new etci rules re; T+E cable sep 2017

Options
  • 18-07-2017 3:27pm
    #1
    Registered Users Posts: 2,400 ✭✭✭


    The new rules are coming into effect soon. Has anybody used the new T&E cable yet? Would it be fair to say its adding approx 10% onto the price of a job due to the increased cost of materials?


«1

Comments

  • Registered Users Posts: 16,969 ✭✭✭✭Sleeper12


    evosteo wrote:
    The new rules are coming into effect soon. Has anybody used the new T&E cable yet? Would it be fair to say its adding approx 10% onto the price of a job due to the increased cost of materials?


    Is the new cable 10% more expensive?


  • Registered Users Posts: 2,400 ✭✭✭evosteo


    I havent used it myself yet. Not sure on cost per cable size. 10% is just a guestimate


  • Registered Users Posts: 1,052 ✭✭✭Tuco88


    Are the talks of a new regs book true?

    Is it an Irish company producing the cable, as far as I am aware it's not a standard in the UK but I know they have a new regs book coming.

    Intresting to see the cost difference of new T+E vs NYM-J.


  • Moderators, Category Moderators, Entertainment Moderators, Sports Moderators Posts: 22,584 CMod ✭✭✭✭Steve


    Interesting.

    From a certain wholesaler's website:
    Old spec:
    2.5 Sq mm Blue/Brown 100M €49.49 ex VAT

    New spec (insulated PE):
    2.5 Sq mm Blue/Brown 100M €79.35 ex VAT

    Edit - NYM-j is still dearer:
    2.5 Sq mm 3 METRE €1.23 ex VAT (€123/100m)


  • Registered Users Posts: 888 ✭✭✭JonnyM


    Different sized wavin will have to be used aswell not much in price difference there.

    Will save time I'm sure when terminating as you won't need earth sleeving.


  • Advertisement
  • Registered Users Posts: 2,400 ✭✭✭evosteo


    Steve wrote: »
    Interesting.

    From a certain wholesaler's website:
    Old spec:
    2.5 Sq mm Blue/Brown 100M €49.49 ex VAT

    New spec (insulated PE):
    2.5 Sq mm Blue/Brown 100M €79.35 ex VAT

    Edit - NYM-j is still dearer:
    2.5 Sq mm 3 METRE €1.23 ex VAT (€123/100m)

    Jesus thats some mark up on price. 30% odd dearer. I never even considered the increased size will cause capacity issues in oval and round conduit especially if walls have to be chased etc. In a domestic setting


  • Registered Users Posts: 2,400 ✭✭✭evosteo


    Tuco88 wrote: »
    Are the talks of a new regs book true?

    Is it an Irish company producing the cable, as far as I am aware it's not a standard in the UK but I kno we they have a new regs book coming.

    Intresting to see the cost difference of new T+E vs NYM-J.

    1st iv heard of a new reg book. Havent the etci been disbanded and the upgraded PE in T+E been their parting gift?


  • Registered Users Posts: 1,052 ✭✭✭Tuco88


    Yes the ETCI have dissolved. Somebody mentioned it here once of a new book, I think it was an apprentice going fas.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators Posts: 10,952 Mod ✭✭✭✭Stoner


    Tuco88 wrote:
    Yes the ETCI have dissolved. Somebody mentioned it here once of a new book, I think it was an apprentice going fas.

    From the NSAI


  • Registered Users Posts: 1,884 ✭✭✭Robbie.G


    I was in Cef yesterday and they were saying around 30% difference in both
    And what were they going to do with old stock as in my branch they have around 40k in stock


  • Advertisement
  • Registered Users Posts: 1,444 ✭✭✭sky6


    What's the Difference between new and old ?.


  • Registered Users Posts: 2,567 ✭✭✭Risteard81


    sky6 wrote: »
    What's the Difference between new and old ?.
    The cpc will be of the same csa as the live conductors and will also be insulated.


  • Registered Users Posts: 2,400 ✭✭✭evosteo


    Here a link to somemore info on the kellihers wholesale site

    http://kellihers.com/news/new-twin-earth-wiring-rules/

    Twin-Earth-poster-Feb-2017.jpg


  • Registered Users Posts: 505 ✭✭✭stiofan85


    While renovating recently I ran a 6sqmm T&E from the fuse board (unconnected) to the back of the kitchen in anticipation of running power to a shed next year. This is the old type of T&E mentioned here.

    Would it now be against the regs to use it to run power to a shed?


  • Moderators, Category Moderators, Entertainment Moderators, Sports Moderators Posts: 22,584 CMod ✭✭✭✭Steve


    stiofan85 wrote: »
    While renovating recently I ran a 6sqmm T&E from the fuse board (unconnected) to the back of the kitchen in anticipation of running power to a shed next year. This is the old type of T&E mentioned here.

    Would it now be against the regs to use it to run power to a shed?

    New regs kick in in September, you're fine.


  • Registered Users Posts: 3,612 ✭✭✭Dardania


    What's the driver for this change. My memory is rusty (last looked at this about 8 years ago when dealing with a Swedish SWA CPC setup), but from what I recall, the earth CSA is sized based on the fault current from the phase. Are fault currents increasing or something?


