Home heating automation

1152153155157158175

Comments

  • Registered Users, Registered Users 2, Paid Member Posts: 8,214 ✭✭✭deezell


    No, it works away as normal. Tado HW is timer only, the cylinder stat will interrupt a timer call when set temperature is reached.



  • Registered Users, Registered Users 2 Posts: 1,146 ✭✭✭Redriddick


    Brilliant, just an FYI, Tado support emailed to say it's not compatible with my system!!



  • Registered Users, Registered Users 2, Paid Member Posts: 8,214 ✭✭✭deezell


    If you have a two independent zone system, with seperate zone valves to switch the flow for HW and CH, then its a direct replacement. If there's an existing wired thermostat (optional connections shown on the wiring box diagram you posted), this is simply turned up, or removed and linked, either in the wall or across the wiring box CH Thermostat terminals.

    Even if your system was a gravity system the Tado can be configured to give "1½ zone", with HW only or CH with HW.

    The only incompatibility with EPH is if your HW Thermostat is an EPH wireless one, but the R27 is just a simple two zone wired controller. I assumed your cylinder stat is wired, if it were wireless it would have to have it's own receiver independent of the R27, but I'm not familiar with an EPH version of this, just the EPH Ember wireless controller which directly recives EPH wireless cylinder stat signals. This controller is not completely compatible with Tado, or a all other controller receivers, and would require either the installation of a wired cylinder stat, or leave the Ember in situ to provide HW stat live supply while moving CH over to the Tado. Thems the scenarios in Ember replacements where an Ember wirelesscylinder stat was fitted



  • Registered Users, Registered Users 2 Posts: 1,146 ✭✭✭Redriddick


    Have no idea why they said that tbh. Hopefully get it installed later and see how it goes, as long as there is hot water for showers etc then it's all good. Only use the CH sporadically and usually only for an hour or two here and there as we have a stove too



  • Registered Users, Registered Users 2, Paid Member Posts: 8,214 ✭✭✭deezell


    If you mentioned stove heat source in the configuration questionnaire it might have thrown them. Work away and enjoy, safety first with mains wires.

    20240805_141758.jpg


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 1,146 ✭✭✭Redriddick


    Didn't mention the stove at all!!!

    Ah ill be sound, I put the Eph system a few years back myself. Plumbed the house too when I built it 20 odd years ago



  • Registered Users, Registered Users 2 Posts: 1,146 ✭✭✭Redriddick


    @deezell installed and came on to hear water this morning. Next to try and get google home to turn it on by voice for am hour

    20240806_084218.jpg


  • Registered Users, Registered Users 2 Posts: 945 ✭✭✭WildCardDoW


    Either the camera, or it, is wonky haha! Congrats on the setup.



  • Registered Users, Registered Users 2 Posts: 1,146 ✭✭✭Redriddick




  • Registered Users, Registered Users 2 Posts: 958 ✭✭✭ninja 12


    Hi Deezell ,

    Finally got around to installing the V3 Starter Kit (well , my friend did all the wiring for me 😀 ) , and it's all working perfectly .

    Thanks again for your help



  • Advertisement
  • Registered Users, Registered Users 2, Paid Member Posts: 8,214 ✭✭✭deezell


    You're welcome. Once your wiring is tidy and traceable it's not too difficult.

    20240828_092116.jpg


  • Registered Users, Registered Users 2 Posts: 958 ✭✭✭ninja 12


    V3+ users can now request Offline Schedule — tado° Community

    I see that owners of the V3+ kits can request offline schedules for their devices .

    There's a link to a google docs form on the Tado page linked above



  • Registered Users, Registered Users 2, Paid Member Posts: 8,214 ✭✭✭deezell


    Nice one.



  • Registered Users, Registered Users 2 Posts: 958 ✭✭✭ninja 12


    I've applied just now ,

    It says it can take three weeks to be applied to my account .

    Well worth enabling .



  • Registered Users, Registered Users 2, Paid Member Posts: 8,214 ✭✭✭deezell


    Iirc, in the event of an Internet outage, schedules continue on the last temperarure setting per device, but you continue to have manual control at the device. The V3 bridge is also visible within your LAN, so can be addressed locally by home automation apps, such as homekit, allowing some access to local automation. If Internet is down because of a power cut, the offline access is moot. I'm a V2 owner, 7 years exactly this week. with possibly one later V3 TRV, so at most I can maintain a TRV schedule, assuming it continues to call the boiler via the V2 wall stat relay.

    I've had only one prolonged Internet outage in that time, well over a week at Xmas when the I assume the eircom techs workers slipped into the pub beside the cabinet, without properly putting everything back, my linechalf plugged in. It was gone 5.00 on Xmas eve when I noticed, admitted days before anyone came back. My solution was a simple WiFi extender plug that had an ethernet port, paired to my phone hotspot.



