Kerosene Flue readings

  • 15-12-2019 9:48pm
    #1
    Registered Users, Registered Users 2 Posts: 215 ✭✭


    Hi

    I was just wondering if I could get your opinion on the attached please. They are 2no readings that were on my flue of the oil boiler I have. It's a riello 3.2 kerosene burner.

    He said it was better to reduce the excess air but I see the efficiency of the boiler reduced.

    Can ye help me understand the readings. Should the CO2 and excess air be lower.

    Thanks in advance


Comments

  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    depends on a lot of things really

    was the boiler up to operating temp when these readings wer taken

    what boiler are we talking about some boilers you can leave at 12 co2 others you cant

    excess air will be what it is as a general rule 35% excess air will give a co2 of 11.5%

    looking at the time difference in those printouts I would guess your second one wasn't far off operating temp


  • Registered Users, Registered Users 2 Posts: 215 ✭✭happylad


    Thanks for getting back to me. Yes the boiler was up to temp. It's a warmflow 150he. It says in book it prob should be 11.5% Co2.

    It doesn't say anything about excess air. Is this important also or should getting the CO2 lower be more important


  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    maybe just me but I wouldn't leave a boiler like a warmflow at 12%co2 at this time of year

    usually 11.5% co2 for me as it allows a bit for difference in air quality


  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    happylad wrote: »
    Thanks for getting
    g back to me. Yes the boiler was up to temp. It's a warmflow 150he. It says in book it prob should be 11.5% Co2.

    It doesn't say anything about excess air. Is this important also or should getting the CO2 lower be more important

    more air will drop the co2

    the boiler eff will vary through out the heating season so don't be reading in to that too much either


  • Registered Users, Registered Users 2 Posts: 215 ✭✭happylad


    Thanks for getting back to me. I will leave it at that. He reduced the oil pressure to 8bar and opened to head to setting no 5. He reckoned it should help with efficiency


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    burners are variable so a lot of different results can be achieved

    once your service eng is happy that's the main thing


  • Registered Users, Registered Users 2 Posts: 215 ✭✭happylad


    Thanks for the assist.

    One final question just trying to understand the report is the Co2 the most important thing that the service engineer is looking at. Does the Co2 reading take preference over the excess air.


  • Registered Users, Registered Users 2 Posts: 3,623 ✭✭✭John.G


    Jimf.
    Is that efficiency the net or gross value?? because the analyser I presume cannot calculate the condensing effect if any as condensing doesn't commence until the boiler return temp is ~ 50/55C and full condensing would only be achieved with a boiler return temp of < 20C which will never happen.
    What is the lowest flue gas temperature you yourself has observed in a condensing oil boiler.?
    What would you expect the flue gas temperature to be or is this not displayed in the report?.


  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    happylad wrote: »
    Thanks for the assist.

    One final question just trying to understand the report is the Co2 the most important thing that the service engineer is looking at. Does the Co2 reading take preference over the excess air.

    the excess air is not really important its only part of the whole combustion set up

    as a service guy myself I look for a co2 that im happy to leave a boiler at

    other things also come into like co emissions again the lower here the better most manf are happy once its under 100ppm but for me I really like to see this lower anywhere around 100ppm and im looking for a reason


  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    John.G wrote: »
    Jimf.
    Is that efficiency the net or gross value?? because the analyser I presume cannot calculate the condensing effect if any as condensing doesn't commence until the boiler return temp is ~ 50/55C and full condensing would only be achieved with a boiler return temp of < 20C which will never happen.
    What is the lowest flue gas temperature you yourself has observed in a condensing oil boiler.?
    What would you expect the flue gas temperature to be or is this not displayed in

    the report?.


    this would be nett value john

    the average fga temp on modern he boilers is approx. 75c john this can vary from boiler to boiler at full working temp


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 215 ✭✭happylad


    Jimf

    Thanks for the info. I just wanted to get an understanding myself of the report. I prob should have asked him when he was here.

    I'm not goin to query it but in your opinion does reducing the pump pressure from 10bar to 8bar make a burner more efficient.


