Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Please note that it is not permitted to have referral links posted in your signature. Keep these links contained in the appropriate forum. Thank you.

https://www.boards.ie/discussion/2055940817/signature-rules
Hi all! We have been experiencing an issue on site where threads have been missing the latest postings. The platform host Vanilla are working on this issue. A workaround that has been used by some is to navigate back from 1 to 10+ pages to re-sync the thread and this will then show the latest posts. Thanks, Mike.
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

Zappi charge points

1235727

Comments

  • Registered Users, Registered Users 2 Posts: 9,474 ✭✭✭TheChizler


    Anyone solve the problem where the rubber cap gets filled with water in the rain? It's causing what seems to be copper corrosion on our one. Thinking of getting a holster so it can be angled so the rain doesn't gather, but I'm wondering would a hole punched in the cap be enough to let the water out, might void the warranty though?

    1tndlg.jpg


  • Registered Users, Registered Users 2 Posts: 1,431 ✭✭✭gunnerfitzy


    TheChizler wrote: »
    Anyone solve the problem where the rubber cap gets filled with water in the rain? It's causing what seems to be copper corrosion on our one. Thinking of getting a holster so it can be angled so the rain doesn't gather, but I'm wondering would a hole punched in the cap be enough to let the water out, might void the warranty though?

    1tndlg.jpg

    I had this problem. I contacted myenergi and they stated that they now include a holster with each Zappi ordered to prevent this. They sent me out a holster free of charge. No issues with water ingress now.


  • Registered Users Posts: 1,770 ✭✭✭Nedved85


    I had this problem. I contacted myenergi and they stated that they now include a holster with each Zappi ordered to prevent this. They sent me out a holster free of charge. No issues with water ingress now.

    So the holster is waterproof? I didn't install my holster yet. Electrician reckoned the rubber cover would be better


  • Registered Users, Registered Users 2 Posts: 1,431 ✭✭✭gunnerfitzy


    Nedved85 wrote: »
    So the holster is waterproof? I didn't install my holster yet. Electrician reckoned the rubber cover would be better

    There is no rubber seal or similar in the holster so I can't see how it is strictly waterproof but it is keeping the rain out much better than the cap. Logically, one would think that the cap would be better than the holster but that is certainly not the case for me.


  • Registered Users, Registered Users 2 Posts: 9,474 ✭✭✭TheChizler


    I had this problem. I contacted myenergi and they stated that they now include a holster with each Zappi ordered to prevent this. They sent me out a holster free of charge. No issues with water ingress now.
    Cheers I'll do exactly that! I got it from Electric Autos but I'll contact myenergi first. The problem is when the plug hangs down the cap acts like a container, even a trickle of water would fill it quickly. The holster would ensure it's always upright so water can't get in.


  • Registered Users, Registered Users 2 Posts: 1,431 ✭✭✭gunnerfitzy


    TheChizler wrote: »
    Cheers I'll do exactly that! I got it from Electric Autos but I'll contact myenergi first. The problem is when the plug hangs down the cap acts like a container, even a trickle of water would fill it quickly. The holster would ensure it's always upright so water can't get in.

    I also bought mine from Phil also but I contacted myenergi directly. No issues and dealt with quickly.


  • Registered Users, Registered Users 2 Posts: 5,904 ✭✭✭daheff


    This is one of the reasons why I want to get one untethered.
    Problem is that they are not released until May, and my grant runs out then...so could be a push to get it done.

    Decisions decisions.


  • Registered Users, Registered Users 2 Posts: 1,431 ✭✭✭gunnerfitzy


    daheff wrote: »
    This is one of the reasons why I want to get one untethered.
    Problem is that they are not released until May, and my grant runs out then...so could be a push to get it done.

    Decisions decisions.

    You can cancel the current application and reapply.


  • Administrators, Computer Games Moderators, Sports Moderators Posts: 32,396 Admin ✭✭✭✭✭Mickeroo


    I got a holster in the box with mine from electric autos. I think any water just drains out of the holster so you don't get that problem.


