Home heating automation

Options
1107108110112113151

Comments

  • Registered Users Posts: 8,615 ✭✭✭grogi


    Clareman wrote: »
    I'm leaning towards the Tado the more I look at it, I've 10 radiators, probably don't need a control on every radiator but if I'm at it I might as well go big

    I started with Tado smart thermostat only. Now I have 6 zones, two wireless temperature sensors and 8 TRV :D It is addictive... :D

    I sometimes regret not getting HomematicIP - it seems it gives you even more control.


  • Closed Accounts Posts: 891 ✭✭✭sebdavis


    Clareman wrote: »
    I'm leaning towards the Tado the more I look at it, I've 10 radiators, probably don't need a control on every radiator but if I'm at it I might as well go big

    Personally I think a standalone smart thermostat is a bit last year. Having the ability to control every room is a lot better solution and should result in reduction in wasted oil. Maybe not in oil itself but just having the right rooms at the right temp instead of one room boiling and every other freezing.

    I have 20+ radiators and have installed in all bar the ones in bathroom. This was recommendation of plumber not to put on the bathroom. I think it is also recommended to have one radiator without a TRV. Not sure when or where I seen that.

    Will Nest integrate with radiator thermostats from another company?


  • Registered Users Posts: 8,615 ✭✭✭grogi


    sebdavis wrote: »
    Will Nest integrate with radiator thermostats from another company?

    No


  • Moderators, Sports Moderators, Regional Midwest Moderators Posts: 23,924 Mod ✭✭✭✭Clareman


    I started in this forum because I got a free piece of kit somewhere, now there's more to be bought :D

    Can someone advise what I should get from here https://www.tado.com/ie-en/bundles-ec?utm_campaign=eos2021_bundles&utm_medium=email&utm_source=intercom please, I have a 1 zone boiler and 10 radiators

    I assume that I should get Wired Smart Thermostat Starter Kit V3+, Smart Radiator Thermostat - Starter Kit + 3 Smart Radiator Thermostats and 5 Smart Radiator Thermostats, that'll give me the controller for the boiler and a control for each radiator except for the bathroom and 1 other 1.


  • Registered Users Posts: 6,521 ✭✭✭deezell


    Clareman wrote: »
    I started in this forum because I got a free piece of kit somewhere, now there's more to be bought :D

    Can someone advise what I should get from here https://www.tado.com/ie-en/bundles-ec?utm_campaign=eos2021_bundles&utm_medium=email&utm_source=intercom please, I have a 1 zone boiler and 10 radiators

    I assume that I should get Wired Smart Thermostat Starter Kit V3+, Smart Radiator Thermostat - Starter Kit + 3 Smart Radiator Thermostats and 5 Smart Radiator Thermostats, that'll give me the controller for the boiler and a control for each radiator except for the bathroom and 1 other 1.

    You don't need the smart radiator stat stater kit, you already have the bridge with the Wired stat kit V3, so just TRVs tor as many rads as you want, 9, 10, 3 threes or two fives.


  • Advertisement
  • Moderators, Sports Moderators, Regional Midwest Moderators Posts: 23,924 Mod ✭✭✭✭Clareman


    deezell wrote: »
    You don't need the smart radiator stat stater kit, you already have the bridge with the Wired stat kit V3, so just TRVs tor as many rads as you want, 9, 10, 3 threes or two fives.

    Great, thanks for that, I'm pulling the trigger now, little Easter project :cool:


  • Registered Users Posts: 12,420 ✭✭✭✭machiavellianme


    Has anyone come across a smart air vent solution? There was a thread here previously recommending "vent-axia freshvent 100 thermo DB" but I can't find these to buy anywhere online. I'm presuming that the tech has moved on a bit since then?


  • Registered Users Posts: 6,521 ✭✭✭deezell


    Has anyone come across a smart air vent solution? There was a thread here previously recommending "vent-axia freshvent 100 thermo DB" but I can't find these to buy anywhere online. I'm presuming that the tech has moved on a bit since then?

    Do you mean the heat recovery type for individual room fitting, with alternated direction fan, as featured on EcoEye repeat a week or so ago. I see them on Amazon. They're more sophisticated than that vent axia one, which is passive, no heat recovery.

