not have that kind of payback.

    Do the sums add up?

    thanks in advance

    Sounds like there's something seriously wrong with your energy usage. That's approx 5 units per hour or more.
    Unless you run a power shower and oven 24/7 I'd be more inclined to see what is using all that power.
    My air to water costs me approx 800 per year (granted in an A3 rated house) but even if that was tripled I couldn't use your levels of power and I'd consider myself a heavy user.

    Edit***
    https://www.seai.ie/tools/solar-electricity-calculator/
    With regards to saving 60% of an 8k per year bill I'd say they're lying through their teeth.
    If you put into in the above calculator (selected south facing, Kildare, someone always at home, 5kw system for €540 saving) it would work out about €900 saving per year. That's less than 15% of your spend.

    Edit 2***
    https://www.photovoltaicsystems.ie/much-electricity-domestic-solar-panels-produce/
    I you go by their sums they reckon a 4kw system can generate 3400kwh per year so and 8kw one like you've been quoted would net you 6400kwh.
    That's 19% of your usage.
    I've just used a unit rate of 18c for these barstool calculations btw.

    These people shouldn't be able to get away with making such outrageous claims.
    https://www.bbc.com/news/amp/uk-england-49566130


  • Registered Users, Registered Users 2 Posts: 12,322 ✭✭✭✭KCross


    digzy wrote: »
    Looking for a bit of free info please
    I live in an old house. I've new windows and attic insulated. I've the air to water system installed. My electricity bills have been seriously steep (6k over last 9 months). hence I'm looking into other sources of electricity.

    There's something seriously wrong there. How could any heat pump use €6k over the last 9 months when a significant portion of that was during the summer where it wouldnt be running at all except for hot water.

    Or did you mean 6k units of electricity?

    How big is the house?
    Do you have underfloor heating or old steel rads?
    Is the house warm?
    Is it draughty? Did you change the external doors when you did the windows? Are they well sealed?
    Do you have night rate electricity?

    digzy wrote: »
    I was told by the rep/engineer that I'd be shaving 60% off the bills which I'd be happy with. However, I'm hearing that these panels may not have that kind of payback.

    Do the sums add up?

    He's bull****ting.

    Your energy use is most likely your A2W heat pump and that will be running hardest at the point where Solar will be generating the least.... winter and night time.


    Solar is not your solution here. Fixing your ridiculous electricity bill is what you need to do. Get a meter on your heat pump and monitor what it is doing and try to figure out why its consuming all that electricity. You will be looking at an early expensive compressor failure if you dont address that first.


  • Registered Users, Registered Users 2 Posts: 66,634 ✭✭✭✭unkel


    It looks like your house wasn't suitable for an A2W heat pump. Not airtight enough. Not enough insulation. Who advised you to buy one?

    That quote is ridiculous BTW, and the array (8kW) is far bigger than is legally allowed by the ESB (max 6kW), some clown of an SEAI improved installer giving you that quote.

    By all means use the SEAI grant to its max and get a 4kW system with a small battery (these are expensive but you can easily add more batteries in a few years time when hopefully they get a lot cheaper) installed for about €5.5k (and consider going 6kW if they quote you a reasonable upgrade cost)


  • Registered Users, Registered Users 2 Posts: 2,837 ✭✭✭air


    He's obviously on 3 phase so up to 11kW is allowed without any fuss IIRC.
    In any case you could connect more panel capacity than the inverter peak output (within the inverter voltage limits) with no possible impact to ESB Networks.
    Obviously the grant tops out at 4kW.
    I think everyone is in agreement that PV is not the answer to the problems with the house though.


  • Registered Users, Registered Users 2 Posts: 66,634 ✭✭✭✭unkel


    air wrote: »
    He's obviously on 3 phase

    Obviously? :)

    How many old private houses in Ireland are on 3 phase? Wouldn't be too many I'd have thought. Or maybe the quote included getting connected to 3-phase :p


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 2,837 ✭✭✭air


    unkel wrote: »
    Obviously? :)

    How many old private houses in Ireland are on 3 phase? Wouldn't be too many I'd have thought. Or maybe the quote included getting connected to 3-phase :p

    Well the quote mentioned a 3 phase inverter, I'm giving the installer the benefit of the doubt and assuming they wouldn't quote for one on a house with a single phase supply.
    Perhaps I'm too generous.


  • Registered Users, Registered Users 2 Posts: 66,634 ✭✭✭✭unkel


    Ha I clearly missed that. My eyes were distraught by that €18,500 figure :p


  • Registered Users, Registered Users 2 Posts: 3,049 ✭✭✭digzy


    Cheers guys. Many thanks for the advice.
    I bought a large house a few years back. 6000 sq feet. As I said, I’ve new windows, attic insulated.
    Didn’t insulate the ground floor as it would’ve involved tearing up all the floors.