  • Advertisement
  • Registered Users Posts: 1,770 ✭✭✭Nedved85


    Funnily enough the rubber cover attached to the charger was completely lodged with water Saturday and the blue residue seen in the photos above were visible on mine.

    More worryingly was that the Zappi was showing an error - "Ground Fault - Disconnect EV and reset Zappi" which I did, multiple times after letting the head air dry but to no avail.

    Electrician is coming around later to have a look. He said they did install a ground wire alright so it could be the water issue that caused this?

    I might try a hair dryer to dry out the head properly (with the zappi is fully disconnected from the mains obviously :) )

    Holster being installed soon hopefully :)


  • Administrators, Computer Games Moderators, Sports Moderators Posts: 32,396 Admin ✭✭✭✭✭Mickeroo


    denismc wrote: »
    So here is my settings screen, which shows the grid limit in kW.
    It looks like your device has the latest firmware version and mine is an older version, hence the difference.
    If you are still not sure about this, give Myenergi a ring, they are usually quick to respond.

    Thanks for this by the way, I e-mailed MyEnergi on Friday and they replied confirming it is indeed Amps on my charger. Must be different firmware or something alright!

    I must say it's so handy coming out to a fully charged and preheated car every morning now, the three weekly trips to the local rapid charger were getting old pretty fast.


  • Registered Users, Registered Users 2 Posts: 65,716 ✭✭✭✭unkel
    Chauffe, Marcel, chauffe!


    Mickeroo wrote: »
    the three weekly trips to the local rapid charger were getting old pretty fast.

    Yeah it's like people going to a "petrol station" to fill their car up with petrol or diesel. It's sooooooo 20th century :pac:


  • Registered Users, Registered Users 2 Posts: 1,269 ✭✭✭deegs


    I got the holster with my zappi and installed under the zappi which keeps it all dry in all weather.

    Can someone help me me with this....

    Got the ioniq and 5m cable and all works great. My wife has bought an outlander and it has a Grammy charger and a 5m type 2 to type 1 charge cable.
    The type 2 end won't connect to the zappi fully. Seems this is a safety design and there are some pics that prevent extenders?

    1) is there any way to charge the outlander from my zappi... Seems it is not set up for "extension" cables etc. And how? Don't want to mix ratings or overpower the outlander

    2) is it possible to charge any other type from a thethered type 2?


  • Registered Users, Registered Users 2 Posts: 7,822 ✭✭✭stimpson


    deegs wrote: »
    I got the holster with my zappi and installed under the zappi which keeps it all dry in all weather.

    Can someone help me me with this....

    Got the ioniq and 5m cable and all works great. My wife has bought an outlander and it has a Grammy charger and a 5m type 2 to type 1 charge cable.
    The type 2 end won't connect to the zappi fully. Seems this is a safety design and there are some pics that prevent extenders?

    1) is there any way to charge the outlander from my zappi... Seems it is not set up for "extension" cables etc. And how? Don't want to mix ratings or overpower the outlander

    2) is it possible to charge any other type from a thethered type 2?

    Never mind. Misunderstood the post. Answer is below.


  • Registered Users, Registered Users 2 Posts: 1,589 ✭✭✭Stealthirl


    deegs wrote: »

    Can someone help me me with this....

    Got the ioniq and 5m cable and all works great. My wife has bought an outlander and it has a Grammy charger and a 5m type 2 to type 1 charge cable.
    The type 2 end won't connect to the zappi fully. Seems this is a safety design

    1) is there any way to charge the outlander from my zappi... Seems it is not set up for "extension" cables etc. And how? Don't want to mix ratings or overpower the outlander

    2) is it possible to charge any other type from a thethered type 2?

    You need a T2>T1 adapter cable for the Zappi, the cable that came with the outlander cant be used to extend a T2 tethered connection. I got mine from evcables.co.uk

    https://evcables.co.uk/index.php/charge-cables-for-type-1-cars/type1-converter/ev-converter-cable-type-2-type-1.html

    I belive Phil in electricautos.ie / theevcompany.com also sells them


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 1,269 ✭✭✭deegs


    Sorted, thanks folks!


