  • Registered Users Posts: 5,422 ✭✭✭just do it


    sas wrote: »
    Yes, it's up and running and going well so far
    sas wrote: »
    Also, I should have underlined that the HRV isn't yet operational.
    sas wrote: »
    We're airing the house out minimally to avoid cooling it down while also trying to avoid moisture issues. I've still got 2 x 8 inch diameter holes in my gable walls fully open to outside.

    So SAS I'd say your house is performing extremely well considering neither the UFH nor the HRV are operational! I believe what bit of passive heat you have has to supply ~300m2? An incremental approach with the same weather conditions would be interesting i.e. HRV for 5 days and then the UFH from solar thermal. (Did I just wish the same weather conditions continue for at least another 10 days:confused::rolleyes:)
    sas wrote: »
    Steady as she goes for now.
    As always, thanks for the updates:)


  • Registered Users Posts: 1,282 ✭✭✭sas


    just do it wrote: »
    That's a large celtic tiger apartment you've got in that one area alone:D. I wonder would such an apartment heat comfortably in 30mins?

    Last night it was up to 20 - 21 degrees within an hour of turning on the rad.
    Once it got turned off though, it was down to 16 after about an hour also. Felt really cold actually.
    Yet this morning, it was 15 and felt much warmer. I'm figuring there is a psychological effect, 16 degrees when it's dark and wet outside feels colder than 15 degrees on a bright sunny morning.

    The rest of the house must be drawing the heat out of the heated room once the rad is turned off, he said hopefully!
    just do it wrote: »
    Sas - how long does this area hold the heat? This is surely where the difference is given you've not had much passive heat thus far to heat the place.

    Not long enough yet.

    I also got to experience the joy of a warm (not hot) shower this morning as 2 days of crap weather resulted in us exhausting the heat reserve. Tank was down to 27 after showers today.


  • Registered Users Posts: 1,282 ✭✭✭sas


    just do it wrote: »
    So SAS I'd say your house is performing extremely well considering neither the UFH nor the HRV are operational! I believe what bit of passive heat you have has to supply ~300m2? An incremental approach with the same weather conditions would be interesting i.e. HRV for 5 days and then the UFH from solar thermal. (Did I just wish the same weather conditions continue for at least another 10 days:confused::rolleyes:)

    Hopefully it's good early signs. I'm upping my timescale plan for the oil backup. I'd like to have it in place asap.

    Will report back again in a few weeks.


  • Registered Users Posts: 1,282 ✭✭✭sas


    We wanted a contemporary feel for our stairs. We already had a concrete stairs in situ so our options revolved around the hand rail and cladding of steps.

    I would have preferred an entirely glass hand rail but it was proving cost prohibitive.

    This is what I came up with by mixing a few themes.

    The cut outs in the pic will be filled with glass. The timber is oak. It's not quite finished but looking good so far.


  • Subscribers Posts: 41,284 ✭✭✭✭sydthebeat


    just make sure the glass is tempered and toughened :)

    looks great though


  • Advertisement
  • Registered Users Posts: 1,691 ✭✭✭fclauson


    sas wrote: »
    Hopefully it's good early signs. I'm upping my timescale plan for the oil backup. I'd like to have it in place asap.

    Will report back again in a few weeks.

    I guess it will take time for the thermal mass to warm all the way through - but once this happens then you should be in business


  • Registered Users Posts: 458 ✭✭kboc


    fclauson wrote: »
    I guess it will take time for the thermal mass to warm all the way through - but once this happens then you should be in business

    any further progress or pictures with your project FC?

    Thanks
    K


  • Registered Users Posts: 5,422 ✭✭✭just do it


    sas wrote: »
    Hopefully it's good early signs. I'm upping my timescale plan for the oil backup. I'd like to have it in place asap.

    Will report back again in a few weeks.

    SAS
    I've been thinking about where you are at the moment and depending on how much work is required to commission the HRV this may prove a more cost effect short term solution. This cold spell is unseasonal and with the current length of day the daylight should be providing ample passive heat given your glazing. I assume the 2 large holes you metioned will be closed at the time of HRV commissioning. With these open your airtightness is poor and therefore what passive heat gain there is is disappearing out these holes and the building mass isn't getting a chance to capture and store the passive heat.

