  • Registered Users, Registered Users 2 Posts: 9,787 ✭✭✭micks_address


    Probably 7 but it seems they don't output their stated power anyway.. apparently no penalty going for the 9kwh grant as it modulates down very low



  • Moderators, Home & Garden Moderators Posts: 7,609 Mod ✭✭✭✭graememk


    What I have:

    I am running the tado system with a heatpump.

    I have motorised trvs on all the radiators. And 2 wireless thermostats. One in the hall and one in the living room. Only the thermostats can generate a call for heat. All the other rooms are set as a limit rather than a target.

    I've even pulled the two hall radiators into a separate room so 95% of the time they will be open - to ensure there's enough radiators open when the HP is running.

    If I was doing it again I'd just stick with the manual trv and have them set as room limits.

    Glyn Hudson just put in a grant heatpump. And he also shown lockshields with flow meters on his radiators that would make balancing easier.

    If all radiators are open, you use the balancing of the radiators to make the room warmer or cooler.



  • Registered Users, Registered Users 2 Posts: 9,787 ✭✭✭micks_address


    Yeah I watched his video. Seems to be doing well..the volumizer didn't seem to make much difference



  • Registered Users, Registered Users 2 Posts: 9,787 ✭✭✭micks_address


    Urban plumber says no problem fitting under window or slightly over a manhole



  • Registered Users, Registered Users 2 Posts: 6,659 ✭✭✭championc


    Vaillant just changed their guidance on locating theirs. Much more flexible. Only a cup full of R290 in them

    As for locating a controller, maybe in that other room downstairs, but you'll need to zone off the open area to be able to include or omit it from heating.

    A friend of mine had zone valves. I simply powered them from 3 pin plugs, connected to smart sockets. So he could control zones as he pleased. So I could have used other smart sensors to trigger opening or closing the zones.

    So think exactly what you want to do, and ensure that you build in enough controls to be able to do it.



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 9,787 ✭✭✭micks_address


    hi folks - what are peoples views on the heatpump grant? i got a quote yesterday from one place to put in a heatpump and use the existing cylinder - was 6.5k after the grant and other discounts.. they priced the heatpump at 15k which sounds way over the top. I know my plumber isnt on the grant scheme setup but im wondering are places just adding the grant onto the price which seems to be fairly common place with other schemes? would you do just as well going without it? with the grant do you need to remove your gas boiler? one of the options my plumber mentioned was leaving the boiler installed and use it as a backup for the heat if the heatpump for some reason wasnt working or was way out on energy consumption etc.. i won't gain a ton of space back by taking on the gas boiler as the press its in is out of the way and will only free up minimal storage. im thinking ill get him to quote for an install only anyway and see how it adds up. i was sort of hoping as i just need a heatpump and pipework, that the grant might cover most of the cost and id end up maybe having to pay 1500 or 2k on top of it but that seems unlikely from initial quotes



  • Moderators, Home & Garden Moderators Posts: 7,609 Mod ✭✭✭✭graememk


    Go for whatever costs the least for you.

    I have heard for the grant, but open to correction, the gas has to be removed. I mean completely and not just capped off in the meter box. Eg the pipe completely removed, which adds on a big cost too.



  • Registered Users, Registered Users 2 Posts: 9,787 ✭✭✭micks_address


    yeah there's no major panic with any of it.. i might see if i can line it up for the spring time..



  • Registered Users, Registered Users 2 Posts: 6,659 ✭✭✭championc


    Madness to keep gas boiler connected. You've done the kWh's calcs. Get rid of the gas meter, and save on the standing charge.

    And I too believe that the gas pipe has to be removed basically to outside your boundary if you go the grant route.

    My similar self install cost me about €4k tops. And the meter is gone, but the feed pipe remains.

    Do the whole sums - cost + running cost, taking into account the current age and expected life of the gas boiler.

    As crazy as it sounds, you might be better off just replacing the gas boiler, if your current one is nearly knackered, given the current low cost of gas



  • Registered Users, Registered Users 2 Posts: 354 ✭✭kildarejohn


    Agree with championc's comment

    "

    As crazy as it sounds, you might be better off just replacing the gas boiler, if your current one is nearly knackered, given the current low cost of gas"

    A few simple calculations show that an efficient gas boiler is likely to be cheaper to run than a heat pump.

    In round numbers, a gas boiler costs 10c. per 1 kWh of heat delivered. To deliver 1 kWh of heat, the heat pump uses only 0.4 kWh ( assuming a COP of 2.5), but if electricity costs 30c. per kWh, then the 0.4 kWh of electricity costs 12c. So using these rough round numbers the heat pump is 20% dearer to run.



  • Advertisement
  • Moderators, Home & Garden Moderators Posts: 7,609 Mod ✭✭✭✭graememk


    Yes run the numbers but.