  • Registered Users, Registered Users 2 Posts: 3,623 ✭✭✭John.G


    jimf wrote: »
    this would be nett value john

    the average fga temp on modern he boilers is approx. 75c john this can vary from boiler to boiler at full working temp

    Does it also just measure the net value on SE boilers?.
    I know you are still gaining ~~ 7% over a SE boiler, I think the last report on my Firebird SE was ~ 230 C flue gas temp, does that sound right.?

    From my industrial oil/gas fired steam boiler days I think +or- 100C resulted in +or- 4.5% efficiency with 15% excess air or somewhere around this.


  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    John.G wrote: »
    Does it also just measure the net value on SE boilers?.
    I know you are still gaining ~~ 7% over a SE boiler, I think the last report on my Firebird SE was ~ 230 C flue gas temp, does that sound right.?

    From my industrial oil fired steam boiler days I think +or- 100C resulted in +or- 4.5% efficiency with 15% excess air or somewhere around this.


    it measures gross value on se boilers john the fga can be switched from he to se mode

    230 c would be spot on for your boiler

    your boiler will be running at somewhere around 84% gross eff


  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    happylad wrote: »
    Jimf

    Thanks for the info. I just wanted to get an understanding myself of the report. I prob should have asked him when he was here.

    I'm not goin to query it but in your opinion does reducing the pump pressure from 10bar to 8bar make a burner more efficient.

    not that you would notice

    maybe he thinks the boiler was oversized for your house


  • Registered Users, Registered Users 2 Posts: 3,623 ✭✭✭John.G


    jimf wrote: »
    it measures gross value on se boilers john the fga can be switched from he to se mode

    230 c would be spot on for your boiler

    your boiler will be running at somewhere around 84% gross eff

    If one accepts the figures in my attachment then I think most condensing boilers rarely do so, and even though the net figure is correct it does give a "bowl of odds" to the lower gross efficiency of SE boilers, a bit academic now I suppose since all new boilers are condensing.


  • Registered Users, Registered Users 2 Posts: 215 ✭✭happylad


    Jimf

    Yes that would make sence. The house is just under 3000sq ft and has UFH.

    He did say it was perhaps too big a boiler for the house.

    I got him back initially as the boiler was misfiring (making an effort to fire the burner but the burner never lite). I assume it was still wasting fuel while doing this.

    Now after he going (Prob around 3weeks since he was here) the boiler mis fires once or even twice before igniting. Doesn't happen all the time just sometimes. Would wind affect it. Flue is sticking out north wall


  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    John.G wrote: »
    If one accepts the figures in my attachment then I think most condensing boilers rarely do so, and even though the net figure is correct it does give a "bowl of odds" to the lower gross efficiency of SE boilers, a bit academic now I suppose since all new boilers are condensing.

    the fga printout from any given boiler john is only the performance of the boiler at that given time

    the seasonal eff is whats really important


  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    happylad wrote: »
    Jimf

    Yes that would make sence. The house is just under 3000sq ft and has UFH.

    He did say it was perhaps too big a boiler for the house.

    I got him back initially as the boiler was misfiring (making an effort to fire the burner but the burner never lite). I assume it was still wasting fuel while doing this.

    Now after he going (Prob around 3weeks since he was here) the boiler mis fires once or even twice before igniting. Doesn't happen all the time just sometimes. Would wind affect it. Flue is sticking out north wall

    hard to guess as to the cause but been overaired would be a cause but from your printout your boiler is not overaired

    there is a slight possibility that the photocell may be acting up and failing to see the flame but I would imagine that this would be more an everyday issue at this stage

    the firing head position too could be an issue I think these come factory set from warmflow at 5


  • Registered Users, Registered Users 2 Posts: 215 ✭✭happylad


    Thanks for getting back to me. I must ask him about that just to see what he says. Hes coming back this week to service my neighbours and hes calling to me anyway. Would it possibly cut down on kerosene usage to close the head down a bit more or is the head purely for combustion air to fuel ratio..Does it mean the bigger the opening on the head the more fuel it uses


  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    happylad wrote: »
    Thanks for getting back to me. I must ask him about that just to see what he says. Hes coming back this week to service my neighbours and hes calling to me anyway. Would it possibly cut down on kerosene usage to close the head down a bit more or is the head purely for combustion air to fuel ratio..Does it mean the bigger the opening on the head the more fuel it uses


    the head is all to do with firing


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 215 ✭✭happylad


    Just a query for ye. My burner doesn't seem to be performing in the sence that it appears to be using a lot of kerosene. It has used nearly 900ltrs in a little over 2months.

