2 single ovens and an induction hob?

  • 15-07-2020 6:47pm
    #1
    Registered Users, Registered Users 2 Posts: 885 ✭✭✭


    Will the existing wiring ( Cooker switch to 32amp fuse in fuse box) be enough or we talking major rewiring, both ovens are 3.5KW each and the hob is 7.4KW total connected load?


Comments

  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    That is too much for one circuit. The hob alone is about right for a 32A MCB.


  • Registered Users, Registered Users 2 Posts: 885 ✭✭✭acalmenvoy


    2011 wrote: »
    That is too much for one circuit. The hob alone is about right for a 32A MCB.
    Thanks for the reply, would the diversity factor be applicable here?


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    acalmenvoy wrote: »
    Thanks for the reply, would the diversity factor be applicable here?

    It would but you are still looking for too much.


  • Registered Users, Registered Users 2 Posts: 2,567 ✭✭✭Risteard81


    It's actually likely fine. 15kW of appliances can go on a 32A circuit owing to diversity. I have an oven and 7kW induction hob on a 32A circuit with 6mm^2 cable here. It is fully functional, safe and compliant. I probably wouldn't add a second oven though personally.


  • Registered Users, Registered Users 2 Posts: 923 ✭✭✭3d4life


    Expect cooking complexites on Christmas day if everything off one breaker. :)


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 2,567 ✭✭✭Risteard81


    3d4life wrote: »
    Expect cooking complexites on Christmas day if everything off one breaker. :)

    That's an imagined problem which simply doesn't happen in the real world. Diversity works.


  • Registered Users, Registered Users 2 Posts: 1,711 ✭✭✭Lenar3556


    Risteard81 wrote: »
    That's an imagined problem which simply doesn't happen in the real world. Diversity works.

    It does when you are dealing with a diverse enough loading profile. But a bit of a stretch in this case. He is talking about over 60 amps of cooking there. Is it a house? If there is need for two ovens it follows that they are both expected to be on at the same time. And it’s not unreasonable to expect to have some hob going along side them.


  • Closed Accounts Posts: 491 ✭✭YellowBucket


    With cooking appliances you'll definitely get scenarios where most of the load could be drawn simultaneously, even if it's only christmas day or some dinner party, you'll find someone won't be too happy if their MCB trips in the middle of some complicated dish.

    We have ours on 2 x 32A circuits.


  • Registered Users, Registered Users 2 Posts: 27,370 ✭✭✭✭GreeBo


    Once its an induction hob I would always give it its own circuit.
    When you can join zones for larger pots etc its just not worth it.

    Maybe my house is different but it would be rare that the oven and hob wouldnt be on at the same time.


  • Registered Users, Registered Users 2 Posts: 2,063 ✭✭✭Cerco


    GreeBo wrote: »
    Once its an induction hob I would always give it its own circuit.
    When you can join zones for larger pots etc its just not worth it.

    Maybe my house is different but it would be rare that the oven and hob wouldnt be on at the same time.

    Maybe, but I can imagine a regular scenario of the vegetables on the hob with the roast in the oven. Probably two rings in use. But then many roast their veg so it depends. Personally I would go for the two circuit option. It’s a once off cost for lasting peace of mind.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 2,567 ✭✭✭Risteard81


    With cooking appliances you'll definitely get scenarios where most of the load could be drawn simultaneously, even if it's only christmas day or some dinner party, you'll find someone won't be too happy if their MCB trips in the middle of some complicated dish.

    We have ours on 2 x 32A circuits.

    It won't be drawn simultaneously as the thermostats will cycle the elements on and off


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    Risteard81 wrote: »
    It's actually likely fine. 15kW of appliances can go on a 32A circuit owing to diversity. I have an oven and 7kW induction hob on a 32A circuit with 6mm^2 cable here. It is fully functional, safe and compliant. I probably wouldn't add a second oven though personally.

    Just because you have not had an issue with your setup does not mean it is acceptable.
    As already stated I accept that diversity can be applied to some extent but this is a bridge too far. Let’s look at the maths as it is quiet simple:

    2 ovens switched on from cold = 6 kW is 26 amps at unruly power factor before a stat even kicks in. If I switch on just one ring of the job (assuming 4 rings of equal rating) that is another 8 amps at unity power factor. This is a total of 34 amps which exceeds the rating of the MCB which is against the regulations.

    How likely is it that someone would switch on 2 ovens and one ring from cold? Very likely in my opinion. Would you get away with it? Most likely yes but it is against best practice and I would strongly advise against it. It is best to comply fully with the National Wiring Rules.

