Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Hi all! We have been experiencing an issue on site where threads have been missing the latest postings. The platform host Vanilla are working on this issue. A workaround that has been used by some is to navigate back from 1 to 10+ pages to re-sync the thread and this will then show the latest posts. Thanks, Mike.
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

Home heating automation

1394042444594

Comments

  • Registered Users, Registered Users 2 Posts: 1,874 ✭✭✭garo


    Thanks. Apologies for the next question. How do I wire it? I found some vague instructions on automatedhome but also caution on not to use this if you don't have a bypass loop as the pump will be pushing against closed valves and that might damage the pump.


  • Registered Users, Registered Users 2 Posts: 6,908 ✭✭✭deezell


    garo wrote: »
    Thanks. Apologies for the next question. How do I wire it? I found some vague instructions on automatedhome but also caution on not to use this if you don't have a bypass loop as the pump will be pushing against closed valves and that might damage the pump.
    That is a minor issue, circulation pumps are inertia vane type, like a fan, it doesn't build up much pressure in static flow. When the flow is totally closed, all TRVs closed and HW valve closed, then there is no path alright. Your system probably could do with a bypass loop, or an open radiator to act as the same, such as a towel rail, especially one thats on a gravity path from the boiler with the pump off. This would give some relief to the residual hot water in the boiler jacket. If you have the boiler stat set to regulate the boiler to say 65°, when it cuts there's unlikely to be enough residual heat in the jacket baffles to boil it too 100°. A timer on the pump is only of use if there's an open path for pumped or gravity flow, so running the pump is not going to solve this problem which probably doesn't exist. Try turning down the general boiler flow temperature, no need to have it scalding, unless you have rooms that need the radiators 'hopping" to heat, but that would be a radiator size or room insulation problem. Your boiler will be more efficient if it's run a few degrees cooler, return water will be cooler and heat transfer higher.

    There's a complicated wiring diagram for the relay on the site, but basically it's a mains triggered relay with a double pole single contact switch, which you would supply with permanent live in and connect the pump live to the relay live out, which is a mirror of the boiler live trigger plus an adjustable delay.


  • Registered Users, Registered Users 2 Posts: 1,874 ✭✭✭garo


    Thanks. So I had the thermostat knob at a bit over 5 which is 77C according to this document. I have since turned it down to 3 which is 66C.
    The document recommends a lower setting for the summer when only HW is needed anyway. Thanks for the prompt deezell. Hope this will resolve the issue and I won't need to worry about the pump overrun. Thanks for the wiring explanation as well. But I expect I won't need it now as the solution you suggest is much simpler.


  • Registered Users, Registered Users 2 Posts: 1,874 ✭✭✭garo


    So I dug into this a bit more and posting it here in case it helps someone else. The Evohome has a "Hot Water Overrun" feature that allows the hot water valve to stay open for a set time. So if you have a boiler that has a pump overrun or put in a delay timer on the pump AND you have a system where there is a valve to the HW, you can set the overrun timer on the evohome and it will leave the hot water valve open for that amount of time after the boiler has stopped firing. I checked today and it works. After the boiler stops, the hot water valve closes after the specified delay.

    I may yet go for that delay timer switch deezell.


  • Registered Users, Registered Users 2 Posts: 6,908 ✭✭✭deezell


    garo wrote: »
    So I dug into this a bit more and posting it here in case it helps someone else. The Evohome has a "Hot Water Overrun" feature that allows the hot water valve to stay open for a set time. So if you have a boiler that has a pump overrun or put in a delay timer on the pump AND you have a system where there is a valve to the HW, you can set the overrun timer on the evohome and it will leave the hot water valve open for that amount of time after the boiler has stopped firing. I checked today and it works. After the boiler stops, the hot water valve closes after the specified delay.

    I may yet go for that delay timer switch deezell.

