New warmflow oil condenser boiler keeps cutting out

  • 24-10-2020 6:50pm
    #1
    Registered Users, Registered Users 2 Posts: 45


    We got a brand new warmflow oil condenser boiler fitted in June. It has been cutting out intermittently ever since. We have had the plumber back out several times but he cannot seem to find a problem. The boiler works fine for maybe 2 weeks at a time and will then just stop working. He originally said it was air locked and it worked fine for a week or so after being bled before the same problem arose. Each time it happens it seems to be follow bad weather either wet or windy. Sometimes it resolves itself when its bled and other times it just randomly starts working after a day or 2. Could this be caused by an electrical fault or is it more likely to be a problem with the boiler? Thanks in advance


«1

Comments

  • Registered Users, Registered Users 2 Posts: 1,206 ✭✭✭Vestiapx


    If you paid the plumber to fit it then it's his issue


  • Registered Users, Registered Users 2 Posts: 3,623 ✭✭✭John.G


    Is it tripping out, ie do you have to press a reset button, it may also be cutting out on high water temperature which needs a different reset, the first is burner failure.


  • Registered Users, Registered Users 2 Posts: 45 needtoknowasap


    Vestiapx wrote: »
    If you paid the plumber to fit it then it's his issue

    He's telling us now it seems to be electrical but we're not convinced as the boiler fires up but cuts out before it actually heats the house or water? There was an exposed wire near the boiler which has been sealed just wondering if it could cause the issue


  • Registered Users, Registered Users 2 Posts: 45 needtoknowasap


    John.G wrote: »
    Is it tripping out, ie do you have to press a reset button, it may also be cutting out on high water temperature which needs a different reset, the first is burner failure.

    No the reset button doesn't illuminate or work when pressed. He told us to use the air lock reset on top which works sometimes but not others? The pipes on top of the boiler are all hot to touch but nothing circulating to the house


  • Registered Users, Registered Users 2 Posts: 3,623 ✭✭✭John.G


    Can or have you bled any air out of the boiler/rads,
    That sounds like a water high temperature limit stat reset.
    Is the circulating pump located in the boiler itself and can you see what the speed settings are or/and take a photo of it and post it, also can you turn the boiler temperature stat down to minimum.
    Also does you system have zoning, ie a programmer and roomstats/cylinder stats and are all the zone (motorised) valves opening.

    Also if a sealed system ensure boiler gauge at 1.5 bar.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 212 ✭✭ShaneC1600


    Was the boiler commissioned after it was installed?


  • Moderators, Home & Garden Moderators Posts: 6,380 Mod ✭✭✭✭Wearb


    530494.jpg
    Is it the button behind that black cover that you have to press to get it going?

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 3,975 ✭✭✭jimf


    did you have a new circulating pump fitted as well as the boiler

    if no then you possibly have an intermittent faulty pump


  • Hosted Moderators Posts: 3,496 ✭✭✭DGOBS


    I recon he has fitted the pump the wrong way around


  • Hosted Moderators Posts: 3,496 ✭✭✭DGOBS


    Also just noticed, Saturday night, bank holiday weekend, and me, Jim, Wearb, Shane and John are all here online.......god we need to get lives


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 3,975 ✭✭✭jimf


    DGOBS wrote: »
    Also just noticed, Saturday night, bank holiday weekend, and me, Jim, Wearb, Shane and John are all here online.......god we need to get lives

    lets all meet at murrays in 2 hours for a party better bring our own drink


  • Registered Users, Registered Users 2 Posts: 3,404 ✭✭✭corkgsxr


    I bet ya it's old or cheap as pump.


  • Registered Users, Registered Users 2 Posts: 45 needtoknowasap


    John.G wrote: »
    Can or have you bled any air out of the boiler/rads,
    That sounds like a water high temperature limit stat reset.
    Is the circulating pump located in the boiler itself and can you see what the speed settings are or/and take a photo of it and post it, also can you turn the boiler temperature stat down to minimum.
    Also does you system have zoning, ie a programmer and roomstats/cylinder stats and are all the zone (motorised) valves opening.

    Also if a sealed system ensure boiler gauge at 1.5 bar.