  • Registered Users Posts: 1,770 ✭✭✭Nedved85


    Stealthirl wrote: »
    You need a T2>T1 adapter cable for the Zappi, the cable that came with the outlander cant be used to extend a T2 tethered connection. I got mine from evcables.co.uk

    https://evcables.co.uk/index.php/charge-cables-for-type-1-cars/type1-converter/ev-converter-cable-type-2-type-1.html

    I belive Phil in electricautos.ie / theevcompany.com also sells them

    I have that exact same one for my Leaf Gen 1 - Works fine :)


  • Registered Users, Registered Users 2 Posts: 14,031 ✭✭✭✭Johnboy1951


    unkel wrote: »
    I bought an Owl intuition monitor on eBay last week. Does exactly that and you can place the wireless display anywhere. Cost me GBP7 shipped :D

    Is this what you got?

    https://www.amazon.co.uk/dp/B008MYXEHW

    for one tenth the cost including delivery?


  • Registered Users, Registered Users 2 Posts: 65,716 ✭✭✭✭unkel
    Chauffe, Marcel, chauffe!


    No mine is the basic version. It has a clamp that you clip onto the incomer in your meter box. It wirelessly transmits the signal to the display unit that you can place anywhere in the house. No apps or fancy internet stats.

    Still some kit for GBP7 shipped :D


  • Registered Users, Registered Users 2 Posts: 14,031 ✭✭✭✭Johnboy1951


    unkel wrote: »
    No mine is the basic version. It has a clamp that you clip onto the incomer in your meter box. It wirelessly transmits the signal to the display unit that you can place anywhere in the house. No apps or fancy internet stats.

    Still some kit for GBP7 shipped :D

    I didn't come across that one when searching, only the one I posted.

    Will search some more.
    If you have a link that would be great.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 65,716 ✭✭✭✭unkel
    Chauffe, Marcel, chauffe!


    Load of them on eBay. Put in some low bids and you're likely to pick up a cheap one like I did :D

    Like this:

    Linky


    Inviting opening offer of GBP2 :D

    Usually some of them on adverts too, but not this cheap


  • Registered Users, Registered Users 2 Posts: 343 ✭✭davidod1


    I've been reading here on the wiring of the Zappi and I would appreciate if someone could confirm if my understanding is correct on a few points.

    I have a local electrician lined up to do an installation for me. He has done a few charger installs before but never a Zappi and never where there was a PV panel installation.

    My PV system contributes power to anything drawing power in the house; be it lights or microwave or water heating. If there is a shortage then the mains takes up the slack. If there is a surplus then the hot water gets a boost or it goes back into the grid. I can see all this on the app. This may be the norm, I just don't know.

    This would mean that the Zappi will be powered from either solar or mains or a combination. My understanding is that this is one of the principal features on the Zappi and the solar/mains information comes from the CT clamp/Harvi. My question, therefore, is there a definite need to fit a CT clamp for tthe Zappi?

    Also, as I have an electric shower. He raised the issue of a board that will cut the power to the charger when the shower is in use. Is this needed with the Zappi.

    From reading here it looks like the wiring up of the Zappi is not really any more complicated than an external socket and should be well within the capabilities of any competent electrician. Am I right on that one as well?

    Thanks for any help received.


  • Registered Users, Registered Users 2 Posts: 12,136 ✭✭✭✭KCross


    Yes, you need the CT clamp. That’s the only way the Zappi knows there is excess going to the grid and therefore divert it to the car. If you don’t have it it’s just a normal charge point that will charge at full power all the time.

    And no, you don’t need the priority switch as the Zappi will know if the shower is on and will reduce its draw to ensure the fuse doesn’t blow.

    Most electricians won’t know what a Zappi is or how it works. You’ll need to educate him or point him to a manual.


