Storage heaters

Options
  • 30-12-2020 4:37pm
    #1
    Registered Users Posts: 57 ✭✭


    Hi all,
    We have 3 storage heaters (Creda) in an apartment that all stopped working at same time. This happened a few weeks before Christmas, managed to get a guy out before Christmas and he said he didn’t know what’s wrong with them and quoted for 3 replacement heaters. He didn’t seem too interested in finding a fault (few minutes at the fuse box, few minutes fiddling with one of the heaters) - more interested in selling new heaters.
    Anyway, want them repaired so will have to get someone else out and pay another call out. Anyone know what I should be asking them to look at here so I can ask if they checked x, y and z and if they are all ok? Or better still recommend someone by PM that knows these things and what to do (Dublin city centre).
    Many thanks.


«1

Comments

  • Banned (with Prison Access) Posts: 124 ✭✭Treseemme.


    Don't get him again anyhow

    I haven't looked at them for a while and there's a few different designs of system

    I'd prob start by energising the contactor and see do they come on

    If they do I'd probably trace the control circuit wiring as best i can . Check the devireg and resistor, stat if there is one.

    Is there anything switched off or turned down?


  • Site Banned Posts: 113 ✭✭Dunfyy


    Have you a night meter


  • Registered Users Posts: 57 ✭✭Jackaroe


    Cheers. I had checked them all and made sure all on and turned up etc. I’m assuming that as they all went off at the same time it’s something to do with the supply getting to the heaters, rather than the heaters themselves having a fault (or at least a fault in one of the heaters caused a break in the supply?). I’m not an electrician so the most I was comfortable with was popping the covers off to see if anything obvious burnt out etc but there’s nothing obvious from a visual inspection.


  • Registered Users Posts: 57 ✭✭Jackaroe


    Dunfyy wrote: »
    Have you a night meter

    Yes there is a night meter


  • Registered Users Posts: 4,733 ✭✭✭meercat


    Is the wall thermostat turned up

    Are there indicator lights on the storage heater switches

    Post a photo of your distribution board


  • Advertisement
  • Registered Users Posts: 57 ✭✭Jackaroe


    Hey, photos attached.


  • Registered Users Posts: 57 ✭✭Jackaroe


    There are lights on the switches, but they are not lighting up since problem started. They were lighting when the heaters worked. There is no separate thermostat.

    The tripped switch by the way is a bathroom heater that burnt out years ago so was just left off to prevent it being turned on accidentally - not related to the current issue.


  • Registered Users Posts: 24,647 ✭✭✭✭punisher5112


    Jackaroe wrote: »
    Hey, photos attached.

    22 MCB is tripped, pull down and click back up, if it trips then there is an issue.


  • Registered Users Posts: 24,647 ✭✭✭✭punisher5112


    The black/grey unit at 11-13 is what control the supply to heaters, this could be the issue.


  • Registered Users Posts: 8,215 ✭✭✭ongarite


    The top dual dial, 710-2, is the same as mine.
    Put the Day dial to O instead of constant & night to 0 initially.
    It looks like its powered on & active as both LEDs are on.
    Edit: You say they aren't on now. The MCB for the storage heater should turn it back on.

    There should be a switch to turn on/off the heaters in each room.
    Is there a booster on any of them? A switch on the heater to turn it into an electric radiator?


  • Advertisement
  • Registered Users Posts: 57 ✭✭Jackaroe


    22 MCB is tripped, pull down and click back up, if it trips then there is an issue.

    Sorry edited the post afterwards to clarify this is a bathroom fan heater that has been off for years as it burnt out - not related as storage heaters worked for years with this off


  • Registered Users Posts: 24,647 ✭✭✭✭punisher5112


    Jackaroe wrote: »
    Sorry edited the post afterwards to clarify this is a bathroom fan heater that has been off for years as it burnt out - not related as storage heaters worked for years with this off

    I knew it wasn't part of the other heaters but thought it may have tripped for a reason....