    Theoretically I would have thought airtightness and HRV would heat your house until at least October and possibly December. Your secondary heat source (oil) would come into play then. Commissioning the oil heating ahead of the HRV and airtightness will mean your wasting oil.

    I'm open to correction on this postulate!


  • Registered Users Posts: 1,282 ✭✭✭sas


    just do it wrote: »
    Theoretically I would have thought airtightness and HRV would heat your house until at least October and possibly December. Your secondary heat source (oil) would come into play then. Commissioning the oil heating ahead of the HRV and airtightness will mean your wasting oil.

    I'm open to correction on this postulate!

    This is all true but I never said I was doing oil before HRV, just that oil would be sooner than planned. Planned was Aug\Sept.

    HRV commissioning was yesterday, all went smoothly.

    House is feeling a little warmer all the time but the weather has been milder too so could be related to that.

    Solar has been doing a great job this week in heating our 1000 litre tank. The bottom of the tank was 64 degrees on Tuesday evening and the middle was 76. We've no stat facility at the top rather annoyingly. Next few days will be interesting to see how we cope with duller weather.


  • Subscribers Posts: 41,284 ✭✭✭✭sydthebeat


    sas wrote: »
    This is all true but I never said I was doing oil before HRV, just that oil would be sooner than planned. Planned was Aug\Sept.

    HRV commissioning was yesterday, all went smoothly.

    House is feeling a little warmer all the time but the weather has been milder too so could be related to that.

    Solar has been doing a great job this week in heating our 1000 litre tank. The bottom of the tank was 64 degrees on Tuesday evening and the middle was 76. We've no stat facility at the top rather annoyingly. Next few days will be interesting to see how we cope with duller weather.

    what temp are you feeding into your UFH??


  • Advertisement
  • Registered Users Posts: 1,282 ✭✭✭sas


    sydthebeat wrote: »
    what temp are you feeding into your UFH??

    I'm not feeding anything right now. Weather is too unpredictable for me to start consistently pushing heat in UFH without me also having something to back up the solar i.e. need to avoid cold showers. Stratification should pretty much avoid this happening but I've not tested that yet.

    On Tuesday night I did run the UFH for a period purely to use the excess heat in the bottom of the tank. I ran it at 35 degrees.

    It wasn't running for long enough to make any perceivable difference but it will all help with warming up the floor slab etc. I believe.


  • Registered Users Posts: 800 ✭✭✭esox28


    best of luck sas with the new home stead

    what area of solar thermal have you for the 1000ltr buffer and what dhw volume have you and is the dhw cylinder seperate to the buffer or tank in tank.

    (cant seem to find that) :rolleyes:


  • Registered Users Posts: 1,282 ✭✭✭sas


    esox28 wrote: »
    best of luck sas with the new home stead

    what area of solar thermal have you for the 1000ltr buffer and what dhw volume have you and is the dhw cylinder seperate to the buffer or tank in tank.

    (cant seem to find that) :rolleyes:

    Thanks!

    Solar aperture area is 9.72 m2.

    My tank is 1 big combined buffer\dhw tank, there isn't even a seperating plate.

    The water in the tank never leaves the tank for DHW, the heat is extracted from the tank using a heat exchanger.

    For heating etc. the water in the tank is directly connected to the UFH circuit.

    The solar heats the tank via another coil at the bottom.

    The stratification appears to work as the bottom of the tank was 22 degress this morning and the middle was 56.

    When DHW is called for, hot water is taken from the top of the tank, passes through the heat exchanger to actually heat the required water and then the cooler water is readded to the tank at the bottom.

    This make sense?


  • Registered Users Posts: 800 ✭✭✭esox28


    yea think i get it, so the dhw when called for at the hot tap it is run through at the lower point and out at the top of big long coil through the buffer? or is there an external plate heatexchanger transfering the heat across the dhw and heating waters.

    did your solar system stagnate today? 23*c at home and solar tank full at 12pm today. 2 panels and 280ltr cylinder.


  • Registered Users Posts: 1,282 ✭✭✭sas


    esox28 wrote: »
    yea think i get it, so the dhw when called for at the hot tap it is run through at the lower point and out at the top of big long coil through the buffer? or is there an external plate heatexchanger transfering the heat across the dhw and heating waters.

    did your solar system stagnate today? 23*c at home and solar tank full at 12pm today. 2 panels and 280ltr cylinder.