  • Registered Users, Registered Users 2 Posts: 65,716 ✭✭✭✭unkel
    Chauffe, Marcel, chauffe!


    You're right on all of it davidod1. Zappi has built in priority switch so you don't need any additional hardware for your setup with your electric shower. Your electrician could do with a bit of researching to keep himself up to date on this stuff. It's a bit sad that amateurs like ourselves have to tell the professionals how to do their jobs...

    And yes, Zappi needs to know if electricity would be going to the grid, so yes it needs a CT clamp on the main incomer from the grid.

    Your main challenge is your immersion diverter ("the hot water gets a boost"). You need this set up in such a way that the house gets what it needs first (worth 18c/kWh), then the Zappi gets what it needs (worth 8c/kWh) and finally the immersion (worth just 4c/kWh). What immersion diverter do you have? If you have the Eddi (from the same company as the Harvi and the Zappi you mention) then this should all work together out of the box

    Edit - LOL KCross beat me to it on most of the points :)


  • Registered Users, Registered Users 2 Posts: 1,545 ✭✭✭denismc


    Just to add to the above, you or your electrician will have to set the grid limit on the Zappi as it's not set by default.
    It is quite easy to do though, the older machines had the setting in kW but the newer ones seem to be in amps.
    And if you are not 100% sure ring Myenergi and they will talk you through it.


  • Registered Users, Registered Users 2 Posts: 343 ✭✭davidod1


    Thanks for those clarifications KCross and unkel.
    One last point; I hope; for my own understanding. Is the CT Clamp wired back to the Zappi? If it is then it may be that I need the Harvi as the distance from the fuse board to the Zappi is about 50 meters. The Harvi might also be pushed as there is a building between the two locations as well as the distance.


  • Administrators, Computer Games Moderators, Sports Moderators Posts: 32,396 Admin ✭✭✭✭✭Mickeroo


    davidod1 wrote: »
    Thanks for those clarifications KCross and unkel.
    One last point; I hope; for my own understanding. Is the CT Clamp wired back to the Zappi? If it is then it may be that I need the Harvi as the distance from the fuse board to the Zappi is about 50 meters. The Harvi might also be pushed as there is a building between the two locations as well as the distance.

    Yep, the CT clamp is wired to the zappi where possible.


  • Registered Users, Registered Users 2 Posts: 2,819 ✭✭✭Silent Running


    davidod1 wrote: »
    Thanks for those clarifications KCross and unkel.
    One last point; I hope; for my own understanding. Is the CT Clamp wired back to the Zappi? If it is then it may be that I need the Harvi as the distance from the fuse board to the Zappi is about 50 meters. The Harvi might also be pushed as there is a building between the two locations as well as the distance.

    The clamp can be extended a very long distance by any twisted pair wire, like Cat 5 or 6 for example. It doesn't need anything special.


  • Registered Users, Registered Users 2 Posts: 65,716 ✭✭✭✭unkel
    Chauffe, Marcel, chauffe!


    davidod1 wrote: »
    Is the CT Clamp wired back to the Zappi? If it is then it may be that I need the Harvi as the distance from the fuse board to the Zappi is about 50 meters. The Harvi might also be pushed as there is a building between the two locations as well as the distance.

    Wireless won't cut it over that distance. As Silent Running said, you need to use standard network cable, you can easily and fairly cheaply get a long roll (they go up to hundreds of meters). You just "split" the cable in two tying the 4 wires from two of the pairs all together and the 4 wires from other two pairs together. Network cable is used because it doesn't pick up any interference from other cables / equipment

    I've the same issue myself wiring my new battery inverter (which works on the same principle as the Zappi), but not quite a 50m run :p


  • Registered Users, Registered Users 2 Posts: 14,031 ✭✭✭✭Johnboy1951


    unkel wrote: »
    Wireless won't cut it over that distance. As Silent Running said, you need to use standard network cable, you can easily and fairly cheaply get a long roll (they go up to hundreds of meters). You just "split" the cable in two tying the 4 wires from two of the pairs all together and the 4 wires from other two pairs together. Network cable is used because it doesn't pick up any interference from other cables / equipment

    I've the same issue myself wiring my new battery inverter (which works on the same principle as the Zappi), but not quite a 50m run :p

    Would it not provide better protection from interference to connect one wire from each pair together and the second wires from each together?

