Heat Pump Running Costs

11920222425

Comments

  • Registered Users, Registered Users 2 Posts: 22,382 ✭✭✭✭Cyrus


    i have the same, all i can get is power usage via a shelly EM, there is some way of getting more info but not as straightforward as other systems.

    I know i have my DHW timed over night so generally can ID what heating and whats DHW. (DHW tends to use circa 2.25KWH)



  • Registered Users, Registered Users 2 Posts: 1,079 ✭✭✭SodiumCooled


    It appears to be saving you money and seems the right choice for you but is it not a compromise on comfortable temps/loss of functionality? We are going into or first winter in a new build and I invested in smart thermostats so I can monitor and control all my zones from the phone (11 stats but some have a few zones e.g. large kitchen). Having the ability to control rooms individually I would see as one of the things I looked forward to having. There is considerable difference in the temperate in some rooms compared to others due to which side of the house they are on plus a variance in how warm you want a room. In your system do you not end up with bedrooms and other rooms that are warmer such as the kitchen being too warm just to push up colder rooms?

    Currently I only have one or two thermostats occasionally calling for heat (and only in the last few days and maybe for an hour each once a day) the compressor is rarely even needing to turn on circulating is enough. My kitchen has yet to drop below 22 degress (which is its set temp also) where as a front room has dropped to 19.5 (set to 21) would seem mad to me to heat the floors in the entire house to heat one room. I think I have 4 or 5 different temps set across the 11 zones depending on type of room and I expect to be tweaking as the weather gets colder.

    To summarise - is saving 20% the ultimate goal or having the best comfort. The answer of course will vary depending on who you ask but for me its the latter as things stand anyway but lets see how the winter goes 😊



  • Registered Users, Registered Users 2 Posts: 2,925 ✭✭✭ECO_Mental


    Hi,

    Like you, I have 12 heating zones. In theory, that’s great, as you are only heating the rooms you need.

    However, what actually happens (and I am assuming you have MHRV) is that if one room calls for heat, the laws of thermodynamics (and common sense!) mean the heat in that room will naturally flow into the colder rooms. In effect, that one room is trying to heat the entire house and will probably struggle to reach its set point. Added to this, a heat pump works best with larger volumes of water at lower temperatures. Heating a small loop results in the return temperature not being low enough, so the heat pump ends up cycling on and off and working very inefficiently.

    My theory, which I think I've proven correct, is that it's better to heat the entire house as a single unit. Your MHRV already treats your house as one sealed unit and moves heat around, so you should heat it that way as well. During the winter, I stagger the upstairs and downstairs by an hour, so the downstairs comes on an hour earlier. I also have more realistic temperature settings in the evening (though still high enough for most zones to come on), so particularly warm rooms will switch off. But at night, around 3 am its balls-to-wall, I have all zones set to 23°C. At 6 cents per kWh, this costs next to nothing—maybe 20-30 cents a night (50 cents at most).

    This strategy works for over 95% of the winter. On the really cold, miserable, windy days, I just let the system do its thing and allow each room to call for heat whenever it needs to. Because it's extra cold on those days, a lot of loops will be open anyway, so the system will be working as efficiently as possible.

    My experiment started as a cost-saving exercise (to max out the EV rate at night) but ended up achieving both: I saved 33% on cost and reduced my actual kWh consumption by 25%. I reckon I could do more if I had a bit more control and could predict solar gain for the following day, but that’s another project.

    Regarding comfort, I’ve had no complaints from the family. The entire house is a nice, even temperature. Yes, one or two rooms might be a degree colder, but it's nothing drastic.

    If this is your first winter with the heat pump, I would say let it do its thing and learn how it works. The last thing you want is an earache from the family while you're experimenting with the heating! But maybe in a month or two, try this strategy for a week and see how it works for you. Also, keep a close eye on your consumption by checking it daily. Have you a live energy meter on your heat pump to see exactly when it's coming on; this is important for understanding what's happening.

    6.1kWp south facing, South of Cork City



  • Registered Users, Registered Users 2 Posts: 3,455 ✭✭✭newhouse87


    Balancing at the manifold regulates how much heat goes to each room when all loops are open as most of us think is best strategy for efficiency. My bathroom right beside plant room a v short loop so I have it at low flow rate for example so it doesn't overheat. All takes time to know what way your house reacts and best strategy for your individual house. My first winter i had all rooms running off individual stats, not efficent and quite expensive, now the whole house is running off 1 stat that i can time to come on and off to utilise night rate in particular. Dezoning best decision I made.



