Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie

Heat Pumps - post here.

Options
134689118

Comments

  • Registered Users Posts: 22 offalygirl08


    hi, I am building a house and before I start work on the plans in detail I want to pick out a heating system for the house. May sound daft to some but its just to ensure I am not short on storage space from cylinders etc.
    I was thinking about using Solar Tubes for the hot water, house will be based on a farm and hot water especially in summer months for showers will be needed.
    I was also looking at the Air to Heat system. I was wondering if anyone is using this effectively and rough average of the bills. Bearing in mind that at the moment I am heating a 4 bed for 3K - 3.5K including ESB per annum.
    My major concern would be also if anyone can suggest a supplier / fitter in Offaly or near by, I want a replicable one that has experience in putting them in properly and that if I will have some come back with.


  • Registered Users Posts: 235 ✭✭steifanc


    mossy74 wrote: »
    Hi All,
    I have some questions some of you may have answers for.

    I have a Ochsner heat pump for my geothermal heating system and on the information plate at the back of it, it says that it should use 3.6 KWh based on 20Amps at 230V with a power factor 0f 0.78. There is also another figure for the maximum current of 23 Amps.

    My issue is that I have measured using a clamp meter a current of up to 28Amps (at 226V), I have also run some tests where I have switched off all circuit breakers in my house except for the ones used by the geothermal system. Taking account of shunt pump and controls the heatpump uses (measured over a few nights) approximately 4.8KWh. The supplier claims that this is due to a lot of heat loss in my house and that therefore the pump has to work harder. I think that this may be a fob off as the information plate clearly states that it should draw a max current of 23 Amps but to use 4.6KWh it must be drawing an average of over 26Amps. Has anyone else seen this? Is it normal? Will it affect the life of my heatpump etc. etc.

    Just a quick note if it says 20 amps at 230 v it cant be 3.6 kw

    Ohms law
    Volts * amps = power

    So
    230*20 = 4600
    Or 4.6 kw

    Voltage is inversely proportional to current also so is your voltage goes down your. Current goes up
    Where you gain with a heat pump is , its cost you 4.6kwh of electricity to get 13.5 kw of heat so that's nearly 3/1

    I'm guessing your heat pump is around 13kw


  • Registered Users Posts: 16 johnfoyvision


    There are 2 reasons why there are high esb costs on heatpumps.

    1. The insulation of the house was not adequet or fitted poorly. (Its not a fob off) Its rather simple to proove. Get a Heat loss test done

    2. The size of the pump is not adequet for the use. Each house needs to be calculated differently. As there are different specs for different house.

    And more importantly.. having "good insulation" means NOTHING if its not fitted correctly If there are gaps in it you are as well have not fitted it at all as it causes a thermal draught

    I am completely agree with your answer. I shall be thankful to all of you discussing heat pumps from which I get a lot of indormation. I am a student and I just studying about heat pumps and found this forum very useful that how we can implement the use of heat pumps by ourseld in real life.


  • Registered Users Posts: 617 ✭✭✭sheff the ref


    I used to work in Geothermal Heating back around 2005/2006 and am wondering if there have been many advances since then. I plan to build a 1800 square foot bungalow with a converted attic.

    From my time in the business I know that ground source Geothermal heat pump with a properly sized, even slightly oversized horizontal ground source area will be very efficient. Excavation costs for the collector are expensive but the tidier alternative of a borehole collector will probably be more expensive though for a smaller house, the difference in cost may not be that huge. However it required top notch insulation and proper in-house heat management to make it run at its very very cheapest. At the time, underfloor heating was required to run it at the lowest costs. Has this changed. Are Rads still considerably more expensive to run using Geothermal??

    At the time Air-To-Water was just coming in and was relatively unproven. Has it advanced much since then, and is it a viable alternative for a house of that size. How does it compare to Ground Source in terms of running costs?

    In the two really hard winters of 2009 and 2010 which would have been the best option???


  • Closed Accounts Posts: 5,433 ✭✭✭sinnerboy


    In the two really hard winters of 2009 and 2010 which would have been the best option???