    Just wondering .....


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 343 ✭✭davidod1


    Thanks for all that. Great to get all that good and sound technical help. Very much appreciated.


  • Registered Users, Registered Users 2 Posts: 343 ✭✭davidod1


    unkel wrote: »
    What immersion diverter do you have? If you have the Eddi (from the same company as the Harvi and the Zappi you mention) then this should all work together out of the box

    Sorry, I forgot to come back re the immersion diverter. It's a Powerdiverter Model 1C. UK Made.

    Anyway, it looks like I'll be using two wired CT Clamps, one on the line from the fusebox to the meter and the other from the PV to the fusebox; presumably.


  • Registered Users, Registered Users 2 Posts: 7,822 ✭✭✭stimpson


    Just to clarify - you will need 2 clamps if you have PV. The Zappi comes with one, so you will need to order a second. One is to measure the power drawn from the mains, and the other is to measure the power drawn from the PV panels. The Zappi then controls how your car is charged based on these readings and your charge mode.

    The manual is up here and worth reading so you can advise your spark - https://myenergi.uk/wp-content/uploads/2017/10/zappi-manual-v1.2.pdf


  • Registered Users, Registered Users 2 Posts: 12,136 ✭✭✭✭KCross


    davidod1 wrote: »
    Is the CT Clamp wired back to the Zappi? If it is then it may be that I need the Harvi as the distance from the fuse board to the Zappi is about 50 meters. The Harvi might also be pushed as there is a building between the two locations as well as the distance.

    In nearly all cases wired is better than wireless but you have to balance that with how difficult it is to get the wires in. Only you will be able to tell whether wired is viable in your case.

    As an alternative you could also put the CT clamp in your meter box rather than the consumer unit. Is that per chance closer to the Zappi?

    The clamp can be extended a very long distance by any twisted pair wire, like Cat 5 or 6 for example. It doesn't need anything special.
    unkel wrote: »
    Wireless won't cut it over that distance. As Silent Running said, you need to use standard network cable, you can easily and fairly cheaply get a long roll (they go up to hundreds of meters). You just "split" the cable in two tying the 4 wires from two of the pairs all together and the 4 wires from other two pairs together. Network cable is used because it doesn't pick up any interference from other cables / equipment

    I've the same issue myself wiring my new battery inverter (which works on the same principle as the Zappi), but not quite a 50m run :p

    As I understand it, if you wire it it has to be screened cable not your bog standard Cat 5e cable. Screened cable is much more expensive. The 5m cable that comes with the CT Clamp is screened and if you extend it you need to use screened as well.

    If you dont use screened cable you run the risk of interference between the mains cable going to the Zappi and the CT cable which, presumably, will be running alongside each other.

    You dont want interference to cause the Zappi to be getting bad data from the CT Clamp. Its an integral part of how Zappi works so you need it accurate/reliable.


  • Registered Users, Registered Users 2 Posts: 7,822 ✭✭✭stimpson


    KCross wrote: »

    As I understand it, if you wire it it has to be screened cable not your bog standard Cat 5e cable. Screened cable is much more expensive. The 5m cable that comes with the CT Clamp is screened and if you extend it you need to use screened as well.

    If you dont use screened cable you run the risk of interference between the mains cable going to the Zappi and the CT cable which, presumably, will be running alongside each other.

    You dont want interference to cause the Zappi to be getting bad data from the CT Clamp. Its an important integration, not a nice-to-have piece of kit.

    The manual says:
    If there is a need to extend the sensor cable, twisted-pair cable like CAT5 or telephone cable must be used. DO NOT use mains
    cable, bell wire or speaker cable. It is important to use only twisted-pair cable to maintain signal integrity. The cable can be
    extended up to 100m.