  • Moderators, Home & Garden Moderators Posts: 7,734 Mod ✭✭✭✭graememk


    Yep I have radiators and smart TRV's but the way I have mine setup only 2 rooms can call for heat, hall and living room. All other rooms cannot call for heat, but can turn themselves off to "limit" the temperature in the room.

    They will take heat when given, but can't turn the HP on. My shortcut to balancing all the rooms 😂



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 22,382 ✭✭✭✭Cyrus


    October 2025

    156 Kwh Day 38.7 and Night 117.7 average of 5kwh and a max of 11.7 kwh (heating and DHW)

    Total cost for the month €26.89

    October 24 was 207 units, i think it has been milder this year.

    Post edited by Cyrus on


  • Registered Users, Registered Users 2 Posts: 863 ✭✭✭staples7


    October 2025

    114.4kwh heating

    53.3kwh hot water

    Almost all night rate @13c (with the exception of of some of the hot water)

    October 2024 was same hot water but 96kwh heating.



  • Registered Users, Registered Users 2 Posts: 483 ✭✭andyd12


    October 2025

    264kWH for heating

    37.7kWh for DHW

    Highest day was strangely high at 21.6kWh. Next highest was 15.1kWh

    The above defo needs some tweaking.

    Currently on the same rate day and night with a 26% discount.

    Monthly cost is €71 not factoring in solar



  • Registered Users, Registered Users 2, Paid Member Posts: 1,658 ✭✭✭JohnySwan


    125kwh for October. 2 x A2A, 1400sq ft.

    9kwh highest day. All night rate plus pv, peanuts to run.



  • Registered Users, Registered Users 2 Posts: 22,382 ✭✭✭✭Cyrus


    That seems very low for the dhw, we use at least 2 units a day ,conversely the heating is high, how big is the house ?



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 483 ✭✭andyd12


    Agreed, its what the app says though.

    Only 2 people in the house currently.

    The house is 215sq metres.

    1000059057.jpg


  • Registered Users, Registered Users 2 Posts: 1,746 ✭✭✭THE ALM


    Does seem high and, like us, it looks like you are running a viessmann unit.

    Here is our readings for the month, smaller house admittedly at 165m2. All consumption on night rate from the 4 hours and battery storage.

    What is your heat curve set at?

    1000026629.jpg

    What is your heat curve set at?

    Post edited by THE ALM on


  • Registered Users, Registered Users 2 Posts: 22,382 ✭✭✭✭Cyrus


    ours is 192 sq/m but with 4 people in it (just as a point of reference) probably some optimising to be done :)



  • Registered Users, Registered Users 2 Posts: 22,382 ✭✭✭✭Cyrus




  • Registered Users, Registered Users 2 Posts: 1,746 ✭✭✭THE ALM


    It is on 24/7 although mild enough at the minute, set at a temp of of mostly 20°. Taking yesterday e.g. the heat pump ran for just over 6 hours.

    I meant from a cost point of view it will all be at the EV rate as the battery (charged at the EV rate) will cover all our electricity needs throughout the remainder of the day.

    Heating schedule is:-

    18° 22:00-04:00

    22° 04:00-06:00

    20° 06:00-22:00

    Hot water set for 02:00-06:00 (it probably takes 1.5-2hrs to heat the water)



  • Registered Users, Registered Users 2 Posts: 22,382 ✭✭✭✭Cyrus




  • Registered Users, Registered Users 2 Posts: 483 ✭✭andyd12


    Yes correct running a Viessmann unit.

    Unsure about what the heat curve is set at.

    Its only a new build so tying feel my way with it without making too many changes at once.

    What is the best to do next:

    1- The 4 bedrooms are on rooms stats and actuators. Currently set at 19.5. Remove these, the house will be fully open loop then and allow the master stat to control the entire house?

    Or

    2. Reduce the heat curve?



  • Registered Users, Registered Users 2 Posts: 22,382 ✭✭✭✭Cyrus


    is it all one floor or are the bedrooms upstairs?

    if all one floor id prob go with 1 first, altho i tend to prefer bedrooms cooler than living areas…



  • Registered Users, Registered Users 2 Posts: 3,455 ✭✭✭newhouse87


    Bedrooms can still be cooler in an open loop system by adjusting flowrates to them rooms at the manifold.