    The boiler was service around 4months ago but it still appears to be misfiring periodically. It will go to ignite but takes 2/3 attempts to actually fire. I had the technician back 2 or 3 times since but after 3/4 weeks it reverts back to continuously misfiring (not holding flame) but still keeps drawing keroscene. The last time he was back he adjusted combustion head to 5 and changed nozzle again to 1.00 80.S. I was tidying up the garage and found a nozzle on the floor 1.00 60s.

    If I look at the burner manual it tells me the angle should be 60deg danfos type s. If I look at boiler manual it says it should be danfos 80deg h. I have attached photos.

    Can anyone assist as to what might be the best course as I am at a loss as to what to do. To be fair to the technician he has said he is stumped as he says he has checked everything and can't figure it. I think the nozzle could be the issue.


  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    happylad wrote: »
    Just a query for ye. My burner doesn't seem to be performing in the sence that it appears to be using a lot of kerosene. It has used nearly 900ltrs in a little over 2months.

    The boiler was service around 4months ago but it still appears to be misfiring periodically. It will go to ignite but takes 2/3 attempts to actually fire. I had the technician back 2 or 3 times since but after 3/4 weeks it reverts back to continuously misfiring (not holding flame) but still keeps drawing keroscene. The last time he was back he adjusted combustion head to 5 and changed nozzle again to 1.00 80.S. I was tidying up the garage and found a nozzle on the floor 1.00 60s.

    If I look at the burner manual it tells me the angle should be 60deg danfos type s. If I look at boiler manual it says it should be danfos 80deg h. I have attached photos.

    Can anyone assist as to what might be the best course as I am at a loss as to what to do. To be fair to the technician he has said he is stumped as he says he has checked everything and can't figure it. I think the nozzle could be the issue.
    Could you post the combustion test results here to see if we can see anything wrong with them?

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 215 ✭✭happylad


    Thanks for the reply.

    Please see below. They appear ok but can't seem to explain why the boiler is misfiring. I think myself if the nozzle.


  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    happylad wrote: »
    Thanks for the reply.

    Please see below. They appear ok but can't seem to explain why the boiler is misfiring. I think myself if the nozzle.
    When was that test done?
    What nozzle then?
    Pump pressure then?


    What model and type Warmflow?

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 215 ✭✭happylad


    Test was done only last week. I borrowed the unit of the technician. The nozzle was the 1.00x80deg s on it. Pressure on pump is 8bar. The burner was firing 2/3times at that stage before it would ignite


  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    happylad wrote: »
    Test was done only last week. I borrowed the unit of the technician. The nozzle was the 1.00x80deg s on it. Pressure on pump is 8bar. The burner was firing 2/3times at that stage before it would ignite


    I am not familiar with this boiler, but I think that 5 on the head setting might be a mis-print and perhaps should be .5. Give warmflow a call or email on that. I have usually had a quick response from them.



    I would always give precedence to the boiler manufacturers instructions over the burner makers and I would expect no trouble with that nozzle (other than any nozzle can be faulty) Perhaps try a new nozzle. I would also try lowering the co2 about .4%



    Do a smoke test on it also.



    Is the cell always clean?

    Is the pump pressure stable and gauze and filter clean?

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 215 ✭✭happylad


    Thanks for coming back to me. I emailed them last week and yes they were helpful and very quick to come back. See response.

    I might ask my man could I borrow the gas analyser and adjust the head to see can I bring it down. Would you think it would do no harm to try 0.5 and work away up if needs be until the correct reading is achieved. Ideally what readings should you see for co and excess air.

    I'll get the technician back either way in the new year when he has a bit more time


  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    is it only doing this when boiler is starting from cold


  • Registered Users, Registered Users 2 Posts: 215 ✭✭happylad


    Yes it does this from cold but in saying that I have seen it doing it after it has been on


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    it may be a longshot but I would chance putting a new photocell in it just to rule this out

    usually they don't fail this way but have had them do funny things when just going out of parameters

    is your engineer happy that you have a good constant fuel supply to the burner


  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    happylad wrote: »
    Thanks for coming back to me. I emailed them last week and yes they were helpful and very quick to come back. See response.