  • Registered Users, Registered Users 2 Posts: 12,136 ✭✭✭✭KCross


    This is what I got from Zappi support as I specifically asked about extending it...
    The CT clamps come with 5 meters of cable connected and can be extended up to 100 meters with a Cat5 or Cat6 cable or good quality twisted pair cable
    There should not be a problem with the Ct cables in the same run as the live feed as the CT cable is screened and if using Cat5 or Cat6 cable that is screened also


    Running power cables next to network cables is generally not recommended. You can take the chance and try to keep them apart. I'd get screened cable.


  • Registered Users, Registered Users 2 Posts: 65,716 ✭✭✭✭unkel
    Chauffe, Marcel, chauffe!


    I'll use the standard cat5 cable that I have a 20m of lying around somewhere. I'd say 99% chance it will be fine ;)


  • Registered Users, Registered Users 2 Posts: 12,136 ✭✭✭✭KCross


    unkel wrote: »
    I'll use the standard cat5 cable that I have a 20m of lying around somewhere. I'd say 99% chance it will be fine ;)

    How will you know?
    When your consumer board melts?! ;)

    They didnt screen the CT cable that comes out of the box for the crack.


  • Registered Users, Registered Users 2 Posts: 65,716 ✭✭✭✭unkel
    Chauffe, Marcel, chauffe!


    KCross wrote: »
    How will you know?
    When your consumer board melts?! ;)

    :rolleyes:

    If the behaviour of the unit is erratic, it could be a sign of interference, but I'd say that's highly unlikely

    The previous owner of my inverter used standard cat 5 cable, it worked fine for him

    Could be different for a Zappi, but probably only in very challenging circumstances. Myenergi even sell wireless clamps (also way overpriced as all their other hardware), if they work then basic cat 5 cable will certainly work ;)

    I've tried wireless clamps from an Owl intuition monitor I picked up for GBP7 in both my outside meter box and on the AC output of my solar inverter and both work fine too. I'd bet money that cat 5 wired will be fine too.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 12,136 ✭✭✭✭KCross


    unkel wrote: »
    If the behaviour of the unit is erratic, it could be a sign of interference, but I'd say that's highly unlikely


    The previous owner of my inverter used standard cat 5 cable, it worked fine for him

    You're taking the "it works for me so it will work for everyone" approach.

    Thats bad advice, particularly when it comes to "high powered" electrics. A 3kW inverter isnt that relevant if it has an issue. A 7kW charger is a significant load to have malfunction.

    unkel wrote: »
    Could be different for a Zappi, but probably only in very challenging circumstances. Myenergi even sell wireless clamps (also way overpriced as all their other hardware), if they work then basic cat 5 cable will certainly work ;)

    I dont get your point here. Because they sell a wireless version then unscreened cable is OK.... there is no connection between those two things. I'm baffled by that one.

    unkel wrote: »
    I've tried wireless clamps from an Owl intuition monitor I picked up for GBP7 in both my outside meter box and on the AC output of my solar inverter and both work fine too. I'd bet money that cat 5 wired will be fine too.

    Sure I have several wireless clamps myself. What does that prove in the case of the Zappi?



    unscreened cat5 might work perfectly for you or any number of people but what about the one time it doesnt work for someone. Safety systems are in place for a reason, you shouldnt be advising a dodgy install.

    e.g. If someone has the cat5e cable lying on top of a bunch of live wires (not just one in your case) what happens then. Just because it works for you or 99% of cases doesnt mean you should condone people trying that.

    The reason I asked myenergi the question is because my RECI electrician said it to me, so he was recommending it and he asked that I confirm with myenergi and they duly confirmed that it is a screened clamp and should be extended with screened cable.

    You should take this stuff more seriously. I know you like your DIY electrics but seriously its not OK to be suggesting flouting their advice.


