Home heating automation

1160161163165166175

Comments

  • Registered Users, Registered Users 2, Paid Member Posts: 8,192 ✭✭✭deezell


    Post a picture of your timer/controller and wall stats



  • Registered Users, Registered Users 2 Posts: 889 ✭✭✭BullBauld




  • Registered Users, Registered Users 2 Posts: 4 Shane73212


    7c4e82da-391f-40d5-88f5-18908d2b1b40.jpg 873f5f95-a890-4a1f-a71e-b9139129b79e.jpg thermostat-tempo-medium.png

    Hi - I'm moving into a property in January and am looking to install smart heating controllers. I've attached pictures of the current setup. The system looks like a 2 zone heating system (one upstairs and one downstairs) with underfloor heating in the kitchen. I'm not sure whether kitchen underfloor is a separate zone of part of downstairs and I'm not sure on hot water (I assume it's a separate zone). The tank is a Kingspan Albion - see attached image.

    IMG_3117.jpg

    What smart thermostat system would you recommend?



  • Registered Users, Registered Users 2, Paid Member Posts: 9,707 ✭✭✭10-10-20


    Nevermind the heating - I'm lovin' the retro/stock-trader's mechanical keyboard! 😁 🤓



  • Registered Users, Registered Users 2, Paid Member Posts: 8,192 ✭✭✭deezell


    1. A really easy solution is two wired Tado thermostats, ( a wired starter kit plus an add on wired stat only) replace your mechanical stats with these, 2 wire diy swap. Leave the old controller and turn the CH timers fully on, continue to use the HW timer. The Tado stats and app will take over all timing and temperature control of the two CH zones.
    2. Replace the old timer with a Tado wireless starter kit. The receiver will take over one CH zone with a wireless stat, and the HW. Replace the wall stat of the other zone with a wired Tado add on. This will give app control of HW in addition to both CH, just a small few wiring steps more to replace the controller and one mechanical stat. The other mechanical stat being replaced by the wireless one is either just turned up full, or removed and the two wires joined, so this is diy doable for a confident competent person.


  • Advertisement
  • Registered Users, Registered Users 2, Paid Member Posts: 8,192 ✭✭✭deezell


    Any wall stats with the two controller CH zones?



  • Registered Users, Registered Users 2 Posts: 4 Shane73212


    Was that a question to me? There's two Warm up wall stats.



  • Registered Users, Registered Users 2, Paid Member Posts: 8,192 ✭✭✭deezell


    Sorry, should have quoted. Are there radiators downstairs as well as kitchen UFH? Is the downstairs stat in the kitchen? Generally zoned heating is a compromise, the measuring stat is often in the hallway, well in from the front door, and it acts as the sensor for all downstairs rooms, though most heavily influenced by its location heating devices, rads or UFH. It's good practice to have at least passive mechanical trvs on the rads in the areas that don't directly heat the thermostat. Normally open doors tend to circulate the heat from all rooms in a zone, evening up any imbalance.

    The warmup thermostats can be used as a simple air temperature measuring device, and in this capacity, can be easily replaced with a wired or wireless smart stat. When used for UFH, there may be a complication. The stats have provision for an underfloor temperature sensor in addition to the normal air temperature sensor, to better gauge the output of the UFH. Replacing with a stat that relies solely on air temperature could risk excessive output or slow response of the UFH , but plumbed UFH will have temperature controlled valve limits on the hot flow into the UFH tubing. That's assuming your UFH is hydronic, hot water based. This particular stat is also designed for electrical mat UFH. If this is what the stat is controlling, the underfloor sensor is probably more critical as a means to limit overheating. The mats are directly powered by the mains switched by the stat, with the capacity to switch a hefty 16 Amps or approximately 4Kw of UFH mat elements. If your UFH is electrical, I would not advise switching this directly with a normal smart stat, without the use of an in-between 16a relay, and would still be inclined to leave the warmup stat in circuit to act as a controller.

    This would not be an issue if the stats are controlling boiler flow to rads or UFH tubing, in that case they could be replaced by wired smart stats or by the receivers of wireless stats. Have a look to see if the kitchen is electrally heated or by boiler, and it will be clearer what your options are.

    https://www.warmup.co.uk/wp-content/uploads/Warmup-OM-Tempo-V1.3.pdf

    Post edited by deezell on


  • Registered Users, Registered Users 2 Posts: 889 ✭✭✭BullBauld


    Thanks for the reply. Why the wireless timer in option 2? Could I go for the wired one for the same result? Cheers.



