Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie

Two Inverters

13»

Comments

  • Registered Users, Registered Users 2 Posts: 3,044 ✭✭✭Buffman


    Ye, been a while since I read it all but IIRC you have to do pay up and do NC7 first and have a connection agreement signed before construction, followed by installation confirmation cert within 12 months. Have a good read of the Mini-gen link I posted as there's a lot involved. Definitely do the sums as adding the fee will effect payback period, but on the plus side VAT on supply and install is gone since your got the first system installed.

    The below is a general 'signature' and not part of any post:

    FYI, if you move to a 'smart' meter electricity plan, you CAN'T move back to a non-smart plan.

    You don't have to take a 'smart' meter if you don't want one, opt-out is available.

    Buy drinks in 3L or bigger plastic bottles or glass bottles or cartons to avoid the DRS fee.



  • Registered Users, Registered Users 2 Posts: 20 Westfest


    Hello everyone,

    I’m reaching out to gain clarity on the recent regulations set by the ESB (Electricity Supply Board) regarding Micro Generation connections. I hope the community can shed some light on my queries.

    1. Max Limit of 5KW Inverter: The new rules state that with a connection at a low voltage of 230 volts (single phase), the max permissible limit is 25 amperes (about 6kVA). This translates to a maximum inverter size of 5KW. My primary query is: Is this 5KW solely for export, or does it account for both export and internal consumption?

    2. Installation of Two 5KW Inverters: Given that our annual energy requirement is between 10,000-12,000 kW, we are contemplating installing two 5KW inverters. Is this allowed under the new regulations?

    3. Functioning of the Two Inverters: If we were to install two inverters, could one be set up primarily for exporting while the other manages the house load? Is it possible for one inverter to exclusively manage the load without exporting any surplus energy?

    Just to mention, I’m based in Sligo, though I doubt that has any bearing.

    Apologies in advance for my limited understanding. I’m a total novice in this area and any guidance would be highly appreciated.

    Thank you for your time and insights!



  • Registered Users, Registered Users 2 Posts: 6,464 ✭✭✭championc


    Who's to stop you installing extra inverters of any size.

    Just make sure you have a mechanism to stop any exports exceeding 5kW.

    Many inverters gave a limited function, to limit export to xkW



  • Registered Users, Registered Users 2 Posts: 9,035 ✭✭✭10-10-20


    1. That limit is the total for all grid-tied inverters, ie any inverters which are attached to the mains supply on the property which have the potential to export, even if not configured to do so. It would not count independent inverters such as a fully-isolated grid (such as on a shed) with zero connection to the ESB mains.
    2. In theory that is possible but I have yet to see a split configuration which would allow greater than 25A to the letter of the NC6 regulations.
    3. Again, in theory yes, but see answer 2.

    BTW, you're confusing two terms in question 2 which is important to get right; it may be leading you into thinking that you need two inverters:

    "Our annual energy requirement is between 10,000-12,000 kW" - It might seem trivial, but it should be kWh. That's the measure of energy over time (hours). So 1kW consumed over a period of 10 hours would equal 10kWh. With inverters then you measure the max instantaneous generation capacity and that's 5kW, but it doesn't tell you what duration that it can supply that wattage for. If you then put solar and a battery behind the inverter then you have storage potential - and that can be measured in kWh. So you can't divide the yearly consumption of 10,000kWh by the inverter's 5kW and size the system that way, you need to break down your usage per-day so that you can obtain a kWh figure.

    An example would be by taking 12,000kWh and dividing that by 365 days to get roughly 33kWh consumed per day. Then you know that you'd ideally like your generation capability to beat that in the Summer months. For Winter you commonly would then take what you get and take the remainder off the grid, but your Summer should be paid-for.

    Here's a Gary Does Solar to explain that in a graphical way:

    In fairness, that's not in the spirit of the rules, the rules are there to protect the electrical distribution network and the ESB are limiting the export potential so that in the event of a fault on your equipment (especially this limitation mechanisim) that it doesn't have the capability of sending excessive current into local distribution.



  • Registered Users, Registered Users 2 Posts: 623 ✭✭✭idc


    Agree with @10-10-20 the ESBN rules for NC6 are quite clear that it excludes export limitation features and is the total max output of all inverters. but I expect people will/can ignore this given I don't expect ESBN to check every house! Also for some reason mp3guy has multiple inverters and export limitation without ESBN having any issue with it on just an NC6.