    No idea if the circulating pump is in the boiler I'll try post a few pictures of all we can see when open it. The rads have been bled and allnhave their own temperature setting on them all set to max. They all work fine when the heating works. No zones all we have is a switch in the hotpress replaced the same time as the boiler to switch from heating rads and water to just heat water during the summer. We haven't touched it since we started having problems to see if it was it causing the problem but it doesn't seem to be


  • Registered Users, Registered Users 2 Posts: 45 needtoknowasap


    ShaneC1600 wrote: »
    Was the boiler commissioned after it was installed?

    Yea it was commissioned but just got a print out from the machine


  • Registered Users, Registered Users 2 Posts: 45 needtoknowasap


    Wearb wrote: »
    530494.jpg
    Is it the button behind that black cover that you have to press to get it going?

    There is no button like,that I'm trying to upload photos of the boiler but internet connection not great


  • Registered Users, Registered Users 2 Posts: 3,975 ✭✭✭jimf


    the warmflow stat is different its more rectangular graded from 1 to 5


  • Registered Users, Registered Users 2 Posts: 45 needtoknowasap


    No idea if the circulating pump is in the boiler I'll try post a few pictures of all we can see when open it. The rads have been bled and allnhave their own temperature setting on them all set to max. They all work fine when the heating works. No zones all we have is a switch in the hotpress replaced the same time as the boiler to switch from heating rads and water to just heat water during the summer. We haven't touched it since we started having problems to see if it was it causing the problem but it doesn't seem to be

    Heres some pictures


  • Registered Users, Registered Users 2 Posts: 45 needtoknowasap


    Heres some pictures

    .


  • Registered Users, Registered Users 2 Posts: 45 needtoknowasap


    .

    .


  • Registered Users, Registered Users 2 Posts: 45 needtoknowasap


    .

    .


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 45 needtoknowasap


    There is no button like,that I'm trying to upload photos of the boiler but internet connection not great

    Its the red valve at the top of the picture you have to turn to release the airlock


  • Registered Users, Registered Users 2 Posts: 3,623 ✭✭✭John.G


    Re third photo in post #20, it might appear to me that that pump is pumping downwards, can you check for a arrow on the pump body, if not take a photo of the bottom of the pump as we can see then where the suction is.

    The red valve is the boiler PRV (safety) valve, normally should only have to use this after refilling system to vent air.

    Also why is the thermostat in turned to max?, turn it down to mid scale.


  • Registered Users, Registered Users 2 Posts: 3,404 ✭✭✭corkgsxr


    Pump shouldn't be fitted facing up either.

    Personally id switch the pump to manual flow. Dabs system is terrible for going too low imo


  • Registered Users, Registered Users 2 Posts: 3,623 ✭✭✭John.G


    Its on constant curve (fixed speed) speed 3 I think?.


  • Registered Users, Registered Users 2 Posts: 45 needtoknowasap


    John.G wrote: »
    Re third photo in post #20, it might appear to me that that pump is pumping downwards, can you check for a arrow on the pump body, if not take a photo of the bottom of the pump as we can see then where the suction is.

    The red valve is the boiler PRV (safety) valve, normally should only have to use this after refilling system to vent air.

    Also why is the thermostat in turned to max?, turn it down to mid scale.

    Even if the pump is on upside down why would it work for 2 to 3 weeks at a time and then suddenly stop? The lights on the evosta2 which I'm presuming is the pump you refer to light up with the 3 bars when turned on but then time out and disappear leaving only the top light on if you get me.


  • Banned (with Prison Access) Posts: 54 ✭✭jenneyk19


    plumber needs to hire some one that can fix boilers also you have to register to get their 7 year warranty

    boilerguide.co.uk/manufacturers/warmflow/repair-advice


  • Registered Users, Registered Users 2 Posts: 3,623 ✭✭✭John.G


    It could work (I have seen one pumping the wrong way for 8 years) but the thermostat is then measuring the return temperature, the boiler is then raising this by another 15 to 25c, and with the stat turned full up will mean that the hi limit stat would certainly operate fairly often.
    Will get back to you re pump, can you try and establish the arrow direction or a photo of the pump bottom.