  • Registered Users, Registered Users 2 Posts: 1,746 ✭✭✭THE ALM


    Regarding the heat curve,

    this is a fairly good read and explanation.

    These are currently our settings in a retrofit with radiators and I would expect a new build with underfloor heating to be as good if not better than this.

    1000026680.jpg


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 483 ✭✭andyd12


    Yes a bungalow.

    Like newhouse87 said, I might need to reduce the flow rates.

    Thanks for that and a good explanation. I will look at the heat curve after tinkering with the bedrooms



  • Registered Users, Registered Users 2, Paid Member Posts: 3,349 ✭✭✭hold my beer


    Anyone know on a Heatmeiser & Samsung system, are you able to have some thermostats on timers, and others on set temperature?



  • Moderators, Home & Garden Moderators Posts: 7,734 Mod ✭✭✭✭graememk


    Just to throw my numbers into the mix.
    Space heating. 282 COP 3.85
    Hot Water : 152 COP 3.24
    Average COP 3.6

    1980's Bungalow, Average Insulation, Radiators. Did upgrade windows this month, I should revisit my weather comp settings.
    Hot water is "polluted" with some space heating as it is not a HW priority, if both are calling for heat both gets it, Possibly could be improving my HW COP!

    Everything is run from solar or batteries so I cost it at roughly 8c/kWh.

    HP was more or less dropped in, in 2023. I did end up replacing 2 radiators and upsizing them.



  • Registered Users, Registered Users 2 Posts: 22,382 ✭✭✭✭Cyrus


    November 2025

    301 Kwh Day 107 and Night 194 average of 10kwh and a max of 25.2 kwh (heating and DHW)

    Total cost for the month €57.57

    For ref Nov 24 was 409 units, cost of 79.62



  • Registered Users, Registered Users 2, Paid Member Posts: 1,658 ✭✭✭JohnySwan


    204 kwh for November. All night rate/solar.



  • Registered Users, Registered Users 2 Posts: 863 ✭✭✭staples7


    November 226 heating & 57 hot water. All night rate @13c (with the exception of some of the hot water @25c)

    Something under the 40 euro mark for Nov


    Nov 2024 was 226 heating and 55 hot water. That’s some consistency given the variables with temperature 🤔



  • Registered Users, Registered Users 2 Posts: 106 ✭✭riccol1966


    Nov 477kwh, cost €115. Radiators, 180sqm, 21 downstairs and 18 upstairs (temps) above average insulation etc. Have accepted that it won't use less kWh having tried various adjustments over the last 2 years.



  • Registered Users, Registered Users 2 Posts: 1,746 ✭✭✭THE ALM


    Nov 224kWh, 191 heating and 33kWh hot water, all on ev rate, so €19.94 for the month. Highest was 17.4kWh with the lowest day at 1.6kWh.

    Nov 2024 was 238kWh, so not a huge variation and have probably tweaked it slightly since then.



  • Moderators, Home & Garden Moderators Posts: 7,734 Mod ✭✭✭✭graememk


    If it makes you feel any better, Mine is 683kWh. COP of 3.38 overall. Heat delivered 2311kWh. 1980 bungalow, Fairly exposed to the North west (Not much between me and Iceland!)

    It does include DHW, but there is some space heating in the DHW numbers as I am not running a Hot water priority setup.

    585kWh is from Battery/Solar (531 battery, 54 Solar) battery charged at EV rate etc.

    I might tweak my heat curve a bit more, but its close enough.



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 184 ✭✭johndoe11


    Nov 25 for me below. Heat curve set to 33 at -7 outdoors, operating with compensation. The measured room temperature is between 20 - 21, only raised by solar gain. Operate the heat pump at 21.5 at night and drop down to 19.5 during the day. 2700sq ft two stories, A1 rated built in 2017 in the midlands.

    Heating Usage

    Heating Supplied

    Heating CoP

    Hotwater Usage

    Hotwater Supply

    Hotwater CoP

    November - 2025

    587Kwh

    2502Kwh

    4.3

    110Kwh

    304Kwh

    2.8

    Post edited by johndoe11 on