  • Registered Users, Registered Users 2 Posts: 65,716 ✭✭✭✭unkel
    Chauffe, Marcel, chauffe!


    For the record: I'm not advising anyone to install a Zappi in any other way than per the manufacturers spec

    I'm not installing a Zappi, I'm installing a battery inverter. From installation instructions I have seen online, people extend the provided (unshielded) cable for both clamps with standard unshielded cat 5 cable. That's what I'm going to do as well

    You should really stop accusing me of having unsafe and dangerous DIY electrics. This is false and malicious. First you did it about my inverter that you claimed would back feed the grid if the grid went down. This is not possible as all inverters have anti-islanding protection built in. Which at the time you didn't seem to understand. And now you suggest I might cause a fire by using unshielded cat 5 cable for my inverter clamps as per the manufacturers' instructions? :rolleyes:


  • Registered Users, Registered Users 2 Posts: 12,136 ✭✭✭✭KCross


    unkel wrote: »
    For the record: I'm not advising anyone to install a Zappi in any other way than per the manufacturers spec

    I'm not installing a Zappi, I'm installing a battery inverter. From installation instructions I have seen online, people extend the provided (unshielded) cable for both clamps with standard unshielded cat 5 cable. That's what I'm going to do as well

    We're talking about the Zappi, not inverters? This is the Zappi thread.

    Go right ahead with the Cat5 for your inverter.

    The clamp for the Zappi is used for a critical function (load limiting).

    Using a clamp for something like an Owl monitor is irrelevant as it doesnt matter if there is interference on that.

    unkel wrote: »
    You should really stop accusing me of having unsafe and dangerous DIY electrics. This is false and malicious. First you did it about my inverter that you claimed would back feed the grid if the grid went down. This is not possible as all inverters have anti-islanding protection built in. Which at the time you didn't seem to understand. And now you suggest I might cause a fire by using unshielded cat 5 cable for my inverter clamps as per the manufacturers' instructions? :rolleyes:

    I understood it fine, thanks.

    The context here was the Zappi and your comments made it look like you were condoning using unscreened cable for that. You've clarified that you are not and that you are referring to your inverter only... so that's fine. We are good.


  • Registered Users, Registered Users 2 Posts: 2,819 ✭✭✭Silent Running


    When I installed my Zappi clamp over a year ago the advice from Myenergi was to use any twisted pair cable. I had some 2 pair phone cable and some Cat 5 in the garage. I used the Cat 5. Just the first pair used (white/blue).

    It runs alongside the feed cable only for a couple of metres. I've had no issues with this setup. If I was transferring large amounts of important data across the cable I would have used screened cable. The clamp is only a sensor.


  • Registered Users, Registered Users 2 Posts: 12,136 ✭✭✭✭KCross


    When I installed my Zappi clamp over a year ago the advice from Myenergi was to use any twisted pair cable. I had some 2 pair phone cable and some Cat 5 in the garage. I used the Cat 5. Just the first pair used (white/blue).

    It runs alongside the feed cable only for a couple of metres. I've had no issues with this setup. If I was transferring large amounts of important data across the cable I would have used screened cable. The clamp is only a sensor.

    You dont think the data that that sensor is sending is important?

    Its not data just for info purposes (i.e. viewing in an app). Its key data to its successful operation to ensure you dont blow a fuse.

    The Zappi has to be able to sense load changes "instantly" so its monitoring that data 24/7.

    If it works for you, great. It wouldnt be for me. I'd rather follow their advice. The clamp in the box is screened so its not like its an after thought on their part.


  • Registered Users, Registered Users 2 Posts: 2,819 ✭✭✭Silent Running


    KCross wrote: »
    You dont think the data that that sensor is sending is important?

    Its not data just for info purposes (i.e. viewing in an app). Its key data to its successful operation to ensure you dont blow a fuse.

    The Zappi has to be able to sense load changes "instantly" so its monitoring that data 24/7.

    If it works for you, great. It wouldnt be for me. I'd rather follow their advice. The clamp in the box is screened so its not like its an after thought on their part.

