Rads Hot Upstairs but Rads Cold Downstairs

  • 01-03-2012 05:17PM
    #1
    Registered Users, Registered Users 2 Posts: 271 ✭✭


    Hi all

    Last night I came home and the radiators upstairs were hot but all 4 downstairs were cold.

    So today I bled all the rads- no air at all only water came out. Then turned the upstairs thermostat to 0 and turned downstairs to 30 degress to try force the heat down. But it didn't work.

    Went outside to look at boiler (firebird) and pump (superpump). I turned the bled screw in the pump and only water came out. I gave it a few gentle taps but still didn't work. The housing on pump is hot and the pipes going in and coming out of pump are hot.

    Any ideas appreciated!!!

    Thanks for reading and would be grateful for any help


Comments

  • Registered Users, Registered Users 2 Posts: 3,952 ✭✭✭aujopimur


    Is the pump running? if it is and you have zones, the motorised valve may be faulty. You can check the mot. valve by using the manual lever on the back of the actuator.


  • Registered Users, Registered Users 2 Posts: 271 ✭✭Ryan T


    aujopimur wrote: »
    Is the pump running? if it is and you have zones, the motorised valve may be faulty. You can check the mot. valve by using the manual lever on the back of the actuator.
    Not sure if the pump is running - tried to listen for it. Is there any other way to check if it's running ?

    Thanks


  • Registered Users, Registered Users 2 Posts: 5,009 ✭✭✭meercat


    " when pump is running remove the large screw in the front of the pump , you should get a small trickle of water , then insert a flat head screwdriver into where the screw came out if you can't feel it spinning try turning it with the screwdriver"


    previous post from sullzz


  • Registered Users, Registered Users 2 Posts: 271 ✭✭Ryan T


    meercat wrote: »
    " when pump is running remove the large screw in the front of the pump , you should get a small trickle of water , then insert a flat head screwdriver into where the screw came out if you can't feel it spinning try turning it with the screwdriver"


    previous post from sullzz
    Thanks

    It's a bit awkward to get at as the bleed screw is not on the front but on side of pump - water keeps coming out and I can't see if I am getting screwdriver all the way in


  • Registered Users, Registered Users 2 Posts: 5,009 ✭✭✭meercat


    Ryan T wrote: »
    Thanks

    It's a bit awkward to get at as the bleed screw is not on the front but on side of pump - water keeps coming out and I can't see if I am getting screwdriver all the way in

    put a large screwdriver into the pump(metal part)
    put your ear to screwdriver
    get someone to turn pump on and off
    dont confuse the sound of the boiler firing up


    problem may be the motorised valve too(as aujopimur says)
    get someone to switch the thermostat on and off while you listen to the spring loaded action of the motorised valve
    there is a manual over-ride lever on it,if you can try that


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 271 ✭✭Ryan T


    meercat wrote: »
    Ryan T wrote: »
    Thanks

    It's a bit awkward to get at as the bleed screw is not on the front but on side of pump - water keeps coming out and I can't see if I am getting screwdriver all the way in

    put a large screwdriver into the pump(metal part)
    put your ear to screwdriver
    get someone to turn pump on and off
    dont confuse the sound of the boiler firing up


    problem may be the motorised valve too(as aujopimur says)
    get someone to switch the thermostat on and off while you listen to the spring loaded action of the motorised valve
    there is a manual over-ride lever on it,if you can try that

    Getting a bit technical for me !!!

    Might call in a plumber

    Thanks for help


  • Registered Users, Registered Users 2 Posts: 271 ✭✭Ryan T


    Ryan T wrote: »
    meercat wrote: »
    Ryan T wrote: »
    Thanks

    It's a bit awkward to get at as the bleed screw is not on the front but on side of pump - water keeps coming out and I can't see if I am getting screwdriver all the way in

    put a large screwdriver into the pump(metal part)
    put your ear to screwdriver
    get someone to turn pump on and off
    dont confuse the sound of the boiler firing up


    problem may be the motorised valve too(as aujopimur says)
    get someone to switch the thermostat on and off while you listen to the spring loaded action of the motorised valve
    there is a manual over-ride lever on it,if you can try that

    Getting a bit technical for me !!!