    We’re a pretty avg family in terms of behavior.
    Just wondering to whom I can turn to sort things out. I appreciate the advice here but I think I need to get someone on site. I’ve had to install 3 phase power to power the air2water system. I’m based in tipperary.

    I’m getting the impression that I’m getting ridden with the quote, which being honest I wouldn’t mind if I got the payback.

    The system was designed by ‘ash grove’ think they’re based in north cork. Plumbers work was top class too.

    It’s a thermia pump


  • Registered Users, Registered Users 2 Posts: 66,634 ✭✭✭✭unkel


    You're a bit vague. Was the A2W system already in the house when you bought it?


  • Registered Users, Registered Users 2 Posts: 3,049 ✭✭✭digzy


    unkel wrote: »
    You're a bit vague. Was the A2W system already in the house when you bought it?

    No. House was oil fired when I bought it. So went a2w before we moved in


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 66,634 ✭✭✭✭unkel


    And who advised you to do that, did you get proper survey done that proved your house was suitable for an A2W setup?


  • Registered Users, Registered Users 2 Posts: 9,817 ✭✭✭antoinolachtnai


    That is really high consumption. Is this all driven by the winter months or is it high year round?

    I think it would help you if you could understand your consumption better before making (another) big investment.


  • Registered Users, Registered Users 2 Posts: 475 ✭✭jspuds


    digzy wrote: »
    No. House was oil fired when I bought it. So went a2w before we moved in

    hi, sent you a PM


  • Registered Users, Registered Users 2 Posts: 116 ✭✭Northumberland


    Hi anyone out there using Pylontech batteries with a Solis inverter?

    The manual for the Pylontech states max charge voltage 54 v and charge current 25A (up to a max of 50 amp) - but that is surely for just one battery? I have two connected of course in parallel.

    I had assumed that the batteries own BMS would know it was connected to a second battey, and the Solis as well would control the show, all connected up as it is with monitoring cables, but now not so sure. 53 volts at 25 amps is 1.3 kW. When the sun is shining, I see that just 1.25 kW is going to charge my batteries, but often an additional 1 to 2kW is being given away free to the grid. Am I right in thinking that with two batteries in parallel I could charge them together with 2.5kW, or 50 amps?


  • Registered Users, Registered Users 2 Posts: 1,627 ✭✭✭quentingargan


    Hi anyone out there using Pylontech batteries with a Solis inverter?

    The manual for the Pylontech states max charge voltage 54 v and charge current 25A (up to a max of 50 amp) - but that is surely for just one battery? I have two connected of course in parallel.

    I had assumed that the batteries own BMS would know it was connected to a second battey, and the Solis as well would control the show, all connected up as it is with monitoring cables, but now not so sure. 53 volts at 25 amps is 1.3 kW. When the sun is shining, I see that just 1.25 kW is going to charge my batteries, but often an additional 1 to 2kW is being given away free to the grid. Am I right in thinking that with two batteries in parallel I could charge them together with 2.5kW, or 50 amps?

    Yes - with two batteries, the charge current should be able to go to 50A. Is there a comms link cable between the two batteries? The comms cable from the inverter goes to the top left port of the first battery. Then a link cable goes from the bottom right port of the first battery to the top right port of the second one. Make sure dip switches are the same on both battreries.

    If you use advanced settings - storage mode - you should then look at control parameters. It should show max charge current at 50A.

    It may sometimes show 20A (10a per battery). This happens if the battery is below 10 degrees, and also under some other circumstances.


  • Registered Users, Registered Users 2 Posts: 116 ✭✭Northumberland


    Thanks so much Quentingargan, your post solved my problem. My installer had wrongly connected the comms cable between the bottom left port of the first battery and to the top left port of the second battery. I just re-connected given your instructions (and following the photos in the battery manual - although the manual is pretty bad and no description in wording), but I turned batteries back on and it worked. There is now a charge of 2.5kW going in to the 2 batteries together, equivalent of about 50 amps which seems perfect, and which will allow the system to operate more efficiently during the few hours of sunshine at this time of the year!

    One more question for you. I now finally have my system set up to power an 'essential load' in the event of a power cut (which we have in my area due to the ESB overhead cable running through a forest). If I want to ensure that I have at least 50% charge in my batteries when a storm is expected, is the easiest way to do this to just turn both batteries 'off' using the rocker switch on each when a storm is expected (and when the batteries have at least 50% charge)?, and then to turn batteries back ON if the power cut actually happens (will the inverter be able to 'power up' from the batteries?)