  • Registered Users, Registered Users 2 Posts: 3,404 ✭✭✭corkgsxr


    John.G wrote: »
    Its on constant curve (fixed speed) speed 3 I think?.

    Is the flat like not fixed curve. Round line proportional?

    It's much harder for pumps to push out air if they are fitted that way. Especially combined with proportional setting


  • Registered Users, Registered Users 2 Posts: 3,623 ✭✭✭John.G


    No, proportional is the "45 deg" line, constant pressure is the "90 deg* straight line(s) and the "curves" are like traditional pump curves, ie traditional fixed speed curves.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 45 needtoknowasap


    John.G wrote: »
    It could work (I have seen one pumping the wrong way for 8 years) but the thermostat is then measuring the return temperature, the boiler is then raising this by another 15 to 25c, and with the stat turned full up will mean that the hi limit stat would certainly operate fairly often.
    Will get back to you re pump, can you try and establish the arrow direction or a photo of the pump bottom.[/quot

    Ok thanks as you can probably tell we have no clue about boilers hence why we paid good money to get it replaced. Its quite hard to see but the only arrow i can see is on the bottom of the pump pointing towards the heating return sticker.


  • Registered Users, Registered Users 2 Posts: 3,404 ✭✭✭corkgsxr


    John.G wrote: »
    No, proportional is the "45 deg" line, constant pressure is the "90 deg* straight line(s) and the "curves" are like traditional pump curves, ie traditional fixed speed curves.

    After much staring I believe your right.

    Still dislike them. I replaced loads I fitted


  • Moderators, Home & Garden Moderators Posts: 6,380 Mod ✭✭✭✭Wearb


    Turn that boiler thermostat to about 1/4 way from fully anticlockwise and it might help until you get it sorted.

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 3,975 ✭✭✭jimf


    can you post a pic of the print out from the passport


  • Registered Users, Registered Users 2 Posts: 3,623 ✭✭✭John.G


    John.G wrote: »
    It could work (I have seen one pumping the wrong way for 8 years) but the thermostat is then measuring the return temperature, the boiler is then raising this by another 15 to 25c, and with the stat turned full up will mean that the hi limit stat would certainly operate fairly often.
    Will get back to you re pump, can you try and establish the arrow direction or a photo of the pump bottom.[/quot

    Ok thanks as you can probably tell we have no clue about boilers hence why we paid good money to get it replaced. Its quite hard to see but the only arrow i can see is on the bottom of the pump pointing towards the heating return sticker.

    Thats no problem.

    Re these four lights. one on the very top and the three others.

    The very top one shows what mode the pump is selected to and the other three, the speed setting, when all three are displayed it means that the top speed is selected, these three should stay illuminated IMO as long as the pump is running and if they are not with the very top light still illuminated it probably means that the pump has cut out and stopped on thermal overload and will self restart when it cools down.
    That setting is far too high IMO, its a 7 meter pump at that setting, also the pump is probably picking up an awful lot of heat in that position, not helping the situation.

    First, Turn down the thermostat NOW to mid way or even lower, the when the pump is again displaying those 3 lines, press the mode button briefly until you only have one line illuminated, you should still get plenty of circulation as it will still be a 4 meter pump.

    The pump is pumping to the return of the boiler which is correct by your description of the arrow direction.


  • Moderators, Home & Garden Moderators Posts: 6,380 Mod ✭✭✭✭Wearb


    John.G wrote: »

    Thats no problem.

    Re these four lights. one on the very top and the three others.

    The very top one shows what mode the pump is selected to and the other three, the speed setting, when all three are displayed it means that the top speed is selected, these three should stay illuminated IMO as long as the pump is running and if they are not with the very top light still illuminated it probably means that the pump has cut out and stopped on thermal overload and will self restart when it cools down.
    That setting is far too high IMO, its a 7 meter pump at that setting, also the pump is probably picking up an awful lot of heat in that position, not helping the situation.

    First, Turn down the thermostat NOW to mid way or even lower, the when the pump is again displaying those 3 lines, press the mode button briefly until you only have one line illuminated, you should still get plenty of circulation as it will still be a 4 meter pump.