    I had been reading a blog about Evohome to find more information about this. There were lots of references to percentage cycling and the like for CH, and complaints about residual cycling, where the Evohome would give the boiler one extra blast after its calling stat had reached set point. The basis of the complaints were that in these cases the room temperature would rise a further few degrees above setpoint, and posters found their system hysteresis too great, plus or minus 2-3°, which caused too hot/ too cold heating pattern. There was no solution offered in the blog, but it got me thinking that perhaps this was caused by a boiler overrun, but effective only if the rad TRVs / CH zone valve were shut and there was an open sink such as a towel rail or an open HW valve. If the posters had just an open rad system without smart TRVs and no CH zone valve of course the rads would heat in this instance. This problem may also have been to do with the Opentherm controlled boilers used by the posters.

    Your boiler is a hard on/off job, but it has only a very small boiler surface as it is a gas boiler, with a small volume heat exchanger, so not a lot of residual heat in there to dissapate. The question now is how does the boiler fire for a HW only request from the evohome?
    Is your HW demand to the boiler directly from the Evohome relay, the same one that calls the boiler for CH? Such a call would facilitate HW only if the system was full TRV, so that CH flow is cut while HW valve is opened. The evohome relay has a seperate HW On Switched Live terminal, this is what is connected to the HW valve to open it.
    Normally, the HW valves's own aux relay is used to fire the boiler, ensuring the boiler doesn't fire for HW until the valve is opened, as a safety feature, and ensuring that a SL from a HW terminal doesn't cause the rads to heat by reverse opening a CH zone valve. (This would occur if the CH and HW SLs were just combined at the boiler.) This of course means that any call to the HW valve, including an overrun, would open the valve, close the relay and fire the boiler, so the overrun in this case would be pointless, nothing more than a short HW timing cycle.
    So it depends on how your Evohome was wired. If the HW valve is passively opened by the evohome HW relay terminal , but the SL to the boiler is a common one for both CH and HW, then this overrun feature could be used to open the HW valve without boiler firing, leaving just the little matter of getting the circulation pump only to spin during this time.
    If the above wiring scheme is true, and IF the HW zone valve has an unused boiler call relay, and IF this relay is a two pole relay with NO ( grey wire) and NC ( white wire) terminals, this relay could be used to control the SL source to the pump. By diverting the boiler SL to the pump via the valve NC terminal, and splitting the HW valve SL call ( brown wire) across to the NO terminal, then connecting the pump to the Common (orange wire) terminal, the pump will always circulate for a HW call or a CH/HW boiler call, but the boiler will only fire when the boiler call is on.
    This solution will work if the HW valve is Not used to fire the boiler, and if it has an unused relay with the NC white wire terminal, many just have the grey and orange wires.
    There's a bit to chew on there, so start examining how your Evohome boiler calls are made, for CH and HW.
    Here's a typical 2 port valve wiring with NC terminal

    images?q=tbn:ANd9GcTJnlfn3LmbqJ4pWfOvREUmxkxgM88YAWZ-nkrJqJJeuQ&s


  • Registered Users, Registered Users 2 Posts: 1,874 ✭✭✭garo


    My setup is similar to Figure 4 on page 46 of this document with a major difference highlighted below.

    I have a full TRV set up and 1 valve to control HW. Prior to the installation of the Evohome it was a single zone system.

    The call for the boiler comes from the Evohome controller - same for CH and HW. I have a pair of BDR91 relays listening to the controller, one controlling the boiler firing + pump and the other the HW valve. This is because the HW valve is close to the HW cylinder and far from the boiler so it wasn't possible to wire the HW valve to the same relay that connects to the boiler. So the two relays both receive all the controller calls wirelessly but act slightly differently.

    When a call comes for CH, only the boiler+pump relay fires. When it comes for HW both the boiler+pump relay and the HW valve relay activate with the latter switching off x minutes after the boiler relay switches off where x is the hot water overrun parameter.

    When both HW and CH are called for simultaneously, it is possible that both the HW valve and some TRVs are open. In this case there is no prioritization and both share the boiler heat.

    Hope that clarifies the setup. I understand that whether just adding a delay timer between the relay and the pump would work depends on what the HW relay does on a CH only firing. If after a CH only call, the HW valve does not open during the boiler overrun period then simply adding a delay before the pump won't work. The TRVs would have closed before the pump stops. OTOH, if the HW valve opens on boiler shutoff for the overrun period then adding a simple delay timer would work.


