2011 wrote: » That is too much for one circuit. The hob alone is about right for a 32A MCB.
acalmenvoy wrote: » Thanks for the reply, would the diversity factor be applicable here?
3d4life wrote: » Expect cooking complexites on Christmas day if everything off one breaker.
Risteard81 wrote: » That's an imagined problem which simply doesn't happen in the real world. Diversity works.
GreeBo wrote: » Once its an induction hob I would always give it its own circuit. When you can join zones for larger pots etc its just not worth it. Maybe my house is different but it would be rare that the oven and hob wouldnt be on at the same time.
YellowBucket wrote: » With cooking appliances you'll definitely get scenarios where most of the load could be drawn simultaneously, even if it's only christmas day or some dinner party, you'll find someone won't be too happy if their MCB trips in the middle of some complicated dish. We have ours on 2 x 32A circuits.
Risteard81 wrote: » It's actually likely fine. 15kW of appliances can go on a 32A circuit owing to diversity. I have an oven and 7kW induction hob on a 32A circuit with 6mm^2 cable here. It is fully functional, safe and compliant. I probably wouldn't add a second oven though personally.
Risteard81 wrote: » It won't be drawn simultaneously as the thermostats will cycle the elements on and off
2011 wrote: » Just because you have not had an issue with your setup does not mean it is acceptable. As already stated I accept that diversity can be applied to some extent but this is a bridge too far. Let’s look at the maths as it is quiet simple: 2 ovens switched on from cold = 6 kW is 26 amps at unruly power factor before a stat even kicks in. If I switch on just one ring of the job (assuming 4 rings of equal rating) that is another 8 amps at unity power factor. This is a total of 34 amps which exceeds the rating of the MCB which is against the regulations. How likely is it that someone would switch on 2 ovens and one ring from cold? Very likely in my opinion. Would you get away with it? Most likely yes but it is against best practice and I would strongly advise against it. It is best to comply fully with the National Wiring Rules.
2011 wrote: » This does not apply when started cold. Stats only switch off when the set point is achieved.
Risteard81 wrote: » Not only is diversity acceptable
It is fully compliant with the Wiring Rules. Why would you think otherwise?
2011 wrote: » Agreed and already stated. However it can only be applied to a point. I have shown why I think the rating of the MCB would be exceeded under quite unremarkable circumstances. How about you show how it won’t be? Simple, the design current under very normal conditions exceeds the rating of the protective device. I only applied 25% loading for the hob which is very generous in terms of diversity and it was still an issue.
Risteard81 wrote: » The design current doesn't exceed the rating of the protective device. It is the total connected load which does. Incidentally these are often quoted for elements which cannot even be simultaneously energised. I'm at work so will prove you wrong with quotes from published books on the matter later.
YellowBucket wrote: » With cooking appliances you'll definitely get scenarios where most of the load could be drawn simultaneously, even if it's only christmas day or some dinner party, you'll find someone won't be too happy if their MCB trips in the middle of some complicated dish...
acalmenvoy wrote: » Will the existing wiring ( Cooker switch to 32amp fuse in fuse box) be enough or we talking major rewiring, both ovens are 3.5KW each and the hob is 7.4KW total connected load?
Risteard81 wrote: » Not only is diversity acceptable - it is essential for economic design. It is fully compliant with the Wiring Rules. Why would you think otherwise?
Risteard81 wrote: » From the "Electrical Installation Design Guide (3rd Edition) - Calculations for Electricians and Designers", published by the Institution of Engineering and Technology:"Example 2: cooker circuit See row 5 of Table 3.1Consider an electric cooker with: * hob comprising 4 off 3kW elements * main oven 2kW * grill/top oven 2kW
Risteard81 wrote: » this works and has for decades.
acalmenvoy wrote: » I should give more information, fascinating discussion by the way. This is really a vanity project. The wife wants her dream kitchen. It will probably be our last. All but 1 of the kids have moved away. The top oven is a glorified microwave. I can see the oven part never being used. Grill and microwave will be used occasionally. Bottom oven will be used as conventional oven, grill part will never be used. I could never see more than 3 zones on the hob being used.Yes, Christmas day would be interesting. That being said, from the advice on this thread, I have a guy calling next week to price a new 32a circuit. Peace of mind is priceless.
Risteard81 wrote: » the IET have explicitly stated that a separate oven and hob can be treated the same as a single cooker.
Millions of installations have this setup without adverse effect - even on Christmas Day.
2011 wrote: » .....The IET are a foreign organisation. In Italy they install sockets in bathrooms....