    Might call in a plumber

    Thanks for help


    Got my dad over for a look at system today and he figured out it's a motorised valve.
    He switched to manual and the downstairs heated up.
    Do I have to replace it or can I leave it on manual.
    Would I use more oil if I didn't replace. Would it be an expensive job to replace the valve

    Thanks for help


  • Registered Users, Registered Users 2 Posts: 5,009 ✭✭✭meercat


    check the roomstat is turned up


    you can leave the valve manually on (this may use more oil)
    sometimes the action of manually switching the valves will resolve the problem
    try releasing the manual switch and it should springload back to the closed position
    then turn it back on electrically

    if this doesnt work,then manually over-ride the motorised valve again


  • Registered Users, Registered Users 2 Posts: 271 ✭✭Ryan T


    meercat wrote: »
    check the roomstat is turned up


    you can leave the valve manually on (this may use more oil)
    sometimes the action of manually switching the valves will resolve the problem
    try releasing the manual switch and it should springload back to the closed position
    then turn it back on electrically

    if this doesnt work,then manually over-ride the motorised valve again

    Meercat thanks for reply

    Do you mean put motorised valve back on auto and see if the problem is resolved. But before i do that try it on manual with the room stat turned up to a higher temp( to see if it still works on manual at a higher temp )

    Thanks for your help


  • Registered Users, Registered Users 2 Posts: 5,009 ✭✭✭meercat


    1 put mv back to auto
    2 turn room stat up full
    3 turn heating off and listen for springloading to return to off position
    4 wait one minute and turn heating back on(check mv opens up again)

    if the mv does not operate then return the mv to the manual position


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 271 ✭✭Ryan T


    meercat wrote: »
    1 put mv back to auto
    2 turn room stat up full
    3 turn heating off and listen for springloading to return to off position
    4 wait one minute and turn heating back on(check mv opens up again)

    if the mv does not operate then return the mv to the manual position

    And would it be ok to leave on manual for good and not replace with a new mv

    Thank you meetcat


  • Registered Users, Registered Users 2 Posts: 5,009 ✭✭✭meercat


    your heating system will be more efficient with a replacement
    if you are handy you may do this yourself( no plumbing necessary,just electric)


  • Registered Users, Registered Users 2 Posts: 271 ✭✭Ryan T


    meercat wrote: »
    your heating system will be more efficient with a replacement
    if you are handy you may do this yourself( no plumbing necessary,just electric)
    Just looking at it - there is no isolation valves ? Would I not have to drain system etc


  • Registered Users, Registered Users 2 Posts: 5,009 ✭✭✭meercat


    not generally
    what type of mv is it
    the electric part usually unscrews without going near the plumbing(2 screws normally and then the motor will release from the valve)
    no water at all
    have you re tested the mv


  • Registered Users, Registered Users 2 Posts: 271 ✭✭Ryan T


    meercat wrote: »
    not generally
    what type of mv is it
    the electric part usually unscrews without going near the plumbing(2 screws normally and then the motor will release from the valve)
    no water at all
    have you re tested the mv
    No gone out for a few pints !!!
    Will try it tomorrow - dad said it was a cheap mv and not a brand he knew and that it was a sealed unit so couldn't replace a part. He knows a lot more than me !!

    Thanks meercat - will try test tomorrow and get back to you for advice


  • Registered Users, Registered Users 2 Posts: 5,009 ✭✭✭meercat


    homer.jpg


  • Registered Users, Registered Users 2 Posts: 271 ✭✭Ryan T


    Can hear a buzzing noise from mv when I turn heating on and off( when switched to auto)
    Does this mean it's working

    Thanks