  • Registered Users, Registered Users 2, Paid Member Posts: 8,192 ✭✭✭deezell


    The receiver for the wireless Tado CH thermostat also has a relay for HW timing, so you can remove the old controller altogether. Option 1 was a very simple DIY job to smart automate your CH zones, while leaving HW timing to the original controller. Removing and replacing the controller is often a task too far for some, so you need to hire an electrician.



  • Advertisement
  • Registered Users, Registered Users 2, Paid Member Posts: 8,192 ✭✭✭deezell


    A third option that will give you two wireless CH stats and HW control is the Drayton Wiser Kit3. It's a good bargain at the moment on Amazon. its receiver replaces your existing zone timer, wire for wire, the wireless stats can be postioned anywhere, and the old wall thermostats can either be turned up full to close the circuit, or removed and their wires joined and concealed. This is a very diyable job, and at the current price great value.

    https://amzn.eu/d/7UtvyXk



  • Registered Users, Registered Users 2 Posts: 889 ✭✭✭BullBauld


    Thanks @deezell appreciate the replies



  • Registered Users, Registered Users 2 Posts: 4,965 ✭✭✭Shane732


    Thanks for the reply.

    One of the Warm Up stats is located in the kitchen and controls the underfloor heating as well as the rads downstairs. Would that mean the UFH is coming off the boiler as opposed to electric?


    Would the best option be to replace the existing the Warm Up stats with smart Warm Up stats?

    Edit: Actually warm up do electric UFH from what I can see.



  • Registered Users, Registered Users 2 Posts: 2,773 ✭✭✭ECO_Mental


    Getting ready for moving all my 12 thermostats and zones and automating them with Shelly relays.

    I going to try and keep it simple and intially convert all of them to two zones and make them come on and off based on set times but a long time around 2 hours or until it hits the average set point for the zone. I have 6 zigbee temp sensors and use the average of these. I am getting a more responsive Shelly temp sensor as you cant rely on the Zigbee but they will do for now.

    I have started setting up my heating dashbord even before I have all the automations or devices in place so this dashboard isnt fully functional but it has helped me get my thoughts together on how I want it to work. You can adjust the set points of the heating and you can turn on an off certain heating strategys. Also have a history graph showing when the heating has come on or off, this will show eventually all 12 zones but grouped into the two zones.

    The new sections dashbord works great also on the phone.

    I looked for some HACS intergrations such as the Advanced Heating control but it was too advanced for me at this stage, so I decided to build my own system. There are things of when the heating times comes on an off have to be done under the bonnet through the setting and not the dashbord but I can expand on that later.

    This will keep me busy for weeks…tweeking and adjusting things🤣

    image.png

    6.1kWp south facing, South of Cork City



  • Registered Users, Registered Users 2, Paid Member Posts: 8,192 ✭✭✭deezell


    If your Warmup stat is powering the UFH electrically, it can still also trigger the boiler for radiators, so it can do both. From your extra EDIT comment, do you mean your Warmup stat is powering Electric UFH in your kitchen? Assuming this is the case, I'd be inclined to suggest the best solution is indeed the Warmup Smart 6iE wifi stat. You'll get all the app options it offers, with the same ability to monitor floor temperature from a remote sensor, and supply the power level for electrical UFH, and also be able to simultaneously trigger the boiler to the ground floor rads.

    There were some good prices for this model on Amazon. You should check inside the Warmup wallbox to see what cables run from it, does it have the underfloor sensors, which are probably essential for electrical UFH element control, less critical for boiler UFH.

    Electrical UFH wouldn't be long about running up a high power bill, but if it's only a single room, it might be worth the comfort.



  • Registered Users, Registered Users 2 Posts: 4 Shane73212


    Sorry on my edit - I'm still not sure whether the UFH is electric or not.

    Can you get smart TRVs with Warm Up?