  • Registered Users, Registered Users 2 Posts: 6,908 ✭✭✭deezell


    garo wrote: »
    ........OTOH, if the HW valve opens on boiler shutoff for the overrun period then adding a simple delay timer would work.

    This is the key. If the above occurs then a timer on the pump is required, or else the HW SL from the relay to the HW valve can be used to supply the pump via the valves aux relay. This would require some wiring though, which you indicated was awkward with the distance between the boiler/pump and the HW valve.


  • Registered Users, Registered Users 2 Posts: 1,874 ✭✭✭garo


    Thanks. When my understanding of the situation is the same as yours, I know I am on the right track.


  • Registered Users Posts: 28 scurran19


    I'm looking for a little help so I can have an informed conversation with a plumber / electrician about getting a smart thermostat.
    I have a Firebird-S 90-120 oil boiler heating both my radiators and hot water and the timer on the boiler has gone. Its a simple old style timer where you pull the pins out, something like this https://heatingpartswarehouse.co.uk/product/firebird-super-q-timeclock/

    The problem is everything I read about smart thermostats has the thermostat on a wall in a room with a control panel. Mine is just a knob on the boiler. Hence I don't know if what I am thinking is even possible.

    In an ideal world I would replace the timer and thermostat on the boiler with a smart thermostat with Alexa integration where I can set the schedule but I don't know if that's possible with my set up.

    For further info there are just 2 zones in the house, upstairs and downstairs and I don't need to be able to control them individually at the moment. It would be nice to be able to heat the water independently of the radiators but I have a feeling that would be a change beyond what I am looking at here and isn't essential.

    All help is appreciated!


  • Moderators, Sports Moderators, Regional Midwest Moderators Posts: 24,006 Mod ✭✭✭✭Clareman


    The thermostat in the room is really just to turn the heat on or off rather than control the amount of heat coming out of it, so if you have the heat set to 22 and the heat in the room is 21 the boiler will come on and when the thermostat hits 22 the boiler will turn off again. I've the Netamo on a Firebird burner and it's a great job, but I only have 1 zone and no separate water


  • Advertisement
  • Registered Users Posts: 6,185 ✭✭✭championc


    scurran19 wrote: »
    I'm looking for a little help so I can have an informed conversation with a plumber / electrician about getting a smart thermostat.
    I have a Firebird-S 90-120 oil boiler heating both my radiators and hot water and the timer on the boiler has gone. Its a simple old style timer where you pull the pins out, something like this https://heatingpartswarehouse.co.uk/product/firebird-super-q-timeclock/

    The problem is everything I read about smart thermostats has the thermostat on a wall in a room with a control panel. Mine is just a knob on the boiler. Hence I don't know if what I am thinking is even possible.

    In an ideal world I would replace the timer and thermostat on the boiler with a smart thermostat with Alexa integration where I can set the schedule but I don't know if that's possible with my set up.

    For further info there are just 2 zones in the house, upstairs and downstairs and I don't need to be able to control them individually at the moment. It would be nice to be able to heat the water independently of the radiators but I have a feeling that would be a change beyond what I am looking at here and isn't essential.

    All help is appreciated!

    Think of any Smart Thermostat as an "external to the boiler" on/off switch. So anyone with a boiler with a similar level of (lack of) control can add a smart thermostat, which will then take the place of the original on/off switch (or be wired in parallel). Of course, you'll need to get wires run from the boiler to where you propose to locate the Smart Thermostat


  • Registered Users, Registered Users 2 Posts: 6,908 ✭✭✭deezell


    Or just use a smart stat with wireless connectivity to a relay located at the boiler, which is pretty much all of them. Hive, Drayton Wiser, Nest, Honeywell are wireless by default. Tado is wired but with optional wireless ext Kit. Netatmo available wired or wireless. Other non smart or 'less" smart options are EPH ember, Climote, hub controller and other internet connectable cheap stats on Amazon, many of Chinese origin.


  • Registered Users, Registered Users 2 Posts: 4,238 ✭✭✭digiman


    Are there any products out there that will digitally display and record the temperature of the water in your hot water tank?


