Is locking fire exit door illegal for pubs ?

  • 19-02-2018 10:17AM
    #1
    Registered Users, Registered Users 2 Posts: 565 ✭✭✭


    Is locking fire exit doors illegal for pubs ?

    Basically I went for a drink the weekend when I noticed the band member was tapping the fire exit emergancy door for me to let him in and when I went over to try let him in the fire exit was locked. The bar man had to come out with a set of keys and on top of that spent about 5 minutes finding the right key and wrestling with the door to get it open.

    This really shocked and angered me, imagine there was a fire and people need to use that fire exit and its locked.

    Have we not learned anything from the stardust disaster.

    Anyway, is this illegal and if it is who can I go compain to ? I have a photo of the bar man trying to open the fire exit with his keys


«1

Comments

  • Subscribers Posts: 43,248 ✭✭✭✭sydthebeat


    It is illegal yes.

    Are you 100% sure it was a fire door?


  • Registered Users, Registered Users 2 Posts: 295 ✭✭Dr_Bill


    If it is a fire door it must not be locked. In terms of lodging a complaint it would be your local fire officer (I believe).


  • Registered Users, Registered Users 2 Posts: 3,009 ✭✭✭Captain_Crash


    Regulation 12(f) of the The Workplace Chapter of the Safety, Health and Welfare at Work (General Application) Regulations 2007 state the following;

    (f) emergency doors and gates are not so locked or fastened that they cannot be easily and
    immediately opened by any person who may need to use them in an emergency


  • Registered Users, Registered Users 2 Posts: 19,187 ✭✭✭✭Del2005


    Is locking fire exit doors illegal for pubs ?

    Basically I went for a drink the weekend when I noticed the band member was tapping the fire exit emergancy door for me to let him in and when I went over to try let him in the fire exit was locked. The bar man had to come out with a set of keys and on top of that spent about 5 minutes finding the right key and wrestling with the door to get it open.

    This really shocked and angered me, imagine there was a fire and people need to use that fire exit and its locked.

    Have we not learned anything from the stardust disaster.

    Anyway, is this illegal and if it is who can I go compain to ? I have a photo of the bar man trying to open the fire exit with his keys

    Was there a emergency exit sign above the door? If yes contact the local fire station if not its just a door.


  • Registered Users, Registered Users 2 Posts: 36,170 ✭✭✭✭ED E


    The local fire officer will take this VERY seriously as will the HSA.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 565 ✭✭✭spongebob89


    Great.

    Yes OP in my photo it clearly states emergency exit only and it was locked. I am going to lodge a complaint and hope they get a serious fine or something.


  • Registered Users, Registered Users 2 Posts: 78,734 ✭✭✭✭Victor


    Note that some emergency doors will only open when the fire alarm is triggered.


  • Registered Users, Registered Users 2 Posts: 11,867 ✭✭✭✭BattleCorp


    Victor wrote: »
    Note that some emergency doors will only open when the fire alarm is triggered.

    This shouldn't be the case. They should open independently of the fire alarm.

    What would happen if there was a fire and the fire alarm was defective?


  • Registered Users, Registered Users 2 Posts: 78,734 ✭✭✭✭Victor


    BattleCorp wrote: »
    This shouldn't be the case. They should open independently of the fire alarm.

    What would happen if there was a fire and the fire alarm was defective?
    I imagine it is designed to fail safe - that the alarm will self-report as defective and the door locks (the bolt on the bush bar will still work) will deactivate, as they can't detect the fire alarm system.


  • Registered Users, Registered Users 2 Posts: 452 ✭✭fishy_fishy


    Victor wrote: »
    Note that some emergency doors will only open when the fire alarm is triggered.

    But they're emergency exits, not just fire exits. There could easily be an emergency that doesnt trigger the fire alarm so i cant see how that would be allowed. Is there a provision in the building regs/whatever governs this to allow for fire exits that are not emergency exits?


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 73,010 ✭✭✭✭L1011


    Victor wrote: »
    Note that some emergency doors will only open when the fire alarm is triggered.

    I have never heard of this and I really suspect they would be illegal. There is no way your supposed failsafe is in fact safe.

    The direct opposite - doors that trigger the alarm when opened - are quite normal.


  • Registered Users, Registered Users 2 Posts: 17,313 ✭✭✭✭Sleeper12


    Is locking fire exit doors illegal for pubs ?


    It's always been illegal but since the Stardust tragedy its really enforced. Quite a few of the 48 people that died that night would be alive today if the doors were unlocked


  • Registered Users, Registered Users 2 Posts: 565 ✭✭✭spongebob89


    I cant find any sort of email address to report this if anyone comes across one please post it


  • Registered Users, Registered Users 2 Posts: 17,313 ✭✭✭✭Sleeper12


    Victor wrote:
    Note that some emergency doors will only open when the fire alarm is triggered.