  • Registered Users, Registered Users 2, Paid Member Posts: 8,192 ✭✭✭deezell


    I haven't seen smart trvs in their website. If you have boiler based UFH, there will be quite a bit of extra plumbing associated with it, pump, mixing valves, temperature control and manifold. The easiest way to check is to turn off the power to the boiler, then turn up the kitchen stat. Check to see if your electricity meter is running faster, and if the UFH warms up. Those stats are specifically designed for high current electric UFH.

    Post edited by deezell on


  • Registered Users, Registered Users 2, Paid Member Posts: 8,192 ✭✭✭deezell


    You can still replace that three zone controller with smart system such as the Drayton Wiser Kit 3. This is a drop in replacement and will give you two smart wireless thermostats for the radiator CH zones, HW control, and the option of Smart TRVs. If the Kitchen UFH is electrical, it can be left on the Warmup, and any link to the plumbed zone removed if present. It could be that the 3 zone timer receives its downstairs zone switched live in from the output of the Kitchen Warmup. On the other hand, if the UFH is plumbed, then it may just be acting as a low current thermostat for just the kitchen UFH, or the entire zone. You won't know until... you know. A few electrical tests will figure it out.



  • Registered Users, Registered Users 2 Posts: 4 Shane73212




  • Registered Users, Registered Users 2, Paid Member Posts: 8,192 ✭✭✭deezell


    does the second warmup stat control any UFH? It may have been used just as normal zone stat for upstairs plumbed. Next thing to test is your three zone controller. I can't make out the brand in the image, but I'm assuming there are boost buttons. Press the boost for downstairs and see does it bring on the downstairs radiators without the kitchen UFH being on. This will provide a clue to the wiring.



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 4,788 ✭✭✭Roberto_gas


    Thanks I have started this setup now…lets see how much gas is used ! One thing i have noticed is that when next time heat is called to the boiler to maintain the temperature, TRVs are opening slightly. But will the boiler still do full fledged heating since its just getting a on call from TRVs in this case ? And energy would be lost ? or it will know only one TRV is calling for heat(return temp would compensate with heating temp ?)

    EDIT - Tado TRVs says its heating radiators with just one tick but no call to boiler for heat(means its doing its thing i would say ? or its a bug of not triggering boiler)

    EDIT2 - It has triggered the boiler



  • Registered Users, Registered Users 2, Paid Member Posts: 8,192 ✭✭✭deezell


    With a very light load of on one or two rads, the boiler will inevitably cycle, that is, it will halt firing at its set internal temperature but will continue to move the heated flow around, to be consumed and cooled by any open zone TRV equipped rad. If you have large numbers of smart TRV's, then you will have conditions for this.

    The only inefficiency that can occur is a reduction in the condensing efficiency of the boiler as the flow temperature rises to boiler se max. The smart stat only has knowledge of the room temperature responses, not the boiler jacket temperature, but notwithstanding this it should know the rate of rise of room temperature is rapid when there's only one or two rads pulling heat from the flow, so it will likely modulate firing bursts to keep the rate of change under control.

    All smart stats use a number of techniques to exercise fine control, including a method called PID mentioned a few posts back by @10-10-20 in a discussion with @ecomental using basic Shelly switches and temperature sensors. PID or Proportional Integral Differential applies those derivatives of the actiual and target temperature differences to the boiler response, along with other tricks like modulation and learning. Very interesting stuff, the maths is hairy as I remember well from my college days, but I leave that up to Tado and the rest of them.

    Post edited by deezell on


  • Registered Users, Registered Users 2 Posts: 4,788 ✭✭✭Roberto_gas


    Quite shocking graph..kept 17 constant throughout the day and gas use was probably 10% more compared to yday(23 Kwh including cooking). The comfort factor was great. Tado was opening TRVs but not calling for heat to boiler(not sure if it’s a feature and it senses existing flow temp).

    IMG_5794.png

    How does the graph look otherwise ? I would like to believe insulation is good(but it was a mild day). This room has an openfire too(partly blocked chimney not fully).

    Is the idea to keep unused room bit lower temp ? Also is it worth keeping heating on at night or totally off or lower temp?



  • Registered Users, Registered Users 2 Posts: 4,965 ✭✭✭Shane732


    What would replace the 3 zone controller with?

    I’m not in the house so haven’t been able to test.