    41K58gKjC8L._AC_SY580_.jpg


  • Registered Users Posts: 12,420 ✭✭✭✭machiavellianme


    deezell wrote: »
    Do you mean the heat recovery type for individual room fitting, with alternated direction fan, as featured on EcoEye repeat a week or so ago. I see them on Amazon. They're more sophisticated than that vent axia one, which is passive, no heat recovery.

    41K58gKjC8L._AC_SY580_.jpg

    I was planning on the passive approach, perhaps with some sort of battery supplied automation to adjust the vent based on temperature/humidity.
    Active might be an option but I'd need to get power to the vent then.


  • Registered Users Posts: 3,377 ✭✭✭Ryath


    There's humidity controlled vents that don't need power. They have a humidity sensitive strip that opens and closes them. We have them installed as part of a Demand Control Ventilation (DCV) system but they can be used passively too.

    https://www.heatmerchants.ie/aereco-eht-acoustic-air-inlet-valve-u48874

    https://www.aereco.ie/


  • Advertisement
  • Registered Users Posts: 1,742 ✭✭✭Bawnmore


    After some reading around, I'm set on the Drayton Wiser system and TRV's. Just want to make sure I'm ordering the right thing.

    So what we have:

    - Boiler, zoned for rads and water.
    - EPH controller that allows for separate schedules for heat and water. We don't have huge hot water needs so have it set for 30 mins in the morning and that's it.
    - Separate mechanical timer for immersion.
    - Wired twisty knob type thermostat in the hall.
    - Hot Water cylinder gravity fed from attic.
    - Manual TRV bodies on each rad.

    So with above in mind, would the following sound right:

    - https://www.screwfix.ie/p/drayton-heating-2-channel-wiser-thermostat-control-kit/9575V?gclsrc=ds which would replace the EPH controller and thermostat.
    - Drayton Wiser TRV's for each of the radiators with the exception of the bathroom.

    And then questions:

    - Is replacing it a DIY job or something we'd need an electrician for?
    - It doesn't say it in the package above, but I'm assuming the Drayton thermostats are wireless and I could move it to a better spot than the current thermostat (above a radiator) and just patch up the wiring hole?


  • Registered Users Posts: 6,521 ✭✭✭deezell


    Bawnmore wrote: »
    After some reading around, I'm set on the Drayton Wiser system and TRV's. Just want to make sure I'm ordering the right thing.

    So what we have:

    - Boiler, zoned for rads and water.
    - EPH controller that allows for separate schedules for heat and water. We don't have huge hot water needs so have it set for 30 mins in the morning and that's it.
    - Separate mechanical timer for immersion.
    - Wired twisty knob type thermostat in the hall.
    - Hot Water cylinder gravity fed from attic.
    - Manual TRV bodies on each rad.

    So with above in mind, would the following sound right:

    - https://www.screwfix.ie/p/drayton-heating-2-channel-wiser-thermostat-control-kit/9575V?gclsrc=ds which would replace the EPH controller and thermostat.
    - Drayton Wiser TRV's for each of the radiators with the exception of the bathroom.

    And then questions:

    - Is replacing it a DIY job or something we'd need an electrician for?
    - It doesn't say it in the package above, but I'm assuming the Drayton thermostats are wireless and I could move it to a better spot than the current thermostat (above a radiator) and just patch up the wiring hole?

    Right on all counts. TRVs are DIY, stat is wireless, receiver a direct replacement for the EPH, simple wiring Remove the old stat, joining its wires together and insulating before popping back in the hole. Turn of mains breaker to all before DIY, as receiver and old stat are switching mains.


  • Registered Users Posts: 6,073 ✭✭✭championc


    Just make sure that your existing TRV's are standard, or you'll have to buy additional adapters.

    Tado come with adapters to work with 10's of different TRV's


  • Registered Users Posts: 6,521 ✭✭✭deezell


    championc wrote: »
    Just make sure that your existing TRV's are standard, or you'll have to buy additional adapters.