    I might ask my man could I borrow the gas analyser and adjust the head to see can I bring it down. Would you think it would do no harm to try 0.5 and work away up if needs be until the correct reading is achieved. Ideally what readings should you see for co and excess air.

    I'll get the technician back either way in the new year when he has a bit more time
    If it's blowing the flame out and not fuel starvation or other, then .5 might make it worse. Seeing as they typed 5 and not .5, I'd have to guess it's not a typo. That's unless they are reading from a typo.
    You could phone a few service guys from around northern Ireland and run this point by them.
    You could carefully try .5 but you would need to do a combustion adjustment immediately to correct the changes in combustion. You would also need to watch out for smoke in case you soit it up.

    Lower the co2. Keep co 0 to 50pp Make sure boiler is at running temp when testing and all readings are stable.

    Take note of Jimf's posts also.

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 215 ✭✭happylad


    Thanks for response.

    The last time he was here he put a new photocall on it and took it off again as he said the old one was fine. Not sure about the fuel supply. It should be good. Is that a case of he should check the suction on the pump or how would you check this.


  • Moderators, Home & Garden Moderators Posts: 6,378 Mod ✭✭✭✭Wearb


    happylad wrote: »
    Thanks for response.

    The last time he was here he put a new photocall on it and took it off again as he said the old one was fine. Not sure about the fuel supply. It should be good. Is that a case of he should check the suction on the pump or how would you check this.
    First check fuel line filters the pump gauze. Then observe pressure gauge for a few minutes to see if it jumps around. Also briefly see if it smoothly adjusts to 9 bar and back again.
    After that I would check vacuum. It should almost zero and certainly below .4

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    happylad wrote: »
    Thanks for response.

    The last time he was here he put a new photocall on it and took it off again as he said the old one was fine. Not sure about the fuel supply. It should be good. Is that a case of he should check the suction on the pump or how would you check this.

    did he take it off the same day

    did the boiler act up while it was in situ


  • Registered Users, Registered Users 2 Posts: 215 ✭✭happylad


    Yes the boiler did the same thing with the new photocell. He felt it must be something to do with the combustion


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    just to recap on this post your boiler has now fitted 1.0 x 60 nozzle at 8bar pressure

    firing head is at 5 this boiler is a 150he warmflow boiler

    there is a possibility that nozzle at 8bar is not atomising very well after all the manf spec is what we go by they ask for 9.5 bar for a 1.00x80h nozzle

    if you need to lower the output of the boiler you can fit a .85x80h at 10 bar pressure

    hard to know for sure without been on site

    golden rule for me manf spec ie correct nozzle at recommended pressure they make the boiler they have the homework done you would presume

    once these are correct that is your starting point


  • Registered Users, Registered Users 2 Posts: 215 ✭✭happylad


    I was thinking the same and I am just after getting a 0.85 80h nozzle and am goin to fit this eve. I'll adjust pressure on the pump also to 10bar. I'll get a gauge to do this. Any recommendations for the combustion head would you start low and work up or what you think. I'll get the flue gas analyser as well and see how it goes


  • Registered Users, Registered Users 2 Posts: 8,565 ✭✭✭K.Flyer


    happylad wrote: »
    I was thinking the same and I am just after getting a 0.85 80h nozzle and am goin to fit this eve. I'll adjust pressure on the pump also to 10bar. I'll get a gauge to do this. Any recommendations for the combustion head would you start low and work up or what you think. I'll get the flue gas analyser as well and see how it goes

    Start at the manufacturers settings. According to the manual for the U150HE the adjustable head should be set at 5.
    Your pump pressure 10 for that nozzle.
    What is your Air setting at now, you should do a smoke test before using the analyser.


  • Registered Users, Registered Users 2 Posts: 215 ✭✭happylad


    Many thanks for all the advice. I'll adjust in line with the manufacturers settings and see how it goes. I'll get the service engineer to look at it as well after the xmas and we'll see what the state of play is.

    Thanks again for all the help.

    Wishing ye a merry xmas and all the best for the new year.


  • Registered Users, Registered Users 2 Posts: 3,974 ✭✭✭jimf


    ley us know how it went