  • Registered Users, Registered Users 2 Posts: 393 ✭✭Gerard93


    Hi

    Would appreciate if you could check if I have this wired correctly I got a Tado Starter Kit today to replace Hub Controller

    There was an old APT Timer originally then replaced by Hub Controller and now Tado.

    Tado is powering up but I am getting no power at the boiler when I the Tado Test Mode.

    The Boiler is an outside boiler.

    Three wires were there after the Hub Controller Live, Neutral, Earth

    Wirted Tado as follows:

    Live

    Neutral

    Live Bridged to CH Com

    CH Com Bridged to HW Com

    Earth to P1

    The Heating Switch (tado) when I click this on and off I can hear the relay click

    Does this look like its wired correctly any feedback would be great

    Boiler is basic 20 years old gravity fed system no Zones

    PIC 1.JPG PIC 2.JPG PIC 3.JPG Tado Wiring.jpg


  • Registered Users, Registered Users 2, Paid Member Posts: 8,214 ✭✭✭deezell


    You're missing a wire, it may have dropped inside the plaster board. The wire to send switched live to the boiler goes to the CH NO, normally open, which connects to the live you jumped to CH Com when the CH comes on. This wire would have been connected to V on the Hub.

    Its possible the Hub was configured in two wire mode, like a mechanical thermostat, with only live in and a switched live out from the V terminal. This was designed to allow the hub replace two wire mechanical thermostats with only live in and switched live out.The hub had a rechargeable battery to operate its electronics, and in the absence of a neutral, it used the load on the v wire, a motorised valve or the boiler switched live in, to provide a trickle path to neutral to keep the battery charged. If this was the case, then there is no direct neutral from the main switch above, and the wire you've connected to the neutral is actually the SL to the boiler. If so,it doesn't help thar it's using blue neutral cable. Can you remember if there was only a live wire into the L terminal, and the other wire was connected to V, with no wire to N?

    Hub wiring with permanent neutral below.

    Screenshot_20240914-191552_Drive.jpg

    Hub wired as two wire, with virtual Neutral.

    Screenshot_20240914-194226_Drive.jpg


  • Registered Users, Registered Users 2 Posts: 393 ✭✭Gerard93


    Hi Deezell,

    Thanks for your reply, there were only 3 x wires coming out from the switch and were wired into the Hub I don't have a 4th wire and its mounted on a block wall so no fear another wire has dropped down behind any plasterboard, I should have taken a picture before I removed the wiring from the hub, I see the unit here (hub) and the its marked N V1 L but I can't remember what colour wiring was whe

    Basically the wiring is powering a twin socket inside the boiler casing and two plugs come of that (I assume one for the pump the other for the boiler) when there is power to the socket the boiler fires.

    Is my wiring wrong for Tado so ?



  • Registered Users, Registered Users 2 Posts: 393 ✭✭Gerard93


    Hi Deezel

    Further to previous post I found a pic that I had taken of the Hub Wiring a while back when I opened the Hub today I noted that the "Earth Coloured" wire had black tape around it I see from the picture it was wired to V1 in the Hub I have this as P1 in Tado so can you advise where I should wire this to in Tado ?



  • Registered Users, Registered Users 2 Posts: 393 ✭✭Gerard93


    HUB Wire.PNG

    I meant to post this the Hub Wiring



  • Advertisement
  • Registered Users, Registered Users 2, Paid Member Posts: 8,214 ✭✭✭deezell


    Whatever wire was wired to V carried the live to the boiler. As you previously had an Apt timer prior to the hub, this would have had a permanent Live and Neutral supply, a switched live (SL) to the boiler and an possibly an earth wire. When the hub was installed, there would be no reason to wire the hub in two wire mode, but perhaps the installers pushing these things in everywhere were only trained to do this, and I note the battery warning sticker on the main power supply, which implies it was working from parasitic charged battery, which implies that the hub was in 2 wire mode. The Tado can supply the switched live to the boiler, and it needs a live and neutral to power it. First step would be to open that labelled switch and see what is being supplied to the hub/tado. Is the blue neutral wire actually the SL to the boiler? Perhaps they used the green/yellow. I've seen this in this thread before.

    Unfortunately there's a cabinet built in top of the switch, so it's not going to be easy to inspect inside. Its a pity you didn't note the wire connections to the hub. Where was the green/yellow connected? There is no earthing point in the hub, as it has no metal casing. I'm putting my money on the following. Live and Neutral were connected to the hub L and N, and the green/yellow was used to send SL to the boiler. If otoh the N wire is actually the SL, then if you unplug both the boiler and pump from inside the boiler casing, and the Tado stops working, this will tell if the Tado is finding a neutral line via the pump/boiler windings and not by a direct connection to the mains neutral point in the obscured switch. These are the two possibilities, and you would properly need to use a meter and phase testers to see what goes where. If you find this too challenging, you will need an electrician to discover exactly which wire was used to direct the SL to the boiler, but using blue or green/yellow is reckless and an accident waiting to happen.