    Tado come with adapters to work with 10's of different TRV's
    In addition to that, I just noticed you said that your cylinder was gravity fed. You can't generally use a two channel timer to control a system with gravity fed HW unless the controller has a gravity mode switch. Does your HW heat all the time the boiler fires for ch, or just when its EPH HW timing is on. If the latter, then your HW is not gravity fed, but individually fed by a pump or valve circuit. The drayton 2 zone controller does not have a gravity mode jumper or switch, so you'll need to establish that your HW and CH can operate independently before going for the wiser kit.
    Its just s small quirk of wiring that facilitates gravity mode, without it a 2 channel programmer can mimic it by having one channel fire the boiler exclusively, which will give gravity HW heating, then the other channel operates the CH pump, which heats the rads provided the HW, boiler call timing is on. Gravity mode on a 2 channel timer builds this in, HW timer is wired to boiler, CH timer to the pump, and HW timer goes off for all events, HW and CH.


  • Registered Users Posts: 1,742 ✭✭✭Bawnmore


    deezell wrote: »
    In addition to that, I just noticed you said that your cylinder was gravity fed. You can't generally use a two channel timer to control a system with gravity fed HW unless the controller has a gravity mode switch. Does your HW heat all the time the boiler fires for ch, or just when its EPH HW timing is on. If the latter, then your HW is not gravity fed, but individually fed by a pump or valve circuit. The drayton 2 zone controller does not have a gravity mode jumper or switch, so you'll need to establish that your HW and CH can operate independently before going for the wiser kit.
    Its just s small quirk of wiring that facilitates gravity mode, without it a 2 channel programmer can mimic it by having one channel fire the boiler exclusively, which will give gravity HW heating, then the other channel operates the CH pump, which heats the rads provided the HW, boiler call timing is on. Gravity mode on a 2 channel timer builds this in, HW timer is wired to boiler, CH timer to the pump, and HW timer goes off for all events, HW and CH.

    Well spotted - by your description above, our HW is actually not gravity fed. The EPH controller can control either independently - each have their own valves. So that all sounds good - will pick up the Drayton system shortly - thanks folks.


  • Registered Users Posts: 4,530 ✭✭✭savemejebus


    For the Drayton there's a bit of a discount on Amazon at the min. A much bigger discount in the wireless extenders from the warehouse if you need them. 30% off the marked price at checkout https://www.amazon.co.uk/Drayton-Wiser-Heating-System-Extender/dp/B07D71BPGK/ref=sr_1_5?dchild=1&keywords=Drayton&m=A2OAJ7377F756P&qid=1616525953&s=warehouse-deals&sr=8-5


  • Registered Users Posts: 1,742 ✭✭✭Bawnmore


    Bawnmore wrote: »
    After some reading around, I'm set on the Drayton Wiser system and TRV's. Just want to make sure I'm ordering the right thing.

    So what we have:

    - Boiler, zoned for rads and water.
    - EPH controller that allows for separate schedules for heat and water. We don't have huge hot water needs so have it set for 30 mins in the morning and that's it.
    - Separate mechanical timer for immersion.
    - Wired twisty knob type thermostat in the hall.
    - Hot Water cylinder gravity fed from attic.
    - Manual TRV bodies on each rad.

    So with above in mind, would the following sound right:

    - https://www.screwfix.ie/p/drayton-heating-2-channel-wiser-thermostat-control-kit/9575V?gclsrc=ds which would replace the EPH controller and thermostat.
    - Drayton Wiser TRV's for each of the radiators with the exception of the bathroom.

    And then questions:

    - Is replacing it a DIY job or something we'd need an electrician for?
    - It doesn't say it in the package above, but I'm assuming the Drayton thermostats are wireless and I could move it to a better spot than the current thermostat (above a radiator) and just patch up the wiring hole?

    Just spotted that discount too. Just to check, this is the same as what I've linked above, but with 2 TRV's included right?