  • Registered Users, Registered Users 2 Posts: 6,908 ✭✭✭deezell


    digiman wrote: »
    Are there any products out there that will digitally display and record the temperature of the water in your hot water tank?

    This, up to 85°C.
    https://www.amazon.co.uk/dp/B0773MX8BH/ref=cm_sw_r_cp_apa_i_LylgFb8X3HPZN


  • Registered Users, Registered Users 2 Posts: 4,238 ✭✭✭digiman


    deezell wrote: »

    How will this know the temperature of the water inside the tank though?


  • Registered Users, Registered Users 2 Posts: 6,908 ✭✭✭deezell


    digiman wrote: »
    How will this know the temperature of the water inside the tank though?

    By attaching the probe to the outside metal surface of 5he cylinder. If you have one if the more expensive double skinned insulated tanks, you'll need something different with a probe sensor to fit into the provided insert tube on the tank.
    Look up the Sonoff switch/stat/thermostat device. You can read the temp on an app, and it can act as a stat as well, to fire the boiler. I'm not sure if the app can log or record on going temperature over time, (this is what you want?), but Sonoff can be picked up by all sorts of smart tech and apps, some of the readers here might have done this already.


  • Registered Users Posts: 653 ✭✭✭Irish_peppa


    Has anyone here with a Nest Smart Thermostat know if you can actually get any decent information from it ie: You used your central heating last week for 5 hours . There seems to be no proper usage menu. I get a silly email at the end of each month talking about "leafs" and how many leafs i saved. My god would be better if you had this infomation:
    December 2019 Central Heating Usage 60 Hours
    December 2020 Central Heating Usage 45 Hours
    its a fantastic device but there is no real data that you can use to manage your usage


  • Registered Users, Registered Users 2 Posts: 6,908 ✭✭✭deezell


    Yes, but referencing unquantified tree bits rather than Joules or Kilowatt hours is much more appealing to the Eco warrior brigade, who queue up to buy at the mere mention of these organic credentials. Maybe they should include a years supply of quinoa or chia with each stat.


  • Registered Users, Registered Users 2 Posts: 533 ✭✭✭chuck eastwood


    Someone hasn't had their coffee yet 😅


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 6,908 ✭✭✭deezell


    No, I'm out of the non GM organic fairtrade no airmiles gender neutral non cancelled coffee, so I'll just have to drink the ozone layer destroying stuff. Ahhh!!!!, there goes another rain forest.


  • Registered Users, Registered Users 2 Posts: 2,025 ✭✭✭blindsider


    Hi All,

    I think this has been covered before, but I can't seem to find the post(s)

    I have:

    - Vokera Mynute Gas boiler + 3 zones: Upstairs, downstairs and HW
    - Solar for hot water only
    - A standard Horstmann Controller
    - Decent internet and wifi via Virgin Media

    I'd like to be able to do the following:

    - Control the heating and HW via an app - time of day for On/Off etc
    - Boost the heating and HW for 1 hour via an app (it's enough to heat the house)
    - I'd like to see the temp of the HW in the tank - but I'd live without it

    I don't need:

    - to control heating by room
    - to adjust thermostats or rads etc by room

    I'd appreciate a recommendation for a cost-effective solution which would do the basics

    Note: we are looking at changing energy supplier too (electricity and gas)

    Thanks for reading!


  • Registered Users, Registered Users 2 Posts: 6,908 ✭✭✭deezell


    blindsider wrote: »
    Hi All,

    I think this has been covered before, but I can't seem to find the post(s)

    I have:

    - Vokera Mynute Gas boiler + 3 zones: Upstairs, downstairs and HW
    - Solar for hot water only
    - A standard Horstmann Controller
    - Decent internet and wifi via Virgin Media

    I'd like to be able to do the following:

    - Control the heating and HW via an app - time of day for On/Off etc
    - Boost the heating and HW for 1 hour via an app (it's enough to heat the house)
    - I'd like to see the temp of the HW in the tank - but I'd live without it

    I don't need:

    - to control heating by room
    - to adjust thermostats or rads etc by room

    I'd appreciate a recommendation for a cost-effective solution which would do the basics

    Note: we are looking at changing energy supplier too (electricity and gas)

    Thanks for reading!