    My heatpump only hits 2.5 when it's at 65c 😂

    Everyone can make the numbers suit

    Adjust that cop to 3.5 and use the cheapest 24 hrs rate (about 25c) that comes out at 7c/kWh of heat. Which then is 30% cheaper than gas.

    3.5 is very doable even with radiators.



  • Registered Users, Registered Users 2 Posts: 9,787 ✭✭✭micks_address


    Id be hoping to run mostly on stored electricity around 5.5 cents a unit. I know it's not the most financially sensible thing for me to do but I've been interested in doing it for a while.. I like the idea of consistent heat in the house rather than cold to hot cold etc..



  • Registered Users, Registered Users 2 Posts: 354 ✭✭kildarejohn


    d be hoping to run mostly on stored electricity around 5.5 cents a unit

    Sounds great, but where are you getting electricity at 5.5 per unit?



  • Moderators, Home & Garden Moderators Posts: 7,609 Mod ✭✭✭✭graememk


    Totally agree, I would even recommend trying to do that now, it would roughly be the same energy requirement Vs blasting the heat just in the evening - unless the house gets really cold during the day/only heating one room

    I'm actually running the target temperature lower than what I would normally be running with traditional means...

    (Only heating one room has it's disadvantages too, possibly trying to over work one radiator to lose the heat to the rest of the house)



  • Registered Users, Registered Users 2 Posts: 6,659 ✭✭✭championc




  • Registered Users, Registered Users 2 Posts: 9,787 ✭✭✭micks_address


    Yep pinergy.. if only they did one more hour I'd be laughing.. 3 hours is a little tight to charge batteries, car etc..



  • Registered Users, Registered Users 2, Paid Member Posts: 15,602 ✭✭✭✭josip


    Gas boiler might be on the way out and looking at replacing it with a heatpump if it's no more expensive to run.

    Our house is a fairly well insulated (internal, not external) 100m2 B3 semi. Gas bills are €1400 per year, c.€150 of which is the standing charge. We're in the house most of the time and keep it at 21/22C. We'd never need to heat the house in a hurry.

    We've got MHRV and I just saw that there are waste-air to water heat pumps. Would these be more efficient than a regular air to water HP and can they be fitted to an existing MHRV setup ?

    We don't have UFH, rads are sized for the gas boiler and only one of them could be replaced with a larger rad, the others are size-constrained by their location.

    Are we wasting our time considering HPs?



  • Registered Users, Registered Users 2, Paid Member Posts: 1,269 ✭✭✭cunnifferous


    What COP are people getting in this weather? Mine is down to 2.2, dunno how these things are supposed to still function down to -20C!



  • Moderators, Home & Garden Moderators Posts: 7,609 Mod ✭✭✭✭graememk


    2.95 for space heating avg temp 1.2c flow temp peaking at 48ish



  • Registered Users, Registered Users 2 Posts: 9,787 ✭✭✭micks_address


    It's a good question. I was watching a video where someone was flying a drone in close to freezing in Ireland and it came down with icles on it. They reckoned the dampness in the air in Ireland just makes it that much colder. That they have flown in -20 in Canada and never seen it. Does our inheritant damp winters adversely affect heat pump performance? Compared to colder temps in drier countries?



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 3,397 ✭✭✭newhouse87


    Causes the heat pump to defrost more i would suspect than dry cold weather like in Scandinavia. Them defrost cycles massively affect cop and overall performance.



  • Registered Users, Registered Users 2 Posts: 324 ✭✭MadeInKerry


    I have several friends who have got heat pumps installed in the last 4 or 5 years. Their houses are very similar to mine. But their heat pumps seem to be costing much more than our gas heating each year.

    We are in a 4 bed detached 180sqm house and have gas heating. Ive been monitoring the gas usage religiously the last 3 years. We use roughly €1400 to €1500 each year. Even weekly it nearly doubles on a week like this week, though there have only been 4 or 5 of those weeks the last few years. My friends with the heat pumps all say the cost of their heating goes up massively on these weeks too.

    One got IR heating in his house 3 years ago and got rid of his oil tank and burner. His electricity bill has increased by over €3000 a year now and he has mould in some rooms that arent heated now. The IR heating was a terrible idea. Needless to say he is now looking at a heat pump too, so this question is for him too.

    I have smart TRVs in each room controlled by thermostats in each room. Only the thermostats call for heat and the rads are set to stay around 20.5c on the thermostats. Step back to 18.5 overnight. Heating is always on whether we are in the house or not. I might step it back to 18.5 if i remember when we are out, but i forget to do that more often than not. Tried geofencing but there is so much coming and going it doesnt work. I have the flow temperature at 61C on the gas boiler.

    Is it economical to go for the grant and get a heat pump? Is it likely to save me any money or should I just keep going as I am. The insulation in the attic is all over the place. Squashed, holes all over the place. Needs to be thrown out and replaced. We have normal internal wall insulation and vents in each room. House built in the mid 90s.