  • Registered Users, Registered Users 2 Posts: 1,627 ✭✭✭quentingargan


    If I want to ensure that I have at least 50% charge in my batteries when a storm is expected, is the easiest way to do this to just turn both batteries 'off' using the rocker switch on each when a storm is expected (and when the batteries have at least 50% charge)?, and then to turn batteries back ON if the power cut actually happens (will the inverter be able to 'power up' from the batteries?)
    You can set this in the advanced settings. Are you familiar with these? PM me if you want the password.

    The exact menu options changed depending on whether you have HMI version above 20.

    You go to advanced settings - storage energy set - battery select. Press enter to leave it on pylon.

    You get an option for over discharge SOC. You can temporarily set this to 50%. Normally it is between 12% and 20%. You then get an option for force charge SOC. This can be set to 48% to prevent the inverter discharging the batteries during long dull spells.

    See section 38/39 of manual. If you don't have the inverter manual, PM me.

    Glad you got the other issue resolved.


  • Registered Users, Registered Users 2 Posts: 116 ✭✭Northumberland


    Thanks a lot, I will try that. Yes I am familiar with advanced settings and with the two different passwords. I have to request an upgrade stick from the Ginlong UK distributor and update my software sometime soon.


  • Registered Users, Registered Users 2 Posts: 985 ✭✭✭AidenL


    I know 6kw is the max allowed to be installed by the ESB.

    Is there anyway to install more, space permitting? One installer suggested to me that they could go over 6?

    I think in the UK, permission is achievable to exceed their 4kw limit.


  • Registered Users, Registered Users 2 Posts: 1,627 ✭✭✭quentingargan


    Max inverter is 6kw. You can typically put 6kw panels onto a 5kw hybrid inverter and put another 1.2kw onto a 1kw inverter on the same site. So max panels is 7.2kw.

    If you want to go beyond that, it'll cost you more than its worth to have G10 relays and approvals.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 985 ✭✭✭AidenL


    Max inverter is 6kw. You can typically put 6kw panels onto a 5kw hybrid inverter and put another 1.2kw onto a 1kw inverter on the same site. So max panels is 7.2kw.

    If you want to go beyond that, it'll cost you more than its worth to have G10 relays and approvals.

    That’s great, thanks for the clarity.

    My house is mostly south facing, I thought it might be useful to have maybe 2 panels facing both east and west for morning and evening maximum benefit, so 1.2kw would suit nicely.


  • Registered Users, Registered Users 2 Posts: 1,627 ✭✭✭quentingargan


    AidenL wrote: »
    That’s great, thanks for the clarity.

    My house is mostly south facing, I thought it might be useful to have maybe 2 panels facing both east and west for morning and evening maximum benefit, so 1.2kw would suit nicely.
    Yes, but those four panels will need optimisers to ensure that the darker ones don't affect the brigher ones. Not a big issue - optimisers are cheap enough.


  • Registered Users, Registered Users 2 Posts: 985 ✭✭✭AidenL


    Yes, but those four panels will need optimisers to ensure that the darker ones don't affect the brigher ones. Not a big issue - optimisers are cheap enough.

    Is it worth the hassle and additional expense, in your opinion?


  • Registered Users, Registered Users 2 Posts: 66,634 ✭✭✭✭unkel


    Optimisers are about €50-€60 per panel. Up to you to make your mind up. Alternatively you could go for a dual or triple string MPPT inverter, then you won't need optimisers for your E or W strings


  • Registered Users, Registered Users 2 Posts: 116 ✭✭Northumberland


    You can set this in the advanced settings. Are you familiar with these? PM me if you want the password.

    The exact menu options changed depending on whether you have HMI version above 20.

    You go to advanced settings - storage energy set - battery select. Press enter to leave it on pylon.

    You get an option for over discharge SOC. You can temporarily set this to 50%. Normally it is between 12% and 20%. You then get an option for force charge SOC. This can be set to 48% to prevent the inverter discharging the batteries during long dull spells.

    See section 38/39 of manual. If you don't have the inverter manual, PM me.

    Glad you got the other issue resolved.

    Thanks, my HDMI is version 14, so I had better request an Upgrade stick and upgrade the HDMI software. I followed your instructions (and I do have the manual), but when I get to over-discharge SOC the max I can set it to is 30%, and when I enter that I get no 'force charge setting screen at all. I see force charge in the manual ok, but have never seen it on my screen.


