Anyone familiar with Gerkros external oil boilers

  • 18-11-2015 10:21PM
    #1
    Registered Users, Registered Users 2 Posts: 76 ✭✭


    Has anyone got a GERKROS external oil boiler or anyone familiar with them and would you recommend them or not?
    Model is a Gem top cleaner 60/95 - house it will heat is 6 rads plus 2 bath rail rads.


Comments

  • Registered Users, Registered Users 2, Paid Member Posts: 12,948 ✭✭✭✭Dtp1979


    Derby1 wrote: »
    Has anyone got a GERKROS external oil boiler or anyone familiar with them and would you recommend them or not?
    Model is a Gem top cleaner 60/95 - house it will heat is 6 rads plus 2 bath rail rads.

    Is this a boiler you're looking to purchase?


  • Registered Users, Registered Users 2 Posts: 76 ✭✭Derby1


    yes it is. I have a stove with back boiler in a cottage. I have all the pipework in place for an external oil boiler as backup for when the house is unoccupied and nobody about to set a fire to keep the place dry.


  • Registered Users, Registered Users 2, Paid Member Posts: 12,948 ✭✭✭✭Dtp1979


    Derby1 wrote: »
    yes it is. I have a stove with back boiler in a cottage. I have all the pipework in place for an external oil boiler as backup for when the house is unoccupied and nobody about to set a fire to keep the place dry.

    For a start the boiler is way too big for 6 rads.
    Gerkros boilers aren't the best. Plus it's a non condensing boiler so your not supposed to fit them. If its second hand, then no decent installer will touch it to be honest


  • Registered Users, Registered Users 2 Posts: 152 ✭✭Walter Becket


    It will do what you want. But it's a cheap second hand boiler. Made by a manufacturer that's out of business because they didn't make great boilers.


  • Registered Users, Registered Users 2, Paid Member Posts: 12,948 ✭✭✭✭Dtp1979


    It will do what you want. But it's a cheap second hand boiler. Made by a manufacturer that's out of business because they didn't make great boilers.

    Plus it's massively oversized


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 76 ✭✭Derby1


    I miscounted - there are seven rads all doubles plus the 2 towel rails (the 5 foot ladder type) plus we have a cylinder of hot water which when he house is occupied would supply 2 bathrooms and the usual in the kitchen inc washing machine.

    Why do you consider the GERKROS unreliable - what sort of issues do you find with them.

    I must confess I am more familiar with the Grant 90 boiler we have at home. We are considering replacing this and installing it in the cottage. That's probably too big as well but it will be effectively free. This has similar BTU so you would probably say it is too big as well but surely better oversized than undersized. What we replace the Grant with is probably a topic for another thread.


  • Registered Users, Registered Users 2, Paid Member Posts: 12,948 ✭✭✭✭Dtp1979


    Derby1 wrote: »
    I miscounted - there are seven rads all doubles plus the 2 towel rails (the 5 foot ladder type) plus we have a cylinder of hot water which when he house is occupied would supply 2 bathrooms and the usual in the kitchen inc washing machine.

    Why do you consider the GERKROS unreliable - what sort of issues do you find with them.

    I must confess I am more familiar with the Grant 90 boiler we have at home. We are considering replacing this and installing it in the cottage. That's probably too big as well but it will be effectively free. This has similar BTU so you would probably say it is too big as well but surely better oversized than undersized. What we replace the Grant with is probably a topic for another thread.

    No oversized is not better. It's much worse. Your boiler will short cycle, using more fuel and making an inefficient boiler even more inefficient.
    If you've a grant 50-90 then get it set to 50. That's really as small as you can go with an oil boiler.


  • Registered Users, Registered Users 2 Posts: 152 ✭✭Walter Becket


    You can get someone to put a small nozzle in it to make the heat output suitable for the house. I didn't say geckos oil boilers are unreliable. They are reliable.


  • Registered Users, Registered Users 2 Posts: 76 ✭✭Derby1


    Thanks for the replies - if they are out of business then its a no from me.