  • Registered Users Posts: 6,073 ✭✭✭championc


    Woooo hoooo - new Tado app v6.5

    One button to shut off app rads. Perfect timing for the incoming summer


  • Registered Users Posts: 533 ✭✭✭chuck eastwood


    championc wrote: »
    Woooo hoooo - new Tado app v6.5

    One button to shut off app rads. Perfect timing for the incoming summer

    Had it in the beta version for the last few weeks. Very handy but it would be far better if you could shut down each zone seperately


  • Registered Users Posts: 6,521 ✭✭✭deezell


    Seems like an admission that there are those who prefer to act as human stats, boost, off, boost, off, like the crudest of timer only controllers. If you trust the smarts, you can just leave it alone.


  • Advertisement
  • Registered Users Posts: 533 ✭✭✭chuck eastwood


    deezell wrote: »
    Seems like an admission that there are those who prefer to act as human stats, boost, off, boost, off, like the crudest of timer only controllers. If you trust the smarts, you can just leave it alone.

    Or there are some with households that both work call outs ever changing shifts etc so the ability to fly out the door and kill the heating is handy without forgetting to use geofencing. If we relied on the software itself to run on scheduling it would cost us a hell of a lot more than it currently does. Control is everything


  • Registered Users Posts: 8,615 ✭✭✭grogi


    deezell wrote: »
    Seems like an admission that there are those who prefer to act as human stats, boost, off, boost, off, like the crudest of timer only controllers. If you trust the smarts, you can just leave it alone.

    I clean the radiators.from time to time... I don't want them hot when I'm cleaning...


  • Registered Users Posts: 6,521 ✭✭✭deezell


    You don't have to 'use' geofencing, set once and forget. Set home schedules and forget. If you have to regularly turn off or boost, then the schedule is wrong, too cold or too warm.
    I get it from Tado's point of view, it'll help sales, a lot of people need to be in control, or at least have the option, and it's cost Tado nothing but a few lines of code. The prominence of the new buttons speaks volumes about the human machine relationship.
    A lady I knew, long departed, would sit by her new automatic washing machine, the older type with the big mechanical program timer, and would manually advance every stage of a programme, convinced that the wash or rinse or spin had gone over time or was stuck, and needed a nudge. After a few years of this, the timer gave up prematurely, so she got her manual machine, sort of.
    Enjoy the buttons!


  • Registered Users Posts: 2,093 ✭✭✭notahappycamper


    I wish Tado° would incorporate hot water control into HomeKit especially since the rooms/rads can be controlled individually by HomeKit.


  • Registered Users Posts: 14,555 ✭✭✭✭Marlow


    After the latest firmware update to my Fritz!Box routers, all Fritz!DECT switches now also measure and show humidity.

    51009384705_6707d7ae1a_c.jpg

    That was a nice update.

    /M


  • Moderators, Sports Moderators, Regional Midwest Moderators Posts: 23,924 Mod ✭✭✭✭Clareman


    My Tado arrived and I'm not sure how to install them on my radiators, I've this type of connection
    Lockshield-Valve-Header-1080x720.jpg


  • Registered Users Posts: 8,615 ✭✭✭grogi


    Clareman wrote: »
    My Tado arrived and I'm not sure how to install them on my radiators, I've this type of connection
    Lockshield-Valve-Header-1080x720.jpg

    This looks like a balancing value to me.

    Check the other side of the radiator. There should be second valve there.


  • Closed Accounts Posts: 891 ✭✭✭sebdavis


    Clareman wrote: »
    My Tado arrived and I'm not sure how to install them on my radiators, I've this type of connection
    Lockshield-Valve-Header-1080x720.jpg

    You are going to look at this

    https://my-plumber.co.uk/blog/how-to-fit-a-thermostatic-radiator-valve-trv/

    Got o 3.14 in the video


  • Moderators, Sports Moderators, Regional Midwest Moderators Posts: 23,924 Mod ✭✭✭✭Clareman


    grogi wrote: »
    This looks like a balancing value to me.

    Check the other side of the radiator. There should be second valve there.

    I've the same on both sides of the rad,it's about 20 years old


  • Advertisement
  • Closed Accounts Posts: 891 ✭✭✭sebdavis


    Clareman wrote: »
    I've the same on both sides of the rad,it's about 20 years old

    Its the old connections. If you don't already have a TRV installed then you need to follow the video above and install.....so its a drain the system and replace job...