    The unit on the bottom right could be sticking, give it a tap, not hard but power all off doing so.

    Then switch everything back on....


  • Registered Users Posts: 57 ✭✭Jackaroe


    ongarite wrote: »
    The top dual dial, 710-2, is the same as mine.
    Put the Day dial to O instead of constant & night to 0 initially.
    It looks like its powered on & active as both LEDs are on.
    Edit: You say they aren't on now. The MCB for the storage heater should turn it back on.

    There should be a switch to turn on/off the heaters in each room.
    Is there a booster on any of them? A switch on the heater to turn it into an electric radiator?

    Thanks I’ll try that. There is an electric heater on one of them which is working ok.


  • Banned (with Prison Access) Posts: 124 ✭✭Treseemme.


    Jackaroe wrote: »
    Hey, photos attached.

    Only just looked at those pictures

    Not great with the contactor there, does a blank even cover it or did it fall off?


  • Registered Users Posts: 57 ✭✭Jackaroe


    Treseemme. wrote: »
    Only just looked at those pictures

    Not great with the contactor there, does a blank even cover it or did it fall off?

    There was a plastic cover on it which I took off to take photos


  • Registered Users Posts: 567 ✭✭✭Kencollins


    On the grey contactor at 11 - 13, is the switch on the bottom left slid over to "0"? If so, try sliding it back over to "1".


  • Registered Users Posts: 57 ✭✭Jackaroe


    Kencollins wrote: »
    On the grey contactor at 11 - 13, is the switch on the bottom left slid over to "0"? If so, try sliding it back over to "1".

    It’s at 0, when I push it to 1 it just springs back to 0 (there’s also a flash when pushing it to 1). Should it stay at the 1 position?


  • Registered Users Posts: 474 ✭✭MintyMagnum


    If you are on a night meter the 'clock' might need to be replaced This is a job for the esb, as its their equipment. In my case one electrician said all the storage heaters were knackered, old & needed replacing. A 2nd opinion electrician said problem was the clock in the meter. That was replaced et voila, problem solved. The heaters themselves weren't actually kaput. Saved a lot of unnecessary cost & hassle even though had two call outs!


  • Registered Users Posts: 24,647 ✭✭✭✭punisher5112


    Jackaroe wrote: »
    It’s at 0, when I push it to 1 it just springs back to 0 (there’s also a flash when pushing it to 1). Should it stay at the 1 position?

    That flash is a spark, I would be near sure it's done and needs replacing.

    Could well be shorting, if the cover was off you may see heat damage but only a reci can do this work.


  • Registered Users Posts: 57 ✭✭Jackaroe


    If you are on a night meter the 'clock' might need to be replaced This is a job for the esb, as its their equipment. In my case one electrician said all the storage heaters were knackered, old & needed replacing. A 2nd opinion electrician said problem was the clock in the meter. That was replaced et voila, problem solved. The heaters themselves weren't actually kaput. Saved a lot of unnecessary cost & hassle even though had two call outs!

    Thanks - I might start there so - do you recall how much it was to get ESB out and to replace the clock?


  • Advertisement
  • Registered Users Posts: 18,225 ✭✭✭✭Bass Reeves


    Jackaroe wrote: »
    Thanks - I might start there so - do you recall how much it was to get ESB out and to replace the clock?

    The ESB will not charge but your electrician must first prove everything is ok inside in house.

    What KW are the heaters

    Slava Ukrainii



  • Registered Users Posts: 57 ✭✭Jackaroe


    That flash is a spark, I would be near sure it's done and needs replacing.

    Could well be shorting, if the cover was off you may see heat damage but only a reci can do this work.

    Cheers. I might look into the night clock first. Now that another poster mentioned it I do recall that the heaters started coming on at funny times before they stopped working. I didn’t think much of it at the time or connect it but that might explain it.


