  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    dupeters wrote: »
    Maybe bruthal,
    but what if it the element has a fault of 28mA? And it was causing the rcd to trip? along with say 3mA of cumulative?
    Adding it to its own rcbo would be ok for now.
    I really don't get your line of thinking. To change an element that is not tripping an rcbo simply because it might in the future is pointless.
    i think for safety sake (and because it is a cheap purchase/remidy) that changing the whole immersion coil would be the right way to continue.
    I know if it was my house with my kids using hot water every day i couldn't sleep knowing my immersion had a fault which i had not repaired but transferred to another device?

    If it is not tripping an rcbo, and is earthed properly, it is fine. There is no danger. If that concerns you that badly, you should avoid using all electrical devices.

    Something leaking 30ma has a leakage impedance of 7666 ohms. Too high to be of much danger.


  • Registered Users Posts: 84 ✭✭Helpmefarm


    Try isolating one element at a time both live and netural needs to be disconnected and find which element has the fault and use the good one to keep you going! New immersions not expensive as cheap as a seperate rcbo and ya wont need an expensive electrican like me!


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    Helpmefarm wrote: »
    Try isolating one element at a time both live and netural needs to be disconnected and find which element has the fault and use the good one to keep you going! New immersions not expensive as cheap as a seperate rcbo and ya wont need an expensive electrican like me!

    He might need an expensive plumber though.


  • Registered Users Posts: 324 ✭✭Gr1f


    Hi guys, any idea where i can get an Immersion Element for decent price in Dublin/Bray? Mine's gone.


  • Registered Users Posts: 56 ✭✭LooksLikeRain


    Eurosales in sandyford usually have them in stock


  • Advertisement
  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,565 Mod ✭✭✭✭2011


    Gr1f wrote: »
    Hi guys, any idea where i can get an Immersion Element for decent price in Dublin/Bray? Mine's gone.
    Chadwicks and Heat Merchants in Bray.


  • Registered Users Posts: 2,036 ✭✭✭Cerco


    You could also try the wholesalers facing Chadwickes on Boghall Rd. - used to T.R. Reilly I think.


  • Registered Users Posts: 324 ✭✭Gr1f


    Gr1f wrote: »
    Hi guys, any idea where i can get an Immersion Element for decent price in Dublin/Bray? Mine's gone.

    Got one and all fixed after much swearing and gnashing of teeth.


  • Registered Users Posts: 51 ✭✭kingden2006


    if you know which circuit it is just bell the cable out using your multimeter from your fuse board to your immersion,that will tell you wether or not there is a break in the cable or not,but you are much better of using an insulation resistance meter/megger,because sometimes if the cable is broke using a multimeter you"ll still get continuity because it"s not completely broken,thats why you should use a megger.
    also if you already have an mcb you only need and rcd not an rcbo.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    if you know which circuit it is just bell the cable out using your multimeter from your fuse board to your immersion,that will tell you wether or not there is a break in the cable or not,but you are much better of using an insulation resistance meter/megger,because sometimes if the cable is broke using a multimeter you"ll still get continuity because it"s not completely broken,thats why you should use a megger.
    also if you already have an mcb you only need and rcd not an rcbo.

    A multimeter would show up open circuits better than the higher voltage meggar, particularly where the open circuit gap is microscopic.


  • Advertisement
  • Closed Accounts Posts: 8,585 ✭✭✭jca


    I'd say its leaking to earth when under mains voltage. I wouldn't take any chances with an Immersion.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    jca wrote: »
    I'd say its leaking to earth when under mains voltage. I wouldn't take any chances with an Immersion.

    What chances are being taken? If its an earth fault, RCD trips. Even in the days before RCDs I often seen elements which had split, so the actual element conductor was into the water. Still no serious danger despite the automatic assumptions of water and electricity = doom.


  • Registered Users Posts: 51 ✭✭kingden2006


    yes your right there bruthal


  • Closed Accounts Posts: 8,585 ✭✭✭jca


    Bruthal wrote: »
    What chances are being taken? If its an earth fault, RCD trips. Even in the days before RCDs I often seen elements which had split, so the actual element conductor was into the water. Still no serious danger despite the automatic assumptions of water and electricity = doom.
    Its tripping the RCD. Replace it, End of.
    Elements exposed to the water:eek: What did you do?? Put a tuppence piece in place of the ceramic fuse.... A tidy merchant...


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    jca wrote: »
    Its tripping the RCD. Replace it, End of.
    I always have to laugh at that "end of" phrase, as if it means infallibility on the users part. Would you replace an immersion that is tripping an RCD if it was a neutral touching an earth in the switch for example? Or under the immersion cover itself? No simple tests, just replace?

    More often than not, they do need replacing, but I like to test and confirm, rather than just replace without question.
    Elements exposed to the water:eek: What did you do?? Put a tuppence piece in place of the ceramic fuse.... A tidy merchant...

    And what do you do when a fuse blows, replace the immersion?


  • Closed Accounts Posts: 8,585 ✭✭✭jca


    Bruthal wrote: »
    I always have to laugh at that "end of" phrase, as if it means infallibility on the users part. Would you replace an immersion that is tripping an RCD if it was a neutral touching an earth in the switch for example? Or under the immersion cover itself? No simple tests, just replace?

