Boiler problems

  • 19-01-2013 3:07pm
    #1


    Hi, I'm having trouble with my 'Ideal LOGIC System 24' and it's flashing error code F1 (which means low water pressure according to the manual). It's just not turning on and it's ridiculously freezing in the house...

    I've looked at the user manual and online and apparently I need to to get the pressure between 1 and 1.5 and at the moment it's at 0.5. Everything's busy telling me how to lower the pressure but how do I get the pressure back up again?

    Any help would be great and if you need any more info I would be happy to comply.


«1

Comments



  • I've tried opening up all the valves but nothing happens...


  • Registered Users, Registered Users 2 Posts: 771 ✭✭✭gdavis


    u must locate filler loop.probably in hot press
    possibly a silver flexi pipe or half inch copper .decent photo of pipework and cylinder would help a lot and we can take from there




  • Cool, ok I'm on it! brb








  • I couldn't find any loopy things anywhere or copper or silver in the hot press...


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 771 ✭✭✭gdavis


    need more pics of pipes in hot press.the pic u did take is showing a pipe .will need to see more of pipe.the 2 pipes coming off ur cylinder that are directly in line maybe 1/3 from bottom of cylinder and second one above it 10-12 inches.these are ur heating pipes we need to see connections on them


  • Registered Users, Registered Users 2 Posts: 6,250 ✭✭✭pixbyjohn


    Would it be the black tap at the gauge in Pic 0038?




  • DSC_0044.jpg

    DSC_0045.jpg

    Just found a loose copper wire there after I took some stuff out of the way...




  • pixbyjohn wrote: »
    Would it be the black tap at the gauge in Pic 0038?

    I've opened all the taps and closed them but nothing happened.


  • Registered Users, Registered Users 2 Posts: 771 ✭✭✭gdavis


    no they are the isolation valves to ur boiler.different kettle of fish altogether


  • Advertisement


  • gdavis wrote: »
    need more pics of pipes in hot press.the pic u did take is showing a pipe .will need to see more of pipe.the 2 pipes coming off ur cylinder that are directly in line maybe 1/3 from bottom of cylinder and second one above it 10-12 inches.these are ur heating pipes we need to see connections on them

    DSC_0036.jpg

    DSC_0041.jpg

    DSC_0046.jpg
    Here's some pics of the pipes.


  • Registered Users, Registered Users 2 Posts: 771 ✭✭✭gdavis


    that is an earth wire that should be clamped to copper pipe.the other pic u took doesnt show where the pipe goes when it gets to wall ,also no pic of the pipe above that,this is like pulling teeth !!!put copper wire back in under copper bracket in pic 41 and tighten screw




  • gdavis wrote: »
    that is an earth wire that should be clamped to copper pipe.the other pic u took doesnt show where the pipe goes when it gets to wall ,also no pic of the pipe above that,this is like pulling teeth !!!

    Sorry man... I'll go do that now.


  • Registered Users, Registered Users 2 Posts: 771 ✭✭✭gdavis


    im joking relax lol.pic 36 is ur heating coil.cannot see top pipe when it goes to wall in corner does it rise up and go down? ie is it a tee or an elbow.pic would help ! lol


  • Registered Users, Registered Users 2 Posts: 771 ✭✭✭gdavis


    good man pic 0038,wher pipe reduces to half inch as it rises,has it a valve above it?




  • gdavis wrote: »
    are pic 36 and 46 the same lower pipe in both?need to see it in corner if it is.think we getting somewhere now!

    Yeah, this and this are the same (the bit with the red tap.


  • Registered Users, Registered Users 2 Posts: 771 ✭✭✭gdavis


    im presuming hot press is upstairs.so u see in them pics where pipe reduces in size and rises.is there a valve on this pipe




  • gdavis wrote: »
    good man pic 0038,wher pipe reduces to half inch as it rises,has it a valve above it?

    You talking about this one? Sorry I think there's a few 0036's now... Em do you want another pic I don't really know what you mean... Sorry! I'm so bad at plumbing!


  • Registered Users, Registered Users 2 Posts: 771 ✭✭✭gdavis


    so,heating coil that u know now,if u follow them over to corner,one of them will go to a tee piece,dropping down into floor and rising in a smaller sized pipe.the smaller sized pipe heading towards ceiling is feeding ur heating system.this should have a red handled valve on it???


  • Advertisement


  • gdavis wrote: »
    im presuming hot press is upstairs.so u see in them pics where pipe reduces in size and rises.is there a valve on this pipe

    Em theres only one valve and it connects to the back pipe like I've shown here: Untitled.jpg

    Sorry it took ages my computer decided it wanted to annoy me...


  • Registered Users, Registered Users 2 Posts: 771 ✭✭✭gdavis


    blue or red??




  • gdavis wrote: »
    so,heating coil that u know now,if u follow them over to corner,one of them will go to a tee piece,dropping down into floor and rising in a smaller sized pipe.the smaller sized pipe heading towards ceiling is feeding ur heating system.this should have a red handled valve on it???

    Yeah so I had another look and the pipe with the red valve does go into a 'tree' or anything it just goes straight down into the ground (and yeah this is upstairs) and straight up too, and I followed it up and found another tap. The other pipe that comes from the top of the immersion heater (hot press) goes down into the ground too and goes up but it goes nowhere and the pipe ends and has a red plug in it.




  • gdavis wrote: »
    blue or red??

    it's a red valve. and you can see it in the picture.