    The first sentence of my post. :)


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 7,822 ✭✭✭stimpson


    KCross wrote: »
    You dont think the data that that sensor is sending is important?

    Its not data just for info purposes (i.e. viewing in an app). Its key data to its successful operation to ensure you dont blow a fuse.

    The Zappi has to be able to sense load changes "instantly" so its monitoring that data 24/7.

    If it works for you, great. It wouldnt be for me. I'd rather follow their advice. The clamp in the box is screened so its not like its an after thought on their part.

    I don’t think screened should be absolutely necessary. Twisted pair is designed so interference on each cable in the pair cancels itself out. It is unlikely to cause an issue. In addition, Cat6 is capable of carrying 10Gb/s over 55m. I doubt the cable is pushing anywhere close to 1Mb/s so even if there is severe interference it’s probably not enough to prevent a low bandwidth signal. I would be very surprised if there were any issues from this as long as the twists are maintained all the way along the cable.

    In the event that there is an issue, then I’m sure the Zappi is designed to fail safe and not cause a catastrophic failure.


  • Registered Users, Registered Users 2 Posts: 12,136 ✭✭✭✭KCross


    The first sentence of my post. :)

    Fair enough. We got different advice from the same company then! :)

    I posted exactly what they sent me.


  • Registered Users, Registered Users 2 Posts: 12,136 ✭✭✭✭KCross


    stimpson wrote: »
    I don’t think screened should be absolutely necessary.

    Absolutely necessary... clearly not since people have it working without it.

    stimpson wrote: »
    Twisted pair is designed so interference on each cable in the pair cancels itself out. It is unlikely to cause an issue.

    In the event that there is an issue, then I’m sure the Zappi is designed to fail safe and not cause a catastrophic failure.

    You'd hope so.
    But clearly interference is a concern since the cable they provide is screened. They could have scrimped on cable and provided a much cheaper one if screening was irrelevant.


  • Registered Users, Registered Users 2 Posts: 9,474 ✭✭✭TheChizler


    stimpson wrote: »
    I don’t think screened should be absolutely necessary. Twisted pair is designed so interference on each cable in the pair cancels itself out. It is unlikely to cause an issue. In addition, Cat6 is capable of carrying 10Gb/s over 55m. I doubt the cable is pushing anywhere close to 1Mb/s so even if there is severe interference it’s probably not enough to prevent a low bandwidth signal. I would be very surprised if there were any issues from this as long as the twists are maintained all the way along the cable.

    In the event that there is an issue, then I’m sure the Zappi is designed to fail safe and not cause a catastrophic failure.
    It's an analog, not digital signal, the amplitude of which should correspond to the current measured by the clamp.

    The current moving through the mains cable induces a voltage across the coil in the clamp, which the Zappi unit measures. Running a length of cable with current flowing in it next to a wire will absolutely induce some voltage and interfere with the intended voltage on the wire. The clamp is just a wire coil next to the cable you're measuring current in, there's no fundamental difference between the clamp and the wire and what they're doing, only the number of turns in the coil (many vs 1).

    I've seen over 100 V induced in a disconnected lighting circuit which must have run next to a live circuit, it's not dangerous to people or the equipment or anything as it can't sustain the voltage across a load, but if you're measuring with a high impedance sensor (like the Zappi is) it will mess up your reading.

    It being twisted pair should cancel most of the interference out, but not all. I'd use shielded outdoor data cable to be safe.

    Best case, there's no effect.
    Second best case, the interference is positive and a higher voltage is measured than the real value, and the Zappi limits the charge prematurely.
    Worst cast, the interference is negative and a lower than true voltage is measured, the Zappi doesn't limit the charge when the electric shower and hob is on and overloads your supply.


  • Registered Users Posts: 1,770 ✭✭✭Nedved85


    Just an update - My hub arrived last week, set it up over the weekend, bit of a convoluted/ trial and error job to be honest.

    They most certainly could improve/simplify the hub setup.