    They are actually called emergency doors. Fire doors actually close when there is a fire. Their job is to help contain a fire. Emergency doors need to be open for all emergencies & not just fire


  • Registered Users, Registered Users 2 Posts: 374 ✭✭GoProGaming


    I cant find any sort of email address to report this if anyone comes across one please post it

    What county are you in? Fire services are ran by each county council. I'm sure they all have general enquiry numbers which can point you in the direction of your local fire prevention office.


  • Registered Users, Registered Users 2 Posts: 27,520 ✭✭✭✭GreeBo


    L1011 wrote: »
    I have never heard of this and I really suspect they would be illegal. There is no way your supposed failsafe is in fact safe.

    The direct opposite - doors that trigger the alarm when opened - are quite normal.

    Those doors are actively closed by the alarm, in the event of alarm failure or alarm sounding the doors unlock.
    At any time you can open the doors by smashing the door release (green box) on the inside.

    If this is not the case then it's just some random door being used as an emergency exit and I would raise it.

    He may have been using keys to open it without sounding the alarm to avoid panic.


  • Registered Users, Registered Users 2 Posts: 738 ✭✭✭Gaillimh1976


    I cant find any sort of email address to report this if anyone comes across one please post it

    Check the website of the relevant county council

    Should have name and contact details of the Fire Officer for the county


  • Registered Users, Registered Users 2 Posts: 9,786 ✭✭✭wakka12


    Thats really sickening and yes illegal


  • Registered Users, Registered Users 2 Posts: 17,313 ✭✭✭✭Sleeper12


    I cant find any sort of email address to report this if anyone comes across one please post it


    Ring your local fire station. They will have a fire officer there within the hour.


  • Registered Users, Registered Users 2 Posts: 19,187 ✭✭✭✭Del2005


    I cant find any sort of email address to report this if anyone comes across one please post it

    Call your local fire station and ask for the fire inspector. If the pub wasn't local they should be able to get you in contact with the correct station.

    IMO safety issues should not be dealt with by email, especially when our infrastructure for the emergency services is so obsolete.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 374 ✭✭GoProGaming


    Sleeper12 wrote: »
    Ring your local fire station. They will have a fire officer there within the hour.

    Keep in mind, if this pub is located in an area that doesn't have a full time station there may not be anyone to answer the call. Most station lines are internal, call your local council office and they will put you in touch with fire prevention.


  • Registered Users, Registered Users 2 Posts: 9,573 ✭✭✭TheChizler


    GreeBo wrote: »
    He may have been using keys to open it without sounding the alarm to avoid panic.

    +1

    Was the door bolted or chained OP? Worth reporting to be safe if you're unsure


  • Registered Users, Registered Users 2 Posts: 17,313 ✭✭✭✭Sleeper12


    Keep in mind, if this pub is located in an area that doesn't have a full time station there may not be anyone to answer the call. Most station lines are internal, call your local council office and they will put you in touch with fire prevention.


    Council office is closed at this hour. Locked emergency exit you ring your local fire station as its dealt as an emergency. If station is closed phone will obviously be automatically transferred to the nearest open station. Fire officer is stationed in the fire station. There are no fire officers at the council office


  • Registered Users, Registered Users 2 Posts: 18,173 ✭✭✭✭fritzelly


    Wonder if someone is getting confused with magnetically held open doors that release when the fire alarm is activated


  • Registered Users, Registered Users 2 Posts: 78,734 ✭✭✭✭Victor


    fritzelly wrote: »
    Wonder if someone is getting confused with magnetically held open doors that release when the fire alarm is activated
    No, it's the reverse. Some doors are held closed until the fire alarm is activated. Otherwise you would have people in shops, etc. running off with expensive items or people entering nightclubs by their friends opening the fire escape.


  • Registered Users, Registered Users 2 Posts: 2,342 ✭✭✭seagull


    We have a number of doors in our building that automatically unlock if the fire alarm is triggered. They can be also be unlocked and opened manually with no key required.


  • Registered Users, Registered Users 2 Posts: 1,283 ✭✭✭Dr Brown


    I've seen alot of bars/clubs lock their fire exits over the years especially on harcourt street.


  • Subscribers Posts: 43,248 ✭✭✭✭sydthebeat


    No escape or fire door should be lockable by a key.


  • Registered Users, Registered Users 2 Posts: 27,520 ✭✭✭✭GreeBo


    sydthebeat wrote: »
    No escape or fire door should be lockable by a key.

    We have yet to determine if it's just unlockable by key.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 18,173 ✭✭✭✭fritzelly


    seagull wrote: »
    We have a number of doors in our building that automatically unlock if the fire alarm is triggered. They can be also be unlocked and opened manually with no key required.

    The fact that you say unlocked and opened goes against all regulation about a fire exit door
    emergency doors and gates are not so locked or fastened that they cannot be easily and
    immediately opened by any person who may need to use them in an emergency

    Cannot also believe that fire exits would rely on a system where they automatically unlock when the fire alarm goes off - any kind of mechanical malfunction and you've got hundreds of dead people