  • Yeah so I had another look and the pipe with the red valve does go into a 'tree' or anything it just goes straight down into the ground (and yeah this is upstairs) and straight up too, and I followed it up and found another tap. The other pipe that comes from the top of the immersion heater (hot press) goes down into the ground too and goes up but it goes nowhere and the pipe ends and has a red plug in it.

    Oh a 'tee', totally misread the man... Yeah it goes into a T junction I suppose. It come from the boiler and then separates and goes up and down.


  • Registered Users, Registered Users 2 Posts: 771 ✭✭✭gdavis


    the red tap u mentioned first feeds heating.is that opened ?turned fully clockwise




  • gdavis wrote: »
    the red tap u mentioned first feeds heating.is that opened ?turned fully clockwise

    Umm I don't knkow... I'll go check.




  • There I just turned it as clockwise as it can go. I twisted it quite far... Do you think that was the problem?


  • Registered Users, Registered Users 2 Posts: 771 ✭✭✭gdavis


    sorry meant anti clockwise, long day!! so must have been opened ?


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 771 ✭✭✭gdavis


    below red tap,is there a brass fitting maybe 3 inches long?




  • That's ok man, you've been great help so far! I've turned it back the other way then.




  • Em, I don't know man- this is what I'm looking at and there's nothing else there.


  • Registered Users, Registered Users 2 Posts: 771 ✭✭✭gdavis


    sorry just realised wrong valve only saw ur pic now.close that one fully clockwise,then open back up one revolution anti clockwise.the one u looking for will be on the vertical heading for ceiling on same pipe




  • gdavis wrote: »
    sorry just realised wrong valve only saw ur pic now.close that one fully clockwise,then open back up one revolution anti clockwise.the one u looking for will be on the vertical heading for ceiling on same pipe

    Yeah I think I found another tap just up from where we were, I think you can kinda tell where it is from the first pic:

    DSC_0037.jpg

    DSC_0038.jpg




  • But um like, you know the problem is with the boiler downstairs yes? It's outside in the outhouse and it's blinking the F1 error. Just thought I'd remind you...


  • Advertisement


  • But I know nothing so don't listen to me. These things are all interconnected, like I know the hot press is connected to the boiler so don't mind me I'm just venting because I'm cold...




  • sorry man, gotta go eat something... Be back soon.


  • Registered Users, Registered Users 2 Posts: 1,884 ✭✭✭Robbie.G


    That last valve the brass one it looks to be the feed to the heating open it count to 5 and close it again then check your pressure




  • Just did that now and I went downstairs to check but the boiler's still got the error code F1 flashing...




  • No more help? Or am I doomed to pay for a professional... :(


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 1,884 ✭✭✭Robbie.G


    Just did that now and I went downstairs to check but the boiler's still got the error code F1 flashing...
    Did you hear any water running or gushing when you opened the valve.Have you tried to reset the boiler again the boiler should work at 0.5 bar
    REsET pROCEDURE
    To reset boiler, turn the mode control knob (B) to reset position and immediately turn knob back to ON


  • Registered Users, Registered Users 2 Posts: 157 ✭✭seamusmacc


    not sure is that any help, my valves for topping up the gauge pressure are actually in the attic, and they are beside the water tank, even though my boiler on the ground floor, and the hot press on first floor.




  • seamusmacc wrote: »
    not sure is that any help, my valves for topping up the gauge pressure are actually in the attic, and they are beside the water tank, even though my boiler on the ground floor, and the hot press on first floor.

    Same.




  • I reset it like you said put it's still flashing F1...




  • So cold... :(


  • Registered Users, Registered Users 2 Posts: 771 ✭✭✭gdavis


    ok,did u open that valve and if so did pressure rise?just open for maybe ten seconds
    then close again.go down and check at boiler gauge.also turn power off to boiler and then back on,then reset procedure again.if problem is low pressure that brass valve will let water in and if u reset as per manual u should be sorted.does manual say anything else for f1?




  • Sorry, I decided to drown my sorrows in tv... But I'm back! Nothing happened when I turned the brass valve in the hot press. I didn't hear any water or anything and the boiler is still flashing F1 no matter how many times I reset it.
    Do you think I should turn the brass valve in the hot press and the valves down under the boiler too?




  • Well, I went ahead and tried my bright idea but nothing again... Now I'm gonna wake up in the morning to a freezing cold house... Yay.


  • Registered Users, Registered Users 2 Posts: 744 ✭✭✭dpofloinn


    Can you find anything that looks like this http://www.wickes.co.uk/content/ebiz/wickes/invt/443011/Combi-Boiler-Filling-Loop_large.jpg or this http://web.tradekorea.com/upload_file2/product/107/P00258107/cbe9caa5_506f7c61_b2be_4884_98a2_f06feadb40b5.jpg near your boiler,or in your hot press, Also check your attic if you have one,they are sometimes installed up there especially in homes that have been retro fitted


  • Registered Users, Registered Users 2 Posts: 771 ✭✭✭gdavis


    the valves under boiler have nothing to do with it.they just isolate the gas,flow and return at boiler as i told u already.i dont have manual at hand so does it say anything else for f1? also leave brass valve opened [anti clockwise] for longer period of time maybe a minute before closing,i think it is tank fed so shouldnt rise dramatically or too high. as said before the boiler should work on 0.5 bar anyway so i would be interested to know what else f1 is as per manual