    Last thing first, energy supplier upgrades are confined to a single zone. Somehow through lies and statistics they can claim whopping EU grant funds on your behalf by installing the most basic single zone stat controller. There's even cases of people with 2 heating zones having their system reverted to one, and these chancers then claim ( on your behalf), that your home in now more energy efficient. Rant over.
    What you need is a 3 zone smart controller, to directly wire in place of your existing Horstman. This will have wireless stats to position in the respective zones, ( usually Hall and landing, or living and landing.) Setting on/off with smart app control systems is more about setting low temperature times and warmer temperature times than just on and off. You'll get used to this. The HW control is just timing, aided by a mechanical cylinder stat if you already have one
    The tidiest system for this at the moment is the Drayton Wiser Kit 3. Replacement controller, a few minutes to wire in place of the Horstman, and two wireless stats you pair to the controller and position in the zones. Job done.
    Taking a reading of cylinder temperature is not high on the agenda of smart controllers, but a few high end options are available, such as the Honeywell Evohome system. You really just want a mechanical stat on the cylinder which will interrupt the HW timer slot when the water hits target temperature.


  • Registered Users, Registered Users 2 Posts: 2,025 ✭✭✭blindsider


    Brilliant!!!

    That's exactly the kind of answer I was looking for!

    I'll go and investigate the Drayton - where to buy etc.

    Thanks a mill!

    I'll update if/when we do it.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,603 Mod ✭✭✭✭2011


    deezell wrote: »
    Last thing first, energy supplier upgrades are confined to a single zone. Somehow through lies and statistics they can claim whopping EU grant funds on your behalf by installing the most basic single zone stat controller. There's even cases of people with 2 heating zones having their system reverted to one, and these chancers then claim ( on your behalf), that your home in now more energy efficient. Rant over.

    Point well made.


  • Registered Users Posts: 6,185 ✭✭✭championc


    I bought a whole Tado suite and personally installed them. Can I personally apply for anything ?


  • Advertisement
  • Registered Users Posts: 310 ✭✭Ethereal Cereal


    championc wrote: »
    I bought a whole Tado suite and personally installed them. Can I personally apply for anything ?

    You need to get the work carried out by a registered contractor
    https://hes.seai.ie/GrantProcess/ContractorSearch.aspx


    I am changing my regular boiler to a combi boiler. Each rad will get a wifi contolled trv. I asked the plumber could I claim this back on the SEI grant, and he said there was too many checks involved, etc etc, and that Id nearly want to spend €2k to get the €700 back.

    Anyone know if this is right?


  • Registered Users, Registered Users 2 Posts: 6,908 ✭✭✭deezell


    You need to get the work carried out by a registered contractor
    https://hes.seai.ie/GrantProcess/ContractorSearch.aspx


    I am changing my regular boiler to a combi boiler. Each rad will get a wifi contolled trv. I asked the plumber could I claim this back on the SEI grant, and he said there was too many checks involved, etc etc, and that Id nearly want to spend €2k to get the €700 back.

    Anyone know if this is right?

    Sadly, yes. Only the utility companies can install the bare minimum and get the dough without you seeing it. It's no surprise that the quote for a grant aided installation seems to be increased by the grant and then more. I recall seeing quotes for single Nest of €1200, after grant. I had to sit down to recover.


  • Registered Users Posts: 174 ✭✭CiaranTheGreat


    Has anyone here gotten a Beok thermostat to work with sky broadband? I had it working with virgin which I have since cancelled and I can’t get it working with the new sky broadband. I’ve logged into the modem and turned the 5ghz off as that was an issue with the virgin broadband but it didn’t work

    Any help would be great


  • Registered Users, Registered Users 2 Posts: 6,908 ✭✭✭deezell


    Has anyone here gotten a Beok thermostat to work with sky broadband? I had it working with virgin which I have since cancelled and I can’t get it working with the new sky broadband. I’ve logged into the modem and turned the 5ghz off as that was an issue with the virgin broadband but it didn’t work

    Any help would be great

    At a guess you might need to do a factory reset on the stat, as it's possibly looking for the Mac address of the old router, rather than IP. With these devices you often have to start by connecting to them via phone app with the stat as the Wi-Fi source, disconnecting your phone from the router wifi, then using the app through the stat wifi to connect to the router. The stat would need to be in 'New from box' mode, hence a reset. There might be a little button, or a key combination. What model is it?