    Naturally if the power factor is not perfect (it generally isn’t) or more rings are switched on with the 2 ovens the current could be far higher.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    Risteard81 wrote: »
    It won't be drawn simultaneously as the thermostats will cycle the elements on and off

    This does not apply when started cold. Stats only switch off when the set point is achieved.


  • Registered Users, Registered Users 2 Posts: 2,567 ✭✭✭Risteard81


    2011 wrote: »
    Just because you have not had an issue with your setup does not mean it is acceptable.
    As already stated I accept that diversity can be applied to some extent but this is a bridge too far. Let’s look at the maths as it is quiet simple:

    2 ovens switched on from cold = 6 kW is 26 amps at unruly power factor before a stat even kicks in. If I switch on just one ring of the job (assuming 4 rings of equal rating) that is another 8 amps at unity power factor. This is a total of 34 amps which exceeds the rating of the MCB which is against the regulations.

    How likely is it that someone would switch on 2 ovens and one ring from cold? Very likely in my opinion. Would you get away with it? Most likely yes but it is against best practice and I would strongly advise against it. It is best to comply fully with the National Wiring Rules.

    Not only is diversity acceptable - it is essential for economic design. It is fully compliant with the Wiring Rules. Why would you think otherwise?


  • Registered Users, Registered Users 2 Posts: 2,567 ✭✭✭Risteard81


    2011 wrote: »
    This does not apply when started cold. Stats only switch off when the set point is achieved.

    For a few minutes only. Time is an important factor when designing.

    It is fine and completely compliant to have an oven and induction hob sharing a 32A cooker circuit. That is an irrefutable fact. 15kW of cooking load is the maximum for a 32A cooker circuit owing to diversity. Fact.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    Risteard81 wrote: »
    Not only is diversity acceptable

    Agreed and already stated. However it can only be applied to a point. I have shown why I think the rating of the MCB would be exceeded under quite unremarkable circumstances. How about you show how it won’t be?
    It is fully compliant with the Wiring Rules. Why would you think otherwise?

    Simple, the design current under very normal conditions exceeds the rating of the protective device.

    I only applied 25% loading for the hob which is very generous in terms of diversity and it was still an issue.


  • Registered Users, Registered Users 2 Posts: 2,567 ✭✭✭Risteard81


    2011 wrote: »
    Agreed and already stated. However it can only be applied to a point. I have shown why I think the rating of the MCB would be exceeded under quite unremarkable circumstances. How about you show how it won’t be?



    Simple, the design current under very normal conditions exceeds the rating of the protective device.

    I only applied 25% loading for the hob which is very generous in terms of diversity and it was still an issue.

    The design current doesn't exceed the rating of the protective device. It is the total connected load which does. Incidentally these are often quoted for elements which cannot even be simultaneously energised. I'm at work so will prove you wrong with quotes from published books on the matter later.


  • Registered Users, Registered Users 2 Posts: 27,370 ✭✭✭✭GreeBo


    Risteard81 wrote: »
    The design current doesn't exceed the rating of the protective device. It is the total connected load which does. Incidentally these are often quoted for elements which cannot even be simultaneously energised. I'm at work so will prove you wrong with quotes from published books on the matter later.

    Modern Induction hobs can have multiple if not all zones on at once.
    I have seen hobs rated at over 7kw.


  • Registered Users, Registered Users 2 Posts: 923 ✭✭✭3d4life


    With cooking appliances you'll definitely get scenarios where most of the load could be drawn simultaneously, even if it's only christmas day or some dinner party, you'll find someone won't be too happy if their MCB trips in the middle of some complicated dish...

    Exactly.

    A single circuit design is not doing any favours to anyone. So why do it ?

    ( of course its fine if your work phone is turned off on Christmas day :) )


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    acalmenvoy wrote: »
    Will the existing wiring ( Cooker switch to 32amp fuse in fuse box) be enough or we talking major rewiring, both ovens are 3.5KW each and the hob is 7.4KW total connected load?

    3.5 + 3.5 + 7.4 = 14.4 kW

    Risteard81 wrote: »
    Not only is diversity acceptable - it is essential for economic design. It is fully compliant with the Wiring Rules. Why would you think otherwise?


    I agree 100% which is why I stated this before you posted on this thread.
    So let's apply a very generous 0.6 diversity factor.

    14.4 x 0.6 = 8.64 kW = 8640 W

    Therefore at unity power factor (best case scenario) 8640/230 = 37.6 amps. If we are to take this as the design current it can be seen that it exceeds the rating of the MCB (32A) as such it fails to comply with the National Wiring Rules.

