Solis inverter settings

1252627282931»

Comments

  • Registered Users, Registered Users 2 Posts: 1,165 ✭✭✭TimHorton




  • Registered Users, Registered Users 2 Posts: 4,184 ✭✭✭pureza


    I’m not going to search Google for YouTube videos you want,you can do that yourself and I don’t mean to be facetious in saying that

    They exist



  • Registered Users, Registered Users 2 Posts: 1,165 ✭✭✭TimHorton




  • Moderators, Home & Garden Moderators Posts: 7,743 Mod ✭✭✭✭graememk


    I don't think it's a setting issue. Possibly a peaking issue. Is it a 5kW inverter?



  • Registered Users, Registered Users 2 Posts: 285 ✭✭olympicweights


    @Dr Robert

    Last year I was getting this below on occasion but they seem to have stopped this year. This one did trip the switch.

    NO-Grid 2015

    My inverter after 3.5 years has decided to start tripping its MCB.

    I get the NO GRID alarm and flashing amber light. There is no pattern to when it happens.

    When I put the switch back up it could work normally for a few weeks or days and then trip again. I will get it checked by an electrician but interested to read you were having a similar issue. Was it happening frequently?



  • Advertisement
  • Registered Users, Registered Users 2, Paid Member Posts: 19,001 ✭✭✭✭Ha Long Bay




  • Registered Users, Registered Users 2 Posts: 285 ✭✭olympicweights


    Perfect thanks for the link. Did you have the tripping from early in your install? Seems strange that it only started after a number of years in my case - maybe the weather is wetter this year for my location/condition. I'll look into upgrading my RCBO. Thanks again.



  • Registered Users, Registered Users 2, Paid Member Posts: 19,001 ✭✭✭✭Ha Long Bay


    I cannot remember when exactly it started happening I think after a few months. It was just from reading the threads here where I found the solution. It has not tripped since the RCBO was replaced.



  • Registered Users, Registered Users 2 Posts: 9 aosf


    Hi,

    My solis inverter makes a noise/humming noise. Although not too load i can hear it in parts of the house.

    it appears to be when charging or discharging the battery at a rate above ~3kw. it happens not just on TOU, but when the house has a larger load too.

    Does anyone else have this. Is there a workaround as its slightly annoying.

    What is causing it?

    Thank you



  • Registered Users, Registered Users 2 Posts: 10,014 ✭✭✭✭micks_address


    What model is it? Some have fans that kick in when they get hot



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 4,184 ✭✭✭pureza


    it’s the fan,mine does it too

    You could put one of those outdoor covers on it that are widely advertised,they’re timber I think,that would muffle the sound a bit maybe enough when it happens



  • Registered Users, Registered Users 2 Posts: 9 aosf


    Ok, didnt realise it had fans. It has a huge heat sync.

    Model 3104

    Series S5-EH1P5K-L

    Is there a certain voltage or current they kick in at? Or maybe a certain temp. As they are not always on?



  • Registered Users, Registered Users 2 Posts: 9 aosf


    Can they be used inside? My inverter is in the attic.

    Its attached to the gable wall and maybe that is adding to the noise, vibration maybe?



  • Registered Users, Registered Users 2 Posts: 10,014 ✭✭✭✭micks_address


    If it has fans kicks in at certain temp.. if you use the home assistant integrations it exposes a sensor with the internal temp

    1000039788.png


  • Registered Users, Registered Users 2 Posts: 108 ✭✭AntonP


    at 60A charge or discharge that noise kicks off.

    nothing you can do besides limiting charge or discharge at economical cost



  • Registered Users, Registered Users 2 Posts: 1,165 ✭✭✭TimHorton


    Up until recently on a Sunny day the AC side of the Inverter was hitting 5.7 kWh - Load + Export , The rest was going back to the battery. Now the AC side sits at 5.2 kWh with the excess going to battery , End result is 16 kWh battery gets to 100% quicker and my clipping kicks in at 5.2kWh ! So daily production suffers. Solis support updated Firmware Yesterday and on restart it got to 5.7kWh on the AC side but soon dropped back to 5.2kWh , I did have an 800w Ecoflow MicroInverter connected to the House for a few days but unplugged it 2 weeks ago. Any ideas ?



  • Moderators, Home & Garden Moderators Posts: 7,743 Mod ✭✭✭✭graememk


    It's kW, not kWh! 😂

    Is it a 5kW inverter? If it is it shouldn't be outputting more than 5kW on the AC.

    Why it did before I don't know.



  • Registered Users, Registered Users 2, Paid Member Posts: 16,084 ✭✭✭✭josip


    If someone nearby recently got solar installed would that have any impact at what power your inverter decides to export?



  • Registered Users, Registered Users 2, Paid Member Posts: 3,952 ✭✭✭Dublin Calling


    Yes. To export power it needs to be at a higher voltage than the mains comes in at. Each inverter on the same mains supply is upping the voltage slightly. There is a maximum voltage allowed set on your inverter, it wll not export beyond this.

    The max limit is 253 volts, but maybe set lower on your inverter.



  • Registered Users, Registered Users 2 Posts: 1,165 ✭✭✭TimHorton


    Ok , So it looks like Grid Voltage dropped 10v (mid 240's to mid 230's) around May 29th , The same day I saw the export drops.