  • Registered Users, Registered Users 2 Posts: 6,908 ✭✭✭deezell




  • Advertisement
  • Registered Users Posts: 174 ✭✭CiaranTheGreat


    deezell wrote: »
    At a guess you might need to do a factory reset on the stat, as it's possibly looking for the Mac address of the old router, rather than IP. With these devices you often have to start by connecting to them via phone app with the stat as the Wi-Fi source, disconnecting your phone from the router wifi, then using the app through the stat wifi to connect to the router. The stat would need to be in 'New from box' mode, hence a reset. There might be a little button, or a key combination. What model is it?

    It’s the boy-313 model. There is a key combo thing you do to reset it before connecting but it always fails. There is no option to connect to it as a WiFi source. I have even connected to my wife’s phone as a hotspot to see would that work if I tried connecting it to that but no joy.


  • Registered Users Posts: 174 ✭✭CiaranTheGreat


    deezell wrote: »

    Unfortunately no. It’s a different model to mine but the basis of it is correct. I have done the reset actions for my model but still nothing. It’s a head melter.


  • Registered Users, Registered Users 2 Posts: 6,908 ✭✭✭deezell


    Unfortunately no. It’s a different model to mine but the basis of it is correct. I have done the reset actions for my model but still nothing. It’s a head melter.

    I've had a look at the instructions
    http://www.tkarena.it/wp-content/uploads/2018/01/BOT-313WIFI-Series-Boiler-Thermostat-Instruction.pdf

    All I can suggest is that you delete the Beok app from your phone and reinstall it. Then setup the device exactly as per the instructions, youll need to see the 'twinkling' Wi-Fi symbol. It doesn't say in the instructions, but you would normally at this point disconnect your phone from the house Wi-Fi, and search for the Beok as a Wi-Fi access point, a and connect to it. Then open the Beok app and proceed with the next step. If you successfully add the Beok to your home Wi-Fi, don't forget to connect your phone back to home Wi-Fi. This is generally how these devices work, a direct connection to your phone until the device is configured to your network. It may be that the app handles some of this Wi-Fi source changing.


  • Registered Users, Registered Users 2 Posts: 6,908 ✭✭✭deezell


    Actually reading the instructions, it seem that the app maintains connection with your router while in direct client mode with the Beok, and I note the additional instructions in the event of band conflict. If your Wi-Fi router is not broadcasting at 2.4Ghz, then you will have to configure the router if possible to this band or dual band ( 2.4 SSID can be set to a different name so the app can be programmed to connect to 2.4 , ignoring 5). All this of course depends on getting to the stat Wi-Fi direct to phone phase. Log onto your router also just to check if the stat is currently seen by the router. Did you replicate your old SSID and password into the new router?


  • Registered Users Posts: 174 ✭✭CiaranTheGreat


    deezell wrote: »
    Actually reading the instructions, it seem that the app maintains connection with your router while in direct client mode with the Beok, and I note the additional instructions in the event of band conflict. If your Wi-Fi router is not broadcasting at 2.4Ghz, then you will have to configure the router if possible to this band or dual band ( 2.4 SSID can be set to a different name so the app can be programmed to connect to 2.4 , ignoring 5). All this of course depends on getting to the stat Wi-Fi direct to phone phase. Log onto your router also just to check if the stat is currently seen by the router. Did you replicate your old SSID and password into the new router?

