ESB did not upgrade to 100A fuse

13»

Comments

  • Registered Users, Registered Users 2 Posts: 66,675 ✭✭✭✭unkel


    The insult was that they charged you over €2,000 for it…



  • Registered Users, Registered Users 2 Posts: 7,329 ✭✭✭zg3409


    As others have said if you time things right and have at least one load sensing charger you should be ok.

    Dishwashers & washing machines mostly draw high power for first 10 minutes of operation do slightly stagger their start time. The charger for each car will take 7kW as long as lots of other things are not on. It will slow charging if lots of things on at same time, but after 10 minutes then dishwasher water will be hot, the washing machine water will be hot and there will be excess power.

    If your commute is say 110km a day you need around 20kWh if energy into the car or 3 full hours charging at top rate. If your commute is less than this 2 hours a night may be ok, but it may take multiple nights at cheapest rates to fully fill back up the car.

    Beware clothes dryers are high consumption most of the time but if using it nightly you should get a low power heat pump model. Ideally set limits way beyond the main fire limits, for most average houses you want a 50amp max continuous draw, and ensure you have lots of smoke alarms if running everything at night. I have 9 radio interlinked battery & heat detectors to wake everyone up if something starts to smoke in the middle of the night. I have already had the "professionally" installed EV charger isolator melt inside as presumably the screws were not tightened correctly.



  • Registered Users, Registered Users 2 Posts: 61 ✭✭Scoobydoobydoo101


    I just recently found out I have an 8kva connect. Is there a cost to upgrade to 12kva?

    I dont see anything on their price list



  • Registered Users, Registered Users 2 Posts: 621 ✭✭✭idc


    When I contacted ESBN they said in most cases there is no cost to change from 8 to 12kVA.



  • Registered Users, Registered Users 2 Posts: 12,328 ✭✭✭✭KCross


    You probably wont get charged from ESB side but you might have to do some internal works yourself to support it and thats your problem, not ESB.

    Anything from the meter box into your house is your property and you have to pay for any potential upgrades there.



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 4,488 ✭✭✭...Ghost...


    Just to update this. I left off last time with an 8kVa MIC, 80A Main ESB fuse and 80A isolator leading to an 80A switch in the CU. I had applied for the 12kVa upgrade.

    A few days ago, after seeing another thread on here about an electrician fitting an under-rated CU, I checked my own and found it is only rated to 63A according to the sticker on the bottom of it. The electrician appears to have installed a CU which isn't fit for purpose.

    I contacted the solar company over a weeks ago and followed up yesterday. The install manager said he missed my first email and would call later this week. I'll see what he suggests.

    I also rang ESB to check on the status of the 12kVa upgrade with the intention of asking what extra it would cost if they put in an enhanced supply (16kVa). I was told they have already upgraded me to the 12kVa and appears it was done in July without any interruption…so presumably no physical change was made.

    Stay Free



  • Moderators, Home & Garden Moderators Posts: 7,064 Mod ✭✭✭✭graememk


    I think the change from 8 to 12 is all on the consumer side. More of a paper exercise and possibly needed a cert sent in to confirm that it's up to 12kVA standard now.

    My house was originally 8kVA. With a screw in fuse board, 63A consumer fuse and 10mm² tails. So it must have had a 80a ESBN fuse.

    I went straight to 16, though, but with a upgrade to 25mm tails and a new consumer unit.