    Honestly - a fossil fuel burning high powered boiler. Those winters were extreme and in my opinion only those with over sized plant stood any chance of keeping warm indoors without coats on.


  • Advertisement
  • Registered Users Posts: 536 ✭✭✭Condenser


    sinnerboy wrote: »
    Honestly - a fossil fuel burning high powered boiler. Those winters were extreme and in my opinion only those with over sized plant stood any chance of keeping warm indoors without coats on.

    Why do you say that? Plants that were performing well before those winters would have performed well through it.

    To answer your question sheff, the technology has not really moved on but then again it doesn't really have to because the better performing installations are very cheap to run. Its generally the installation or application which lets systems down. So stay away from running rads of the units and stick with ufh. And a properly designed ufh at that. Not one designed towards an oil boiler installation.

    Air to water will always be more expensive to run than ground source. Firstly there is the factor of having to run a fan motor to move air across the evaporator and also the factor that the energy source temp is variable. Colder outside temps mean all heat pumps have to work harder because of extra heatloss but air source have to work even harder again to overcome the fact that its extracting energy from colder air.

    What has moved on is the insulation levels of homes. This in conjunction with air tightness means much smaller heat pumps can be used to heat comparable houses from 2005/2006.


  • Registered Users Posts: 617 ✭✭✭sheff the ref


    From my time in it, I would have to say that a properly installed and properly managed horizontal ground source system was the best allright.

    The borehole would have been the tidiest to be honest. Hidden factors with horizontal collectors include the actual area that needs to be dug can be massive depending on the size of the house. Trees cannot be planted on that area either or it can never be concreted, meaning a massive area of grass to be cut.


  • Closed Accounts Posts: 5,433 ✭✭✭sinnerboy


    Condenser wrote: »
    Why do you say that? Plants that were performing well before those winters would have performed well through it.

    Because by definition plants that work well at external temperatures of -20 degrees are oversized for Ireland .


  • Posts: 21,179 ✭✭✭✭ [Deleted User]


    How about these ?

    http://dreamheatpumps.co.uk/12.5kw_heat_pump_HOME.html

    3kw in 12.5 out, they say it's a direct replacement for an oil boiler. My oil boiler is about 6 years old.

    50 degrees water temp is all I'd need at a maximum , cavities are pumped and 12 inches of insulation in the attic.

    Seems like heat pumps are becoming more popular and starting to appear in clothes dryers and electric cars.

    I worked it out that at 3 kw for 5 hours per day over 7 days for 6 months would work out at 403 euros per year of required heat. I would use the immersion as normal for the shower in summer. Oil costs around 440 for 500 litres and we get away with about 500 litres in a normal winter using it sparingly. We use the electric heater sometimes when we don't need to heat the whole house.

    But if the heat pump was that good we could heat the house for longer with night saver and have a warm house for longer for less than oil ?

    3 kw in 12.5 out ?


  • Registered Users Posts: 536 ✭✭✭Condenser


    sinnerboy wrote: »
    Because by definition plants that work well at external temperatures of -20 degrees are oversized for Ireland .

    Not true. A plant should be designed to cover the average winters day heatloss in an 8-12hr running period. That would leave an entire 12hr window to cover additional losses. You do not design plant to run 24hrs for your average winter temps. All plant should be designed with a degree of redundancy involved. Besides, that same plant will be then oversized for the remainder of the year but it doesn't effect efficiency or running cost. I'd don't see how you use your argument to support that an oil boiler would be more efficient.


  • Advertisement
  • Registered Users Posts: 536 ✭✭✭Condenser


    How about these ?

    http://dreamheatpumps.co.uk/12.5kw_heat_pump_HOME.html

    3kw in 12.5 out, they say it's a direct replacement for an oil boiler. My oil boiler is about 6 years old.

    50 degrees water temp is all I'd need at a maximum , cavities are pumped and 12 inches of insulation in the attic.

    Seems like heat pumps are becoming more popular and starting to appear in clothes dryers and electric cars.