  • Registered Users Posts: 24,647 ✭✭✭✭punisher5112


    Jackaroe wrote: »
    Cheers. I might look into the night clock first. Now that another poster mentioned it I do recall that the heaters started coming on at funny times before they stopped working. I didn’t think much of it at the time or connect it but that might explain it.

    That's just because the time was wrong I'd say. Use to see this a lot....

    If they are doing a fault find I would start with each heater one by one testing supply, this consists of adding a supply to them to check they work as during the day it would be impossible to know as night meter would be off.

    Then I'd move to relay contactor.

    I'd also suggest while at it, clean out the inner of heaters as huge dust build ups can be a danger and we'll worth a clean out.

    2 screws usually hold the outer cover on at the bottom on each side.

    Hope you get sorted.


  • Registered Users Posts: 57 ✭✭Jackaroe


    The ESB will not charge but your electrician must first prove everything is ok inside in house.

    What KW are the heaters

    Thanks. One of them is 24kwh storage capacity and the other two are 12kwh capacity.


  • Registered Users Posts: 57 ✭✭Jackaroe


    Hi all, just to update this and hopefully close it out! I spoke to the ESB this morning and they were able to give me a meter reading they took a few days ago, and comparing it to the current reading the night units haven’t changed. So it looks like the night meter isn’t working and they said that’s likely the cause of the storage heater issue. They are sending someone out on Tuesday to see if they can reset the clock or whatever they need to do.
    So fingers crossed that’s it.
    Thanks to all for your help/advice on this!


  • Registered Users Posts: 4,733 ✭✭✭meercat


    Jackaroe wrote: »
    Hi all, just to update this and hopefully close it out! I spoke to the ESB this morning and they were able to give me a meter reading they took a few days ago, and comparing it to the current reading the night units haven’t changed. So it looks like the night meter isn’t working and they said that’s likely the cause of the storage heater issue. They are sending someone out on Tuesday to see if they can reset the clock or whatever they need to do.
    So fingers crossed that’s it.
    Thanks to all for your help/advice on this!


    Not saying it’s not a faulty meter but I’ve never come across one given the setup you have here. I’ve replaced devireg controllers before and also the contactors. Check your wall roomstat is turned up. Id still say the problem is on the control circuit somewhere. A competent electrician should identify the problem in minutes

    If you turn the day button to constant does the indicator light change to red.

    Any chance of a photo of meter setup and most importantly a closeup of the clock controller

    https://www.boards.ie/vbulletin//attachment.php?attachmentid=186000&d=1324508064


  • Registered Users Posts: 474 ✭✭MintyMagnum


    Jackaroe wrote: »
    Thanks - I might start there so - do you recall how much it was to get ESB out and to replace the clock?

    I don't recall any esb charge, coz 'twas their equipment failed, only I had to pay two electricians before that! Hope it's a simple fix for you.


  • Banned (with Prison Access) Posts: 124 ✭✭Treseemme.


    Timing being off would be the main issue I've encountered with dual tariff

    Not much else


  • Registered Users Posts: 57 ✭✭Jackaroe


    meercat wrote: »
    Not saying it’s not a faulty meter but I’ve never come across one given the setup you have here. I’ve replaced devireg controllers before and also the contactors. Check your wall roomstat is turned up. Id still say the problem is on the control circuit somewhere. A competent electrician should identify the problem in minutes

    If you turn the day button to constant does the indicator light change to red.

    Any chance of a photo of meter setup and most importantly a closeup of the clock controller

    https://www.boards.ie/vbulletin//attachment.php?attachmentid=186000&d=1324508064

    Cheers. Here’s a close up of the clock. The light stays green even after changing to const. The other light flashes red all the time.


  • Advertisement
  • Registered Users Posts: 4,733 ✭✭✭meercat


    Jackaroe wrote: »
    Cheers. Here’s a close up of the clock. The light stays green even after changing to const. The other light flashes red all the time.

    Hard to make photo out looks like it’s on 0 not constant