    If you plan on demonstrating that both ovens ad hob can be fed from a single 32A MCB you will have to apply a much lower diversity factor which in my opinion is inadvisable. However anyone doing this would need to be able to justify it with numbers rather than simply stating it is ok as a "fact".


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 2,567 ✭✭✭Risteard81


    From the "Electrical Installation Design Guide (3rd Edition) - Calculations for Electricians and Designers", published by the Institution of Engineering and Technology:

    "Example 2: cooker circuit
    See row 5 of Table 3.1

    Consider an electric cooker with:

    * hob comprising 4 off 3kW elements
    * main oven 2kW
    * grill/top oven 2kW

    Therefore the total installed capacity = 16kW at 240V.

    As in example 1, I=(1000P/Uo cos Theta) and cos Theta = 1 for a resistive load

    Hence, I = ((1000 * 16) / (240 * 1)) = 67A

    From Table 3.1, row 5 circuit load is:

    'The first 10A of the rated current plus 30% of the remainder of the rated current plus 5A if a socket-outlet is incorporated in the control unit.'

    Therefore I = 10 + (30 (67-10)) /100 = 27.1A

    Hence, a 30 or 32A circuit is selected."


    The reality is that this works and has for decades - even on Christmas Day, and even with an induction hob.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    Risteard81 wrote: »
    From the "Electrical Installation Design Guide (3rd Edition) - Calculations for Electricians and Designers", published by the Institution of Engineering and Technology:

    "Example 2: cooker circuit
    See row 5 of Table 3.1

    Consider an electric cooker with:

    * hob comprising 4 off 3kW elements
    * main oven 2kW
    * grill/top oven 2kW

    See the part in bold? That diversity is applied to a single unit.
    The OP has 3 units. So it would be 10 amps per unit + 30% of the remainder.

    Besides, the above diversity equation was in an earlier version of ET101 and the ETCI decided to remove it well over 10 years ago (with good reason). As you know we do some things differently in the ROI than they do in UK.
    Now that we have powerful induction hobs applying these levels of diversity would not be a good idea.

    As the OP has decided to have 2 ovens we have to assume that they will be used simultaneously from cold unless we have a very good reason to think otherwise.
    When switched on together from cold it is a 6 kW load straight away (over 26 amps). Your assertion that the rating of the MCB will only be exceeded for “a few minutes only” (which you seem to have abandoned) is incorrect as ovens can take 25 minutes to preheat.

    Fact: Your proposal is to apply a calculation intended for one unit to three units, that is from another jurisdiction, which was very deliberately removed from our own national rules a very long time ago to support your position.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    Risteard81 wrote: »
    this works and has for decades.

    So had twin and earth with smaller cpc, no earthing on light fittings, 3 or 4 fuses for a house, no rcds on sockets, and the list goes on.


  • Registered Users, Registered Users 2 Posts: 885 ✭✭✭acalmenvoy


    I should give more information, fascinating discussion by the way. This is really a vanity project. The wife wants her dream kitchen. It will probably be our last. All but 1 of the kids have moved away.
    The top oven is a glorified microwave. I can see the oven part never being used. Grill and microwave will be used occasionally.
    Bottom oven will be used as conventional oven, grill part will never be used.
    I could never see more than 3 zones on the hob being used.
    Yes, Christmas day would be interesting.
    That being said, from the advice on this thread, I have a guy calling next week to price a new 32a circuit.
    Peace of mind is priceless.


  • Registered Users, Registered Users 2 Posts: 2,567 ✭✭✭Risteard81


    You are very wrong @2011 - the IET have explicitly stated that a separate oven and hob can be treated the same as a single cooker. Just admit you made a mistake.

    Millions of installations have this setup without adverse effect - even on Christmas Day. You're not infallible.


  • Closed Accounts Posts: 491 ✭✭YellowBucket


    Decades ago most cookers were also single appliances and had their loads fairly tightly calculated to be within the range of a single classic “cooker circuit”.

    Very large cookers like the wider “stove” type devices often sat on a 45amp circuit

    They were designed as single units though and the manufacturers managed the overall max load.

    Some even had interlocks to prevent certain very high draw combinations being selected. Actually, most hobs will prevent you exceeding the maximum ratings as they will turn down the output on other zones if you apply boost etc

    These days cooking appliances are much more diverse and the vast majority of kitchens, certainly since the 1990s use separate ovens and hobs.

    Ovens now often have self clean options and quite high consumption rapid heat modes and induction hobs have very high consumption boost modes.

    Over all these appliances are more efficient - ovens are much better thermally insulated for example and induction hobs manage to get more heat into the pots and less into the air / wasted through thermal radiation, but they are all far more likely to have big initial power needs during rapid heating cycles.