    Oh my god I never thought about that. That could work. I still have the virgin modem so I’ll have a go tonight and change the name. Although because you do a reset before trying to connect it to the WiFi ,it may not even remember the old network and not work but it’s worth a shot


  • Registered Users Posts: 174 ✭✭CiaranTheGreat


    deezell wrote: »
    Actually reading the instructions, it seem that the app maintains connection with your router while in direct client mode with the Beok, and I note the additional instructions in the event of band conflict. If your Wi-Fi router is not broadcasting at 2.4Ghz, then you will have to configure the router if possible to this band or dual band ( 2.4 SSID can be set to a different name so the app can be programmed to connect to 2.4 , ignoring 5). All this of course depends on getting to the stat Wi-Fi direct to phone phase. Log onto your router also just to check if the stat is currently seen by the router. Did you replicate your old SSID and password into the new router?

    Tried the duplicate name of the old router which didn’t work. I am genuinely at a loss. I genuinely haven’t a breeze as to why it isnt working. There is no WiFi signal from the thermostat to connect to but there is no mention of that in the instructions.

    I’m half tempted to just buy a new different stat


  • Registered Users, Registered Users 2 Posts: 3,398 ✭✭✭xckjoo


    Tried the duplicate name of the old router which didn’t work. I am genuinely at a loss. I genuinely haven’t a breeze as to why it isnt working. There is no WiFi signal from the thermostat to connect to but there is no mention of that in the instructions.

    I’m half tempted to just buy a new different stat


    Did you get the reset working so that you can see the "quick and frequent twinkling" WiFi icon?


  • Registered Users Posts: 174 ✭✭CiaranTheGreat


    xckjoo wrote: »
    Did you get the reset working so that you can see the "quick and frequent twinkling" WiFi icon?

    Yeah it only fails at the trying to connect to the network part


  • Registered Users, Registered Users 2 Posts: 3,398 ✭✭✭xckjoo


    Yeah it only fails at the trying to connect to the network part
    I'd guess you're falling victim to an aging wireless chip that doesn't quite implement the WiFi standards right. It should technically still work but I don't know if you'll find easy step-by-step instructions and there's a chance it's just not going to work for whatever reason.


    I did find someone with a similar issue here and they managed to get it working. Looks like they switched their router to use and older WiFi standard, got the stat connected and then switched the WiFi back to something more modern. Might be worth a try


  • Registered Users Posts: 6,185 ✭✭✭championc


    It's quite possible that the wifi must be on 2.4ghz, on modes 802.11b or g (not n). Most phones, tablets and laptops will use 5ghz, but all devices will support 2.4ghz on 802.11b. b is the slowest speed.

    The likes of wireless thermostats could well use 434mhz radio signals


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 6,908 ✭✭✭deezell


    championc wrote: »
    It's quite possible that the wifi must be on 2.4ghz, on modes 802.11b or g (not n). Most phones, tablets and laptops will use 5ghz, but all devices will support 2.4ghz on 802.11b. b is the slowest speed.

    The likes of wireless thermostats could well use 434mhz radio signals

    It does, check the instructions I linked. Your phone would also need to be searching for 2.4G.


  • Registered Users, Registered Users 2 Posts: 1,874 ✭✭✭garo


    Are you able to get it to connect to your phone after the reset?

    For the router, make sure you enable b/g/n on the 2.4GHz frequency. Only having the n mode may cause an issue. And newer routers have n mode only turned on by default.


  • Registered Users, Registered Users 2 Posts: 6,908 ✭✭✭deezell


    Try the following:
    Download a Wi-Fi analyser app to your phone, such as, er, 'Wi-Fi Analyser",
    Go into settings on your phone, select your current Wi-Fi network, and click 'Forget'. Also, turn off mobile data.
    Using the Wi-Fi Analyser app, see if you can discover the 2.4Ghz signal from the Stat while it's in Twinkly mode.
    Use the app to select this signal as your AP.
    Now run the Beok app and see does it connect to the device.
    If success,
    Then configure your router as a 2.4 only, all types. Give it a unique SSID and pass.
    Configure the stat via the Beok app to use this AP
    Now finish the installation, and reconnect the phone to the 2.4 AP of the router, (use the WiFi analyser for this also if the phone doesn't discover it and add to the wifi networks list. and check for connection to the app.

