Replace APT Timer with Heatmiser Thermostat

  • 29-10-2023 09:07PM
    #1
    Registered Users, Registered Users 2 Posts: 107 ✭✭


    I'm looking to replace an APT Timer for my boiler with a Heatmiser Wifi thermostat. Below is what is currently installed (a simple on/off thermostat for the boiler.)

    PXL_20231029_163121226.jpg

    And I want to replace it with this:

    PXL_20231029_163145854.jpg

    I've opened the cover on the thermostat to have a look at the wiring and this is what it looks like:

    PXL_20231029_162329036.MP.jpg

    And here's it's wiring diagram:

    PXL_20231029_163129496.jpg

    Firstly can anyone tell me if it is voltfree or not? I'm guessing not. Also which of the two wiring diagrams for the new thermostat should I follow? I have an idea but I want to be sure I don't break anything.

    PXL_20231029_163209803.jpg

    Any help is much appreciated!



Comments

  • Registered Users, Registered Users 2 Posts: 4,957 ✭✭✭kirk.


    It's the diagram on the left.

    The wifi stat has a voltfree contact so needs a link for your setup

    The boiler needs a means of isolation nearby , an isolating switch or even a socket



  • Registered Users, Registered Users 2 Posts: 107 ✭✭Daniel112


    Thanks for the help. So terminal 1 cable from the APT Timer will go into A2 on the Heatmiser, Terminal 2 on the APT will go into L on the Heatmiser (with a cable running from L to A1 also to bridge them.) And finally Terminal 3 on the APT timer will go into N on the Heatmiser?

    Is that all correct?

    There is a fused switch underneath the APT timer (as shown on Photo 1 in my last post) That provides power to the APT timer & Boiler when switched on.



  • Registered Users, Registered Users 2 Posts: 4,957 ✭✭✭kirk.


    Ya that's right



  • Registered Users, Registered Users 2 Posts: 46 pukeko


    Hi OP H

    How did you get on with this job? I have a similar setup so thinking of doing the same. Although my current APT timer has no isolation nearby - i presume your fuse at the switch there is 3A? Assume this is essential i.e. the Neo load rating is 3A

    thanks.