    I worked it out that at 3 kw for 5 hours per day over 7 days for 6 months would work out at 403 euros per year of required heat. I would use the immersion as normal for the shower in summer. Oil costs around 440 for 500 litres and we get away with about 500 litres in a normal winter using it sparingly. We use the electric heater sometimes when we don't need to heat the whole house.

    But if the heat pump was that good we could heat the house for longer with night saver and have a warm house for longer for less than oil ?

    3 kw in 12.5 out ?

    Chinese crap. Not even the top european air to water units have a COP of 4.6. And if you want to heat up to 50C the COP will drop by almost half. You wouldn't even buy the compressor and the fan motor for the price they're selling it for. You'd be as well off burning the money as you'd get more heat out of it and it'd cost you less.


  • Registered Users Posts: 14,544 ✭✭✭✭Poor Uncle Tom


    Condenser wrote: »
    Chinese crap. Not even the top european air to water units have a COP of 4.6. And if you want to heat up to 50C the COP will drop by almost half. You wouldn't even buy the compressor and the fan motor for the price they're selling it for. You'd be as well off burning the money as you'd get more heat out of it and it'd cost you less.

    +1
    One of the best responses I've ever read....


  • Posts: 21,179 ✭✭✭✭ [Deleted User]


    Condenser wrote: »
    Chinese crap. Not even the top european air to water units have a COP of 4.6. And if you want to heat up to 50C the COP will drop by almost half. You wouldn't even buy the compressor and the fan motor for the price they're selling it for. You'd be as well off burning the money as you'd get more heat out of it and it'd cost you less.

    Thanks for that, I guess it was too good to be true!

    So are heat pumps for heating a waste of money and for now we should keep using oil and gas ?

    It would have been good just replacing the oil boiler.


  • Closed Accounts Posts: 5,433 ✭✭✭sinnerboy


    Condenser wrote: »
    Not true. A plant should be designed to cover the average winters day heatloss in an 8-12hr running period. That would leave an entire 12hr window to cover additional losses. You do not design plant to run 24hrs for your average winter temps. All plant should be designed with a degree of redundancy involved. Besides, that same plant will be then oversized for the remainder of the year but it doesn't effect efficiency or running cost. I'd don't see how you use your argument to support that an oil boiler would be more efficient.

    I never said an oil boiler is more efficient.

    Otherwise we are on the same page. But the question asked was - what about the severe cold recent winters ? Whatever system you use it will either struggle to keep you warm and/r guzzle fuel to cope with those conditions.

    I am saying that those with a gas or oil boiler during that period would not have seen the same spike in running costs compared to heat pump system.

    A heat pump sized to average Irish winter temperatures , I believe , would struggle to perform and result in a big spike in ESB bills.

    Now I am not arguing against heat pumps here . I fact I will say this - there is a flaw in the question - what about the extreme winters ? One should not design to that circumstance.


  • Users Awaiting Email Confirmation Posts: 280 ✭✭engineermike


    Condenser wrote: »
    Chinese crap. Not even the top european air to water units have a COP of 4.6. And if you want to heat up to 50C the COP will drop by almost half. You wouldn't even buy the compressor and the fan motor for the price they're selling it for. You'd be as well off burning the money as you'd get more heat out of it and it'd cost you less.

    Fully in agreement with Condenser here - better to burn your money to stay warm than waste it on a cheap pump. You'll have a frozen ice box instead of a functioning compressor when harsh winters arrive again.
    There are plenty of good air source pumps from reputable brands available on the market, the usual let down factors are poor installation of the pump, incorrectly matched for the property, poorly insulated property or in properly designed heat distribution system in the home. If all those boxes are ticked a heat pump will do as it says on the tin.
    Also there are models with back up immersions in the pump to provide heat should there be a fault or abnormal external temp's - Ok your efficiency goes out the window at that point, however your house is warm & then you continue to make savings the rest of the year around.
    Comparison graph of 2 models with COP at normal Irish mean temperatures & also COP at the 'harsh winter' temps experienced recently
    ( I'll PM the link to you, because there's manufactures detailed on the grpah, and i don't want to anoy the boards 'god's' ) :)
    mike f


  • Posts: 21,179 ✭✭✭✭ [Deleted User]