    More often than not, they do need replacing, but I like to test and confirm, rather than just replace without question.



    And what do you do when a fuse blows, replace the immersion?
    Obviously after doing wiring checks and the wiring is perfect, the RCD keeps tripping/the fuse keep blowing when re-connected to the immersion, yep, replace the immersion...end of.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    jca wrote: »
    Obviously after doing wiring checks and the wiring is perfect, the RCD keeps tripping/the fuse keep blowing when re-connected to the immersion, yep, replace the immersion...end of.

    A right, thats a different "end of" than...
    Its tripping the RCD. Replace it, End of.

    Obviously, from the sound of it, you have not experienced split immersion failures. They were common enough in failures before RCDs were used on immersions. Immersion element open circuits inside casing, and arcs across the tiny opening, burning the mineral insulation, eventually splitting the copper jacket.

    With no RCD to trip from earth fault, they continued working with the owner oblivious except that the water heated slower, if at all, with some current flowing into the water and onto the element casing. It could clearly be heard, as instead of a clean buzzing sound, (2 different tones for bath and sink if you put ear to cylinder when its on), it would make a distinctive sizzling sound, as the element conductor was exposed to the water.

    And fuses didnt really blow with the above, as it was usually far enough from the live end of the element that the element conductor resistance was high enough to not blow fuses. The resistance of the bath element is about 18 ohms, so if the failure was half way along or more toward the neutral end, that would be 9 ohms, not enough to blow a 20 amp fuse, especially when the element conductor probably didnt contact the copper jacket, or if it did, it was not good contact, it often just ended up exposed to the water.


  • Closed Accounts Posts: 8,585 ✭✭✭jca


    Bruthal wrote: »
    A right, thats a different "end of" than...

    Obviously, from the sound of it, you have not experienced split immersion failures. They were common enough in failures before RCDs were used on immersions. Immersion element open circuits inside casing, and arcs across the tiny opening, burning the mineral insulation, eventually splitting the copper jacket.

    With no RCD to trip from earth fault, they continued working with the owner oblivious except that the water heated slower, if at all, with some current flowing into the water and onto the element casing. It could clearly be heard, as instead of a clean buzzing sound, (2 different tones for bath and sink if you put ear to cylinder when its on), it would make a distinctive sizzling sound, as the element conductor was exposed to the water.

    And fuses didnt really blow with the above, as it was usually far enough from the live end of the element that the element conductor resistance was high enough to not blow fuses. The resistance of the bath element is about 18 ohms, so if the failure was half way along or more toward the neutral end, that would be 9 ohms, not enough to blow a 20 amp fuse, especially when the element conductor probably didnt contact the copper jacket, or if it did, it was not good contact, it often just ended up exposed to the water.
    One of the reasons not to ignore RCD/ELCB trips especially regarding the Immersion. It happened in the Fathers place back in the 70's on the bath element. The whole cylinder was delivering mild shocks to myself and the brother much to our amusement. The aul lad wasn't so impressed and he fixed it in typical miserly 70's style. Yep you've guessed it....He disconnected the bath element and it was sink only:pac::pac: For the next 20 years:D Oh yea a grand sparing man...


  • Registered Users Posts: 686 ✭✭✭DieselPowered


    you need a megger

    Which megger is needed for this type of troubleshooting?


  • Closed Accounts Posts: 8,585 ✭✭✭jca


    Which megger is needed for this type of troubleshooting?
    I think you need to replace it;);)


  • Advertisement
  • Registered Users Posts: 686 ✭✭✭DieselPowered


    jca wrote: »
    I think you need to replace it;);)

    Thats not the question :p


  • Closed Accounts Posts: 8,585 ✭✭✭jca


    Thats not the question :p
    Is that you Da?


  • Registered Users Posts: 686 ✭✭✭DieselPowered


    jca wrote: »
    Is that you Da?

    I'll hold out for someone that knows what they are talking about.


  • Registered Users Posts: 563 ✭✭✭adrian92


    Suggest remove the immersion circuit from the RCD ciruit. The normal leakage may be tripping all. Re wire to a non-RCD circuit or re-wire it with its own RCD.


  • Registered Users Posts: 51 ✭✭kingden2006


    an insulation resistance meter or megger as they are more commonly known as on building sites,they are used for measuring the resistance of insulation by sending a higher voltage down the cable normally 500 volts or 1000volts,you test between live and neutral,live and earth and neutral and earth the reading should be in the megaohms...this test only insure"s that there is no damage to the cable/insulation or leakage,whichever you like to call it.
    i think the elcb is done away with now,as far as i know,but i could be wrong.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,565 Mod ✭✭✭✭2011


    adrian92 wrote: »
    Re wire to a non-RCD circuit
    No, that is not permitted.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,565 Mod ✭✭✭✭2011


    i think the elcb is done away with now,as far as i know,but i could be wrong.
    It has not been done away with, just a name change. It is now referred to as an "RCD"


  • Closed Accounts Posts: 8,585 ✭✭✭jca


    I'll hold out for someone that knows what they are talking about.

    I think the posters here and the immersion itself are telling you to replace the immersion. You've checked the wiring and it's ok? You've checked the switch and its ok? You may bite the bullet and replace the elements. A horrible job.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,565 Mod ✭✭✭✭2011


    I would think that everything has been covered thoroughly now.