Heat Pumps - post here.

1129130131133135

Comments

  • Registered Users, Registered Users 2 Posts: 194 ✭✭Jo Satan


    The offset value is set at 2c, but is not applied.



  • Registered Users, Registered Users 2 Posts: 194 ✭✭Jo Satan


    Your heating is set to come on when the outside temp is 15c.You could try dropping it later in the year when the outside temp is 14/15c if the house doesn't need heat.

    Your second point looks like 45c when the outside is -3c. That is too high. Consider dropping the second point down to 35c and leaving it run. Use a thermometer to check the temperature in your living room, adjust the second point to get to where you want. I personally think -3c is not low enough. The outside temps could go down to -5c this week. I'd want a bit of extra heat if the temps go down to -5c.

    I am not sure that making these changes will necessarily reduce your consumption as your current set up allows the home to drop in temp. But you will have a constant indoor temp which will be more comfortable.

    Apparently reducing your flow temp by 1c reduces electricity usage by 2 to 3 %

    I wouldn't worry about the BER/HLI its really only useful when selecting a heat pump or confirming its way out of spec if your bills are outrageous.



  • Registered Users, Registered Users 2 Posts: 6,659 ✭✭✭championc


    Use this graph to set the points at +15ish and the -5ish ends of any heat curve. Focus more on the black line below the red line.

    1000081598.png


  • Moderators, Home & Garden Moderators Posts: 7,609 Mod ✭✭✭✭graememk


    Heat geeks advice is keep reducing it until complaints happen (eg the house is a bit chilly), then you've known you've gone too far.

    Even they say it's the only really true way for really getting it dialed in.

    45 is enough for radiators, nevermind underfloor.

    As long as you record settings as you go, you can always revert.



  • Registered Users, Registered Users 2 Posts: 244 ✭✭Grey123


    I have turned off the programme in the thermostats and set the temp on them to 30deg so I presume they are just calling for heat and the weather curve will do its thing and drive the temp. once I know what its currently doing I can then start the dial back.

    I might set some thermometers for rooms.

    If the 45 is too high I should I see the temperatures push past 22 ya? I think it doing 40deg now when it is 6 outside.



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 6,659 ✭✭✭championc


    Yes, it will blow past 22 and keep going. Obviously, if you have UFH, that takes much longer to react. That unit will be stop starting like mad for sure 😮



  • Registered Users, Registered Users 2 Posts: 244 ✭✭Grey123


    I have radiators upstairs and down. Is 45 more in line for them?



  • Moderators, Home & Garden Moderators Posts: 7,609 Mod ✭✭✭✭graememk


    Fixed or weather compensation?

    Again go as low as you can go, the lower you go the more efficient it will be.

    But will reach a point where you went get enough heat into the house.



  • Registered Users, Registered Users 2 Posts: 244 ✭✭Grey123




  • Registered Users, Registered Users 2 Posts: 6,659 ✭✭✭championc


    I have rads throughout

    My flow temperature today was around 35

    Here's my live data - https://emoncms.org/app/view?name=championc&readkey=5e5a2bd11d69740be46a55e1793e551d

    Post edited by championc on


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 244 ✭✭Grey123


    Interesting. I don't know what "a ads" is though? Is that how you pull the data? Am I reading that right 40kwh a day or so on heating? Seems a lot!

    @Jo Satan I ran it overnight with the thermostats maxed but didnt adjust the weater compensation profile, seemed to get rooms up to about 22 degrees and was constantly cycling looking at the energy profile. I thought it might go higher.

    I went to adjust the profile this morning and brought the 45 down to 40. However it looks like the lowest I can go for the low temp is 35degrees. I not you are at 20degrees. That a big difference! Any idea why?

    My low outside temp is 0, not -3 as you thought it might be. The text is just not centred.

    Do you have under floor heating?



  • Registered Users, Registered Users 2 Posts: 9,787 ✭✭✭micks_address




  • Registered Users, Registered Users 2 Posts: 1,737 ✭✭✭THE ALM


    We are in a 2006 upgraded bungalow, HLI 1.785, all steel rads. No internal temp control and purely run on weather compensation. I do have stats in all the rooms to monitor temp etc. and this maintains a temp of approx. 20°C, there is probably a fluctuation of +/- 0.3°C

    This is our weather curve with the max temp set on the heat pump of 40°C

    Screenshot_2026-02-16-11-24-07-549_com.viessmann.vicare.jpg

    These are readings showing the flow temps, power used, outside temp and the daily power amount used over the last three days, when we had a mix of fairly mild with Sat being a cold day/night. The spikes are when heating the water or running a defrost cycle.

    ASHP_DAILY.jpg ASHP_FLOW_POWER.jpg ASHP_OUTSIDETEMP.jpg


  • Registered Users, Registered Users 2 Posts: 1,336 ✭✭✭fitzparker


    What price would I be looking at to replace Oil with a heat pump.

    Hot water not necessarily needed (we use electric shower)

    8 radiators in total

    I cant gauge a price anywhere online



  • Registered Users, Registered Users 2 Posts: 9,787 ✭✭✭micks_address


    thats hard to answer.. you will need to know the heatloss of your property. Your rads might be too small to use with a heatpump. If they need replacing will add to the cost. If you dont need hot water (what about handwashing/sink/dishes?) I know champion uses his system only for space heating. From what ive been told typically its around 12-16k with few rads replaced, hot water cylinder & heatpump installed but at lot depends on your requirements. Only an installer who can do a heatloss calc for you and size rads etc can give you a proper answer.