  • Registered Users Posts: 2,567 ✭✭✭Risteard81


    Dardania wrote: »
    What's the driver for this change. My memory is rusty (last looked at this about 8 years ago when dealing with a Swedish SWA CPC setup), but from what I recall, the earth CSA is sized based on the fault current from the phase. Are fault currents increasing or something?
    Probably arising more out of harmonisation than anything else. The fault currents will vary by installation and therefore when using T&E with a reduced csa cpc the adequacy of the cpc should be verified via the adiabatic equation (S = sq rt((I^2)t)/k) - this is obviously generally met in domestic installations with low prospective fault currents.

    Another advantage of the full sized cpc is that it will reduce touch voltage as well during a fault.

    Any excess stock old-style T&E cable could still be sold into the north.


  • Registered Users Posts: 2,675 ✭✭✭exaisle


    evosteo wrote: »
    The new rules are coming into effect soon. Has anybody used the new T&E cable yet? Would it be fair to say its adding approx 10% onto the price of a job due to the increased cost of materials?


    How much more expensive is the new type cable?

    How much is T&E cable as a proportion of a total job?


  • Registered Users Posts: 2,675 ✭✭✭exaisle


    evosteo wrote: »
    Jesus thats some mark up on price. 30% odd dearer. I never even considered the increased size will cause capacity issues in oval and round conduit especially if walls have to be chased etc. In a domestic setting

    That's 60% dearer..or an increase of 60% on 49.49 per metre


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    Risteard81 wrote: »

    Another advantage of the full sized cpc is that it will reduce touch voltage as well during a fault.

    Any example of where that will become meaningful?


  • Advertisement
  • Registered Users Posts: 2,400 ✭✭✭evosteo


    i was speaking to a contractor friend of mine about the new regs coming into force soon. he mentioned to me about upgrading the standard 10mm2 earth cable to 16mm2 in a domestic set up (earth rod, hotpress, boiler, gas meter, water). i was thinking to myself that this was overkill or did i miss some new reg introduction?

    he said it should be the same size csa as the new upgraded 16mm2 T+E cable????


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    evosteo wrote: »
    i was speaking to a contractor friend of mine about the new regs coming into force soon. he mentioned to me about upgrading the standard 10mm2 earth cable to 16mm2 in a domestic set up (earth rod, hotpress, boiler, gas meter, water). i was thinking to myself that this was overkill or did i miss some new reg introduction?

    he said it should be the same size csa as the new upgraded 16mm2 T+E cable????

    16 square for bonding and earth rod would be way overkill in domestic installations.


  • Registered Users Posts: 2,400 ✭✭✭evosteo


    Bruthal wrote: »
    16 square for bonding and earth rod would be way overkill in domestic installations.

    Completly agree


  • Registered Users Posts: 61 ✭✭Mondo44


    How are 2 10mm earth wires from 10 squared t&e going to fit in a shower pull cord with one earth connector


  • Registered Users Posts: 2,567 ✭✭✭Risteard81


    Mondo44 wrote: »
    How are 2 10mm earth wires from 10 squared t&e going to fit in a shower pull cord with one earth connector
    Personally I favour the 50A Click and Crabtree round pullcords as they are, in my opinion, superior to the other offerings out there not least because they contain dual screws for all of the live conductors within. As for the protective conductor, realistically with two of the new-style 10mm^2 IS201 T&E cables then it's going to be a bit awkward no matter what you use - but good quality materials is still a major part of the answer.


  • Registered Users Posts: 61 ✭✭Mondo44


    Risteard81 wrote: »
    Personally I favour the 50A Click and Crabtree round pullcords as they are, in my opinion, superior to the other offerings out there not least because they contain dual screws for all of the live conductors within. As for the protective conductor, realistically with two of the new-style 10mm^2 IS201 T&E cables then it's going to be a bit awkward no matter what you use - but good quality materials is still a major part of the answer.

    Absolutely no way of getting 2 10mm earths in the same connector


  • Registered Users Posts: 61 ✭✭Mondo44


    Risteard81 wrote: »
    Personally I favour the 50A Click and Crabtree round pullcords as they are, in my opinion, superior to the other offerings out there not least because they contain dual screws for all of the live conductors within. As for the protective conductor, realistically with two of the new-style 10mm^2 IS201 T&E cables then it's going to be a bit awkward no matter what you use - but good quality materials is still a major part of the answer.

    Absolutely no way of getting 2 10mm earths in the same connector


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,558 Mod ✭✭✭✭2011


    Mondo44 wrote: »
    How are 2 10mm earth wires from 10 squared t&e going to fit in a shower pull cord with one earth connector

    My preference would be to avoid pull cord switches altogether and use a wall switch instead.


  • Registered Users Posts: 16,969 ✭✭✭✭Sleeper12


    Mondo44 wrote:
    How are 2 10mm earth wires from 10 squared t&e going to fit in a shower pull cord with one earth connector


    We use hager 50amp pull cords. They have 2 earth connectors. As 2011 says though wall switch is the way to go. Only a little extra work & a better quality job


  • Advertisement
  • Registered Users Posts: 2,567 ✭✭✭Risteard81


    Sleeper12 wrote: »
    Mondo44 wrote:
    How are 2 10mm earth wires from 10 squared t&e going to fit in a shower pull cord with one earth connector


    We use hager 50amp pull cords. They have 2 earth connectors. As 2011 says though wall switch is the way to go. Only a little extra work & a better quality job
    Although the Hager 50A pullcords are of good quality (as all Hager gear), unfortunately they do not offer dual screws for the terminations of the live conductors which makes me select products which do.