    Is there anything I can do ?



  • Advertisement
  • Moderators, Home & Garden Moderators Posts: 7,743 Mod ✭✭✭✭graememk




  • Registered Users, Registered Users 2 Posts: 3,058 ✭✭✭Dr Robert


    Hi,

    I was getting the tripped MCB a few times in the first few years, then last summer I got quite a few. My plan was to see would it happen again this summer and if so I'd get the installer back.

    But it has dried up. Instead I get this error: OV-G-V.

    The MCB does not trip with this error.

    Is the Inverter now able to handle the issue now without tripping? Perhaps, I've no idea.



  • Registered Users, Registered Users 2 Posts: 285 ✭✭olympicweights


    Does the inverter go into alarm mode and stop working with the over grid voltage error? I had something similar, my inverter was shutting down as the grid voltage exceeded 253.4V or thereabouts. I even had ESBN out to check everything. Subsequently I changed the Network standard on the inverter to allow for a higher voltage and no problem since.



  • Registered Users, Registered Users 2 Posts: 2,086 ✭✭✭tnegun


    I installed a 15kwh battery in my parents place a couple of weeks back and have been slowly commissioning it to ensure it's working as expected. I'm aiming to have it charging during the 2am-5am slot, export excess Solar at all times and have the battery cover load when required. It's almost there, but the last couple of mornings I've noticed the battery didn't supply power until later in the day, pulling from the grid until there was sufficient solar and then if the load exceeded PV the battery is used until the following 2am. I have it in Feed In Priority with just one charge slot 2am-5am

    Any ideas what I'm missing?

    Screenshot 2026-06-27 at 09.16.58.png Screenshot 2026-06-27 at 09.16.43.png Screenshot 2026-06-27 at 08.47.19.png


  • Registered Users, Registered Users 2, Paid Member Posts: 489 ✭✭mjatkey


    What is the battery and what battery setting are you using on the Solis? Does the inverter "see" the battery ok SOC wise?

    Maybe try change to self use for a bit then change back to feed in?

    If not open TT with Solis, if battery is Seplos tell them its Dyness or something other wise they may give you the old "we don't support that battery" line.

    🌞 6.96kWp PV System. West Dublin🌞



  • Registered Users, Registered Users 2 Posts: 2,086 ✭✭✭tnegun


    It's a Deligreen battery, and I'm using the user-defined config as it was throwing alarms with any other setting. It has comms, and the BMS is advertising SOH/SOC and managing the charge/discharge current. Besides, this issue everything seems to be working perfectly. I was wondering if the battery was going into overvoltage toward the end of charge but I don't see any evidence of it or alarms/alerts on the inverter itself. I'm remote so only going on what I can see in SolisCloud, but the pics I took of the BMS settings when installing vs what the inverter is reporting as its voltage, it should be ok. It's one I'd like to confirm and double check what the BMS reports the voltage to be vs what the inverter is reading to be sure.



  • Registered Users, Registered Users 2 Posts: 7,588 ✭✭✭witnessmenow


    I'm after setting up my Solis S6 with HA. I originally had some issues with it knocking the solis cloud offline, but I reached out to solis and they remotely updated my datalogger and it seems to have solved the issue now. Super quick, raised the issue just before bed and it was done by the morning. (im now on 100141d9)

    I would like to setup some automation to manage the battery SOC and have been "discussing" it with Gemini, but I'm not sure if its going about it the right way. My main goal is mange clipping on the days solar is predicted to be decent

    Its suggesting this:

    "

    • 02:00 – 05:00 → Timed Charge (Value 35): The battery slams to 100% on the 7c rate.
    • 05:00 – Until Empty Target → Forced Export (Value 36): The inverter opens the floodgates and exports the battery at a flat 5000W directly into the grid at 18.5c.
    • Afternoon → Feed-In Priority (Value 96): The exact moment the battery hits your target empty size (20% or 50%), Home Assistant turns off Forced Export and shifts the inverter into Feed-In Priority. Your panels take over, maxing out the grid export while routing the midday clipping overflow straight into the newly created battery space.

    "

    So basically on 40kWh+ solar day it would discharge the battery to 20% in the morning, 25-40kWh day discharge til 50%

    Does this seem logical? Or anyone have a different strategy or automation they could share? Unfortunately "move to pinergy" is not an option anymore!

    For context, I have a 8.7kW system split between a South East (9 panels) and South West roof (10 panels, but 5 are in full shade in the morning) and a 20kWh battery.



  • Registered Users, Registered Users 2 Posts: 329 ✭✭ptogher14


    I believe the latest firmware update on the datalogger supports dual polling. Makes sense if its no longer knocking the cloud offline.

    The values look like binary values for setting the storage mode. Are you doing this over modbus or using a HA intergration?

    Your logic looks like it'll work. You might need to monitor and make some tweaks. Potentially there could be a gap when you discharge to 20% and the the array can't cover load earlier in the morning.

    I have mine set up slightly different. I change the battery it a different level given the forecast day. HA will look at the forecast at 1.55. The higher the forecast the lower the charge. At sunrise HA make a choice of what storage mode to operate in the in. I also have some automations to reset to self use mode of certain conditions are met. Works well but I would not be maximising every gain compared to your logic.