  • Registered Users, Registered Users 2 Posts: 1,336 ✭✭✭fitzparker


    Thanks a million, complete novice and just looking into it.



  • Registered Users, Registered Users 2 Posts: 9,787 ✭✭✭micks_address


    yeah im not far off novice level myself.. the challenge with heatpumps is to get them running optimally careful calcs need to be done for heating requirements. You probably know this but the idea is your run your rads at approx half the temp of a gas/oil boiler leaving them on pretty much all the time.. this slow and low heat heats your property consistently over time.. if you put a heatpump in thats to large and it cant modulate down it will use more power than you need to provide the heat.. if your rads arent big enough it will need to run harder to provide the heat.. if your pump is sized to small it will never get your property up to temp so will also use more power.. its not a complete mystery but if looking for installers the first conversation should be about heatloss and they should be looking for your most recent ber report if you have one, heat loss indicator.. or if not available a technical assessment should be done etc.. no one should be quoting you for an install without at least a site visit to check out the property and doing some calcs for your requirements.



  • Registered Users, Registered Users 2 Posts: 194 ✭✭Jo Satan


    No underfloor heating just radiators.
    When was your house built?
    Is your A3 BER after solar was installed?
    If you have an older house and your BER is improved by means other than the upgrading the fabric of the house, ie installing a heatpump, upgrading controls, solar it does not improve the Heat Loss of your home. So the home still needs the same amount of energy to heat it, its just more efficient.



    Do you have the model/number of your Daikin Heat pump?
    There may be a separate setting restricting your set point temperature range. See the video linked below.
    You should first check the specs of your heat pump to see its flow temperature range.

    (3) How to Change Temperature Range on Daikin BRC1E62 Controller - YouTube

    Post edited by Jo Satan on


  • Registered Users, Registered Users 2 Posts: 1,737 ✭✭✭THE ALM


    When looking at heat pumps and BER's the more important figure is the HLI, the lower the better.

    For the grant and homes built before 2007 this needs to be 2.3 W/(K.m2) or lower, from 2007 onwards it is assumed that this will be the case.

    You could have a G rated house and stick enough solar panels on to get an A rating, this will not alter the fact that it will leak heat like a sieve.



  • Registered Users, Registered Users 2 Posts: 244 ✭✭Grey123


    2017.

    A3 is pre solar but also pre extension (maybe 5m by 3m) without an additional rad. Will be getting a BER assessment done soon now as it was included in solar.

    EHVH08518CB3V

    Will have a look at the video later.



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 244 ✭✭Grey123


    How do you get this info? Does your heat pump have an app?



  • Registered Users, Registered Users 2 Posts: 22,121 ✭✭✭✭Cyrus




  • Registered Users, Registered Users 2 Posts: 6,659 ✭✭✭championc


    @Grey123 should have said RADS.

    From the data, the 40kWh is the HEAT, delivered from less than 10kWh of power. On the graphs, blue is power and orange is heat energy

    As for adjusting the heat curve, you have to consider both ends of the slope. You may not have been able to lower one end further if the other end was still higher

    Have you a buffer tank ?

    Post edited by championc on


  • Registered Users, Registered Users 2 Posts: 244 ✭✭Grey123


    I presume you need a heat pump that transmits data? I dont think mine does. Or is there an add on? I have some idea what HA is but dont have it set up.



  • Registered Users, Registered Users 2 Posts: 863 ✭✭✭staples7


    100% - Ive been doing this for 8 years and it works like a dream. Slight tweak needed when we get to minus temps. Very low annual bill for 2800 sqft house. It really does help if you have an APP connected to your HP to simplify schedule etc



  • Registered Users, Registered Users 2 Posts: 1,737 ✭✭✭THE ALM


    What make of heat pump are you using? Some have integrations built into home assistant like these

    The power figures I measure using a CT from a myenergi Harvi.



  • Registered Users, Registered Users 2 Posts: 244 ✭✭Grey123


    IMG_1735.png

    Here is my energy use for the day. From 2am to 4am the hot water tank was doing its thing.

    My EV was charging from 4am to 8am.

    The overnight spikes are approx every 30min. However I dropped the top of the curve from 45deg to 40deg at 9am and the spike (pump runs I guess?) have become more frequent, that doesn't look very efficient or good for the pump, they are probable every 15min.



  • Registered Users, Registered Users 2 Posts: 244 ✭✭Grey123


    It’s a Daikin. That list just has them for AC.

    Yes an app would be much better. The unit isn’t the most user friendly.

    Most of the setting were in the hidden menu.



  • Administrators, Computer Games Moderators, Sports Moderators Posts: 32,899 Admin ✭✭✭✭✭Mickeroo


    Hard to know for certain just from that but that looks like the unit could be short cycling. Do you know what size heat pump you have? It's possible it's over sized for your property so it can't modulate low enough to run continuously.

    You mentioned EHVH08518CB3V earlier which is an indoor unit, do you know what the outdoor unit is?



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 244 ✭✭Grey123


    ERLQ006CAV3

    Does this tell you enough?

    What would be the cause of short cycling?