    All assuming the system is clean and not gunked up.

    Was it power flushed before new install?

    Please follow site and charter rules. "Resistance is futile"



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 45 needtoknowasap


    John.G wrote: »

    Thats no problem.

    Re these four lights. one on the very top and the three others.

    The very top one shows what mode the pump is selected to and the other three, the speed setting, when all three are displayed it means that the top speed is selected, these three should stay illuminated IMO as long as the pump is running and if they are not with the very top light still illuminated it probably means that the pump has cut out and stopped on thermal overload and will self restart when it cools down.
    That setting is far too high IMO, its a 7 meter pump at that setting, also the pump is probably picking up an awful lot of heat in that position, no helping the situation.

    First, Turn down the thermostat NOW to mid way or even lower, the when the pump is again displaying those 3 lines, press the mode button briefly until you only have one line illuminated, you should still get plenty of circulation as it will still be a 4 meter pump.

    Thanks its turned down now and will see how it goes in the morning hopefully it will work. The open fire blazing all day so no need for heating tonight thankfully.


  • Registered Users, Registered Users 2 Posts: 45 needtoknowasap


    jimf wrote: »
    can you post a pic of the print out from the passport

    .


  • Registered Users, Registered Users 2 Posts: 3,623 ✭✭✭John.G


    Just before you go can you say that those 3 lights were lighting sometimes and not at other times?, also set the pump to that one light setting.

    Friend told me that you should have got a error code if pump stopped for any reason and more than likely that the lights go out a few seconds after you finish your selection or press the mode button briefly to see the settings.


  • Registered Users, Registered Users 2 Posts: 3,975 ✭✭✭jimf


    .


    its not bad but a bit overaired for a bx burner

    anyway this is not the cause of your issue atm

    does anybody know if dab have sorted the issues they had with pumps


  • Registered Users, Registered Users 2 Posts: 45 needtoknowasap


    John.G wrote: »
    Just before you go can you say that those 3 lights were lighting sometimes and not at other times?, also set the pump to that one light setting.

    Friend told me that you should have got a error code if pump stopped for any reason and more than likely that the lights go out a few seconds after you finish your selection or press the mode button briefly to see the settings.


    Where would the error code appear? Tried everything suggested this morning and still same happening it fires up at first then cuts out. Lights go off after a few seconds of it starting. When press the mode button they come back on briefly. I have set it to just one light, the pipe marked heating flow is hot to touch but not getting heat to the house.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 3,623 ✭✭✭John.G


    I think that the lights do go out normally after making your selectiom, especially when they come on again briefly when you press the mode button again. I will dig out the eManual later, if you keep your hand on the pump you should feel a slight tremor if its running continuously. For the moment assume that it is. Any error codes I would think would be displayed where those lights are. But I am pretty sure that the pump is running continuously.

    Are you still venting air out of the PRV when you open it, if so then you may have a open vented system with a small (Feed & expansion) tank in the attic, you should also see a bigger tank alongside it, check if this (small) tank has got say 6 ins of water in it and see if its hot.
    If you haven't got this open vented system you will have a pressurised system and you will see a red expansion vessel somewhere, there should be a pressure gauge near it, have a look for this after checking for the feed and expansion tank first.

    Forgot to say to slacken the vent plug right in the middle of the pump to release any air but do not overtighten it when closing.

    Also, if you look at photo 1 in post#19 you will see a automatic air vent in right bottom corner, just slacken the black cap on this and let any air out, you can leave it open except that it is dribbling water, if so, close it again.


  • Registered Users, Registered Users 2 Posts: 212 ✭✭ShaneC1600


    Do you need to reset anything to get it to work or is it out of action now completely?
    Does the high limit stat kick in or is the burner going out before reaching a high temperature? Pump is incorrectly installed facing up as stated earlier but if water is not circulating when the boiler is on the next action would be activation of the high limit stat.


  • Registered Users, Registered Users 2 Posts: 3,623 ✭✭✭John.G


    The control stat might be catching it before it reaches the hi limit level 0f ~ 110/113C.