    Our Grant is a 90 Mark II so not an option to set lower. At home here it runs 11 rads. How much oversized is it for the cottage? I know you would need room sizes, outside walls etc for a proper calculation, but what btu should I be aiming for considering I have NO outside walls - the house is entirely drylined and insulated and house contains 1 living room, 1 kitchen, 3 bedrooms, 1 en-suite and 1 shower room and is approx. 70m2.

    Maybe it is a false economy to be buying second hand not only for the obvious wear and tear reasons but also for the fact I would be getting a new efficient condensing boiler. I wonder how much more efficient are they?


  • Registered Users, Registered Users 2, Paid Member Posts: 12,948 ✭✭✭✭Dtp1979


    Derby1 wrote: »
    Thanks for the replies - if they are out of business then its a no from me.

    Our Grant is a 90 Mark II so not an option to set lower. At home here it runs 11 rads. How much oversized is it for the cottage? I know you would need room sizes, outside walls etc for a proper calculation, but what btu should I be aiming for considering I have NO outside walls - the house is entirely drylined and insulated and house contains 1 living room, 1 kitchen, 3 bedrooms, 1 en-suite and 1 shower room and is approx. 70m2.

    Maybe it is a false economy to be buying second hand not only for the obvious wear and tear reasons but also for the fact I would be getting a new efficient condensing boiler. I wonder how much more efficient are they?

    If highly insulated then your gonna need as small a boiler as possible. Firebird go down to 40k but I'd rather fit a grant @50


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 152 ✭✭Walter Becket


    Derby1 wrote: »
    Thanks for the replies - if they are out of business then its a no from me.

    Our Grant is a 90 Mark II so not an option to set lower. At home here it runs 11 rads. How much oversized is it for the cottage? I know you would need room sizes, outside walls etc for a proper calculation, but what btu should I be aiming for considering I have NO outside walls - the house is entirely drylined and insulated and house contains 1 living room, 1 kitchen, 3 bedrooms, 1 en-suite and 1 shower room and is approx. 70m2.

    Maybe it is a false economy to be buying second hand not only for the obvious wear and tear reasons but also for the fact I would be getting a new efficient condensing boiler. I wonder how much more efficient are they?
    Add your reply here.

    I serviced a grant non condensing today efficiency was 87%. A new grant vortex is above 97%.


  • Registered Users, Registered Users 2, Paid Member Posts: 12,948 ✭✭✭✭Dtp1979


    Add your reply here.

    I serviced a grant non condensing today efficiency was 87%. A new grant vortex is above 97%.

    Your talking about combustion efficiency. That's totally different.


  • Closed Accounts Posts: 1,590 ✭✭✭agusta


    Derby1 wrote: »
    Thanks for the replies - if they are out of business then its a no from me.

    Our Grant is a 90 Mark II so not an option to set lower. At home here it runs 11 rads. How much oversized is it for the cottage? I know you would need room sizes, outside walls etc for a proper calculation, but what btu should I be aiming for considering I have NO outside walls - the house is entirely drylined and insulated and house contains 1 living room, 1 kitchen, 3 bedrooms, 1 en-suite and 1 shower room and is approx. 70m2.

    Maybe it is a false economy to be buying second hand not only for the obvious wear and tear reasons but also for the fact I would be getting a new efficient condensing boiler. I wonder how much more efficient are they?

    15 to 18 percent at least, provided the boiler is sized correctly


  • Registered Users, Registered Users 2 Posts: 4,052 ✭✭✭jimf


    Add your reply here.

    I serviced a grant non condensing today efficiency was 87%. A new grant vortex is above 97%.


    what was the fg temp with the 87% eff


  • Moderators, Home & Garden Moderators Posts: 6,707 Mod ✭✭✭✭Wearb


    jimf wrote: »
    what was the fg temp with the 87% eff
    Getting dangerously low and probably under-fired to boot, would be my guess.


  • Registered Users, Registered Users 2 Posts: 76 ✭✭Derby1


    fg?


