Thickness of Insulated Slab Relative to Cavity Insulation

  • 28-11-2009 8:35pm
    #1
    Closed Accounts Posts: 136 ✭✭


    HI,

    I have seen on boards before that the insulated slab should not be bigger than the cavity insulation. I have also seen that the insulated slab should only be half of the cavity insulation.

    Any thougths?


Comments

  • Closed Accounts Posts: 5,433 ✭✭✭sinnerboy


    This is a rule of thumb - a guide in the absence of a design calculation using condensation risk software . Some , not all , insulation providers have this software and will provide calculations.

    The aim is to keep the inner leaf as warm as possible because if it cools you condensation can form there . So most of the insulation must be located towards the external .