    Is there a grant for all of this?



  • Registered Users, Registered Users 2 Posts: 1,737 ✭✭✭THE ALM


    Looking at the data from yesterday where temp in the midlands went from -2 to about 3°.

    We are in a 2006 165m3 bungalow with extensive upgrades, insulation, doors , windows, solar, ashp and mvhr.

    The heat pump used 21.59kWh, measured, for both heat and hot water. Power used varied from about 600-850w with peaks for the defrost cycles and hot water. The thermal energy produced was 84.4 giving a COP of 3.91.

    040126Power.jpg

    All steel radiators with three upgraded from the oil boiler, 1 triple and the rest doubles. The flow temp varied from 31-32.5°, excluding the peaks for defrost and hot water.

    040126SupplyTemp.jpg

    We run the temps at 20° from 06.00-22.00, setback 18° from 22.00-04.00, 22° from 04.00-06.00. This maintains an average temp of 19.5°.

    Thanks to the solar and battery storage this is all on the cheap EV rate, cost €1.92.

    Rather than looking at the BER rating the more important figure (which should be on the advisory report) is the heat loss indicator (HLI). To qualify for the grant, in most cases as there are exceptions, this needs to be below 2.3 and the lower the better.

    A rough guide to the size of the heap pump required is HLI x floor area in m2 x 24. A more detailed survey should then be carried out.



  • Registered Users, Registered Users 2 Posts: 9,787 ✭✭✭micks_address


    can i ask what your HLI is/was when heatpump was installed? Ours is 1.91.. we don't have external insulation (hollow block construction) but triple glazed windows/doors. and a lot of the house is glazing/doors with insulated attic.. all rads.. in the process of getting heat pump quotes.. so interested to see how it works out.. what supplier / tarrif do you use? we are currently on pinergy 3 hours.. which is great but we can only import abotu 16kw per night.. for nov/dec/jan solar could vary from nothing to max 10kw.. i expect i need to move to a longer tarrif window if we go heatpump so we can get more into the batteries (32kw)



  • Registered Users, Registered Users 2 Posts: 21,915 ✭✭✭✭Water John


    No matter what the heating, the insulation is the key. Tackle that first. Josip, you could use aluminium rads, they will give more output for any given size, than steel rads. You could also consider vertical rads in a tight width. Worth going for the grant if installing HP, but look at insulation, windows and external doors too. Consider PV panels if you're not borrowing the money.



  • Registered Users, Registered Users 2 Posts: 1,737 ✭✭✭THE ALM


    Ours was 1.785 before we installed the mvhr, would expect it to be a bit less now at about 1.55. We had a good airtightness test which also helped.

    We are on the Energia EV rate at 0.089c from 2-6am. Pinergy would have worked out slightly better for us but preferred the 4 hour charge window for the EV etc.



  • Registered Users, Registered Users 2 Posts: 9,787 ✭✭✭micks_address


    Thanks… all more we can do is external insulation but the cost is prohibitive. Might be worth doing the cable wall as its got the least glazing/doors.. stayed in a b & b at the weekend.. they were running multiple heat pumps.. underfloor heating.. single glazed.. drafty… old building but it was warm.. i assume the consumption of power was quite high!



  • Registered Users, Registered Users 2 Posts: 444 ✭✭Biker1


    On the topic of steel or aluminimium radiators. The output of any radiator is declared in Watts and it doesn't matter whether its steel, aluminium or any other material. E.G. a 500w steel radiator has the same output as a 500w aluminium radiator. The only difference will be the size of the radiator which is very little. Aluminium are three times the price of steel rads and presumably a bigger profit margin for the supplier also which seems to be why they are heavily promoted.



  • Registered Users, Registered Users 2 Posts: 9,787 ✭✭✭micks_address


    i guess aluminium heats up quicker than steel? but steel holds it heat longer? we have a mix of both and that seems to be the way… probably doesnt make much difference with heat pumps as its lower heat over longer periods?



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 6,659 ✭✭✭championc


    I got 3.45 for space heating yesterday - 21kWh used and 72.4kWh generated

    The COP (and running cost !!!) can be excellent or enormous - and hugely dependent on the heat curve - provided the unit wasn't oversized in the first place.

    And so many installer still appear to be in the gas/oil boiler mindset - installing heatmizers and any number of 3rd party controls and thermostats, and secondary pumps.

    Actuators on UFH manifolds have no place in downstairs or main living areas circuits / loops. They cause stop starts. Same with a heatmizer main controller - designed to stop and start. And 3rd party wall thermostats ….. same.

    Set thermostats higher than needed (to act as Limiters only), and control the heatpump output by correctly setting the heat curve / compensation curve (Water Law on Samsung's)