  • Moderators, Home & Garden Moderators Posts: 6,707 Mod ✭✭✭✭Wearb


    Derby1 wrote: »
    fg?

    Flue gas


  • Registered Users, Registered Users 2 Posts: 152 ✭✭Walter Becket


    what was the fg temp with the 87% eff[/quote]

    I don't know I don't keep a printout for myself I've enough paper to keep for the tax man.


  • Registered Users, Registered Users 2 Posts: 8,560 ✭✭✭K.Flyer


    I don't know I don't keep a printout for myself I've enough paper to keep for the tax man.

    If you can remember the date you did the service, then you can find the data in your FGA's stored logs.


  • Moderators, Home & Garden Moderators Posts: 6,707 Mod ✭✭✭✭Wearb


    what was the fg temp with the 87% eff

    I don't know I don't keep a printout for myself I've enough paper to keep for the tax man.[/QUOTE]

    I fill all that info on my service sheet and would have that info on the duplicate. Also -at the weekends- I download the FGA logs onto customer folders on my PC. Seems a lot of work at first, but it doesn't take too long. Its very handy to have a look through before the next visit.

    Anyway we're just making the point that you can go too low with FG temps and also that you shouldn't go below the lowest firing settings set by the manufacturer. Doing that can produce higher eff. on the fga, but you are really just shortchanging the customer.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 152 ✭✭Walter Becket


    For the first few years I did record my work carefully , I won't go into it but basically customer info got into the real world and I asked myself why am I keeping this info? I have a responsibility under data protection to keep customers info confidential and only to keep info that I need. Now I am careful what info I keep, where i keep it and won't keep it without a good reason. Once bitten twice shy.


  • Registered Users, Registered Users 2, Paid Member Posts: 12,948 ✭✭✭✭Dtp1979


    For the first few years I did record my work carefully , I won't go into it but basically customer info got into the real world and I asked myself why am I keeping this info? I have a responsibility under data protection to keep customers info confidential and only to keep info that I need. Now I am careful what info I keep, where i keep it and won't keep it without a good reason. Once bitten twice shy.

    Not being smart but how would fga details have anything to do with data protection?


  • Registered Users, Registered Users 2 Posts: 152 ✭✭Walter Becket


    Dtp1979 wrote: »
    For the first few years I did record my work carefully , I won't go into it but basically customer info got into the real world and I asked myself why am I keeping this info? I have a responsibility under data protection to keep customers info confidential and only to keep info that I need. Now I am careful what info I keep, where i keep it and won't keep it without a good reason. Once bitten twice shy.

    Not being smart but how would fga details have anything to do with data protection?

    Well I run my business my way and am not telling you how run yours . My rule is don't keep info I don't need.


  • Registered Users, Registered Users 2 Posts: 152 ✭✭Walter Becket


    We're getting off topic Derby1 wants to decide new or 2nd hand. I say new if you can afford it 2nd hand if it's costing almost nothing but plan to replace it.
    I fitted a 2nd hand one when I built the house because I had no money left. I should have made a plan to replace it and saved up but instead it wasted oil for 10 years before I did. It was a cast iron Italian boiler worse than a Gercros.


  • Registered Users, Registered Users 2 Posts: 4,052 ✭✭✭jimf


    walter the reason I asked about the fg temp is as im sure you know if the boiler is not up to working temp you can get a false efficiency reading looks good giving the printout to the customer

    serviced a se warmflow boiler today eff reading 90% at 110 dg when up to working temp of 205dg efficiency levelled out at 84%


  • Registered Users, Registered Users 2 Posts: 152 ✭✭Walter Becket


    jimf wrote: »
    walter the reason I asked about the fg temp is as im sure you know if the boiler is not up to working temp you can get a false efficiency reading looks good giving the printout to the customer

    serviced a se warmflow boiler today eff reading 90% at 110 dg when up to working temp of 205dg efficiency levelled out at 84%

    I know where you're coming from.