    There's an external heat exchanger. So as you said, fresh cold water in at the bottom of the heat exchanger, fresh hot water out at the top.

    The system had stagnated when I got home at 6pm.
    The panels were reading 135 and the bottom of the tank was 57.
    The mid tank temp was 76.

    The UFH circuit pump had been run for 30mins continuously at lunch time to dump some of the heat.

    So all in all it was a very impressive solar day. I ran the UFH again for 45 mins tonight just to free capacity for tomorrow.

    The middle of the tank is still reading 72 degrees.


  • Registered Users Posts: 800 ✭✭✭esox28


    what volumes of fresh cold water are is stored in the external h exchanger,
    could you possibly post a pic or pm the product name.

    heard of a german company about 1 year ago working on at 'jelly' type substrate which would be capible of storing large volumes of heat energy when the sun was out for periods of time and then the energy cuold br extracted to form a heating circuit at night to run steam genertors producing electricity.
    havent seen any thing on this 'jelly' product since, with the domestic solar collectors in mind wouldent it be great to store the solar energy generated over the last few days and use it to get us over the long winter months.


  • Registered Users Posts: 4,748 ✭✭✭Do-more


    There is a Dutch company who have patents on solutions that could develop into viable inter-seasonal stores in the next few years but they are not fully commercialised yet.

    Best not to derail this thread with off-topic discussion, I have PM'd you with some further details.

    invest4deepvalue.com



  • Registered Users Posts: 1,282 ✭✭✭sas


    esox28 wrote: »
    what volumes of fresh cold water are is stored in the external h exchanger,
    could you possibly post a pic or pm the product name.

    I'm not sure I follow. There isn't any cold water stored as such in the h exchanger. I'll pm on the tank details.
    esox28 wrote: »
    heard of a german company about 1 year ago working on at 'jelly' type substrate which would be capible of storing large volumes of heat energy when the sun was out for periods of time and then the energy cuold br extracted to form a heating circuit at night to run steam genertors producing electricity.
    havent seen any thing on this 'jelly' product since, with the domestic solar collectors in mind wouldent it be great to store the solar energy generated over the last few days and use it to get us over the long winter months.

    There is a storage tank that a friend of mine is using which has both water and a wax within it. The wax changes state to absorb energy, it has a higher storage capacity than water is my basic understanding.

    Interseasonal storage is proving cost prohibitive if you go with large insulated tanks of water based on a study I read. If you go for specialist jellsy etc. I can only imagine that it's ridiculously cost prohibitive.


  • Registered Users Posts: 4,748 ✭✭✭Do-more


    My frame arrived this morning at 7am.

    WP_000271.jpg

    What? More insulation...

    WP_000300.jpg

    Last section of wall goes in with a little gentle persuasion...

    WP_000306.jpg

    I haven't been on site for a few hours, but the lads hope to be done with the crane this evening, so I should have a few more photos later.

    invest4deepvalue.com



  • Registered Users Posts: 4,748 ✭✭✭Do-more


    Time and the 25 degree heat beat the lads in the end but they put in a huge days work of 13 and a half hours flat out all the way.

    This photo isn't from the very end of the day, they just have one gable to swing in tomorrow.

    WP_000325.jpg

    invest4deepvalue.com



  • Advertisement
  • Registered Users Posts: 458 ✭✭kboc


    Do-more wrote: »
    Time and the 25 degree heat beat the lads in the end but they put in a huge days work of 13 and a half hours flat out all the way.

    This photo isn't from the very end of the day, they just have one gable to swing in tomorrow.

    WP_000325.jpg

    Do-more,
    I must say it looks well, and impressive in the efficientcy in which it was errected.

    Any info on the wall build-up in your new project and why you choose this over other wall build-up's?

    thanks
    K


  • Registered Users Posts: 4,748 ✭✭✭Do-more


    kboc wrote: »
    impressive in the efficientcy in which it was errected.

    Sure 'tis hard to beat the Galway lads!

    Although they are much happier with the weather today, 12 C and soft rain, much more like what their used to than the 25C and blazing sunshine yesterday.

    kboc wrote: »
    Any info on the wall build-up in your new project and why you choose this over other wall build-up's?


    You might see from some of the photos that the walls come in a closed panel from the factory here in Sweden with the windows and doors pre-installed.