  • Registered Users, Registered Users 2 Posts: 793 ✭✭✭reklamos


    Yes, but those four panels will need optimisers to ensure that the darker ones don't affect the brigher ones. Not a big issue - optimisers are cheap enough.
    Before going with optimizers, check your inverter. Solis RHI ones are Dual MPPT so you can connect those panels to second MPPT without optimizers


  • Registered Users, Registered Users 2 Posts: 12,322 ✭✭✭✭KCross


    Yes, but those four panels will need optimisers to ensure that the darker ones don't affect the brigher ones. Not a big issue - optimisers are cheap enough.

    If you have a dual string inverter could you connect both East and West facing panels to one input and the south facing panels to the other input and it would happily manage the east/west panels or would they interfere with each other?

    Or would you need a triple string inverter?


  • Registered Users, Registered Users 2 Posts: 985 ✭✭✭AidenL


    Yes, but those four panels will need optimisers to ensure that the darker ones don't affect the brigher ones. Not a big issue - optimisers are cheap enough.
    unkel wrote: »
    Optimisers are about €50-€60 per panel. Up to you to make your mind up. Alternatively you could go for a dual or triple string MPPT inverter, then you won't need optimisers for your E or W strings
    reklamos wrote: »
    Before going with optimizers, check your inverter. Solis RHI ones are Dual MPPT so you can connect those panels to second MPPT without optimizers

    I just measured up there, I think id only get one panel on each side of the outcrop.

    My house faces South West, and I have 6m clear space one side of the living room outcrop, on the east side, and 4m clear space on the west side, and that's leaving 0.5m clear from the gables.

    I guess a South West orientation would be decent? Maybe id not need the extra 4 panels.

    Could I install twenty 615 watt panels, with a 5kw ? It would put me a little over the ESB allowance, but is that within margin of error, or is it a total nono?

    Finally, a big question for me - one installer has said no issues fitting in the attic, no heat or fire issues. Another installer has said he would much prefer to install in my steeltech shed, citing more space, less heat issues and better for the inverter. Hes quoting around 1000 euros more, but he would have trenching, armoured cable and so on included. Its around 2m from the side gable of my house. He taken for fireproof board as a backing wall for the equipment and so on.

    Any opinions on this, safety, worth the additional cost, etc? Attic is insulated, but it still gets cold in winter and hot in summer though. To be fair, so does the shed, same , or approximately the same temp extremes in all honesty, the shed not heated, so would run to freezing and below in winter, which I believe has an effect on batteries not charging and not discharging.

    Id appreciate thoughts on pros and cons on the tow locations please?


  • Registered Users, Registered Users 2 Posts: 14,227 ✭✭✭✭joujoujou
    Unregistered Users


    Hello everybody. Long time lurker, first time poster here. ;)

    What say you, good or bad? :)

    493822.png

    493823.png


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 793 ✭✭✭reklamos


    AidenL wrote: »
    Could I install twenty 615 watt panels, with a 5kw ? It would put me a little over the ESB allowance, but is that within margin of error, or is it a total nono?

    Finally, a big question for me - one installer has said no issues fitting in the attic, no heat or fire issues. Another installer has said he would much prefer to install in my steeltech shed, citing more space, less heat issues and better for the inverter. Hes quoting around 1000 euros more, but he would have trenching, armoured cable and so on included. Its around 2m from the side gable of my house. He taken for fireproof board as a backing wall for the equipment and so on.

    Any opinions on this, safety, worth the additional cost, etc? Attic is insulated, but it still gets cold in winter and hot in summer though. To be fair, so does the shed, same , or approximately the same temp extremes in all honesty, the shed not heated, so would run to freezing and below in winter, which I believe has an effect on batteries not charging and not discharging.

    Id appreciate thoughts on pros and cons on the tow locations please?
    I assume 615 is a typo and should be 315Watt.
    Would you have space for 20panels as it does not seem that you do? I would also go for less but higher wattage ones. I'm not sure on ESB part here but because they would be spread over multiple directions you would never get to 6kWh. SEAI grant could be a show stopper if you plan apply for it.

    The location of the inverter depends on the ambient temperature. I have mine installed in the attic that is insulated and facing south. The inverter itself is passive cooled and in July it was getting hot. I could barely hold my hand on the radiator for more than few seconds. The internal monitoring was going close to 70 degrees and that was too hot for me. I have installed 2 fans temperature controlled fans that spin up once it goes above 38 and now the temp rarely goes above 40.
    I'm not convinced about shed as it does not really solve the problem. The temperature would fluctuate there even more and humidity would be higher.