    Fully in agreement with Condenser here - better to burn your money to stay warm than waste it on a cheap pump. You'll have a frozen ice box instead of a functioning compressor when harsh winters arrive again.
    There are plenty of good air source pumps from reputable brands available on the market, the usual let down factors are poor installation of the pump, incorrectly matched for the property, poorly insulated property or in properly designed heat distribution system in the home. If all those boxes are ticked a heat pump will do as it says on the tin.
    Also there are models with back up immersions in the pump to provide heat should there be a fault or abnormal external temp's - Ok your efficiency goes out the window at that point, however your house is warm & then you continue to make savings the rest of the year around.
    Comparison graph of 2 models with COP at normal Irish mean temperatures & also COP at the 'harsh winter' temps experienced recently
    ( I'll PM the link to you, because there's manufactures detailed on the grpah, and i don't want to anoy the boards 'god's' ) :)
    mike f

    Thanks I got the link, but I must admit I'm none the wiser.

    I'm a bit clueless about heat pumps for instance what does cop mean ?

    So if a heat pump used 3 kw and gives out 12 kw, I presume that's dependant on the outside temp and if it's -5 out would it be consuming more than 3kw ?


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    Thanks I got the link, but I must admit I'm none the wiser.

    I'm a bit clueless about heat pumps for instance what does cop mean ?

    So if a heat pump used 3 kw and gives out 12 kw, I presume that's dependant on the outside temp and if it's -5 out would it be consuming more than 3kw ?

    Its not so much that it gives out 12kw, but it transfers 12kw from one medium to another. The colder the outside temp, the higher the volume of the medium from which the heat is being extracted is required to pass over the evaporator.

    A bath of room temp water has more heat in it than a red hot nail for example, even though the nail is at a far higher temp.

    So 20,000 litres of air at 0 degrees C has more heat in it than 1000 litres of air at 20 degrees C (as a random plucked from the air example). So the lower the outside temp, compared to the inside one, the higher volume of air that would have to be passed over the heat pump evaporator outside, to maintain the same volume of air inside at the same temp.

    The COP is the coefficient of performance, or the heat transferred compared to work input, or your 3kw v 12kw.


  • Registered Users Posts: 536 ✭✭✭Condenser


    Thanks I got the link, but I must admit I'm none the wiser.

    I'm a bit clueless about heat pumps for instance what does cop mean ?

    So if a heat pump used 3 kw and gives out 12 kw, I presume that's dependant on the outside temp and if it's -5 out would it be consuming more than 3kw ?

    Your COP is the coefficient of performance or how many kw heat energy you get out per kw electrical input. It can only be established at given criteria so for example the european standard for air to water is A2/W35 i.e an air temp of 2C and heated water outlet at 35C. If you decrease the first figure you will decrease the COP, if you increase the 2nd figure you will also decrease the COP. However the inverse is also correct, so your COP is not a set figure, its floating. A well designed system will aim to have the first figure as high as possible and the 2nd figure as low as possible to maximise COP. The problem with air to water is that the installer can really only control the water outlet (2nd) figure.

    Consumption won't increase very much if the outside temp drops but energy output will as the energy is harder to collect when the air temp is low hence the reason that ground source units are a much better option, as both figures are in the hands of the installer.


  • Posts: 21,179 ✭✭✭✭ [Deleted User]


    Thant's great info lads thanks.

    Engineermike, in the link you sent me they quoted one of the units was able to heat water to 60 degrees with an air temp of -3 ? That seems incredible. Surely that could be a replacement for my oil boiler to heat the radiators ?

    There are 2 units though which I don't understand, I get the heat pump one, but the other ? also they don't mention the electricity consumption.

    I like the idea of using the pumps for cooling in summer, or when needed like now when it's warm and very humid.


  • Users Awaiting Email Confirmation Posts: 280 ✭✭engineermike


    Thant's great info lads thanks.

    Engineermike, in the link you sent me they quoted one of the units was able to heat water to 60 degrees with an air temp of -3 ? That seems incredible. Surely that could be a replacement for my oil boiler to heat the radiators ?