  • Advertisement
  • Registered Users, Registered Users 2 Posts: 6,464 ✭✭✭championc


    Once we all have Smart Meters, that will most likely become the "policing" mechanism. If you export over 5kWh in any hour, you're likely to show up with red flags (if they create such reports to flag these)



  • Moderators, Home & Garden Moderators Posts: 7,088 Mod ✭✭✭✭graememk


    It was before they really "cared" or noticed

    It was also before the nc7 was a thing.

    That horse has already bolted but the rest in the stable are restrained



  • Registered Users, Registered Users 2 Posts: 3,979 ✭✭✭mp3guy


    Exactly. This is also what my original installer reckons. My system is "grandfathered in" so to speak. I put my NC7 on ice last December due to voltage concerns but things will be changing for my supply locally in the next few months so I'm going to resurrect it.



  • Registered Users, Registered Users 2 Posts: 4,510 ✭✭✭...Ghost...


    I assume one would run the dumb inverter to the CU either directly, or via a shed/garage mini CU?

    If that is the case, and there is no communication between the dumb inverter and the main (hybrid) inverter, does this mean that any generation running through the dumb inverter simply offsets the the load potentially needed from the grid and would feed any batteries connected to the hybrid inverter?

    Examples:

    (a) House load is 8kW. Main solar generating 4kW. Extra solar generating 3kW.

    Result = Importing 1kW from grid.

    (b) House load is 6kW. Main solar generating 4kW. Extra solar generating 3kW.

    Result = Sending 1kW to battery.

    Would the above be correct with the setup below? If not, what is missing?

    GEN-SETUP.png

    Stay Free



  • Posts: 2,768 [Deleted User]


    @...Ghost...

    You can set the hybrid Inverter to either recognise the export/production of the dumb inverter and charge the batteries, or to ignore it and let it go to the grid. The dumb inverter will first feed the house load before exporting or charging the batteries.

    Microinverters would work very well on your shed. You can get 4 port micro's. A string inverter might work out cheaper though.



  • Advertisement
  • Moderators, Home & Garden Moderators Posts: 7,088 Mod ✭✭✭✭graememk


    On the sunsynk/deye you can select it.

    On the solis you can't, but will pick up the excess from other inverters

    On givenergy it doesn't pickup the excess from other inverters

    Have first hand experience on the first 2 but have been told about the third



  • Posts: 2,768 [Deleted User]


    My mistake, I assumed they would all have the option.

    That's poor enough, I wonder is this just a software limitation.



  • Registered Users, Registered Users 2 Posts: 6,464 ✭✭✭championc


    Yes

    A Hybrid will see power going towards the grid, and grab it.

    I doesn't know where it is coming from, neither does it care



  • Registered Users, Registered Users 2 Posts: 4,510 ✭✭✭...Ghost...


    Hoping I don't need to start new thread, as this one is on topic with 2 inverters. Note that a RECI will be completing all relevant work, but I want to know what I am talking about.

    I plan to have 30-45kWh of storage (2 or 3 batteries) with the first 15kWh being built this week hopefully. Currently have a 5kW Solis hybrid inverter with a 5.2kWp system on the house. Smart meter installed.

    I plan to add about 5kWp to the shed and ground floor extension (2 strings). I know a dumb inverter can feed into a mini CU in the shed and from there to the main CU, or I could bypass the mini CU, set the dumb inverter up beside the hybrid inverter and then feed into the main CU, but I would like some help please, as I am not sure what direction is best to go. Here is my goal…

    I want to be able to charge and discharge up to 10kW from the batteries if possible, which would almost eliminate any day rate grid import for me. Likewise, I would like to be able to charge the batteries up over a 3 hour window. What is the best way to do this assuming I have 2 x 15kWh Seplos batteries? The second (maybe 3rd) battery will be bought and ready by August.

    From the thread, I see an upgraded hybrid inverter could be an answer, but I would prefer to add to what I have rather than replace, because I will have a total of 4 strings and I don't want to change out the new inverter so soon. Also I think I would still have a battery discharge limit of 5kW???

    I currently avail of a standard night rate which I could use to fully charge a full compliment of 45kWh @ 5kW/h over the night, but then I can't take advantage of much cheaper boost rates, or advantageous peak dump rates. Help me out before I start buying stuff please 😊

    Stay Free



  • Registered Users, Registered Users 2 Posts: 9,035 ✭✭✭10-10-20


    Likewise, I would like to be able to charge the batteries up over a 3
    hour window. What is the best way to do this assuming I have 2 x 15kWh
    Seplos batteries?

    But that's impossible without a 10kW inverter…? If the largest allowed inverter is ~5.5kW, then three times that is 16.5kW. So are you planning on going for NC7 or similar?