    There also needs to be consideration given for the fact that kitchens may see new appliances go in with some of those functions in the future.

    To me running one circuit to a kitchen for those is just asking for inconvenience for the sake of saving a relatively minor bit of work. The wiring will in all likelihood follow the same route back to the distribution board and it’s also practical to be able to isolate the ovens and hob separately.

    I know we had a situation where someone applied that diversity concept to our old utility room, which contained a dryer, washing machine and dishwasher.

    We replaced a washing machine with a Miele which must have had a bigger element and it resulted in the breaker tripping if the washing machine and dishwasher both hit heating cycles at the same time.

    Overall both newer appliances were much more efficient than their predecessors - less water and power used but they both were capable of pulling a lot more energy for brief periods as they ran through their programmes.

    The other aspect is these are all continental designs and they will be assumed to be installed on separate radials to the manufacturer spec. Ireland and the U.K. are both outliers on this by not doing so.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    acalmenvoy wrote: »
    I should give more information, fascinating discussion by the way. This is really a vanity project. The wife wants her dream kitchen. It will probably be our last. All but 1 of the kids have moved away.
    The top oven is a glorified microwave. I can see the oven part never being used. Grill and microwave will be used occasionally.
    Bottom oven will be used as conventional oven, grill part will never be used.
    I could never see more than 3 zones on the hob being used.
    Yes, Christmas day would be interesting.
    That being said, from the advice on this thread, I have a guy calling next week to price a new 32a circuit.
    Peace of mind is priceless.

    The part in bold is the part of your post you should focus on.
    Risteard81 wrote: »
    the IET have explicitly stated that a separate oven and hob can be treated the same as a single cooker.

    You have ignored the following facts:
    - The IET are a foreign organisation. In Italy they install sockets in bathrooms, should we also be guided by their regulations?
    - The ETCI saw fit to remove this calculation from our rules a very long time ago. Should we ignore this? Was that a mistake?
    - Ovens can take 25 minutes to preheat
    Millions of installations have this setup without adverse effect - even on Christmas Day.

    Already addressed here.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    Just to add I think the IET are a great bunch of lads, they presented me with a cash prize and certificate as a design award many years ago :)


  • Registered Users, Registered Users 2 Posts: 923 ✭✭✭3d4life


    2011 wrote: »
    .....The IET are a foreign organisation. In Italy they install sockets in bathrooms....

    :)

    Good for them ... the natural home of the lavatrice is in the bathroom ( in apartments anyway )

    :D

    ( Probably star wired dedicated protection anyway)


  • Advertisement
  • Banned (with Prison Access) Posts: 73 ✭✭Terminator.


    With 2 ovens and a hob

    I'd be inclined to treat the 2nd oven as a separate appliance needing a separate connection


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    With 2 ovens and a hob

    I'd be inclined to treat the 2nd oven as a separate appliance needing a separate connection

    Agreed, or you could have one circuit for the ovens and one for the hob.

    I think a pattern is emerging:)


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    Risteard81 wrote: »
    You are very wrong @2011 - the IET have explicitly stated that a separate oven and hob can be treated the same as a single cooker. Just admit you made a mistake.
    What do they say about 2 ovens and a hob?


  • Closed Accounts Posts: 491 ✭✭YellowBucket


    You also have to look past the lowest common denominator in a design. Barely complying with the technical minimum requirements is often less than ideal and may be impractical.

    From a cost:benefit point of view, having two circuits supplying these devices makes a whole lot of sense.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    You also have to look past the lowest common denominator in a design. Barely complying with the technical minimum requirements is often less than ideal and may be impractical.

    From a cost:benefit point of view, having two circuits supplying these devices makes a whole lot of sense.

    Agree 100%

    But you always get someone using the its worked fine up until now / my grandfather never needed earths / sure I replaced the fuse with a nail and its grand type arguments.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    Risteard81 wrote: »
    'The first 10A of the rated current plus 30% of the remainder of the rated current plus 5A if a socket-outlet is incorporated in the control unit.'

    Therefore I = 10 + (30 (67-10)) /100 = 27.1A

    Hence, a 30 or 32A circuit is selected."[/I]

    The reality is that this works and has for decades - even on Christmas Day, and even with an induction hob.

    Great. So now the same premises adds in another oven. Obviously we can just ignore this load from the above calculation then, and connect to the same mcb, is that it? Or can they now add in as many ovens as they like, and claim its all one cooking appliance?


  • Advertisement
  • Banned (with Prison Access) Posts: 73 ✭✭Terminator.


    Bruthal wrote: »
    Great. So now the same premises adds in another oven. Obviously we can just ignore this load from the above calculation then, and connect to the same mcb, is that it? Or can they now add in as many ovens as they like, and claim its all one cooking appliance?