    There are 2 units though which I don't understand, I get the heat pump one, but the other ? also they don't mention the electricity consumption.

    I like the idea of using the pumps for cooling in summer, or when needed like now when it's warm and very humid.

    Hi,
    You'd have to change the rads to forced air rads to have any real value from a pump that can cool during summer. Normal rads won't be effective and you find condensation being a problem on the traditional rads if you have a pump that heats / cools. - (during the cooling cycle).
    The COP - basically means the work you will achieve i.e a cop of 3.5 means that for every 1 kw of electricity you pump uses - you will get 3.5 kw of heat & hot water into the property.

    I'll send you a couple of other links that help explain it more clearly - the concept and useage figures for various pumps
    mike f


  • Advertisement
  • Registered Users Posts: 4,748 ✭✭✭Do-more


    one of the units was able to heat water to 60 degrees with an air temp of -3 ? That seems incredible. Surely that could be a replacement for my oil boiler to heat the radiators ?

    There are some (mainly Japanese I think) manufacturers doing high temperature (HT) heat pumps which have two compressors working in series and can output water temperatures up to 70C. I've seen them mentioned on some UK forums where they seem to be a popular retrofit for oil and gas boilers but haven't noticed them mentioned on here. It might be worth your while searching for feedback on them.

    invest4deepvalue.com



  • Posts: 21,179 ✭✭✭✭ [Deleted User]


    Thanks for the replies lads, I'm sure this technology will only improve in the future.

    Direct boiler replacements would be what I'd be looking for. I live in a mid terrace house so I wonder how loud they would be ? Luckily enough it's not hard to heat and the cavity insulation and attic insulation has made a noticeable difference, however my windows are old and pretty rubbish and are in bad need of replacement, so I think I'd be far better off for now upgrading them to modern windows. However if a heat pump could heat the house as cheap or cheaper than oil I would be very happy. Our oil consumption is around 500-700 litres a year, with the heat being on 4-5 hours per day. Id does warm up quick enough as it's small enough 3 bed terrace house and being a mid terrace I only have 2 external walls.

    The rear of the house is south facing and even in the coldest of winters if the sun shins in the back of the house it's very warm.

    I think I got a C for my energy rating, the windows knocked it down a few points but I could possibly get a high C or possibly B with decent windows.

    The plan down the road is to build or renovate to fully passive standards with heat pump and solar P.V and wind turbine.


  • Registered Users Posts: 617 ✭✭✭sheff the ref


    Condenser wrote: »
    Your COP is the coefficient of performance or how many kw heat energy you get out per kw electrical input. It can only be established at given criteria so for example the european standard for air to water is A2/W35 i.e an air temp of 2C and heated water outlet at 35C. If you decrease the first figure you will decrease the COP, if you increase the 2nd figure you will also decrease the COP. However the inverse is also correct, so your COP is not a set figure, its floating. A well designed system will aim to have the first figure as high as possible and the 2nd figure as low as possible to maximise COP. The problem with air to water is that the installer can really only control the water outlet (2nd) figure.

    Consumption won't increase very much if the outside temp drops but energy output will as the energy is harder to collect when the air temp is low hence the reason that ground source units are a much better option, as both figures are in the hands of the installer.


    Therefore even in extreme conditions, the temperature of the ground is pretty much constant in winter time when the horizontal pipes are laid roughly 1metre under the ground or down a borehole. The chilled liquid is sent out into the ground and the ambient temperature takes the cold sting out of it, and raises the temperature by a couple of degrees in the collector.

    Air Temperature went as low as -10 and possibly lower in the winter of 2010. How much more expensive would the Air to Water system be to run during such a cold spell per hour of heat produced. Would there be much of an ESB cost difference from say +2 degrees, to 0 degrees, to -2 degrees, to -4 degrees to -6 degrees to -8 degrees to -10 degrees.

    For initial investment purposes the decision to be made is, to evaluate if the occasional cold snap is worth taking a hit on with an Air to Water system, when compared to the excavation/well drilling costs for a Ground Source system.


