  • Registered Users, Registered Users 2 Posts: 870 ✭✭✭iknorr


    Got a strange one going on…..

    Recently installed a Solis S5-EH1P(3-6)K-L 5kw.

    System seems to be performing as expected however, when decently generating, e.g. above 3kw, there seems to be a click or a sudden tick noise that happens every now and then. Edit (noticed it does this when its on battery also, e.g. night time 3kw load.)

    It appears to happen more frequently when im generating above 5kw, every 5-10 minutes.

    Its coming from inside the invertor. Any ideas what this could be?

    Post edited by iknorr on


  • Registered Users, Registered Users 2 Posts: 224 ✭✭oaklands


    Possibly a relay turning a fan on/off????



  • Registered Users, Registered Users 2 Posts: 870 ✭✭✭iknorr


    The fan is very noticeable, so i dont think its that. If its a relay, its slapping the contacts very hard.

    It almost sounds like those lighters that has the electric spark. Actually, it sounds like an electrical ark.



  • Moderators, Sports Moderators Posts: 19,814 Mod ✭✭✭✭slave1


    contactors?



  • Registered Users, Registered Users 2 Posts: 8,872 ✭✭✭10-10-20




  • Advertisement
  • Registered Users, Registered Users 2 Posts: 466 ✭✭Liam2021


    Hi all,

    Just trying to find out can I let my dyness batteries go below 20% SOC? Is it possible to go to 10% only need the extra 10% once a week.



  • Registered Users, Registered Users 2 Posts: 870 ✭✭✭iknorr




  • Registered Users, Registered Users 2 Posts: 8,872 ✭✭✭10-10-20




  • Registered Users, Registered Users 2 Posts: 9,261 ✭✭✭con747


    AFAIK Dyness are warrantied to 90% dept of discharge but just double check the model of your batteries on their website to be certain.

    Don't expect anything from life, just be grateful to be alive.



  • Registered Users, Registered Users 2 Posts: 934 ✭✭✭tommythecat


    Bit of an odd one. I have a solis hybrid inverter with a weco 5kw battery. I have the battery set to charge slowly from 2am to 6am.

    I will also charge the car between these times.

    What's happening is that the battery is at 100% and at 5.55am it will start discharging at 5kw to the car for five minutes. This is annoying as it's a waste of the battery and it's also extremely noisy and wakes us up.

    Just wondering why it would start to discharge at this rate before the set time? I know the battery doesn't like to stay at 100% but it usually discharges a very small amount and then charges back up. Not this massive discharge.

    I am going to extend the charge time to 6.05am and see if that helps the situation.

    4kwp South East facing PV System. 5.3kwh Weco battery. South Dublin City.



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 286 ✭✭S'


    Is the time clock on car charger, solis inverter and ESB meter the same?



  • Registered Users, Registered Users 2 Posts: 934 ✭✭✭tommythecat


    That's it! The inverter has somehow managed to change by 10 minutes! Hopefully that sorts it. Thanks!

    4kwp South East facing PV System. 5.3kwh Weco battery. South Dublin City.



  • Registered Users, Registered Users 2 Posts: 8,872 ✭✭✭10-10-20


    The inverter doesn't appear to support NTP (internet source time) for it's timekeeping, so you'll need to check that time clock reasonably often. That in adding in buffers of a few mins so that the car stops charging a few mins before the change-over of the smart meter to the new tariff, etc.



  • Registered Users, Registered Users 2 Posts: 2,048 ✭✭✭jkforde


    has anyone's PV suddenly stopped generating without any inverter issues or alarms? was fine up to 1125 today and since then no juice... got a local PV installer coming to take a look (he mentioned fireman switch may have flipped) but any ideas from others that this may have happened to?. I restarted the inverter but didn't help.

    🌦️ 6.7kwp, 45°, SSW, mid-Galway 🌦️

    "Since I no longer expect anything from mankind except madness, meanness, and mendacity; egotism, cowardice, and self-delusion, I have stopped being a misanthrope." Irving Layton



  • Registered Users, Registered Users 2 Posts: 49 GarlicBed




  • Registered Users, Registered Users 2 Posts: 2,048 ✭✭✭jkforde


    thanks but issue is resolved, seems the grid was having a wobble as the area soon after had a power outage and it's working fine since ESB rectified the power outage. but weirdly the inverter had no warnings for voltage etc before it happened. anyways, all good again, phew!

    🌦️ 6.7kwp, 45°, SSW, mid-Galway 🌦️

    "Since I no longer expect anything from mankind except madness, meanness, and mendacity; egotism, cowardice, and self-delusion, I have stopped being a misanthrope." Irving Layton



  • Registered Users, Registered Users 2 Posts: 34 viewofthehill


    Just seen some unexplained behaviour with the inverter the last couple of days. This is the solar production graph from yesterday. It seems that production is slow until something kicks in around 10:30 and then again at 13:30.

    image.png

    This seems to tally up the power being generated from the two strings but here again you can see big jumps in production at 10:30 on string 1 and 13:30 on string 2.

    image.png

    There is no shading on the panels which would be causing the sudden jumps in production.

