vokera boiler not coming on

  • 20-10-2010 03:08PM
    #1
    Closed Accounts Posts: 644 ✭✭✭


    hi all i cant get my boiler to come on (it is a mynute 20HE), it had not been used for a few months.
    Initially there was no pressure, but sorted this by opening feed valve in hot press for a while.
    So now there is pressure now but when I turn on boiler there is a lot of groaning and croaking (!) -like water is trying to get through- heard coming from the boiler but it soon cuts out.

    I bled air from the boiler using the screw on top but still no joy- any advice greatly appreciated! (Ps i know there are other vokera threads here which i have read but couldn't find anything)


Comments

  • Registered Users, Registered Users 2 Posts: 145 ✭✭Plombier


    Loosen two small phillips head screws above switches and gauges and the panel will drop down inside you will see a circulating pump with a large chrome screw in front of it remove this screw completely (it might drip some water thats ok) then insert a flat screwdriver until it engages the slot turn this a few times to free the pump, this should work.


  • Closed Accounts Posts: 644 ✭✭✭filthymcnasty


    cheers tried that and shes working now- thanks a lot