    Finally, you can configure the routers 5Ghz AP and turn it on, for faster connections, and select this for your phone.The stat should stay connected via 2.4.


  • Registered Users Posts: 174 ✭✭CiaranTheGreat


    Hi guys,

    Thanks a million for your help. I got a whiskey ready and was planning on spending the night reading through the replies and going through every step outlined by you guys again. We got sky q in today and the box required me to use a WPS button on the router (which even though is quite obvious now, took ages to find) to connect the box to the WiFi.

    Couldn’t hurt to press the button while i tried to sync the phone to the thermostat and low and behold it worked. Couldn’t believe it and kept turning it on and off on my phone to make sure that I wasn’t dreaming.


    I’ve no idea what that magic button does but it did it.


    Thanks a million for the help, I will put money in the charity box at the shop tomorrow in your honour.

    Thanks a million


  • Registered Users, Registered Users 2 Posts: 6,908 ✭✭✭deezell


    "I’ve no idea what that magic button does...."

    It accepts for a short period any connections being sought by devices without the device having the id or passkey of the router. It would also connect via the appropriate band, so it seems your router picked up the connection request directly from the Beok, gave it the id and passkey and configured it to the 2.4Ghz band, without you having to intervene via the phone app to supply these crucial parameters. Happy days, and a new trick learned.
    I've had a few sticky moments trying to join Lenovo devices to my network using it's device configuration app. I can't even remember if I may have pressed the wps router button in frustration, but that could be it. We should be thanking you.


  • Registered Users Posts: 174 ✭✭CiaranTheGreat


    I’m that happy that it’s working that when my wife asked me to put the heating on I didn’t even complain that it is still August


  • Registered Users, Registered Users 2 Posts: 284 ✭✭strangel00p


    Hi there,
    I have a traditional gas boiler and would be interested in getting a Nest system installed for home automation.



    I know zilch about heating and plumbing and have no idea how to install this.


    So would anyone have a very rough ball park figure on how much it would cost for plumber to install this Nest thermostat for a 3 bed house with 7 basic radiators? None of the radiators have thermostats installed.


    Thanks


  • Registered Users Posts: 6,185 ✭✭✭championc


    Hi there,
    I have a traditional gas boiler and would be interested in getting a Nest system installed for home automation.



    I know zilch about heating and plumbing and have no idea how to install this.


    So would anyone have a very rough ball park figure on how much it would cost for plumber to install this Nest thermostat for a 3 bed house with 7 basic radiators? None of the radiators have thermostats installed.


    Thanks

    As I understand it, a Nest is just a more intelligent room stat, so since your system has no radiator thermostats, you will have a room stat in the hall or sitting room, and the nest would simply replace that - so a quick DIY job

    I think it only gets complicated if you had a room stat upstairs too, or zone valves, but I stand to be corrected


  • Administrators, Computer Games Moderators, Sports Moderators Posts: 32,401 Admin ✭✭✭✭✭Mickeroo


    championc wrote: »
    As I understand it, a Nest is just a more intelligent room stat, so since your system has no radiator thermostats, you will have a room stat in the hall or sitting room, and the nest would simply replace that - so a quick DIY job

    I think it only gets complicated if you had a room stat upstairs too, or zone valves, but I stand to be corrected

    You also need to replace your heating controls with the heat link for the thermostat to work. If the system is zoned then you need two stats (and two heat links).

    Electric Ireland were doing an offer where you can get one installed for €130 if you switch to them.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 6,908 ✭✭✭deezell


    Hi there,
    I have a traditional gas boiler and would be interested in getting a Nest system installed for home automation.



    I know zilch about heating and plumbing and have no idea how to install this.


    So would anyone have a very rough ball park figure on how much it would cost for plumber to install this Nest thermostat for a 3 bed house with 7 basic radiators? None of the radiators have thermostats installed.


    Thanks
    Do you have a wall thermostat? Do you have more than one? Do you have a controller box with programable heating times, and possibly programable Hot water times.
    Do you have a HW cylinder in a hot press, or does you HW come directly from the gas boiler on demand. The above will determine the ease with which a Neat stat can be connected.


Advertisement