    Below is a graph from March where the production ramp up is much smoother without the jumps.

    image.png

    This rapid jump has been a feature over the last week or so but there is nothing to explain why this is the case. I have shutdown and restarted the whole system but am still seeing the same patterns following it.

    Can anyone give some pointers as to why this may be happening?



  • Moderators, Home & Garden Moderators Posts: 7,015 Mod ✭✭✭✭graememk


    Are you at home when this happens?

    It really feels like shading, because it generates a little and boom when it clears it's full power



  • Registered Users, Registered Users 2 Posts: 2,662 ✭✭✭bullit_dodger


    Hmm, from the charts I'd agree with you that it looks like a shading performance profile. But the chart he included from March (which would have the same general sun orientation as now Sept) doesn't seem to have it. So I'm inclinded to think that it's not from that point.

    Unless there's been some recent addition which causes shading, perhaps the neighbour has installed a new satelite dish (or something you get the idea)

    @viewofthehill what's the size and orientation of both your arrays?



  • Registered Users, Registered Users 2 Posts: 397 ✭✭NedNew2


    Possibly any nearby trees would not have leaves in March but they would in September?



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 34 viewofthehill


    The two arrays are 4.56Kw SSE and 3.8Kw WSW at right angles. The SSE array is on a single storey with a hedge about 10 metres from it. The WSW is on a two storey. The hedge is abou 6m high.



  • Registered Users, Registered Users 2 Posts: 8,872 ✭✭✭10-10-20


    That's my guess. Are there optimisers on all or any of the panels? How many strings?



  • Registered Users, Registered Users 2 Posts: 34 viewofthehill


    Just had a look back at this time last year. Apologies for the graphs but the app doesn't store data from more than 6 months ago. The chart below is an example from the almost the same day last year (21 September). As you can see on the graph there is the same ramp up as in the March graph. The only thing that has changed in the last year is that the hedge is now probably 2m lower than it was originally. Past the hedge the nearest object that would cast a shadow is a hedge about 60m from that.

    image.png

    For comparison purposes I have the same graph for 18 September this year

    image.png

    Looking at the two you can see it starts producing at a similar time but there seems to be a big jump at 9:30 and again at 12:30 (time on the graphs are out due to system time vs. Summer time). PV1 is the SSE array and PV2 is the WSW array



  • Registered Users, Registered Users 2 Posts: 34 viewofthehill


    Two strings with no optimisers on any panel. Each array is on a separate string.



  • Registered Users, Registered Users 2 Posts: 34 viewofthehill


    I had a look this morning and it seems that the voltage is causing the problem

    image.png

    The voltage on both strings appear to rise to 100 and then stay there for a time period before going to 300/350 for the strings.

    Voltage graph from last September. It seems the voltage rise was when the panels started producing.

    image.png


  • Registered Users, Registered Users 2 Posts: 3,492 ✭✭✭randombar


    my ground mounted is acting up at the moment, guessing moisture etc. getting into places. After about half nine in morning things are ok, I think cause things have dried out a bit. Anything like that maybe?



  • Registered Users, Registered Users 2 Posts: 8,872 ✭✭✭10-10-20


    Normally voltage climbs very early on when the panel starts up, it should get up to between the panel's stated Voc and it's Vmpp, then the current starts climbing after that and voltage stays relatively stable. If all of the panels are in full sun when this condition occurs (that being the voltage hovering around 100v DC) then I'd wonder if the panels are going into a bypass state, but normally this would be triggered by by a low-light condition. Are the panels clean of dirt and definitely not in shade when that condition occurs?



  • Registered Users, Registered Users 2 Posts: 34 viewofthehill


    Unable to see the panels on the two storey for dirt but they are facing into a field with nothing behind them for 200m so no shading. The lower panels are clean and have no shading early in the morning or throughout the day. The closest hedge was reduced in height by 3m earlier this year and there was no shading before that. There is some shading on the single storey array in the height of the summer late in the evening when the sun catches the corner of the two storey.



  • Registered Users, Registered Users 2 Posts: 8,872 ✭✭✭10-10-20


    Not a clue. I'd forward those images of the voltage and power for both strings onto the installer and see what they make of them. But keep us posted please.



  • Advertisement
  • Moderators, Home & Garden Moderators Posts: 7,015 Mod ✭✭✭✭graememk


    Little bit concerned about the huge voltage spikes too on last year (800v nearly)

    Do you see that happening this year?

    Really odd though, is it happening every day?



This discussion has been closed.