  • Registered Users Posts: 536 ✭✭✭Condenser


    Therefore even in extreme conditions, the temperature of the ground is pretty much constant in winter time when the horizontal pipes are laid roughly 1metre under the ground or down a borehole. The chilled liquid is sent out into the ground and the ambient temperature takes the cold sting out of it, and raises the temperature by a couple of degrees in the collector.

    Air Temperature went as low as -10 and possibly lower in the winter of 2010. How much more expensive would the Air to Water system be to run during such a cold spell per hour of heat produced. Would there be much of an ESB cost difference from say +2 degrees, to 0 degrees, to -2 degrees, to -4 degrees to -6 degrees to -8 degrees to -10 degrees.

    For initial investment purposes the decision to be made is, to evaluate if the occasional cold snap is worth taking a hit on with an Air to Water system, when compared to the excavation/well drilling costs for a Ground Source system.

    Plus you have to factor in the fact you have more moving parts (fan motors, 4 way valve etc) that can go wrong. And also that the outdoor unit will be exposed to the elements year round and so is unlikely to have a lifespan of more than 10yrs. The cheaper units will look very rough even before then.


  • Registered Users Posts: 617 ✭✭✭sheff the ref


    Ya. That is the issue allright and a very valid point. A ground source heat pump can be indoors either in an internal Boiler House well free from all elements or in the Garage.

    An external Oil Boiler is well protected and sealed from the elements in fairness but an Air to Water Heatpump cannot be protected, because it needs to be exposed to operate. Anything exposed to the weather in Ireland is subject to all forms of long term maintenance issues, like you said there are hidden costs such as replacing wear and tear parts. The likelihood is that in say 10 years time time a new heatpump may well be a cheaper option than replacing parts, because like a washing machine, once one goes, they all go.

    I think ground source may well be the best option.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    Condenser wrote: »
    Plus you have to factor in the fact you have more moving parts (fan motors, 4 way valve etc) that can go wrong. And also that the outdoor unit will be exposed to the elements year round and so is unlikely to have a lifespan of more than 10yrs. The cheaper units will look very rough even before then.

    The specific heat capacity of air is 4 times less than water per gram as well, and a gram of air is a lot higher volume than water, so a condensor collecting heat from ground water will likely be more efficient than an air source one, besides the more stable ground temperature as well.


  • Posts: 21,179 ✭✭✭✭ [Deleted User]


    robbie7730 wrote: »
    The specific heat capacity of air is 4 times less than water per gram as well, and a gram of air is a lot higher volume than water, so a condensor collecting heat from ground water will likely be more efficient than an air source one, besides the more stable ground temperature as well.

    Would it be possible to integrate the heat pump into a normal well ?

    Drilling a well specifically for the heat pump would be really expensive but would probably be better than laying pipes over a large area of the garden ?


  • Registered Users Posts: 536 ✭✭✭Condenser


    Would it be possible to integrate the heat pump into a normal well ?

    Drilling a well specifically for the heat pump would be really expensive but would probably be better than laying pipes over a large area of the garden ?

    Amost neglibibly more efficient once the ground conditions are right.

    You could use a water to water system with a standard well but you'd have to drill a dump well and have high quantities of mineral free water such as lime, iron etc


  • Posts: 21,179 ✭✭✭✭ [Deleted User]


    Condenser wrote: »
    Amost neglibibly more efficient once the ground conditions are right.

    You could use a water to water system with a standard well but you'd have to drill a dump well and have high quantities of mineral free water such as lime, iron etc

    Thanks for the answer.

    So am I guessing that the most efficient way to use heat pumps is ground pipes and underfloor heating ?


  • Advertisement
  • Registered Users Posts: 536 ✭✭✭Condenser


    Thanks for the answer.

    So am I guessing that the most efficient way to use heat pumps is ground pipes and underfloor heating ?

    Yes, as horizontal systems are cheaper and ufh can be run at very low temps if designed correctly.Poor installers can mess up other areas of the system but once these fundamentals are right, fixing any problems caused by an incorrect install is possible and relatively cheap.
    But put time into choosing your installer and get it right first time.


Advertisement