    If there is a lot of air in the system then you will normally hear it as/in a fairly noisy pump, it should be relatively easy to see if the pump is running even if it can't be heard by removing the vent screw and looking at the end of the shaft. (assuming it is some what similar to a conventional pump end).
    These A rated pumps are sensitive to magnetite I think so hope its just not stopped but one would expect some error code
    Jimf also said there pumps can be troublesome.


  • Hosted Moderators Posts: 3,496 ✭✭✭DGOBS


    When I zoomed into pic, pump flow direction does seem to look correct.
    Maybe just the pic angle, but it the pump valve nearest heating return half closed? (I think its just the angle)

    Just saying:

    530556.jpg

    530557.jpg


  • Registered Users, Registered Users 2 Posts: 3,623 ✭✭✭John.G


    Not recommending it but should it fail so rapidly, I know of one Grundfos Selectric running away merrily in a upright position for at least the past 16 years


  • Moderators, Home & Garden Moderators Posts: 6,380 Mod ✭✭✭✭Wearb


    John.G wrote: »
    Not recommending it but should it fail so rapidly, I know of one Grundfos Selectric running away merrily in a upright position for at least the past 16 years
    Lots of them do run in that position. The problem arises if there is "air" in the system, it gets trapped in that part of the pump where it needs water to lubricate the shaft.

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 45 needtoknowasap


    John.G wrote: »
    I think that the lights do go out normally after making your selectiom, especially when they come on again briefly when you press the mode button again. I will dig out the eManual later, if you keep your hand on the pump you should feel a slight tremor if its running continuously. For the moment assume that it is. Any error codes I would think would be displayed where those lights are. But I am pretty sure that the pump is running continuously.

    Are you still venting air out of the PRV when you open it, if so then you may have a open vented system with a small (Feed & expansion) tank in the attic, you should also see a bigger tank alongside it, check if this (small) tank has got say 6 ins of water in it and see if its hot.
    If you haven't got this open vented system you will have a pressurised system and you will see a red expansion vessel somewhere, there should be a pressure gauge near it, have a look for this after checking for the feed and expansion tank first.

    Forgot to say to slacken the vent plug right in the middle of the pump to release any air but do not overtighten it when closing.

    Also, if you look at photo 1 in post#19 you will see a automatic air vent in right bottom corner, just slacken the black cap on this and let any air out, you can leave it open except that it is dribbling water, if so, close it again.


    The red expansion tank is in the hotpress but there is no pressure gauge anywhere. Have tried to loosen the black cap and the vent plug it fired up for about 2 mins then cut out same as usual. Its like as if its heating the water in the boiler but just failing to pump it into the house.


  • Registered Users, Registered Users 2 Posts: 3,623 ✭✭✭John.G


    The expansion tank (in a hot press) and system is normally pressurised to 1bar to1.25bar by opening a isolating valve (or two) somewhere and there will "have to" be a pressure gauge somewhere as well, sometimes on the boiler.
    There are two other alternatives, one is that the open vented system has been converted into a semi sealed system where the cold feed from the (small) tank has a non return valve and will replinish any water loss or loss due to venting automatically so no pressure gauge is needed, if no small tank then sometimes this cold feed is just taken off the cold water outlet from the main cold water storage tank, again with a non return valve and no pressure gauge fitted or required.

    You will have to do a bit of searching, follow the expansion vessel pipe back to where it joins into another one and you may come across something.

    Also, have you two (big&small) tanks in your attic or just one big one.

    If no water has been making up the loss due to venting etc then you will get no circulation through the system if the water level is very low.

    So you will have to sort this out before even firing the boiler again.

    These are the sort of items you are looking for.


  • Registered Users, Registered Users 2 Posts: 3,623 ✭✭✭John.G


    See the above attachments, may be of help.


  • Hosted Moderators Posts: 3,496 ✭✭✭DGOBS


    I think we can safely assume its a pump, water pressure (leak) or circulation issue.
    You should not be having to deal ith this yourself, thats what your installer is for, and I think at this point you need to get him back.

    While we are all willing to help you here, I don't think there is much more anyone can do for you remotely.