  • Registered Users, Registered Users 2 Posts: 4,510 ✭✭✭...Ghost...


    Only seeing this now. I'm not sure what is possible, or allowed. Would a second inverter with grid export switched off be possible? Could this let me me increase the battery charge/discharge limits from 5kW to 10kW? I'm putting it out there because I have seen inverters hooked up together to do this, but I don't know exactly how, or if it is allowed here. No plans to apply for NC7.

    Stay Free



  • Registered Users, Registered Users 2 Posts: 9,035 ✭✭✭10-10-20


    Id love to tell you otherwise but it's not allowed under the rules and there isn't an inverter or solution on the market which offers a true 'zero export' option. I'd be riding that bus for sure if it was an option.



  • Registered Users, Registered Users 2 Posts: 623 ✭✭✭idc


    I expect your only option would be independent circuits - ie one connected to grid and others that have no connection to grid at all, but don't know if there electrical rules around that. Eg what happens in case of fire - they disconnect you at meter and have no idea half the house is still fully powered! Then again thats no different to inverters with a backup circuit. Firemen cut power to house but backup circuits are still live from battery!!



  • Registered Users, Registered Users 2 Posts: 6,464 ✭✭✭championc


    You could parallel an external battery charger



  • Moderators, Sports Moderators Posts: 19,903 Mod ✭✭✭✭slave1


    A second inverter can be CT clamped at the CU to stop exporting at whatever limit you want, so as an extreme example if Inverter A was exporting at 6kW then Inverter B would effectively shut down as it has no bandwidth to export.

    Apparently some folk have this setup and working rock solid

    My stuff on Adverts, mostly Tesla Pre Highland Model 3

    Public Profile active ads for slave1



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 623 ✭✭✭idc



    The only issue is any such setup breaks rules of NC6. ESBN don't allow for export limitation on NC6 - it is entirely defined as max combined inverters can not exceed 25Amp on single phase. But honestly I don't see how they'll know.



  • Registered Users, Registered Users 2 Posts: 6,464 ✭✭✭championc


    Which is why I am suggesting an external separate charger. Would be 100% compliant with NC6



  • Registered Users, Registered Users 2 Posts: 623 ✭✭✭idc


    @championc yep no issue with your suggestion 😀 whereas @slave1 suggestion won't be 100% compliant, but no doubt plenty of people do that anyway!



  • Registered Users, Registered Users 2 Posts: 84 ✭✭Thewitheredowl


    Hi All,

    Just looking for some advice on my setup here:

    Originally had a Sunsynk 3.6kW inverter in my attic. 2 x 5kWh batteries attached and 4kWp of panels on the roof. All worked fine, but decided I didn't really want the batteries in the attic, so I moved the Sunsynk inverter and batteries to my shed. Found a solution with the help of one of the guys on this forum for sending power meter (I have an inline power meter as opposed to CT) readings of my main incomer over ethernet which I then pick up in my shed and route it into the Sunsynk. The inverter can see my live power consumption and it's accurate.

    I then installed a Huawei 5kW hybrid inverter in the attic to connect to the solar panels. I didn't connect a power meter/CT to this inverter (I can do this easily if it's needed), I just let it take power from the panels.

    So, in theory, any excess generated by the panels by way of the Huawei should really be picked up by the Sunsynk in the shed in order to top up the batteries, but this is not happening. The batteries are consistently taking only 350w of the excess panel production, even at times when there is up to 3kW available. 350w will to to the batteries and 2650w will be exported.

    I can see on the Sunsynk that it has a grid power reading of -3000w in the instance above, but it's not grabbing that and sending it to the batteries.



  • Moderators, Home & Garden Moderators Posts: 7,088 Mod ✭✭✭✭graememk




  • Registered Users, Registered Users 2 Posts: 84 ✭✭Thewitheredowl


    Worked perfectly. Really appreciate the input



  • Registered Users, Registered Users 2 Posts: 100 ✭✭daesal


    Great thread. Full of useful information. Sorry if this is a bit of a long gap.

    I'm currently running a Sunsynk 5kw with 6k of panels attached to a 6.4kwh battery. This is powering one house and selling excess back to grid.

    I would like to also power a separate building. Ideally separately and also sell excess to grid.

    I am thinking of getting another SS 5k , 13kwh if Seplos battery and 7kw of panels for the 2nd building.

    Is it possible to run both these set ups and export excess?

    There is only one ESB connection to the property.

    What happens if one inverter is importing while the other is exporting?

    Thank you all



Advertisement