    They might get away with it ,but the diversity calculation was for a single appliance and a single householder imo


  • Registered Users, Registered Users 2 Posts: 12,881 ✭✭✭✭Calahonda52


    It really saddened me to read through this thread and see what amounts to a pi$$ing match between two masters of their trade.

    I know from previous threads that you are both highly skilled in this technical field.

    Get out of the octagon, acknowledge your own contribution and greatness and just add value.

    The simple answer would have been, prolly best to do another circuit for peace of mind.

    Now: I have 3 ovens, 2 showers, a heat pump ad a Tesla home charger: :D

    Keep safe and well.

    “I can’t pay my staff or mortgage with instagram likes”.



  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    Incase you haven't noticed there have been many other contributors to this thread and nobody seems to be upset.

    It good to challenge and be challenged, that is how you learn. Bruthal, Stoner and Risteard have all disagreed with me many times, I don't take offence and yes, sometimes I am wrong (and have stated this more than once).

    I don't take issue with anything Risteard has posted on this thread. In fact I like that he posted a calculation from a reputable source, I just disagree with it for the reasons stated. I sure Risteard does excellent installation work and I think he has made some valuable contributions to discussions. So in summary there is no octagon for me.
    I have 3 ovens, 2 showers, a heat pump ad a Tesla home charger: :D

    According to my source in Gibirrovia you can feed them all from one circuit and call it diversity :D


  • Registered Users, Registered Users 2 Posts: 1,054 ✭✭✭Tuco88


    So a gas cooker it is then????


  • Banned (with Prison Access) Posts: 73 ✭✭Terminator.


    Diversity isn't an exact science and it's easy enough to get caught out

    I've seen it happen where a kitchen gets a change of use and becomes effectively a commercial kitchen, cooker circuit and installation load increase

    https://www.tlc-direct.co.uk/Book/6.2.3.htm

    More diversity allowed for a household


  • Advertisement
  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    Diversity isn't an exact science and it's easy enough to get caught out

    Very true, however diversity has to reflect the largest loading that is likely to occur.
    I've seen it happen where a kitchen gets a change of use and becomes effectively a commercial kitchen, cooker circuit and installation load increase

    I have seen it cause a heat tracing panel to go on fire on a site. Anther poster from this site was present with me at the time. A diversity factor was applied that did not take into account that all of the heat tracing would have to start from cold following a plant shutdown. For this reason we have to recalculate based on a diversity factor of 1. Typically heat tracing circuits in this plant took 4 hours to heat up before any stats switched any circuits off. It was a good lesson for me.
    https://www.tlc-direct.co.uk/Book/6.2.3.htm

    More diversity allowed for a household

    Values look realistic.


  • Banned (with Prison Access) Posts: 73 ✭✭Terminator.


    Reminds me of another one:

    Back in the day ESB designed all electric homes and allowed for 8KW of NSH plus the GD load of panel heaters and appliances on a 63amp main fuse


    Problem was a lot of these places were holiday homes, people arrived and switched the lot on together.
    They had to change the design afterwards.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    They had to change the design afterwards.

    Yes, I remember seeing a double pole 63A fuse used to deal with this.


  • Banned (with Prison Access) Posts: 73 ✭✭Terminator.


    2011 wrote: »
    Yes, I remember seeing a double pole 63A fuse used to deal with this.

    That's right, it would be considered a bodge now.

    They put the GD and the NSH on the 2 poles and the tails were protected by the ESB fuse

    It came up on a slide at a verfication and testing course i was at .It was highlighted as a dangerous installation but that was actually the design at the time.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    It was highlighted as a dangerous installation but that was actually the design at the time.

    Was it really dangerous though? Certainly in some cases but not always. It would depend on a number of factors such as the rating and characteristics of the ESB fuse and the size and length of the tails.


  • Banned (with Prison Access) Posts: 73 ✭✭Terminator.


    2011 wrote: »
    Was it really dangerous though? Certainly in some cases but not always. It would depend on a number of factors such as the rating and characteristics of the ESB fuse and the size and length of the tails.

    Most likely not imo


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    It really saddened me to read through this thread and see what amounts to a pi$$ing match between two masters of their trade..
    I think risteard was right for a hob and oven, although I prefer a more analytical view myself rather than quoting exact non flexible figures in books etc. But the addition of the second independent oven changes the setup to a minimum of 2 separate appliances, so the diversity for a hob and oven as a single cooker appliance can't realistically be applied, because now it's a hob and oven, plus another oven.

    Nothing wrong with posters posting differing views on such matters anyway imo.