  • Registered Users, Registered Users 2, Paid Member Posts: 8,214 ✭✭✭deezell


    Just seen your new photo. Where has that black wire gone? Thats your SL to the boiler.



  • Registered Users, Registered Users 2 Posts: 393 ✭✭Gerard93


    Hi Deezell

    The black wire is the Earth Wire (had black tape over it) I have this at P1 in Tado which I need to change



  • Registered Users, Registered Users 2, Paid Member Posts: 8,214 ✭✭✭deezell


    Is this it tucked behind the brown? That goes to CH NO.

    20240914_215744.jpg


  • Registered Users, Registered Users 2, Paid Member Posts: 8,214 ✭✭✭deezell


    Bloody 'ell. Who wired the APT originally? Using green/yellow to carry live is criminal. Sticking a bit of black tape on it is ironic, suitable colour for death



  • Registered Users, Registered Users 2 Posts: 393 ✭✭Gerard93


    Hey Deezell

    Thanks for your help and responses I am going to check the wiring in the sockets (at the far end in the boiler enclosure) tomorrow and also see if I can get the switch cover off.

    Post edited by Gerard93 on


  • Registered Users, Registered Users 2, Paid Member Posts: 8,214 ✭✭✭deezell


    It'll work if you move that taped wire to CH NO. That's possibly the supply to those sockets, but ideally the boiler should be powered from a normal permanent powered socket, and the SL from Apt/Hub/Tado should go to a relay terminal in the boiler to fire it. This way, the device is not supplying the large current required to kickoff and maintain the boiler, just a lower current to switch the mains in the boiler. Is this an older boiler? Some old simpler boiler house models were often just direct powered on and off. The relays in the digital type devices might not be able to cope with the surge, the higher amperage might fuse the contacts. Apt timers were designed for this with heavy duty contacts. If you have the boiler model name and number, I can check and see if it has permanent live and switched live control it would have to be ancient not to. That said, sometimes modern boilers are wired incorrectly with just a switched live turning the whole thing on and off like a light bulb, with no standby power when it's not firing.



  • Registered Users, Registered Users 2 Posts: 393 ✭✭Gerard93


    Hi Deezell

    I attach pictures of the Boiler setup its the original in the house 23 years old

    Thats interesting because as I previously said there was an APT timer first, when we bought the house the builders spec was the On/Off switch we got the APT timer put in over the years a 2nd one replaced the original.

    The Hub controller I initially got went after about a year just blew and they replaced and the replacement tripped last week it was still powering up but not controlling the boiler it bwould not switch it on.

    If you slide the temp guage up / down you would normally hear a clicking this had stopped and Hub Controller would not reply to any emails etc.

    Will the Tado be able to handle this or should I get the boiler wired as you suggested ?

    Boiler_1.JPG Boiler_2.JPG Boiler_3.JPG Boiler_4.JPG


  • Registered Users, Registered Users 2, Paid Member Posts: 8,214 ✭✭✭deezell


    That is the most basic boiler setup possible, straight mains into the Riello burner. Its a low power consumer, only 115w when running, so the current capacity of the Tado relay is not an issue. The problem usually lies with the surge from this and the circulation pump at startup. These motors can pull quite a kick initially, and the condenser on the motor may be well below spec, which can increase the surge, but able to 'kick' the motor still. Its this kick of current that can cause arcing over the small relay contacts fitted in the controllers. I'd be fairly certain that's what took out the relay in your Hub. There have been a couple of posts over the years from lads with stuck contacts on the Tado wall stat, or the extension kit, and direct boiler power is the culprit.

    My advice is to connect the V wire (black taped yellow/green) to the CH NO terminals and get the system running. You should then consider getting either a mains to mains relay of at least 15A to shift the inductive load from the Tado, or perhaps upgrade your boiler to a condenser model with modern always powered controller. That old grant is shoving 20% or more of your heat out the flue. It doesn't have a controller

    I had a similar setup 23 years ago when I moved in to my present abode, the boiler was a huge cast German thing with an RBD burner, already maybe 15 years old, only 68% efficienc. The timer was a grasslin segment clock like an APT, it soon after failed from burned contacts, and I replaced it with similar. It also burned the contacts of the boiler stat, the box you see inside the cabinet, I managed to clean and repair those. When I decided to modernise the heating in about 2017, I new I'd need to lose the old boiler before fitting electronic thermostats with delicate mains relays.



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 393 ✭✭Gerard93


    Hi Deezell

    Connected up the black taped wire as suggested and now have power and the boiler is firing up.

    Its due a service as I am having a bit of trouble since I started using it this season so I will talk to my service guy if I can get this winter out of it and look at a replacement then.

    But its likely that this system setup fried the previous Hub controller.

    Thanks again for your help and responses really appreciated it.