    There is calcium silicate board on the outside then a ventilation gap and then bitumen paper then 145mm mineral wool batts then plasterboard which is redundant.

    Next week I will start on putting up another 145mm of mineral wool batts

    IMG_1659resize.jpg

    Then the airtightness layer and then a 70mm stud insulated with more mineral wool and then the plasterboard.

    The main reason for going this way was one of the supplier having the experience, cost and material. The main alternative for passive or low energy houses here is to build with massive slabs of aerated concrete up to 475mm thick but that didn't appeal to me.

    invest4deepvalue.com



  • Registered Users Posts: 1,282 ✭✭✭sas


    Do-more wrote: »
    Sure 'tis hard to beat the Galway lads!
    .

    I was wondering why it all looked so familiar.

    House building in Sweden must be expensive when you would choose them under the cost category!


  • Registered Users Posts: 4,748 ✭✭✭Do-more


    sas wrote: »
    I was wondering why it all looked so familiar.

    House building in Sweden must be expensive when you would choose them under the cost category!

    When I was building my last time in Ireland in 2001 I had a look at their price list then and thought they were very expensive. But I now realise that I wasn't comparing like for like and considering how much is included and the quality of what you are getting I now consider them to be very fair value.

    The biggest difficulty I have at the moment is working around all the materials that are in the house. In terms of the structure of the house the only significant thing that isn't included is the stairs, they have supplied almost everything else required including the HRV and ducting. I will have very little in the way of materials to purchase to finish the house.

    And in terms of quality, my engineer who is overseeing the build is a master carpenter by trade originally and he considers the house to be top of the league in build quality.

    As for building costs here in Sweden when we were organising our 10 year building failures insurance I got quotes from the 2 major companies who do that cover here. One of them was significantly higher than the other and when we queried it one had taken my detailed estimated price of 2.2 million SEK (about €245,000 at today's rate) and the other had disregarded it and used a price from their database of prices, they estimated that by average Swedish prices our 215m2 house would cost us a minimum of 4.3 million SEK to build (about €488,000 at today's rate).

    I was discussing prices with the Irish lads today and they reckon that what I have to pay for the plumbing is almost three times the current rate in Ireland and the electrics is double the Irish rate, but I am snookered as for the insurance I must have locally certified trades doing that work, I can't fly lads in.

    The cost for applying the render system is 50% higher than bringing lads over even allowing for air fares and B&B's but that could turn pear shaped if the weather was bad and they ended up sitting around here for some while so I will probably have to just swallow the Swedish price on that as well.

    To keep the overall cost in check I will do most of the internal work myself and the overall cost will be about the same as if I weren't having to lift a finger in Ireland.

    I'd imagine (but only guessing) that the spec I am building to here would probably reach certified levels for Irish weather data and I think that allowing for all costs from a green field to moving in furniture at €1140/m2 is probably fair value.

    invest4deepvalue.com



  • Registered Users Posts: 4,748 ✭✭✭Do-more


    Should be weather tight in another hour or two...

    004.jpg

    002.jpg

    invest4deepvalue.com



  • Registered Users Posts: 5,422 ✭✭✭just do it


    Do-more wrote: »
    Should be weather tight in another hour or two...

    004.jpg

    002.jpg
    Great stuff do-more, it must be a great feeling to see it suddenly appear before your eyes after all the planning


  • Registered Users Posts: 4,748 ✭✭✭Do-more


    just do it wrote: »
    Great stuff do-more, it must be a great feeling to see it suddenly appear before your eyes after all the planning

    It is indeed great to see it go up. The lads have put in a huge weeks work, minimum 12 hour days and they should get finished with there bit by lunch time on Saturday.

    The other side of the coin is looking at the amount of work that I have taken on myself to finish the inside fills me with dread! There will be a lot of long weeks for me if we are to get in for Christmas as we hope.

    invest4deepvalue.com



  • Registered Users Posts: 166 ✭✭about2build


    Cpngrats Do-More . Hollowcore being craned in today for me...looking forward to it. Still cant establish how to post photos so if anyone knows pm rather than diluting thread


  • Registered Users Posts: 4,748 ✭✭✭Do-more


    The lads got finished with their bit of the build at 10am this morning and have a 8 hour trip up the west coast of Sweden to do it all again with another house on Monday.

    Couldn't be happier with the job they have done.

    008resize.jpg

    005resize.jpg