  • Registered Users, Registered Users 2, Paid Member Posts: 8,192 ✭✭✭deezell


    The ideal replacement is the Drayton Wiser Kit3 controller with 2 wireless CH thermostats. The 3 zone timer that's currently there is a Time guard TRT038 3 channel timer. It's not showing a display in your photo, probably powered off. This unit should control of the 2 radiator zones and HW, the Drayton kit3 wires in directly in place, but has smart thermostats integrate wirelessly to provide flexible app control of time and temperature schedules for the CH.

    Wait till you're there and you can make a few checks. One thing I'm sure of, the TimeGuard doesn't supply power to the kitchen UFH as its contacts are rated only 1 amp per zone.

    If you want to buy the Drayton Wiser Kit3, there are some good prices on Amazon right now, which may last into January, or not.



  • Registered Users, Registered Users 2 Posts: 27 Dand88


    Hi all, just purchased the Drayton wiser kit 3 from amazon. Going to replace my eph system which consists of a wired controller with 3 zones, US heat, DS heat and hot water. There are two basic turn wheel stats downstairs and upstairs. New drayton wiser hasent arrived yet but wondering is there much in replacing my current setup for the new one? Thanks in advance.



  • Registered Users, Registered Users 2, Paid Member Posts: 9,707 ✭✭✭10-10-20


    Yes, PID is the main control element under many of the smart sensors. It's hairy at a mathematical level because it's dynamically calculated on the basis of the temperature inputs and the three P, I and D values, it's not really one to be working out on a beer mat. A good image to understand it by is this one from from HASmartThermostat:

    image.png

    The purple line is the target temperature (set by the user at the controller) and the blue line is the temperature read by a sensor in the room where the heating device is. The orange lines indicate the times when the heating was turned on and the thickness is the duration. So obviously the orange line is thicker when the heating is on more, and thinner when the heating needs to back off. By controlling the heating in that way you end up with better regulation of the temperature and less overshoot (the D part) where the system doesn't react fast enough (the P part) or doesn't get up to speed quick enough (the I part).

    The funny thing is that the type of switching above isn't really suitable for a gas or oil based heating system - it's fine for electrical heating and such. Oil and gas need longer run-times to allow them to get into condensing mode (and preserve the boiler's parts), so you then manage that better by lowering the water temperature and giving the system more time to run at the optimal temperature, rather than switching it on and off like a loony. That's a reason why controllers for gas/oil systems aren't suitable for other appliances as their reaction and run-times differ significantly. Maybe that's of interest to some.



  • Registered Users, Registered Users 2, Paid Member Posts: 8,192 ✭✭✭deezell


    That's probably where the learning element comes in. You can calculate the PID to warm a given volume to a given temperature with a classic response curve provided you have Proportional control of the heating souce. Boilers are full on or off, not variable, so that's where modulation comes in. The load can vary significantly too, depending on the number of open rad/zone valves, and variation in cooling due to outside temperature. Smart stats are constantly doing the sums on this, including using online local temperature and weather data. There's no one size fixed Pid value that can turn a basic on/off temperature switch into a smart one, but you can probably get a decent compromise, otherwise it's no better than a mechanical stat. The issue of condensing flow temperatures further overeggs the pudding though, most homes' radiators wouldn't heat the rooms comfortably in the really cold days we've had recently if the flow temperature was restricted to ideal condensing temperatures, so again its a compromise.

    I wonder could @ECO_Mental have left his 12 thermostats in situ, on the basis that they probably had some level of pid built into them, and just used the shelly as timers to activate switched power to the stats relay commons when heating was needed in specific zones. the Shelly could bring the stats in and out of service on a timed and also secondary limiting temperature basis. This would give some remote control of the zones while retaining the thermostats' response profile for comfort level heating, assuming they weren't just dumb cliff edge thermostat switches. I haven't looked them up to see their spec.



  • Registered Users, Registered Users 2 Posts: 4,965 ✭✭✭Shane732


    Thanks for all your help here.

    Is it the one? https://amzn.eu/d/gyKAPnl



  • Advertisement
  • Registered Users, Registered Users 2, Paid Member Posts: 9,707 ✭✭✭10-10-20


    Yes, that's why I was suggesting to him to use room sensors over ZigBee and then putting the Shelly's as the control device as some of the PID controllers have an autotune mode which can help to discover the basic inputs to P, I and D and then allow for an easier setup after that.

    https://github.com/ScratMan/HASmartThermostat/tree/master